Still cycling at 8 mins on 20 seconds off with room stats at 25 degrees. Water outlet (flow temp I assume) is up a couple of degrees but the outside temp has also dropped tonight.Â
Posted by: @craig1980Still cycling at 8 mins on 20 seconds off with room stats at 25 degrees. Water outlet (flow temp I assume) is up a couple of degrees but the outside temp has also dropped tonight.Â
Hi Craig,
To try to find the root cause of the problem, it is necessary to observe how your system is actually operating, and compare this against how we think the system should be operating.
Below are a few checks and observations to make.
Carefully time how long the system is 'on' and how long the system if 'off', ideally to the nearest second. We can then see if there is any variations.
Record the changes in the readings displayed on the controller for LWT, outdoor temperature, and any other temperature and flow readings that are available. Pay particular attention to changes from just before the heat pump stops, during the 20 second shutdown period, and after the heat pump restarts.
Â
I have attached a copy of a manual which details all the various parameter settings, which are listed from page 24 onwards.
I would suggest that you go through your system and make a note of all the values.
I have my doubts over this section.Â
Â
Could this be set incorrectly?Â
Its set the same for this and external thermostat application #1 (floor) and #2 (FCU).
I have no UFH so is the "floor" part irrelevant or have the set the zone 1 and 2 up as "floor" and "FCU" respectively?Â
I've also just changed the 2041 Heating water law for auto mode to WL2-FCU from WL1-Floor. Is that the right thing to do as I don't have UFH?Â
My idea was to first gather the information, then give it a close dose of inspection, and then try to decide what needs to be changed.
Based upon normal operation, I would expect your system to perform in the following manner when in WC mode.
The outdoor air temperature sensor measures the ambient air temperature and conveys this reading to the controller. The controller calculates the required LWT. If either of the room thermostats are calling for heat, and the actual LWT is below the calculated value, by a specified margin, then the heat pump will start operation.
When the actual LWT exceeds the calculated value, by a specified margin, the heat pump will stop operation. When the actual LWT falls below the calculated value, plus the specified margin, the heat pump should restart. This process will probably continue during milder ambient temperatures.
What values did you record during the monitoring process?
Â
Posted by: @craig1980@derek-m I'm just doing the monitoring now.Â
Where would I find the LWT? I'm assuming that's leaving water temp? I have my thermometer nowÂ
The LWT is what is labelled Current Water Outlet on the 'normal' display on the controller.
I assume that your heat pump is still switching back on after only 20 seconds?
The objective of the testing, is to see what is happening to the various temperatures around your heat, as it stops and then restarts. Since the heat pump should not normally restart after only 20 seconds shutdown, something must be causing it to do so.
Â
Images of all figures and settings on the field settings manual. I hope it makes sense?
It is on for exactly 7 mins 58 second and off for exactly 20 seconds.Â
Water outlet 24.8 turns off 24.8 turns on at 21.5 indoor temp on wired remote but 18.5 on room stats confirmed by independent stats. Climbs to 27.2 at the middle of the cycle and drops back to 24.8 by the end.Â
Just checked flow and return temps on rad closest to UVC and it's 25.2 -22.6
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 29 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Heat Pump Damage on install - useable or dealbreaker?
They have already been dishonest by not telling you abo...
By GrahamF , 2 hours ago
-
Testing new controls/monitoring for Midea Clone ASHP
Hi all, I thought it might be of interest to others i...
By benson , 2 hours ago
-
-
RE: Electricity price predictions
@diverted-energy sounds like good tariff for you. Octop...
By JulianC , 3 hours ago
-
RE: Who’s Caved and Switched the Heating On Already?
In the last week, the external temperature in south Man...
By GrahamF , 5 hours ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 6 hours ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 6 hours ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
I hear you on the locality issue @transparent, and I ag...
By Scalextrix , 8 hours ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 9 hours ago
-
RE: Midea ASHP – how to set weather compensation
@pash44pump Referring to the problem of rooms with diff...
By Tasos , 10 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
Er true, it should have read l/hr!
By JamesPa , 11 hours ago
-
@damon thanks. I will do as you suggest. Hopefully I wi...
By bontwoody , 1 day ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 2 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@dgclimatecontrol I attach the responses from 2 potenti...
By pash44pump , 2 days ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 3 days ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
I realise im overdue an update on my situation. first...
By Cleardene-ashp , 3 days ago
-
RE: Replacing Worcester oil boiler with an ASHP
@toodles thanks. I was told by the engineer that this h...
By JulianC , 3 days ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
A week later, I'm finally picking up this comment... ...
By Transparent , 3 days ago
-
RE: COP is not the only measure of efficiency
We keep all our TRVs fully open using the whole house a...
By Old_Scientist , 4 days ago