RDSAP10 effect on existing heat pump EPC rating?

26 Posts
5 Users
1 Reactions
1,450 Views
(@aaron)
Active Member Member
Joined: 8 months ago
Posts: 9
 

There is  a real disconnect between how performance is captured for RHI and what ends up being used for EPCs via RDSAP.

The SPF of 4.1 you got  probably reflects the real-world performance of your GSHP. But RDSAP, being a cut-down version of the full SAP methodology, often uses default or oversimplified figures—hence that laughable COP of 1.7. That number doesn’t reflect the capabilities of a modern MCS-certified system like MCS HP0016/08, especially if it’s been properly designed and commissioned.

To improve the EPC rating and get a COP/SCOP that reflects reality (especially at 40°C flow temp), you ideally want to use the Product Characteristics Database (PCDB). If your heat pump is listed in there, SAP can pull in the correct performance figures. If not, RDSAP defaults will drag the rating down every time.

And no—SPF and COP aren’t interchangeable. SPF takes into account the whole system and how it behaves across seasons, whereas COP/SCOP is a performance figure under fixed conditions. Related, yes. Swappable? No.

Honestly, if you’re aiming to push the rating from a D to a C and you’ve already got detailed performance data from the RHI assessment, it’s far better to do a full SAP. It’s more work and takes longer, but it allows you to input all the real data properly—emitters, controls, flow temps, measured demand, and system design. That’s where you stand a decent chance of getting the rating



   
ReplyQuote
 AF1
(@af1)
Eminent Member Member
Joined: 3 years ago
Posts: 13
Topic starter  

@aaron  There's the rub, the database does not list my HP, it appears to begin in 2016. So does this mean we cannot get a COP figure at all?  https://www.ncm-pcdb.org.uk/sap/pcdbsearch.jsp?heatPumpType=1&emitterType=3&type=362&serviceProvision=1&brand=&model=&modelQualifier=&pid=31

No Bosch or IVT GSHPs listed.

 


This post was modified 4 months ago by AF1

   
ReplyQuote
(@mike-patrick)
Honorable Member Member
Joined: 5 years ago
Posts: 177
 

With the change to RdSAP in June I have just followed up with an EPC assessor to ask if it would make a difference to get our house re-rated. We have an overall rating of D, despite having done everything 8 years ago when the ASHP was installed. He was familiar with the problem of ASHPs resulting in worse ratings than a gas boiler in an identical property. Unfortunately his message was that the new RdSAP will make no difference and might even give a worse result. It's down to the model and he said his firm now gives warnings in advance to customers that their EPC rating will likely not have improved despite spending £000's on an ASHP installation. He said, we only collect the data, the rating is down to the underlying model.

We all know this to be true but strange how no one from government or those groups pushing heat pumps ever seem to mention this inconvenient detail.

For now I will sit tight and hope for future changes to RdSAP that tip the balance in favour of heat pumps.

 

Mike

 


Grant Aerona HPID10 10kWh ASHP


   
ReplyQuote



(@tim441)
Prominent Member Contributor
Joined: 3 years ago
Posts: 345
 

@mike-patrick interesting!

Funnily enough we've just arranged a new EPC even though current one was done 5 years ago. Both for my property and one belonging to my son.

Current one was pre our heat pump or added solar & batteries. Our assessor indicated the heat pump WILL improve matters. I'll report back once epc ratings received in coming days. Assessor was chosen for willingness to engage and do thorough assessment. Over 1.5 hours each property.

Also noting

  • 2020 epc was done go get RHI with little effort to prove insulation etc. Both properties a D 67 & 68 points
  • 2025 epc I've provided building regs Certs for extensions etc, mcs Certs for heat pump & solar panels  pics of insulation, receipts etc
  • Assessor indicated batteries would not add more than solar already added. However he took details and promised to check that point.
  • I'm moderately hopeful we'll get both to a C. Obviously useful target for potential lettings as well as sales.
  • I used ChatGpt to get inputs on what changes have happened 2020-2025. I uploaded existing epc and details of all changes since. ChatGpt suggested both will be likely to achieve C

My understanding is that the next EPC update will be a change to HEM. Plan is for:

  • The current expectation is that the new EPC methodology (HEM) will come into use in the second half of 2026.
  • This should take a lot more detail & metrics into account. But I suspect there will be winners and losers vs current system
  • Worth checking up via ChatGPT interrogation:
  • https://chatgpt.com/s/t_68da9d262abc8191b63ecd587ae15658

This post was modified 6 days ago 5 times by Tim441

Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV


   
ReplyQuote
(@mike-patrick)
Honorable Member Member
Joined: 5 years ago
Posts: 177
 

Our circumstances were slightly different in that the current EPC was issued after a ground up restoration of a semi-derelict building. We'd had a full MCS survey to receive the RHI grant at the time. So after all that and a £300k spend (inc underfloor heating) I was more than a little disappointed to get a D 62 rating with advice that I could reach C 69 by additionally installing solar hot water and solar PV.  Even if that were so it wouldn't have changed the fact that the certificate assessed the main heating and hot water as Poor. The house is 100% electric as there is no gas supply in our area.

I've done no further work on the house since, so my conversation with the assessor was about whether or not the latest RdSAP would result in an improved rating - which apparently it would not. Once the HEM is introduced I'll try again. I won't do solar panels - although I have consent for them. They'd not look great in our Cotswold village and I think the payback period on the capex is too long.

Mike


Grant Aerona HPID10 10kWh ASHP


   
ReplyQuote
 AF1
(@af1)
Eminent Member Member
Joined: 3 years ago
Posts: 13
Topic starter  

@mike-patrick Hi, I found that the previous EPC assessor had used a very low "Default efficiency value" for our "poor" GSHP. I got in touch with Bosch who found the correct figure which the RDSAP10 assessor used and it jumped from D to C.



   
ReplyQuote
(@tim441)
Prominent Member Contributor
Joined: 3 years ago
Posts: 345
 

@mike-patrick fo you use ChatGPT? Could be worth a conversation!! Upload your current epc as well as details of previous works and heat pump etc. Plus heat pump controls as they impact it too.

Maybe start here

https://chatgpt.com/s/t_68db8489b4108191a4237450ec358b98

I wonder if the original epc in fact did not take into account some of your works correctly?

My understanding from both my assessor and ChatGPT is that a Heat pump will make  difference to New EPCs. But I'll update once mine arrives!

ChatGPT says Rule of thumb:

A correctly documented ASHP installation (with weather compensation and thermostatic controls) is typically worth at least a band jump (5–10 points) if the house was previously gas-heated, and more if replacing direct electric.


This post was modified 6 days ago by Tim441

Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV


   
ReplyQuote
(@mike-patrick)
Honorable Member Member
Joined: 5 years ago
Posts: 177
 

This is interesting.

Attached is the page from my EPC which shows the Poor rating of the Main Heating and Hot Water. You've prompted me to look at the same page from the EPC from when we bought the house and before the retoration. Overall it had an F rating but the important point was that it had storage heaters and used an immersion heater for hot water. On the old certificate these were both rated Average! Storage heaters better than an ASHP - that can't be correct?

Screenshot 2025 09 30 at 09 37 45 Energy performance certificate (EPC) – Find an energy certificate – GOV.UK

So maybe some wrong boxes were ticked when the EPC survey was done. It was the same assessor in both cases although having checked I find they are no longer an assessor. Is it possible to access the detailed report which shows what data went into an EPC to check this?

 

Mike


Grant Aerona HPID10 10kWh ASHP


   
ReplyQuote
(@tim441)
Prominent Member Contributor
Joined: 3 years ago
Posts: 345
 

@mike-patrick  I think at the time of your EPC the heat pump would have come out badly - but things have changed since then. So maybe less a case of box ticking incorrectly... more the changes in calcs.

The controls will help on new EPC as well especially if you use weather compensation and have Thermostats/TRVS (even if unused).

I'm not sure if your underfloor insulation should show as a rating help? But may need evidence? e.g. receipts, pics etc

It needs an assessor willing to spend a bit of time on the survey as well as completion of the modelling. 

I have a couple of rentals. 

One was rated an E in 2021 but I had done a massive refurbishment. So after some toing and froing with assessor 2 or 3 years later and paying a further fee .. we got it to a C! Mostly by providing evidence.

In another example we had a new build in 2013 that was rated A. We needed a new EPC this year to relet. I expected a drop to B due to changes in standards. But came back as A again.

So I can only encourage you to persevere... ask around for a decent assessor via estate agents? Facebook? .... I think my hard working guy cost £10 more than a cheap one! Well worth it.

I am unaware you can access the data input by assessor.


This post was modified 5 days ago by Tim441

Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV


   
ReplyQuote



(@tim441)
Prominent Member Contributor
Joined: 3 years ago
Posts: 345
 

From my understanding..

The short version

 

  • Before June 2022 (SAP 2012 rules) → Heat pumps often hurt EPC scores compared to mains gas.

  • Since June 2022 (SAP 10.2 rules) → Heat pumps generally help EPC scores, especially if fitted with weather compensation and thermostatic controls.

So, when exactly?

  • Any EPC lodged before 15 June 2022 used SAP 2012 → heat pumps rarely improved the score vs. gas.

  • Any EPC lodged on or after 15 June 2022 uses SAP 10.2 → heat pumps usually improve the score by +5 to +12 points vs. a gas boiler.


Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV


   
ReplyQuote
(@tim441)
Prominent Member Contributor
Joined: 3 years ago
Posts: 345
 

How many times and dates have epc sap rules been changed?

Key Changes to EPC Methodology

1. Introduction of SAP (Standard Assessment Procedure)

  • 1995: The first version of SAP was published, providing a standardized method for assessing the energy performance of dwellings.

2. Adoption in Building Regulations

  • 1994: SAP was cited in the Building Regulations as the means of assessing the energy performance of dwellings. elmhurstenergy.co.uk

3. Introduction of RdSAP (Reduced Data SAP)

  • 2005: RdSAP was introduced as a simplified method for assessing existing dwellings, reducing the amount of data required for the assessment. GOV.UK

4. Major Overhaul with RdSAP 10

  • 15 June 2025: A significant update to RdSAP, known as RdSAP 10, was implemented. This version introduced more detailed data collection requirements, including individual window measurements, wall types, and ventilation details, aiming to provide more accurate EPC ratings. NicheCom+1

5. Transition to Home Energy Model (HEM)

  • Second half of 2026: The UK government plans to transition from SAP/RdSAP to the Home Energy Model (HEM) for EPC assessments, reflecting advancements in energy efficiency standards and technologies. GOV.UK


📅 Summary of Key Dates

Date Change Description
1995 Introduction of SAP
1994 SAP cited in Building Regulations
2005 Introduction of RdSAP
15 June 2025 Implementation of RdSAP 10
Second half of 2026 Transition to Home Energy Model (HEM)

 

In addition to the major updates introduced with RdSAP 10 on 15 June 2025, several minor adjustments have been made to enhance the accuracy and relevance of Energy Performance Certificates (EPCs) in the UK. These refinements aim to better reflect the energy performance of homes, incorporating modern technologies and more precise data collection methods.


🔧 Minor Methodology Changes in RdSAP 10

  1. Enhanced Heating System Assessment
    The updated methodology incorporates the latest data to provide a more accurate appraisal of various heating systems. Notably, electric heating systems, including heat pumps, may achieve improved ratings due to changes in how energy use is calculated. Strutt & Parker - Rural Hub

  2. Improved Recognition of Renewable Technologies
    Properties equipped with photovoltaic panels or solar thermal systems may see enhanced ratings, thanks to more precise methods for evaluating their contributions to energy efficiency. Strutt & Parker - Rural Hub

  3. Detailed Building Element Data
    Assessors are now required to capture more precise details about windows, wall exposure, wall insulation, and ventilation. This shift from relying on preset options to collecting specific data enables a more nuanced understanding of a building's performance. Strutt & Parker - Rural Hub

  4. Introduction of a New Age Band for Modern Homes
    A new age band has been introduced to reflect that newer homes, built from 2023 onwards in England, Wales, and Northern Ireland (and from 2024 in Scotland), are constructed to higher energy-efficiency standards. Strutt & Parker - Rural Hub

  5. Refined Insulation Data Collection
    The methodology now includes more detailed descriptions of insulation types and their effectiveness, allowing for a more accurate assessment of a property's thermal performance. EPC Training

  6. Updated Thermal Properties of Insulation Materials
    Adjustments have been made to the thermal properties of insulation materials to reflect advancements in insulation technology and manufacturing processes, improving the accuracy of energy efficiency calculations. EPC Training

  7. Inclusion of Air Pressure Test Results
    The updated methodology allows for the inclusion of air pressure test results, providing a more accurate assessment of a property's airtightness and its impact on energy performance. NicheCom

 

 

This post was modified 5 days ago by Tim441

Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV


   
ReplyQuote
(@mike-patrick)
Honorable Member Member
Joined: 5 years ago
Posts: 177
 

Here's the EPC printout to illustrate the point I made in a post last week. Sorry to keep banging on about this - but it is bonkers.

On the left the property's ratings before a total renovation when it had storage heaters. (Overall G)

On the right the EPC rating of the features in my house after the heat pump was installed. (Overall D)

The overall EPC rating had improved but not, apparently, because of the heat pump.

I still can't get to the bottom of whether this is just a "feature" of the EPC algorithm or the assessor ticking a wrong box when entering the data about the property.

Screenshot 2025 10 05 at 18 23 11 Energy performance certificate (EPC) – Find an energy certificate – GOV.UK
Screenshot 2025 10 05 at 18 22 21 Energy performance certificate (EPC) – Find an energy certificate – GOV.UK

Mike


This post was modified 3 hours ago by Mike Patrick

Grant Aerona HPID10 10kWh ASHP


   
ReplyQuote
Page 2 / 3



Share:

Join Us!

Latest Posts

Click to access the login or register cheese
x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
ShieldPRO