Digest of UK Energy Statistics
Posted by: @ianmk13I am in Milton Keynes - a new city, so you might think the local infrastructure would have plenty of capacity. However, many of the sub-stations already have limited availability for prospective solar generation, batteries and EV chargers.
Unfortunately MK was designed when the national grid was still viewed as a system to deliver electricity.
Little thought would've been given to 'reverse power' from local generation.
The local situation is a 'mixed bag'.
The following map shows the Bulk Supply Point (BSP) and Primary Substation available capacity to receive local generation.
Green pins have available headroom for more local generation, red is 'at or over capacity' and blue is 'not enough data to define'.
If I zoom in to a lower level and pick out a typical 500kW local substation (11kV input) in the Titchmarsh area, then I can see
- 400kW Daytime peak demand
- 512kW Night peak demand (marginally outside spec)
- 191kW Total connected generation
- and there are 5 properties with EV charge points
That's fairly typical for SE England.
Consumption per household is particularly high, and the region is dependent on substantial energy supplies from elsewhere in Britain and the overseas Interconnectors.
That can be seen from the orange arrows on the grid-flow maps from National Grid ESO.
I've picked up this area, not just because it's of interest to Ian, but that it shows deficiencies in the DUKES statistical approach.
The more GB uses electricity generated from distributed renewable sources, the less useful it is to create policy based on national traits.
We need to think much more strategically about how we use the generation sources that are local to us.
Save energy... recycle electrons!
The Titchmarsh area was one of the first areas to be built in the new town, including housing for people who built the new town. Fishermead in that area is particularly poor quality housing so I am not surprised that area is an issue. I wonder if the in fill of flats around the center and the expansion of retail, snowdome and business sites also exacerbated the challenge in that area. It is very different to the wider new town estates.
I wonder if some of the other red areas are historical and pre date the new town. They look like Wolverton and Newport Pagnell rather than Milton Keynes.
I use to live in next to the old Milton Keynes Village.
Posted by: @jeffThe Titchmarsh area was one of the first areas to be built in the new town, including housing for people who built the new town.
Amazing. I've lived a couple of miles north of Fishermead for over 40 years and never heard of any 'Titchmarsh' area. I thought he was a gardener on the telly.
@Transparent. I'm on the local substation by Broughton and if I remember correctly (which I may not), this has available capacity for local generation but its my local neighborhood substation that's creaking at the seams.
@ianmk13 - There are two Primary Substations (33kV/11kV) at Broughton:
Kingston 940070; 23MW transformer; 9MW demand headroom, 10MW reverse-power (generation) headroom
Fox Milne 940043; 23MW; 1.5MW demand headroom, 6MW reverse-power headroom
In both cases, the National Grid data suggests that these transformers could be opened up to far more generation assets than the reverse-power headroom figure suggests. There will be technical reasons for this which are not explained by the raw figures.
Just because the local substations (11kV/440v) have generation constraints on them doesn't prevent you from making better use of the available reverse-power headroom.
Instead of thinking at the level of each individual house, consider the issue in a wider context.
A local Community Energy Group should be opening discussions with NGED about adding community-operated solar/wind/anaerobic-digester types of generation. You could connect at the 11kV level within the area already served by those two Primaries.
Alternatively, NGED may be even more attracted by the possibility of community-run battery storage, especially in areas of higher-density social housing.
The available Demand Headroom at these two Primaries is defined by the Peak Demand in the early evening.
If a community operated storage network could deploy batteries which remove 10% of the housing from any demand at peak time, then that would alleviate thermal stresses on underground cables and prevent outages. That's highly desirable from NGED's viewpoint.
The problem you're up against is a low level of social enterprise, partly due to the way in which Milton Keynes was designed.
Save energy... recycle electrons!
While I agree with your suggestions, and have made similar ones myself on a number of occasions, the point at which I feel it falls down is when you state 'community-run battery storage'.
For such systems to operate in the most efficient and cost effective manner, the battery storage would need to be under the control of NG and/or the DNO's. Afterall, they are the ones controlling the supply of electrical energy to the various consumers, so are in a much better place to know how best to fully utilise such a system.
I realise that at present NG and the DNO's are prohibited from doing so, because it is deemed to be generation, and therefore violates their license to operate. This limitation needs to be changed, such that energy storage is not classified as generation.
@transparent Are you advocating communities collaborating on storage at the 11kV level only, or an alternative of a cluster of homes somehow collaborating at the 440V level (potentially complicated by the 3-phase element) ? As far as I am aware, no suppliers are (yet) offering a ToU Export tariff, but you seem to be suggesting that NGED may welcome the idea.
Incidentally, an error/fault/anomaly occurred on my newly-installed home battery system a week or so ago and neither battery inverter nor solar inverter's G100 system activated. I am restricted to 5kW but I actually exported at 6-8kW for a while with my grid voltage knocking on 253V. Presumably this will have increased the grid voltage of others on the same phase, but I didn't hear any neighbours shouting 😉 .
Feel free to comment @katler
Very few consumers know anything about how our UK energy supplies operate.
Would it help if we understood it better?
I wonder what drew you here to this topic. 🤔
Are you aware that today is the final day on which National Grid Electricity System Operator (ESO) will be running the supply network?
Tomorrow, 1st October, all British energy supplies will be managed by a new organisation, the National Energy Systems Operator.
Save energy... recycle electrons!
Posted by: @transparent@ianmk13 - There are two Primary Substations (33kV/11kV) at Broughton:
Kingston 940070; 23MW transformer; 9MW demand headroom, 10MW reverse-power (generation) headroom
Fox Milne 940043; 23MW; 1.5MW demand headroom, 6MW reverse-power headroom
In both cases, the National Grid data suggests that these transformers could be opened up to far more generation assets than the reverse-power headroom figure suggests. There will be technical reasons for this which are not explained by the raw figures.
Just because the local substations (11kV/440v) have generation constraints on them doesn't prevent you from making better use of the available reverse-power headroom.
Instead of thinking at the level of each individual house, consider the issue in a wider context.
A local Community Energy Group should be opening discussions with NGED about adding community-operated solar/wind/anaerobic-digester types of generation. You could connect at the 11kV level within the area already served by those two Primaries.
Alternatively, NGED may be even more attracted by the possibility of community-run battery storage, especially in areas of higher-density social housing.
The available Demand Headroom at these two Primaries is defined by the Peak Demand in the early evening.
If a community operated storage network could deploy batteries which remove 10% of the housing from any demand at peak time, then that would alleviate thermal stresses on underground cables and prevent outages. That's highly desirable from NGED's viewpoint.
The problem you're up against is a low level of social enterprise, partly due to the way in which Milton Keynes was designed.
May also be the new build houses going up near there, many of those may have solar etc.
The Milton Keynes city "boundary" has been dramatically expanded over the years, both for housing and business. Last time I drove in I barely recognised the outskirts and there is still a lot of building work going on from what I saw
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 31 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Midea ASHP – how to set weather compensation
@jamespa is right, typically they are far from linear, ...
By cathodeRay , 41 minutes ago
-
RE: Humming sound on new install.
Cant hear a thing with my 7kW Vaillant* so something is...
By JamesPa , 46 minutes ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Vat free applies to supply and install only no DIY. &...
By JamesPa , 2 hours ago
-
Funny story Graham, when I started looking to ...
By DREI , 9 hours ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 13 hours ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
I realise im overdue an update on my situation. first...
By Cleardene-ashp , 15 hours ago
-
RE: Replacing Worcester oil boiler with an ASHP
@toodles thanks. I was told by the engineer that this h...
By JulianC , 16 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Yes Octopus only have the £9 a month service plan for t...
By NJT , 17 hours ago
-
RE: Who’s Caved and Switched the Heating On Already?
@allyfish Dogs have owners - Cats keep staff. You are o...
By Toodles , 18 hours ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
A week later, I'm finally picking up this comment... ...
By Transparent , 18 hours ago
-
RE: COP is not the only measure of efficiency
We keep all our TRVs fully open using the whole house a...
By Old_Scientist , 23 hours ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
I am pleased to say at 4pm today we have added another ...
By ASHP-BOBBA , 2 days ago
-
RE: Renewables & Heat Pumps in the News
To unpack this a little.... 1) how many of us in this...
By Lucia , 2 days ago
-
RE: Vaillant aroTherm Plus 10kW thoughts?
@realevil the fans and fan speed / coil size (height, w...
By ASHP-BOBBA , 2 days ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@morgan this can just be done by your sepecilist when t...
By ASHP-BOBBA , 2 days ago
-
RE: Anyone still weathering it out with Agile?
@toodles I guess it all comes down to import averages. ...
By Tim441 , 3 days ago
-
RE: 300 Liter Tank - Do I have to heat it all?
The size of DHW tank affects the anti-legionella cycle....
By Transparent , 3 days ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
@scalextrix Name plate capacity
By HCas , 3 days ago
-
RE: Solar Thermal DHW and ASHP
I was originally contemplating a solar thermal installa...
By jamespetts , 3 days ago