Posted by: @makia2023I'm told 48v as the cut off is the best options as that is approx 10% soc. Is this your view and can you provide any advised values for me to confirm what I've read (or not).
Also, I'm assuming Pylontech setting for the inverter should work with the seplos BMS?
Let's deal with the BMS settings first.
Very few people seem to question what is meant by an assertion that a BMS or inverter is somehow compatible with a product from a different manufacturer.
It might be referring to the voltage settings which are required for the connected devices...
... or it might be that data is being transferred across a CANbus or Modbus communications link.
That would enable measurements made by the BMS get reported/recorded by the App issued for the Inverter, or vice versa.
It may have nothing to do with protecting your precious batteries.
So beware!
There are also many views across the internet as to the 'best' parameters which you should apply to your LiFePO4 cells.
Will Prowse, who has been publishing hundreds of You Tube tutorials on inverters, solar panels and batteries over the years, currently suggests:
48V LiFePO4 Battery w/ BMS
- Absorption: 58V
- Float: 54.4V
- Inverter Cut-off: 42.8V-48V
Individual 3.2V LiFePO4 Raw Cell (for individual cell capacity testing)
- Absorption: 3.625V
- Float: 3.4V
- Low voltage disconnect for capacity testing: 2.5V
Whoever you choose to believe, the basic principle remains the same.
The Inverter/Charger parameters are those which you set to define the voltage envelope within which your batteries are charged and discharged.
The BMS parameters are set outside of those.
The BMS acts rather like a fuse. If there's a fault, or an error in configuring the inverter, then it will step in and disconnect the battery before any damage is done.
Putting it the other way around; The inverter parameters are inset from those of the BMS.
Here are the absolute maximum and minimum voltages you should consider using: with a LifePO4 cell.
The inner pair of voltages are those which are set in the inverter (or charger) per cell.
A cell should not fall below 2.6v, nor be charged higher than 3.55v
which equates to a range of 41.4v to 56.8v for a 16S battery (sixteen cells in series).
The outer pair of voltages are applied to the BMS.
If the charge/discharge system fails, then the BMS prevents any cell falling below 2.35v or rising above 3.65v
You might suppose that equates to a maximum voltage of 16 x 3.65v (58.4v) for a 16S battery.
But that's not so.
Remember, the BMS has sense wires across each individual cell.
It will cut off the charge-current as soon as the first cell in that battery rises to 3.65v.
In practice I wouldn't configure my inverters and battery BMS units to these absolute minimum and maximum values.
But everyone will have their own opinion on how much they wish to inset from those extremes.
Save energy... recycle electrons!
@robl when i assembled mine last year around June time i think it was, i used a piece of 18mm melamine (kitchen cupboard shelf) in the bottom, i used EVE 280AH cells and ignored the plastic strips but used the foam between the cells. Using 18mm melamine meant that i could then hold the cells in compression.
some others have 3d printed a mesh type support that fits neatly in the bottom of the case. i have also recently heard that Seplos have now sorted the issue ....?
- 26 Forums
- 2,364 Topics
- 53.6 K Posts
- 180 Online
- 6,029 Members
Join Us!
Worth Watching
Latest Posts
-
Not a silly idea, @downfield, but not quite what I'm lo...
By Majordennisbloodnok , 14 minutes ago
-
Which is one reason why I now talk about the economic s...
By JamesPa , 2 hours ago
-
RE: Setback savings - fact or fiction?
Exactly. We only need to compare conditions, to decide ...
By cathodeRay , 2 hours ago
-
RE: Balancing financial efficiency and comfort using the Octopus Cosy tariff
I found because I have very low heat loss I can set bac...
By RadWhisperer , 5 hours ago
-
RE: Need Help Optimising My Rushed ECO4 Install: 12kW Bosch Heat Pump
Welcome @mickamills We too have an oversized 12kW Sa...
By Old_Scientist , 11 hours ago
-
RE: My Powerwall 3 Consumes 3-4 kWh/Day in Self-Consumption: Is This Normal?
@caron I can confirm that the power usage of the PW3 is...
By Old_Scientist , 12 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@andrewj they will release smarter controls, its been m...
By swwils , 15 hours ago
-
RE: Speedcomfort radiator fans
Thats true, but having tried (and succeeded) in constru...
By JamesPa , 15 hours ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
@bash brilliant, thanks for the feedback
By energy9165 , 17 hours ago
-
RE: Heat Pump Heats the House… But It’s Not Cosy. Emitter Changes or System Tweak?
@alastair There I was, feeling grumpy, he said “Cheer u...
By Toodles , 19 hours ago
-
RE: Grant Aerona: Is there a setting to keep the 2-port valve open during pump blockade
Depends on OAT. Mine cycles at OAT>10 and of course...
By JamesPa , 20 hours ago
-
RE: New Fogstar 15.5kWh upright solution
@transparent My conclusion is as you have noted, tha...
By Bash , 21 hours ago
-
RE: Mitsubishi Ecodan R290 10kW performance
And to you too. Wishing you a very enjoyable festive s...
By Sheriff Fatman , 23 hours ago
-
RE: External pipework insulation
They do? But that isn't apparent from the photos we'r...
By Transparent , 1 day ago
-
RE: Say hello and introduce yourself
@velcro welcome to the forums. Please feel free start a...
By Mars , 2 days ago
-
Daikin EDLA11D3V3 DHW Settings
I have a newly installed EDLA11D3V3 which I'm still get...
By Velcro , 2 days ago
-
RE: Midea ASHP – how to set weather compensation
@curlykatie did you get sorted with this?
By MickaMills , 2 days ago
-
RE: MyVaillant Connect Regular Disconnect
Thanks. Yes, if the time is consistently 11pm every nig...
By buckwem , 3 days ago