Seplos Mason DIY Kit - Ancillaries - Advice
Posted by: @makia2023I'm told 48v as the cut off is the best options as that is approx 10% soc. Is this your view and can you provide any advised values for me to confirm what I've read (or not).
Also, I'm assuming Pylontech setting for the inverter should work with the seplos BMS?
Let's deal with the BMS settings first.
Very few people seem to question what is meant by an assertion that a BMS or inverter is somehow compatible with a product from a different manufacturer.
It might be referring to the voltage settings which are required for the connected devices...
... or it might be that data is being transferred across a CANbus or Modbus communications link.
That would enable measurements made by the BMS get reported/recorded by the App issued for the Inverter, or vice versa.
It may have nothing to do with protecting your precious batteries.
So beware!
There are also many views across the internet as to the 'best' parameters which you should apply to your LiFePO4 cells.
Will Prowse, who has been publishing hundreds of You Tube tutorials on inverters, solar panels and batteries over the years, currently suggests:
48V LiFePO4 Battery w/ BMS
- Absorption: 58V
- Float: 54.4V
- Inverter Cut-off: 42.8V-48V
Individual 3.2V LiFePO4 Raw Cell (for individual cell capacity testing)
- Absorption: 3.625V
- Float: 3.4V
- Low voltage disconnect for capacity testing: 2.5V
Whoever you choose to believe, the basic principle remains the same.
The Inverter/Charger parameters are those which you set to define the voltage envelope within which your batteries are charged and discharged.
The BMS parameters are set outside of those.
The BMS acts rather like a fuse. If there's a fault, or an error in configuring the inverter, then it will step in and disconnect the battery before any damage is done.
Putting it the other way around; The inverter parameters are inset from those of the BMS.
Here are the absolute maximum and minimum voltages you should consider using: with a LifePO4 cell.
The inner pair of voltages are those which are set in the inverter (or charger) per cell.
A cell should not fall below 2.6v, nor be charged higher than 3.55v
which equates to a range of 41.4v to 56.8v for a 16S battery (sixteen cells in series).
The outer pair of voltages are applied to the BMS.
If the charge/discharge system fails, then the BMS prevents any cell falling below 2.35v or rising above 3.65v
You might suppose that equates to a maximum voltage of 16 x 3.65v (58.4v) for a 16S battery.
But that's not so.
Remember, the BMS has sense wires across each individual cell.
It will cut off the charge-current as soon as the first cell in that battery rises to 3.65v.
In practice I wouldn't configure my inverters and battery BMS units to these absolute minimum and maximum values.
But everyone will have their own opinion on how much they wish to inset from those extremes.
Save energy... recycle electrons!
@robl when i assembled mine last year around June time i think it was, i used a piece of 18mm melamine (kitchen cupboard shelf) in the bottom, i used EVE 280AH cells and ignored the plastic strips but used the foam between the cells. Using 18mm melamine meant that i could then hold the cells in compression.
some others have 3d printed a mesh type support that fits neatly in the bottom of the case. i have also recently heard that Seplos have now sorted the issue ....?
- 22 Forums
- 2,064 Topics
- 45.2 K Posts
- 58 Online
- 3,335 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Antifreeze top up for my heat pump - is this a rip off?
@editor @sallyl As Mars said, there are 2 different typ...
By Brendon Uys , 31 minutes ago
-
-
RE: Renewables & Heat Pumps in the News
Here on the Forum we're going to need to be increasingl...
By Transparent , 5 hours ago
-
RE: Commencing on an ASHP Installation Process
Good spot on the data. The physical size of the 7,kW m...
By JamesPa , 6 hours ago
-
What I Wish I Knew Before Installing a Heat Pump
I’m putting together the next Homeowners Q&A episod...
By Mars , 6 hours ago
-
RE: Load Compensation and Weather Compensation
@jamespa anytime. you would not believe how many times ...
By ASHP-BOBBA , 6 hours ago
-
RE: Planning Update: 1 Metre Boundary Rule for Heat Pumps Has Been Scrapped
In Scotland they still follow the MCS rules, so the noi...
By Johnmo , 8 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@johnmo and @benson Thanks! I was aware there was a p...
By MarcT , 18 hours ago
-
RE: Is your heat pump insured?
My insurer just asks the question: "Is your home heated...
By AndrewJ , 1 day ago
-
-
RE: Say hello and introduce yourself
@cathoderay Ah yes, that’s the name! The Heat Pimp, It’...
By Toodles , 1 day ago
-
RE: Jokes and fun posts about heat pumps and renewables
@editor Oh come on…. it’ll only take him 10 or 15 minut...
By Toodles , 2 days ago
-
By the way, I also think our industry need to get on bo...
By ASHP-BOBBA , 3 days ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
That's a curious conclusion with which I am struggling,...
By JamesPa , 4 days ago
-
RE: Rate the quality of your heat pump design and installation
Cool sounds good
By Johnmo , 4 days ago
-
RE: Grant Aerona3 - Home Assistant control via Modbus
That's interesting, @grantmethestrength. I'm a little s...
By Majordennisbloodnok , 4 days ago
-
@allyfish That's impressive. We are on a similar journe...
By ChandyKris , 4 days ago
-
RE: Enabling WiFi: Samsung ASHP on Smart Things App
Hi, good to hear. To be honest, I've given up with the ...
By Profzarkov , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
I feel like a record is on it's way this month. Scotlan...
By Andris , 5 days ago