@windymiller The Tesla Powerwall is in the extension along with the wiring to the grid connections at my meter and control gear for the 8.1 kWp. solar PV. The Tesla Gateway does all of the switching required via the IOS app. 27kW/h of energy will run the house and heating for approx. 10 hours or more depending on how hard the heat pump needs to work. Usually, there are sufficient hours during the night when greenest and cheapest rate allow me to fill the battery again. I have not knowingly ever had to take power from the grid during the ‘peak time’ of 16:00 to about 19:30 or so. Normally, I’ll tell the MyEnergi Eddi to charge the Sunamp Thermino during the night as that cheap rate then allows me to export more of my solar PV at 15p. Per kW/h during the day - though I can of course let the sun take the DHW strain if required too. Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
From observations I've made at substations, the main issue with ASHPs is the switch-on surge.
A typical domestic (single-phase) heat pump can take 30-35A when starting, which drops down to less than 10A once the compressor has got the fluids up to working pressure.
Plus there's a spike as the compressor motor starts which lasts around 1/10th second whilst the magnetic flux builds up.
So any inverter with a HP as a load must be able to deliver that output surge current whilst keeping the voltage within the required envelope.
What's the maximum continuous current and the surge current capability of the inverter within your Hyundai?
If you're 'running an extension lead', what's its current rating or conductor specification?
Save energy... recycle electrons!
- 21 Forums
- 1,827 Topics
- 39.6 K Posts
- 67 Online
- 2,142 Members
Join Us!
Latest Posts
-
RE: How To Balance Radiators & the Role of the Lockshield Valve: A Homeowner's Guide
Thanks James , hopefully getting there. By the way its ...
By Alfapat , 7 minutes ago
-
RE: Heat Pump starting current
@transparent to give context to my results of slow swit...
By Judith , 20 minutes ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
@gunboatdiplomat Yes, the lead installer did say that a...
By ChandyKris , 37 minutes ago
-
RE: Is My Midea Heat Pump Inherently Defective?
@cathoderay thanks for sharing that data. There's not ...
By BobTSkutter , 41 minutes ago
-
RE: Totally bewildered with my ECO4 heat pump installation
@toodles Thanks for support. From a previous discussi...
By Dwynwen , 1 hour ago
-
Update: it looks like Daikin do exactly what I’m lookin...
By SUNandAIR , 2 hours ago
-
RE: Grant Aerona3 R32 HPIDI17 performance in low temperatures
That's a very clear explanation and not exactly a ringi...
By davidm06 , 3 hours ago
-
RE: Vaillant Arotherm ASHP gets noisier when it gets colder outside
nevertheless it had just finished a de-icing cycle and ...
By Judith , 3 hours ago
-
RE: Best temperature wave form for best economy and efficiency .
still gathering data to help me decide . a few more gra...
By ivanhoew , 5 hours ago
-
RE: hum/whine from Wilo circulation pump
@richard24738 Fair enough, however please bear in mind ...
By Toodles , 9 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@johnnyb Have you looked at the Temperature Flexibility...
By Toodles , 9 hours ago
-
RE: Ideal Logic 10kW Heat Pump Pipes Noisy and Very Expensive to Run
Good to hear you have some progress. Is it mounted on r...
By Elton , 21 hours ago
-
RE: Running my new Nibe ASHP efficiently
@luke would love to hear more about how you went about ...
By jamieheatpumpnew , 22 hours ago
-
RE: Samsung ASHP owners what have you set your weather compensation to?
Not sure if this is working , smaller rooms a bit colde...
By Alfapat , 1 day ago
-
RE: Solar thermal with combi boiler
We too can help with which pipes go where and the defin...
By Transparent , 1 day ago
-
Are MCS are finally improving (some of) their guidelines?
Look: MCS has published an updated version of MCS ...
By Lucia , 1 day ago
-
RE: The good, the bad and the not that great – my heat pump installation
16 days again so far running trouble free no flow error...
By Burtis , 1 day ago
-
RE: Hybrid ASHP and gas boiler - operating together
@nigel-w I have a bivalent system setup which comprises...
By TechnoGeek , 1 day ago
-
RE: The Definitive Guide to Weather Compensation and Curves for Air Source Heat Pumps
Yes mine does, my warm end of the curve is set to 33@7⁰...
By @sand , 1 day ago
Latest Topics
-
By ANR 1 day ago
-
By Broadsman 2 days ago
-
By s_gatorator 5 days ago
-
Investment or not Solar/Battery instllation
By Alfapat 5 days ago
-
By Jancold 6 days ago
-
By MikeF 1 week ago