Anyone want to share costs on batteries?

233 Posts
20 Users
170 Likes
26.8 K Views
(@batalto)
Famed Member Member
3655 kWhs
Joined: 3 years ago
Posts: 1091
Topic starter  

@chickenbig my cells should be balanced. But I'll check them before I do anything when connecting. As to torque, I'll probably just buy a digital torque wrench

12kW Midea ASHP - 8.4kw solar - 29kWh batteries
262m2 house in Hampshire
Current weather compensation: 47@-2 and 31@17
My current performance can be found - HERE
Heat pump calculator spreadsheet - HERE


   
ReplyQuote
Transparent
(@transparent)
Famed Member Moderator
7937 kWhs
Veteran Expert
Joined: 2 years ago
Posts: 1319
 
Posted by: @chickenbig

these are 400A Zeeman ANMH fuses; they have an interrupt rating of 2,000A@80V DC. Has anyone performed testing around what interrupt capacity is actually required for LiFePO4 batteries

We need to think of this from the alternative viewpoint.

If a short-circuit were to occur, a 16S (48v) LiFePO4 battery would supply about 20kA. It is unlikely to experience serious damage from doing so, because that's the consequence of its chemistry. The cells survive.

However, the downstream device which caused the short-circuit will not emerge unscathed. If it's the charger/inverter, then the energy conversion to heat could easily cause a fire. 3.6MJ in 1mS is available if the electronics tries to 'take it'.

A Type-T fuse is preferable because it's designed to operate very fast at such currents. The charger/inverter will still be damaged, but the house doesn't burn down.

If I was an Insurer, or a Loss Adjuster working on their behalf, that's the level of protection I'd expect to see.

 

The UK doesn't (yet) have any regulatory controls or guidance for connection of off-grid ELV battery storage. If it did, then I suspect that house insurers would refer to that document in order to assess their level of risk.

In the meantime, it's down to Forums like this to promote common-sense safe practice, based on experience and the laws of physics. I've done basic research into Type-T fuses, which is why I made that recommendation, whereas I have little knowledge of the Zeeman ANMH fuses as yet.

Equally, I reserve the right to change my mind as we share information and find our way forward together! 😎 

Save energy... recycle electrons!


   
Derek M and Derek M reacted
ReplyQuote
Jeff
 Jeff
(@jeff)
Noble Member Member
2615 kWhs
Joined: 3 years ago
Posts: 425
 

Out of curiosity why not use a cheaper manual torque wrench with a calibration certificate and meeting the ISO standard +-3% accuracy? 

Is it that you trust your digital wrench more? Do you often get it recalibrated? 

I am no expert, just curious.

 


   
ReplyQuote



Jeff
 Jeff
(@jeff)
Noble Member Member
2615 kWhs
Joined: 3 years ago
Posts: 425
 

Again out of curiosity. Did you inform your building and contents insurance company you were installing solar panels and batteries in your home? Did they have any questions or requirements? Is there any mention of solar panels or storage batteries in your policies?

Does having solar panels and batteries increase the cost of insurance due to their value? 


   
Derek M and Derek M reacted
ReplyQuote
Transparent
(@transparent)
Famed Member Moderator
7937 kWhs
Veteran Expert
Joined: 2 years ago
Posts: 1319
 
Posted by: @jeff

why not use a cheaper manual torque wrench with a calibration certificate

Is that question for me @jeff ?

When researching the range of torques I was likely to require for installing LiFePO4 batteries it was clear that I needed one that would operate below the usual ranges. Wera is well known to me as a high quality manufacturer of screwdrivers, and I found a supplier of their A6 torque wrench which was then at a substantial discount.

When fitting busbars to EVE cells I usually torque first to 6Nm and then re-visit each nut to torque again at 8Nm, which is the level specified by the manufacturer.

Posted by: @jeff

Is it that you trust your digital wrench more?

I don't have a digital wrench.

Posted by: @jeff

Did you inform your building and contents insurance company you were installing solar panels and batteries in your home?

No. I have had off-grid PV panels for 15+ years and changed insurers several times. When they did ask questions, they were only interested in panels connected to the grid via an inverter. That may not seem logical to me because such panels will have been installed by an accredited professional, but who am I to argue?!

I've now had grid-connected PV panels and a grid-connected storage battery for about 18-months. When I switched to my current insurer, there were no questions about renewable-energy installations at the home.

Save energy... recycle electrons!


   
ReplyQuote
Jeff
 Jeff
(@jeff)
Noble Member Member
2615 kWhs
Joined: 3 years ago
Posts: 425
 
Posted by: @transparent
Posted by: @jeff

why not use a cheaper manual torque wrench with a calibration certificate

Is that question for me @jeff ?

When researching the range of torques I was likely to require for installing LiFePO4 batteries it was clear that I needed one that would operate below the usual ranges. Wera is well known to me as a high quality manufacturer of screwdrivers, and I found a supplier of their A6 torque wrench which was then at a substantial discount.

When fitting busbars to EVE cells I usually torque first to 6Nm and then re-visit each nut to torque again at 8Nm, which is the level specified by the manufacturer.

Posted by: @jeff

Is it that you trust your digital wrench more?

I don't have a digital wrench.

Posted by: @jeff

Did you inform your building and contents insurance company you were installing solar panels and batteries in your home?

No. I have had off-grid PV panels for 15+ years and changed insurers several times. When they did ask questions, they were only interested in panels connected to the grid via an inverter. That may not seem logical to me because such panels will have been installed by an accredited professional, but who am I to argue?!

I've now had grid-connected PV panels and a grid-connected storage battery for about 18-months. When I switched to my current insurer, there were no questions about renewable-energy installations at the home.

No the questions deliberately were not just directed at you @Transparent.

I was curious about a variety of view points and experience to be honest. Your knowledge is always very useful. 

I appreciate some of my questions are not well formed as i am no expert. For example a torque and a wrench, manual and digital torque ranges etc. 

Thanks for the responses, useful to know.

I am sometimes wary about asking anything in case i come across as an idiot as with the whole torque and fuse stuff as examples. So thanks for your patience. 

This post was modified 2 years ago 3 times by Jeff

   
ReplyQuote
Jeff
 Jeff
(@jeff)
Noble Member Member
2615 kWhs
Joined: 3 years ago
Posts: 425
 

Am curious about fuses. 

Do we have examples of what installers are fitting for battery storage, not because i think they may good or bad necessarily, just out of curiosity about what sort of solution they are putting in?

Do those with batteries on this forum know what they have?

 


   
ReplyQuote
(@batalto)
Famed Member Member
3655 kWhs
Joined: 3 years ago
Posts: 1091
Topic starter  

@transparent what size fuse do you think is present in the box?

12kW Midea ASHP - 8.4kw solar - 29kWh batteries
262m2 house in Hampshire
Current weather compensation: 47@-2 and 31@17
My current performance can be found - HERE
Heat pump calculator spreadsheet - HERE


   
ReplyQuote
(@batalto)
Famed Member Member
3655 kWhs
Joined: 3 years ago
Posts: 1091
Topic starter  

@jeff this is the Torque wrench I am considering - https://www.amazon.co.uk/ACDelco-ARM601-3-Digital-Torque-Wrench/dp/B08YK8ZH47

5-50Nm

12kW Midea ASHP - 8.4kw solar - 29kWh batteries
262m2 house in Hampshire
Current weather compensation: 47@-2 and 31@17
My current performance can be found - HERE
Heat pump calculator spreadsheet - HERE


   
ReplyQuote



Transparent
(@transparent)
Famed Member Moderator
7937 kWhs
Veteran Expert
Joined: 2 years ago
Posts: 1319
 
Posted by: @batalto

what size fuse do you think is present in the box?

In which box? ... the Mason enclosure manufactured by Seplos?

And do I assume we're discussing the 'size' in Amps, as opposed to millimeters? 🤔 

I'm suggesting that the Breaking Capacity is every bit as important as the rated value. The Bussman type-T which I'm currently using is rated 250A, with a breaking capacity of 200kA.

I wouldn't expect the 250-FM fuse to 'blow' because my inverters have taken slightly more than 250A through it. I've got DC circuit-breakers for that level of current protection. The fuse is there to provide fire/explosion protection in case of a short-circuit.

At the moment I'm building my own fuse-holders with an outer cover. I can't find a supplier with stock of the Bussmann BH-1133 modular fuse-blocks.

Type T holders

 

Save energy... recycle electrons!


   
ReplyQuote
(@batalto)
Famed Member Member
3655 kWhs
Joined: 3 years ago
Posts: 1091
Topic starter  

@transparent Yes the amp rating. ChickenBig said "I confirmed with a Seplos tech-support person that these are 400A Zeeman ANMH fuses; they have an interrupt rating of 2,000A@80V DC"

12kW Midea ASHP - 8.4kw solar - 29kWh batteries
262m2 house in Hampshire
Current weather compensation: 47@-2 and 31@17
My current performance can be found - HERE
Heat pump calculator spreadsheet - HERE


   
ReplyQuote
Transparent
(@transparent)
Famed Member Moderator
7937 kWhs
Veteran Expert
Joined: 2 years ago
Posts: 1319
 

Zeeman is a Chinese manufacturer. Their website provides scant detail of their ANMH fuse range.

It isn't even clear if the 'ANMH' name refers to the fuse characteristics, or merely the case style!

Similar looking 'ANH' and 'ANS' fuses from other manufacturers are commonly used in electric vehicles.

It's a 'slow blow' fuse, and similar to the Type-T in that respect. It will tolerate surges when motors start up, for example.

I'm wary of three points:

  • Zeeman quote an Interrupting Rating of 2000A. That's not the same as a Breaking Capacity, and is much lower than the instantaneous current which would flow from a 48v LiFePO4 battery if the attached inverter went short-circuit.
  • The ceramic casing may well 'contain' the arc as the fuse ribbon melts, but it doesn't look physically large enough to contain any silica-based quenching agent.
  • The blow-time of 0.1 to 1 second at 2kA of current seems too long. To prevent a 'flash fire' in the electronics of an inverter, I'd want to see a fuse operating much faster than that - say, within 1mS.

I'd want to know more detail before I'm confident that the Zeeman ANMH really would prevent fire from an accidental short circuit.

 

Remember, you don't have to stick with the internal fuse which Seplos supply in the Mason box. You can always add a second fuse in series. If it's physically too large to go inside the box, then add it externally.

The whole point is that both you and a house insurer would feel confident that you've taken reasonable steps to minimise risk. (That's what Loss Adjusters want to see.)

This post was modified 2 years ago 2 times by Transparent

Save energy... recycle electrons!


   