EV charger installation question – I don't want to bury the cable
Those markings are not the ones which tell us the conductor size, unfortunately.
Do you happen to have vernier calipers which could be used to measure the diameter of the black, grey or brown internal wires?
Save energy... recycle electrons!
I'm assuming that the SWA cable has copper conductors of either 1.5mm² or 2.5mm²
Those sizes are difficult to discriminate based solely on external dimensions.
But perhaps this might help:
The exact figures differ between manufacturers.
Each SWA cable might use different plastics as the insulator.
The major problem with SWA are the losses, especially if it's in a duct or directly buried.
The IET assumes that direct burial is in dry ground, resulting in little heat escaping.
Running the cable in wet clay soils can allow you to pass higher currents, albeit you're then not complying with the IET specification.
Save energy... recycle electrons!
- 26 Forums
- 2,171 Topics
- 47.8 K Posts
- 50 Online
- 5,744 Members
Join Us!
Podcast Picks
Latest Posts
-
That's probably the most important point, maybe see if ...
By cathodeRay , 14 minutes ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
Unfortunately I'm not that well connected 😂 ...
By Scalextrix , 41 minutes ago
-
RE: How to choose Towel Rails for an ASHP
@jamespa yes, to essentially prevent them consuming unn...
By Mars , 1 hour ago
-
Thank you for raising your concerns. Customer safety, s...
By Mixergy , 3 hours ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
It is interesting to see what our new Grant Aerona 290 ...
By GrahamF , 3 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
I've never physically seen it, but I seem to recall som...
By cathodeRay , 3 hours ago
-
@jamespa Ours is a Daikin EDLA03 8 kW and the Delta T =...
By Toodles , 4 hours ago
-
RE: Big Changes Coming to Our Heat Pump System
Day one is done. The system’s been fully flushed and ...
By Mars , 19 hours ago
-
RE: Midea ASHP – how to set weather compensation
I noticed that too and thought the same thing, but then...
By cathodeRay , 20 hours ago
-
RE: Ya can’t win! It is S*d’s Law!
@old_scientist If IOF is still running next late spring...
By Toodles , 21 hours ago
-
RE: Electricity price predictions
Those of you on Agile will do well tomorrow; there are ...
By Toodles , 21 hours ago
-
RE: Who’s Caved and Switched the Heating On Already?
We've been running our Ecodan system, installed in June...
By Sheriff Fatman , 1 day ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 2 days ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 2 days ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
Er true, it should have read l/hr!
By JamesPa , 2 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 4 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@dgclimatecontrol I attach the responses from 2 potenti...
By pash44pump , 4 days ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 5 days ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
I realise im overdue an update on my situation. first...
By Cleardene-ashp , 5 days ago