EV charger installation question – I don't want to bury the cable
I'm planning to install EV charger to front of garage.
Main supply is at the other corner of the house and garage is built on the other corner, after the garden.
I'd like to have an EV charger connected back to existing house supply, but not have to bury the cable.
Please help me with your expertise.
Hello @hem. And I see that @editor has very quickly found a suitable spot for this topic! 🙂
An outside cable like this would normally be Steel Wire Armoured (SWA).
For a standard domestic EV charger, it would need to be able to deliver 32A (assuming a charger rated at 7.5kW).
There will be voltage drop along the cable route. The distance matters.
But you can quickly assess the required cable size by using an online cable cable calculator, such as this one from TLC.
There is no requirement for an SWA cable to be buried underground.
You could run it above ground, clipped at low level to a wall or a fence, for example.
The important issue is that it must be protected from mechanical damage.
Save energy... recycle electrons!
Thank you Transparent.
in on of the forum you had suggest SWA - 4 CORE ( Can't remember where). is that you suggest for EV charger installation.
I have no knowledge of electrics , please ignore my stupidity.
I can't remember where either 😖
Can I check if you are intending to use a recognised EV Charger installer in order to take advantage of a grant?
Or are you simply buying a charger and getting a local electrician to fit it?
It's possible that the grant-aided schemes only work if they supply the cable.
That needs checking first.
However, the approved installer might still offer a discount if you were offering to run such a long cable yourself!
If the choice of cable is entirely up to you, then I'd usually expect it to be a 3-core SWA type.
That means both the armoured sheath and one of the cores is earth.
If it was simply a run to provide power in the garage, then an electrician might've been happy with 2-core cable.
But earthing on EV chargers is a 'hot topic' and I'd be surprised if an installer would be prepared to use an earth connection which operates only through the steel armour. It's not a great conductor if a fault should occur.
Having said all that, some EV charger installations require a local earth rod, rather than depending on a connection back to the house.
To assess that, can you say whether your house currently has its own earth rod?
Or is the earth provided by the Electricity Distribution company?
A photo of your 100A service fuse and meter would be helpful.
Save energy... recycle electrons!
Depending on the charger you install, an option may be to use an SWA cable with an integral cat5 cable. This may be used either for an internet connection if it is a 'Smart' device, to avoid using WiFi, or to connect remote current transformers to facilitate load management features in the charger (so as not to draw too much power from your home supply. Your electrician should be able to advise.
@hem that's a good observation from @ianmk13
Here's a link to that SWA with integral CAT5e data cable, also from TLC Direct.
Note that they sell it per metre, which is very helpful.
If you zoom back out to the wider selection of products sold by TLC for use with EV chargers, you'll notice that the combined power and data cable is only available with 3-cores. That's a pretty strong indication of what the market is using!
Save energy... recycle electrons!
Just a reminder @hem - we do need to know whether your house has its own earth stake, or if earth is provided via the 100A service fuse.
You should either have an earth wire coming from your service fuse, or you have an earth stake. Not both!
Which do you have?
I want to post the relevant wiring diagram for you to see.
Save energy... recycle electrons!
I'm planning and paid Podpoint .
They washed their hands advising me to get the cable from power source via garden ( ground work) to garage by myself.
Attached power source photo and a site sketch
Thanks🙏
- 27 Forums
- 2,520 Topics
- 58.6 K Posts
- 729 Online
- 6,800 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Daikin Altherma 3 LT compressor longevity question
This mess is intriguing: I wonder if this represent...
By bobflux , 22 minutes ago
-
RE: Say hello and introduce yourself
Hi. I'm Mike. Thank you for letting me join. My partn...
By Fretless6 , 2 hours ago
-
RE: Connecting Growatt SPH5000 over wired ethernet rather than wireless
The simplest wired option is usually the Growatt Ethern...
By Jonatan , 5 hours ago
-
RE: Peak Energy Products V therm 16kW unit heat pump not reaching flow temperature
ASHPs do have a minimum compressor speed. The minimum h...
By bobflux , 12 hours ago
-
RE: Electricity price predictions
@jamespa And it seems some of the nasty public cloud...
By Batpred , 12 hours ago
-
RE: Tell us about your Solar (PV) setup
Location: near Lyon, France 12kWp on the roof, 2x Sol...
By bobflux , 12 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
Technology is rapidly advancing. BBC News reported th...
By Transparent , 15 hours ago
-
What matters for flow and pressure drop is internal dia...
By bobflux , 16 hours ago
-
RE: Do Fridges and Freezers have COP ratings?
@editor Thank you all for your replies and submitted in...
By Toodles , 18 hours ago
-
I know and yes. The secondary deltaT wont necessaril...
By JamesPa , 22 hours ago
-
RE: Designing heating system with air to water heat pump in France, near Lyon
Just love the way you put it! 🤣
By Batpred , 2 days ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thank you for sharing. So it seems that your Schneid...
By Batpred , 2 days ago
-
RE: Forum updates, announcements & issues
@upnorthandpersonal thanks for the thoughtful, consider...
By Mars , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@mk4 All 21 panels have their own Enphase IQ7a microinv...
By Toodles , 2 days ago
-
RE: Setback savings - fact or fiction?
Great, so you have proven that MELCloud is consistently...
By RobS , 3 days ago
-
RE: Mitsu PUHZ120Y 'Outdoor Temp 'error?
Thanks David & James It almos...
By DavidAlgarve , 3 days ago
-
RE: Surge protection devices SPDs
@trebor12345 - your original Topic about the right type...
By Transparent , 3 days ago
-
RE: Help needed with Samsung AE120RXYDEG
@tomf I’ve been sent this from a service engineer at Sa...
By Mars , 3 days ago
-
RE: Buying large amp bidirectional RCD and RCBO
Yes... I went through this particular headache and ende...
By bobflux , 4 days ago
-
O-oh! Let's take this as an opportunity to 'pass the ...
By Transparent , 4 days ago
-
RE: Homely setup on daikin heat pump
@craigh I refer to our somewhat elevated temperature of...
By Toodles , 4 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
My turn, this describes the future installation, only t...
By bobflux , 4 days ago