EV charger installation question – I don't want to bury the cable
I'm planning to install EV charger to front of garage.
Main supply is at the other corner of the house and garage is built on the other corner, after the garden.
I'd like to have an EV charger connected back to existing house supply, but not have to bury the cable.
Please help me with your expertise.
Hello @hem. And I see that @editor has very quickly found a suitable spot for this topic! 🙂
An outside cable like this would normally be Steel Wire Armoured (SWA).
For a standard domestic EV charger, it would need to be able to deliver 32A (assuming a charger rated at 7.5kW).
There will be voltage drop along the cable route. The distance matters.
But you can quickly assess the required cable size by using an online cable cable calculator, such as this one from TLC.
There is no requirement for an SWA cable to be buried underground.
You could run it above ground, clipped at low level to a wall or a fence, for example.
The important issue is that it must be protected from mechanical damage.
Save energy... recycle electrons!
Thank you Transparent.
in on of the forum you had suggest SWA - 4 CORE ( Can't remember where). is that you suggest for EV charger installation.
I have no knowledge of electrics , please ignore my stupidity.
I can't remember where either 😖
Can I check if you are intending to use a recognised EV Charger installer in order to take advantage of a grant?
Or are you simply buying a charger and getting a local electrician to fit it?
It's possible that the grant-aided schemes only work if they supply the cable.
That needs checking first.
However, the approved installer might still offer a discount if you were offering to run such a long cable yourself!
If the choice of cable is entirely up to you, then I'd usually expect it to be a 3-core SWA type.
That means both the armoured sheath and one of the cores is earth.
If it was simply a run to provide power in the garage, then an electrician might've been happy with 2-core cable.
But earthing on EV chargers is a 'hot topic' and I'd be surprised if an installer would be prepared to use an earth connection which operates only through the steel armour. It's not a great conductor if a fault should occur.
Having said all that, some EV charger installations require a local earth rod, rather than depending on a connection back to the house.
To assess that, can you say whether your house currently has its own earth rod?
Or is the earth provided by the Electricity Distribution company?
A photo of your 100A service fuse and meter would be helpful.
Save energy... recycle electrons!
Depending on the charger you install, an option may be to use an SWA cable with an integral cat5 cable. This may be used either for an internet connection if it is a 'Smart' device, to avoid using WiFi, or to connect remote current transformers to facilitate load management features in the charger (so as not to draw too much power from your home supply. Your electrician should be able to advise.
@hem that's a good observation from @ianmk13
Here's a link to that SWA with integral CAT5e data cable, also from TLC Direct.
Note that they sell it per metre, which is very helpful.
If you zoom back out to the wider selection of products sold by TLC for use with EV chargers, you'll notice that the combined power and data cable is only available with 3-cores. That's a pretty strong indication of what the market is using!
Save energy... recycle electrons!
Just a reminder @hem - we do need to know whether your house has its own earth stake, or if earth is provided via the 100A service fuse.
You should either have an earth wire coming from your service fuse, or you have an earth stake. Not both!
Which do you have?
I want to post the relevant wiring diagram for you to see.
Save energy... recycle electrons!
I'm planning and paid Podpoint .
They washed their hands advising me to get the cable from power source via garden ( ground work) to garage by myself.
Attached power source photo and a site sketch
Thanks🙏
please find photo attached
- 22 Forums
- 2,031 Topics
- 44.2 K Posts
- 43 Online
- 3,236 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Agile: average import cost vs other tariffs?
@old_scientist I have been imitating a hawk towards the...
By Toodles , 23 minutes ago
-
RE: help sizing rads based on room by room heat loss
@jamespa thanks for the info but I think I must have so...
By AdamK , 26 minutes ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
@phoenix15 I'm no plumber so please don't take this as ...
By dnagre , 40 minutes ago
-
RE: Is this normal? Click of the DHW returning to space heating
@grantmethestrength Oh sorry to hear that, there should...
By ASHP-BOBBA , 5 hours ago
-
@ashp-bobba TBH the ladies are rather disorganised, so ...
By Cathyem1 , 5 hours ago
-
The Rise and Fall of Europe’s Most Generous Green Subsidy
This story came to my attention thanks to Graham Hendra...
By Mars , 5 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
And for those of us without an automatic irrigation sys...
By Majordennisbloodnok , 5 hours ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Thermal Off's
From the Full SAP Report: Space heating requirements:...
By trebor12345 , 6 hours ago
-
Logically, the lower frequency = more gentle, yes, but ...
By SUNandAIR , 10 hours ago
-
I'm just trying to imagine this construction approach @...
By Transparent , 12 hours ago
-
RE: Ideal Logic ASHP - change from 55°C to 35°C Heating?
Good point. I’ll keep my eye on the manifold temperatur...
By Tomdad , 12 hours ago
-
RE: How hard and expensive would it be to change panel and add battery?
@transparent It is a setting that Octopus make via the ...
By Toodles , 13 hours ago
-
RE: Performance of Heat Pumps in Mild Weather
@heatgeek The flow rate isnt controlled by Mitsub...
By RobS , 15 hours ago
-
RE: Say hello and introduce yourself
I might put a couple of speakers in the ceiling if fund...
By Fingers , 1 day ago
-
RE: Bathroom Radiator replacement
@rob-nezard can you please offer your professional advi...
By Mars , 1 day ago
-
-
RE: Questions on my Hitachi Yutaki SCombi Heat Pump
OK, thats good and low. With low flow temperatures lik...
By JamesPa , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@jamespa “They are all equal but, some are more equal t...
By Toodles , 2 days ago
-
RE: Is it KISS or constant – weather compensation vs. set flow temperature?
@cliffhanger Mine has a 'space heating off' setting! O...
By JamesPa , 2 days ago
-
RE: Replacing Worcester oil boiler with an ASHP
Is this something you are thinking of doing? Or has thi...
By Cliff-Arnold , 3 days ago