EV charger installation question – I don't want to bury the cable
I'm planning to install EV charger to front of garage.
Main supply is at the other corner of the house and garage is built on the other corner, after the garden.
I'd like to have an EV charger connected back to existing house supply, but not have to bury the cable.
Please help me with your expertise.
Hello @hem. And I see that @editor has very quickly found a suitable spot for this topic! 🙂
An outside cable like this would normally be Steel Wire Armoured (SWA).
For a standard domestic EV charger, it would need to be able to deliver 32A (assuming a charger rated at 7.5kW).
There will be voltage drop along the cable route. The distance matters.
But you can quickly assess the required cable size by using an online cable cable calculator, such as this one from TLC.
There is no requirement for an SWA cable to be buried underground.
You could run it above ground, clipped at low level to a wall or a fence, for example.
The important issue is that it must be protected from mechanical damage.
Save energy... recycle electrons!
Thank you Transparent.
in on of the forum you had suggest SWA - 4 CORE ( Can't remember where). is that you suggest for EV charger installation.
I have no knowledge of electrics , please ignore my stupidity.
I can't remember where either 😖
Can I check if you are intending to use a recognised EV Charger installer in order to take advantage of a grant?
Or are you simply buying a charger and getting a local electrician to fit it?
It's possible that the grant-aided schemes only work if they supply the cable.
That needs checking first.
However, the approved installer might still offer a discount if you were offering to run such a long cable yourself!
If the choice of cable is entirely up to you, then I'd usually expect it to be a 3-core SWA type.
That means both the armoured sheath and one of the cores is earth.
If it was simply a run to provide power in the garage, then an electrician might've been happy with 2-core cable.
But earthing on EV chargers is a 'hot topic' and I'd be surprised if an installer would be prepared to use an earth connection which operates only through the steel armour. It's not a great conductor if a fault should occur.
Having said all that, some EV charger installations require a local earth rod, rather than depending on a connection back to the house.
To assess that, can you say whether your house currently has its own earth rod?
Or is the earth provided by the Electricity Distribution company?
A photo of your 100A service fuse and meter would be helpful.
Save energy... recycle electrons!
Depending on the charger you install, an option may be to use an SWA cable with an integral cat5 cable. This may be used either for an internet connection if it is a 'Smart' device, to avoid using WiFi, or to connect remote current transformers to facilitate load management features in the charger (so as not to draw too much power from your home supply. Your electrician should be able to advise.
@hem that's a good observation from @ianmk13
Here's a link to that SWA with integral CAT5e data cable, also from TLC Direct.
Note that they sell it per metre, which is very helpful.
If you zoom back out to the wider selection of products sold by TLC for use with EV chargers, you'll notice that the combined power and data cable is only available with 3-cores. That's a pretty strong indication of what the market is using!
Save energy... recycle electrons!
Just a reminder @hem - we do need to know whether your house has its own earth stake, or if earth is provided via the 100A service fuse.
You should either have an earth wire coming from your service fuse, or you have an earth stake. Not both!
Which do you have?
I want to post the relevant wiring diagram for you to see.
Save energy... recycle electrons!
I'm planning and paid Podpoint .
They washed their hands advising me to get the cable from power source via garden ( ground work) to garage by myself.
Attached power source photo and a site sketch
Thanks🙏
- 26 Forums
- 2,271 Topics
- 50.8 K Posts
- 240 Online
- 5,933 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: My DIY Heat Pump installation
@temperature_gradient Building regs I had my initial...
By Polar bear , 8 hours ago
-
This is a plot from a Shelly EM monitoring the supply t...
By Ubert767 , 8 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Hi again all, Just to update on this... I've now ad...
By benson , 10 hours ago
-
RE: Request for feedback on where we're at with our quest to get an ASHP or ideas.
thanks, heatpunk looks great, being able to do the calc...
By giryan , 11 hours ago
-
RE: Is Your House Warmer Upstairs Than Downstairs?
Why arent you expecting them to make much difference. ...
By JamesPa , 11 hours ago
-
RE: Oil Boiler & Heat Pump Hybrid System
@paultheheating I wonder if you are being a bit pessimi...
By GrahamF , 11 hours ago
-
@toodles sounds good. I started with cosy but then plug...
By Eliuccio , 11 hours ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
It has been just over a year since we changed over to a...
By npru , 13 hours ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
He showed me a photo of 5-10l/min. However a...
By Crimson , 14 hours ago
-
RE: Finding a Thermostatic Shower Valve That Works with Heat Pump Systems
@morgan I should just have written ‘Mea Culpa’ shouldn’...
By Toodles , 15 hours ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
'We learn from history that we do not learn from histor...
By Lawrence Leask FInstR , 15 hours ago
-
Mitsubishi Ecodan FTC7 Legionella date set
I can set the number of days between Legionella cycles ...
By DRB01 , 20 hours ago
-
RE: When to use Octopus Intelligent Go tariff with my heat pump and battery
@treewizard Yes, I like the extra facilities that NetZe...
By Toodles , 22 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk downstairs rads are less prone to airlocks, you ...
By AgentGeorge , 23 hours ago
-
RE: My Octopus Cosy 6 Heat Pump Journey: From Quote to Completion
@editor thanks for highlighting my name. Yes I did get ...
By Chansug , 1 day ago
-
RE: balancing radiators with a mixture of different size pipework and a few undersize rads.
@editor Thanks for your input Mars. No I think the comm...
By baxtDave , 2 days ago
-
RE: Rate the quality of your heat pump design and installation
We’re looking to expand our list of recommended list of...
By Mars , 2 days ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@transparent Along with the right workers, they can’t b...
By Toodles , 2 days ago
-
RE: Midea ASHP – how to set weather compensation
I have just looked at my heat pump 'long interval' (27 ...
By cathodeRay , 2 days ago