I'm planning to install EV charger to front of garage.
Main supply is at the other corner of the house and garage is built on the other corner, after the garden.
I'd like to have an EV charger connected back to existing house supply, but not have to bury the cable.
Please help me with your expertise.
Hello @hem. And I see that @editor has very quickly found a suitable spot for this topic! 🙂
An outside cable like this would normally be Steel Wire Armoured (SWA).
For a standard domestic EV charger, it would need to be able to deliver 32A (assuming a charger rated at 7.5kW).
There will be voltage drop along the cable route. The distance matters.
But you can quickly assess the required cable size by using an online cable cable calculator, such as this one from TLC.
There is no requirement for an SWA cable to be buried underground.
You could run it above ground, clipped at low level to a wall or a fence, for example.
The important issue is that it must be protected from mechanical damage.
Save energy... recycle electrons!
Thank you Transparent.
in on of the forum you had suggest SWA - 4 CORE ( Can't remember where). is that you suggest for EV charger installation.
I have no knowledge of electrics , please ignore my stupidity.
I can't remember where either 😖
Can I check if you are intending to use a recognised EV Charger installer in order to take advantage of a grant?
Or are you simply buying a charger and getting a local electrician to fit it?
It's possible that the grant-aided schemes only work if they supply the cable.
That needs checking first.
However, the approved installer might still offer a discount if you were offering to run such a long cable yourself!
If the choice of cable is entirely up to you, then I'd usually expect it to be a 3-core SWA type.
That means both the armoured sheath and one of the cores is earth.
If it was simply a run to provide power in the garage, then an electrician might've been happy with 2-core cable.
But earthing on EV chargers is a 'hot topic' and I'd be surprised if an installer would be prepared to use an earth connection which operates only through the steel armour. It's not a great conductor if a fault should occur.
Having said all that, some EV charger installations require a local earth rod, rather than depending on a connection back to the house.
To assess that, can you say whether your house currently has its own earth rod?
Or is the earth provided by the Electricity Distribution company?
A photo of your 100A service fuse and meter would be helpful.
Save energy... recycle electrons!
Depending on the charger you install, an option may be to use an SWA cable with an integral cat5 cable. This may be used either for an internet connection if it is a 'Smart' device, to avoid using WiFi, or to connect remote current transformers to facilitate load management features in the charger (so as not to draw too much power from your home supply. Your electrician should be able to advise.
@hem that's a good observation from @ianmk13
Here's a link to that SWA with integral CAT5e data cable, also from TLC Direct.
Note that they sell it per metre, which is very helpful.
If you zoom back out to the wider selection of products sold by TLC for use with EV chargers, you'll notice that the combined power and data cable is only available with 3-cores. That's a pretty strong indication of what the market is using!
Save energy... recycle electrons!
Just a reminder @hem - we do need to know whether your house has its own earth stake, or if earth is provided via the 100A service fuse.
You should either have an earth wire coming from your service fuse, or you have an earth stake. Not both!
Which do you have?
I want to post the relevant wiring diagram for you to see.
Save energy... recycle electrons!
I'm planning and paid Podpoint .
They washed their hands advising me to get the cable from power source via garden ( ground work) to garage by myself.
Attached power source photo and a site sketch
Thanks🙏
please find photo attached
- 26 Forums
- 2,129 Topics
- 46.8 K Posts
- 49 Online
- 5,654 Members
Podcast Picks
Latest Posts
-
RE: Mitsu Wireless Controller and MelCloud
It would seem that I have a problem (at least one!) in ...
By DavidAlgarve , 2 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
For reference, our installer has just contacted us afte...
By Old_Scientist , 21 hours ago
-
@toodles Of course. I've also used Tim and Kat's Gree...
By Old_Scientist , 21 hours ago
-
RE: Who's your electricity provider and what's your tariff?
Yes, I noticed that change too. The software really doe...
By Old_Scientist , 22 hours ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
@old_scientist me too. Just installed my new heat pump ...
By Eliuccio , 2 days ago
-
RE: Is your heat pump insured?
Yup just spoke to Privilege to inform them of my impend...
By Scalextrix , 2 days ago
-
RE: Forum updates, announcements & issues
Just to keep everyone in the loop, as the site continue...
By Mars , 2 days ago
-
RE: Fast DHW setting on Midea (Clivet) heat pump
@simon-w, is this something you could potentially assis...
By Mars , 2 days ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
Fwiw I called my installer out for the first time a few...
By JamesPa , 3 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@sandy, I'll send Vaillant an email tomorrow and see if...
By Mars , 3 days ago
-
RE: Long term efficiency degradation
@jamespa yes as I thought thanks. We have a reaso...
By Scalextrix , 3 days ago
-
RE: Who has a V2G EV installation
I agree, but a word of caution. V2X is also sometimes u...
By Majordennisbloodnok , 4 days ago
-
RE: Sunamp Thermino Heat Battery
@jamespa A few days after the installation had been com...
By Toodles , 4 days ago
-
RE: Planning Permission May 2025
Fair enough. I have read the legislation and MCS020a ...
By JamesPa , 6 days ago
-
RE: How do I choose a single room MVHR to prevent losing heat in my bathroom ?
An update on the Heatsava. It is the most difficult thi...
By heat-pump-newbie , 6 days ago
-
RE: ASHP heat output monitoring
@carlo - not much better, is it. It looks more like a u...
By cathodeRay , 7 days ago
-
RE: Renewables & Heat Pumps in the News
this document extensively describes (in a non-blame, ne...
By Judith , 7 days ago
-
RE: Ecodan - Legionella Operation Time and Target Temperature
Once the white plastic cap is removed, my immersion loo...
By Old_Scientist , 1 week ago
-
RE: Replacing Refrigerant on Mitsubishi Heat Pump
@dgclimatecontrol I don't know, but they were not happy...
By DavidAlgarve , 1 week ago
-
RE: Why do we need pressurised systems?
A good question @toodles. My old open thermal store and...
By AllyFish , 1 week ago