DHW Efficiency
I'm currently looking at two installer options.
Eon and IMS heat pumps.
Eon are proposing either a Vaillant Aurotherm plus 7kW on brackets (not a fan) or Ideal Logic Air 8kW floor mounted. On both options they have quoted a DHW efficiency of 1.75, can anyone help understand what the actual efficiency would be? 55 degree store temp for a 200L.
IMS are proposing a Samsung gen 7, 7kW, with Adia. Their efficiency for DHW is reportedly 3.41(which seems impressive). Again, 55 degree store temp for 200L.
I know DHW is only one section of the puzzle here, especially with Adia having zero rad changes (for now), but something that might help steer my decision on the installer quality.
Thanks in advance
Our DHW this year (Jan & Feb) has given a COP of 3.6. That is 5 days a week heating to 48C once a day at 1pm and once a week to 69C for a legionnaire cycle which then stays above the 43C limit set, despite use the following day. Your exact COP will depend a lot on detail settings which depends on use required and we all differ. We have a 200L tank and there’s two of us who don’t shower for ages.
The potential suppliers might be considering worst case of a larger tank heated hotter to last longer (or more times per day) or your household details. 1.75 is low and 3.x credible.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
@judith thanks! I think Eon basically haven't bothered to work out then DHW COP for any pump or design presented, which is slightly concerning... However, they've had sensible conversations with me about the design and the two year monitoring period seems reasonable or ensure it's set up properly.
I know actual COP would vary, I just assumed I'd be able either calculate the estimate myself or find something from the manufacturer online like the published SCOP data for heating
Posted by: @lakeyI know actual COP would vary, I just assumed I'd be able either calculate the estimate myself or find something from the manufacturer online like the published SCOP data for heating
Estimating COP for DHW is complicated by the fact that the flow temperate is not constant, but rises steadily over the heating cycle.
Manufacturers will publish data that allows you to calculate COP at a given outside ambient temperature for a given flow temp. This, for example, makes it easy to look up what the COP should be when it's 7C outside and you have a flow temp of 35C.
But when heating DHW to 55C, the flow temp may start at 20C and finish at 65C, and the COP will vary (decrease) as the flow temperature increases to allow more heat to be transferred to the DHW tank. This makes it far harder to estimate the overall COP for heating the DHW tank, which probably accounts for the wildly differing values you have been quoted. Then we will have the seasonal variation due to changing outside ambient temperatures throughout the year.
I don't normally measure COP individually for DHW alone, but I'm guessing somewhere around 3 or just below is not unreasonable, but will depend on other factors such as how hot you heat the hot water, and the starting temp it has cooled to each day. I'd be surprised if it's as low as 1.75, unless you are heating it at 4am each day when it's 0C outside, and you reheat your DHW to 60C. Heating it at 2-3pm when it's warmest would be a lot more efficient.
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
@old_scientist Thank you! Right, so I shouldn't consider the manufacturers stated or estimated values when comparing my quotes, they're basically all much of a muchness... I was hoping they'd differ based on size of heating coils in the cylinder or something tangible.
Like I say, I don't think Eon has calculated it, if you download the MCS spreadsheet it's the default value. I'm just surprised they put it on the quote when they haven't thought about it... Possibly signs to steer clear of them as installers.
Posted by: @lakeyEon are proposing either a Vaillant Aurotherm plus 7kW on brackets (not a fan)
It would be a lot quieter without a fan 😉
Two other points:
1: A DHW temp of 55°C is on the high side.
By way of comparison, it I were to buy a Temperature Regulating valve to protect against scalding,
the default temperature setting would most likely be 42°C.
OK - so I've moved mine a bit higher.
But it doesn't even go as high as 55°C because that's very close to the point where the human body reflex causes you to withdraw!
2: Yes the surface area of the heat-exchange coil in a DHW tank does matter more when it's being supplied from a lower-temperature source.
Greater surface area is usually offered by tanks which have external Plate Heat Exchangers.
An installer who is aware of this is likely to be more skilled/experienced.
Save energy... recycle electrons!
@transparent thank you!
I was planning to turn it down from 55 myself and monitor the daily changeover so I could work out how best to minimise excess legionella treatment runs.
All four quotes I've received have had DHW of 55 (local heat geek, local Vaillant supplier, Eon and then another local installer heat geek accredited but I haven't gone through heat geek). That said, the first HG had my flow at 55 for heating (single room heatloss and radiator issues I made another post about).
If the efficiency of an external plate heat exchanger is greater than an internal coil, then why are the majority of installs done with manufacturers own cylinders that have a coil with ~3 - 4 m2 surface area? Are external heat exchangers significantly more expensive?
Posted by: @lakeyIf the efficiency of an external plate heat exchanger is greater than an internal coil, then why are the majority of installs done with manufacturers own cylinders that have a coil with ~3 - 4 m2 surface area? Are external heat exchangers significantly more expensive?
PHE plus UVC direct cylinder (no coil) plus pump is cheaper than most heat pump cylinders. However its 'different' and people dont like 'different'. Plus its an extra active component.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I can't really comment on pricing @lakey
I'm a self-builder rather than a heating installer.
My intention is merely to introduce you to the alternative approaches whilst you're still exploring what you want.
Mixergy are a well-known brand who offer DHW tanks with Plate Heat Exchangers.
They have a page of technical explanations which is worthwhile reading.
As for why installers take particular courses of action...
... who knows?!
If they all implemented best practice, then this Forum wouldn't need to exist 🙂
Save energy... recycle electrons!
@jamespa @transparent, Thank you both!
What do you mean by an extra active component? Surely it's the same, just the location of the heat exchanger is different? Just to clarify, that's a Plate Heat Exchanger with an Unvented Cylinder with no coil is cheaper than one with a coil typically and made to go with the heat pump? What's the direct/indirect section regarding?
Mixergy page is very useful, thank you. I'll try probing each of the installers a bit further to help in understanding the DHW side too which seems to be mainly omitted/a by-product of the rest of the installation/design.
That Mixergy internal HP & cylinder certainly looks interesting, shame it's unpriced/out of stock!
Posted by: @lakeyWhat do you mean by an extra active component? Surely it's the same, just the location of the heat exchanger is different? Just to clarify, that's a Plate Heat Exchanger with an Unvented Cylinder with no coil is cheaper than one with a coil typically and made to go with the heat pump? What's the direct/indirect section regarding?
You need an extra pump that pumps the water from the DHW tank through the heat exchanger which is external to the DHW tank. The other side of the PGE has water from the heating circuit pumped through (by the ASHP pump) it as normal.
A direct cylinder has only an immersion, An indirect cylinder has immersion plus coil. You can buy a direct unvented cylinder for about £400 and a PHW plus pump for about £400. You will struggle to get an indirect cylinder with a heat pump coil for that.
The vast majority of installers will fit a UVC with a heat pump coil. Often they will fit the manufacturers 'pre plumbed' UVC which has the diverter valve and a few other components included; this may or may not be a good fit to your circumstances and if it isnt they will have to do unnecessary plumbing to get it to work. In particular those installers that employ rookie plumbers to do the actual work will do this, because it makes the plumbing job nearly foolproof. The same installers will often fit LLHs/Buffers which you almost certainly don't want, so beware.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,208 Topics
- 48.7 K Posts
- 158 Online
- 5,868 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Radiator sizing for heat pump installation by British Gas - are these correct?
You are spot on. I don't know TBH as I don't have ...
By JamesPa , 45 minutes ago
-
RE: Heat loss calculations and how they work in conjunction with heat pump sizing
It's not necessary to be precise, it's only necessary t...
By JamesPa , 60 minutes ago
-
-
RE: Heat Pump Installers: Competence, Illusion and the Hard Truth Homeowners Must Face
@Fiona, you can also send me the report if you'd like f...
By Mars , 3 hours ago
-
RE: Ecodan Energy Monitoring Pack
Interesting. I tried very hard to monitor energy consum...
By Carpenterstation , 4 hours ago
-
RE: Daikin Octopus installation update - I saw my first defrost. 😍😂
@editor Just had my first defrost of this season. ...
By Mike Patrick , 4 hours ago
-
RE: Renewables & Heat Pumps in the News
@batpred We run our aircon in the summer not just to ke...
By dgclimatecontrol , 5 hours ago
-
RE: New Fogstar 15.5kWh upright solution
You're intending to link up a wind turbine? How would...
By Transparent , 6 hours ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
That will be producing significant losses due to phase ...
By Transparent , 21 hours ago
-
RE: Isolating the system for a planned power cut
When I said we'd need to know more about the RCD, MCB a...
By Transparent , 21 hours ago
-
Which tells us something (including possibly everything...
By cathodeRay , 23 hours ago
-
RE: Flexi-Orb Heat Pump Scheme Update: Progress, Pilots and Why This Matters for Homeowners
Thanks for sharing. Sounds promising, ISO are indepe...
By Batpred , 1 day ago
-
RE: Specifying batteries, pv solar etc using ChatGPT
I have been positively surprised when I asked it to spe...
By Batpred , 1 day ago
-
Thank you. That simultaneously answers my question abou...
By Transparent , 1 day ago