ASHP hot water vs solar PV via diverter - tank average temperature
I've noticed that my hot water cylinder temperature stays warmer for longer if it is heated using the ASHP. When I heat using the immersion, it seems the heating effect in the cylinder is not uniform, and the cylinder cools quicker once HW is drawn off, and even when not. Even drawing a small mount of hot water off drops the cylinder thermostat display several degrees, whereas this does not happen if the ASHP has heated it via the coil.
The conclusion I draw is that the 3kW immersion provides uneven water heating resulting in a lower average water temperature as the surface area contact between heating device and water is much smaller compared to a quick recovery coil. Anyone else noticed this? My cylinder is a Grant 250l pre-plumbed quick recovery.
Heating by ASHP usually takes about 3/4hr on the timer. Thermostat demand is satisfied at 50degC. The maximum heat input from the ASHP is around 8-9kW (10kW unit up to 55degC flow in HW mode)
Heating by solar PV diverter - usually about 2-3hrs based on power diverted to 3kW immersion. Thermostat inside immersion heater unit satisfied about 53degC indicated temperature on the HW cylinder stat. Thereafter, the immersion cycles on the internal thermostat.
Could well be the case. Is the ASHP coil below the immersion? Some tanks have a circulation pump that helps even out these variations
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@alleyfish I would assume that the immersion element (back up heating device) sits slightly higher up in the tank as it plays second fiddle to the heating coil, thus it only gets to heat a smaller volume of water.
Posted by: @allyfishI've noticed that my hot water cylinder temperature stays warmer for longer if it is heated using the ASHP. When I heat using the immersion, it seems the heating effect in the cylinder is not uniform, and the cylinder cools quicker once HW is drawn off, and even when not. Even drawing a small mount of hot water off drops the cylinder thermostat display several degrees, whereas this does not happen if the ASHP has heated it via the coil.
The conclusion I draw is that the 3kW immersion provides uneven water heating resulting in a lower average water temperature as the surface area contact between heating device and water is much smaller compared to a quick recovery coil. Anyone else noticed this? My cylinder is a Grant 250l pre-plumbed quick recovery.
Heating by ASHP usually takes about 3/4hr on the timer. Thermostat demand is satisfied at 50degC. The maximum heat input from the ASHP is around 8-9kW (10kW unit up to 55degC flow in HW mode)
Heating by solar PV diverter - usually about 2-3hrs based on power diverted to 3kW immersion. Thermostat inside immersion heater unit satisfied about 53degC indicated temperature on the HW cylinder stat. Thereafter, the immersion cycles on the internal thermostat.
The most probable reason is that the immersion heater is positioned higher in the hot water cylinder than the heating coil for the heat pump, therefore the immersion heater is heating less of the tank volume before being switched off by the thermostat. Also check the setting of the thermostat for the immersion heater, which should ideally be set at 60C, thereby achieving almost constant disinfection at this time of year.
@derek-m thanks. The immersion heater thermostat on Grant cylinders is pre-set to 65degC and it cycles on/off on that. However, the separate cylinder thermostat sensor, at the same elevation on the tank as the immersion, (about 1/3 height), indicates 53degC maximum. That tends to suggest the heating of the water is laterally uneven, so the effectiveness of using the immersion for anti-Legionella control may be questionable. At draw off location, top of tank, water could be 60degC+
Either way of heating, ASHP or solar PV & diverter, I've never had the water run cold on me yet. 🙂
@allyfish at this time of the year if you have copious PV you can turn the immersion stat up to maximum thereby dump the max amount of free energy into the cylinder. the greater temperature differences may then be enough to create internal circulation and warm more of the volume. after a long sunny day my whole cylinder is at 70C. but my immersion is low down, just above the bottom of the coil.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank Yup, tried that, but the tank maxes out at 55degC indicated on the cylinder. The immersion thermostat cuts in and it then cycles on that. I think that's due to immersion location vs tank thermostat sensor location, immersion can never reach thermostat set point on tank if it's above 55degC. I've definitely realised heating with the ASHP is most energy efficient, and I can export more at 15p/kWh to Octopus when simply leaving hot water charge c/o the ASHP each day.
@allyfish mm ok, there must be something else making it cut out because you should be able to go as hot as the immersions limiter, maybe grant have done something clever in your wiring that stops this. In my case being on a deemed export tariff, its better for me to keep the energy and use as much of it as possible, even if at a lower efficiency. which means for me, that an immersion heated tank (whole tank to 70) lasts a lot longer than an ASHP heated one (same tank to 50). I do not need any ASHP reheat of DHW in summer. But the key point is that you get 15p for your actual export, so in your case its better to export , then re-import at higher efficiency when you need it. Oh the intricacies of it all....
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Posted by: @iancalderbank@allyfish at this time of the year if you have copious PV you can turn the immersion stat up to maximum thereby dump the max amount of free energy into the cylinder. the greater temperature differences may then be enough to create internal circulation and warm more of the volume. after a long sunny day my whole cylinder is at 70C. but my immersion is low down, just above the bottom of the coil.
If you live in a 'hard' water area, I believe heating the hot water cylinder much above 60C can cause limescale to be deposited on the internals of the tank, so care should be exercised.
- 26 Forums
- 2,153 Topics
- 47.3 K Posts
- 76 Online
- 5,673 Members
Podcast Picks
Latest Posts
-
RE: Midea ASHP – how to set weather compensation
@pash44pump - good, you are on the case. Jaw jaw is alw...
By cathodeRay , 1 hour ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
Sufficient system volume is also essential for ensuring...
By Old_Scientist , 1 hour ago
-
RE: Boiling Mad: Exposing Radiatorgate
@rob-nezard you can see more of Drei's rad dramas here ...
By Mars , 1 hour ago
-
I have just completed my first year with my Gen 7 12Kwh...
By Broadsman , 1 hour ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
@drei I will say again that Im sorry to heat about your...
By JamesPa , 2 hours ago
-
@drei I was very sorry to read this heartbreaking story...
By GrahamF , 3 hours ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
As someone who has suffered from a Heat Pump installati...
By DREI , 13 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
1040kw Even beat June and July. Great month.
By Andris , 14 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Hope they know what they're doing regarding paint types...
By PatrickVito , 15 hours ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
I’ve also got a dual fuel Rangemaster. We originally ha...
By Majordennisbloodnok , 17 hours ago
-
RE: Octopus tariffs - a quick comparison
@tim441 I’d agree wholeheartedly with that, with 2 x Po...
By Toodles , 19 hours ago
-
RE: Electricity price predictions
@bontwoody Maybe one for @editor to consider whether a ...
By ChandyKris , 1 day ago
-
RE: is a home battery without an EV worth it?
You would think, but when I had my Powerwall 3 installe...
By Old_Scientist , 1 day ago
-
@mars That response surely deserves a nomination for Tu...
By JamesPa , 2 days ago
-
Specifying batteries, pv solar etc using ChatGPT
I thought I'd try to use ChatGPT to specify my requirem...
By Tim441 , 2 days ago
-
RE: Ecodan & MelCloud scheduling
When I interviewed Mitsubishi Electric at Installer ear...
By Mars , 2 days ago
-
RE: Rodents! A word of warning for heat pump owners
@lucia One look at that protection and the rodents will...
By Toodles , 2 days ago
-
What is the Heat Geek Guarantee?
We regularly hear from homeowners who are researching i...
By Mars , 3 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk, interesting point. I’ve not focused much on Hea...
By Mars , 2 days ago