Apologies to @toodles - thread has been well and truly hijacked.
will try not to do it again
Our experiences with solar pv, ASHP, battery, and EV: ourhomeelectric.co.uk
@steevjo That’s Ok Steevjo, fascinating reading and who would have thunked it that an ‘innocent’ question such as my Earth Bonding one would ‘spark’ off such a thread! I’m not sure I am able to say whether I should leave my gas pipe earth bond in place or not, but to be safe, I think I probably should - whether the connection now goes anywhere or not. I had a gas boiler, hob and the only other gas consuming device in the house was a radiant fire that is going out the door quite soon as it has been ousted by the air source heat pump anyway. Regards, Toodles.
Toodles, 76 years young and hoping to see 100 and make some ROI on my renewable energy investment!
Posted by: @steevjoMaybe I have found a spoiler!
I want to run this past my DNO engineering manager.
That article states
The earthing arrangement of most EESS in island mode, where the installation has a low voltage public supply connection, is therefore always TN-S.
But that's not within the province of the consumer to arrange!
Either the feed cable from the local substation has a combined earth & neutral, or else it has separate earth and neutral conductors.
That choice has already been made by the DNO.
If it's Combined (TN-C), then the consumer can't possibly use an earthing arrangement which is TN-S.
The diagrams in the article indicate that houses supplied using the TN arrangement
have their own earth stakes.
That's clearly not the case. Only a few do, and I can see those on NGED's maps.
@steevjo - I've now looked at your own house supply on the NGED mapping tool.
Neither you, nor any of your neighbours, have an earth connection to the ground.
It is provided solely by the centre tap of the substation transformer.
So that's an excellent example for me to discuss with their engineers!
Save energy... recycle electrons!
Posted by: @transparentThe diagrams in the article indicate that houses supplied using the TN arrangement
have their own earth stakes.
Only those that have batteries capable of operating when the grid is down
Posted by: @transparentI've now looked at your own house supply on the NGED mapping tool. Neither you, nor any of your neighbours, have an earth connection to the ground.
For sure I have an earth stake - added as part of the Powerwall battery installation. G99 connection was approved mid-March - presumably NGED haven't gotten around to updating the relevant record. Measured and included on the Electrical Installation certificate provided after the Powerwall installation.
Posted by: @transparentThe earthing arrangement of most EESS in island mode, where the installation has a low voltage public supply connection, is therefore always TN-S.
My reading of this is that when the grid is down the island is operating in TN-S mode - it can't rely on the incoming combined earth and neutral.
But, as I've said before, I'm just doing my best to understand - I don't really know!
Really appreciate your expert input.
Our experiences with solar pv, ASHP, battery, and EV: ourhomeelectric.co.uk
Posted by: @transparentPosted by: @transparentThe earthing arrangement of most EESS in island mode, where the installation has a low voltage public supply connection, is therefore always TN-S.
My reading of this is that when the grid is down the island is operating in TN-S mode
Hmmm. That's not what the author is claiming.
You can't implement an earthing arrangement which is always TN-S (ie based on Separate Earth & Neutral), if the feed belonging to the DNO is TN-C (Combined).
The separate earth wire isn't present in a TN-C feeder cable.
Save energy... recycle electrons!
@transparent The diagram in the article isn't saying the earthing arrangement is always TN-S, I think it's saying the earthing arrangement becomes TN-S when the grid is down and the isolators and bond relay have done their stuff. When the grid is operating normally the earthing arrangement is as shown in the connected mode diagram and is TN-C-S.
When the grid is down it could be for lots of reasons - one of which is the overhead cables to my house have been disconnected by a tree falling on them. At that point there really isn't a feed belonging to the DNO.
Our experiences with solar pv, ASHP, battery, and EV: ourhomeelectric.co.uk
Posted by: @transparent3: A gas pipe is still regarded as a gas pipe if the meter is removed.
4: To maintain earth continuity between two gas pipes which were originally connected via a meter, an earth-link is installed.
As it connects to the incoming service pipe, it is not your property and may not be disturbed or removed.
Re your earth bonding. I think the answer is in @transparent’s first reply. Leave it in place.
Our experiences with solar pv, ASHP, battery, and EV: ourhomeelectric.co.uk
@steevjo I intend to, untidy though it will be on the front of the house. There are various lengths of unused gas pipe under the floors going ‘nowhere’ - but at least they still have an earth bond! As the gas meter box disintegrated some years back and the flap was being held with a bamboo cane, I saw no reason to ask ‘someone’ (don’t know who that would be even) to replace repair the dilapidated box so it is now reduced to the back plate, piping, brackets and some heavy gauge earthing connections. A bushy plant will be grown in front of the remains of the box. Regards, Toodles.
Toodles, 76 years young and hoping to see 100 and make some ROI on my renewable energy investment!
Posted by: @steevjothe article isn't saying the earthing arrangement is always TN-S, I think it's saying the earthing arrangement becomes TN-S when the grid is down and the isolators and bond relay have done their stuff.
Erm... that's the point I'm making.
Earthing can't "become TN-S" unless there is a separate earth wire in the feed cable.
Perhaps the author is simply being too loose in terminology. Does he perhaps mean:
- the earthing becomes TN-S if the feed is TT or TN-S
- the earthing becomes TN-C if the feed is TN-C
"Becoming TN-S" implies that an earth wire suddenly appears in the feed for TN-S sites.
Either way, the phrase is confusing. We need to learn what the 'rules' are, and then come up with our own simple guideline...
... which I'm minded to be diagramatic in nature!
Let's look at this from the DNOs' viewpoint.
You only have to spend 5mins on this Forum to see that there is widespread failure to install renewable energy systems correctly.
To pick up just one technology, I have yet to read a description of a heat-pump site which actually complies with Building Regs Part-L (energy/heat).
Given this plethora of errors, how confident can we be that the installers have successfully implemented Part-P (electrical) in respect of the earthing arrangement?
Save energy... recycle electrons!
Let's pause for a moment whilst I lay out some of the issues I'm wanting to see clarified:
1: We are in the early days of seeing widespread roll-out of numerous new energy technology products which are installed in a home:
- Smart Meters
- PV Solar panel inverterss
- Heat Pumps
- EV chargers
- electricity storage batteries
If a house on a PME electricity feed installs more than one of these technologies, how may earth stakes would the home-owner expect to see?
I think the answer is 2, but that's what I want my DNO to clarify.
2: What's the situation if my Tesla Powerwall contains a double-pole isolation relay and a Neutral-earth bond relay, but my hybrid on/off-grid solar inverter does not?
Is the overall installation able to obtain consent from the DNO because the inverter's Neutral takes advantage of the N-E bond relay in the Powerwall?
And, if so, what's the situation if the Powerwall is faulty and has to be removed for a few days?
3: Since I have yet to learn of any heat pump site which fully complies with Building Regulations Part-L (heat).
What level confidence should the home-owner or Local Planning Authority have that the same installation complies with Part-P (electricity)?
If neither us consumers nor the LPA know enough to check these Building Regs notifications, why are we using taxes to pay for the service?
4: The IET guidance document we've been discussing here has a diagram which shows trips for mains appliances operating from the grid and others operating off-grid sharing the same consumer unit:
How is it OK for an electrician to work inside that unit?
Haven't we just devalued the requirement for a consumer unit to have a double-pole disconnector labelled MAIN SWITCH in red?
Save energy... recycle electrons!
@transparent Wot have I started (in my innocents, I might add!)?
Toodles, 76 years young and hoping to see 100 and make some ROI on my renewable energy investment!
A further (possible?) complication is about to rear its’ ugly head here; Virgin Media have informed us our telephone service is about to be changed and we will be provided with ‘adaptors’ to connect our telephones to our wif-fi equipment. I think that the present system has an earth connection alongside the telecommunications signal cable from the nearby street side connection box. I don’t know how this new system will work but suspect we are going to have to provide a 240v. mains supply to plug into. Might this external cable from the street side connection box also carry an ‘earth’? Regards, Toodles.
Toodles, 76 years young and hoping to see 100 and make some ROI on my renewable energy investment!
- 25 Forums
- 1,442 Topics
- 30.2 K Posts
- 12 Online
- 1,225 Members
Join Us!
Latest Posts
-
-
RE: Are Octopuses Slowing Consumer Adoption of Heat Pumps?
Yes, it is one of those two who first alerted me to the...
By IvanOpinion , 9 hours ago
-
RE: EV charger installation question – I don't want to bury the cable
The fact that the MCB is rated 16A tells us what we nee...
By Transparent , 10 hours ago
-
RE: Are You Getting the Most Out of Your Renewable Energy?
Thanks, @editor. Ideally it’d be someone who would li...
By Majordennisbloodnok , 12 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
Unless adequately controlled it could devour your bank ...
By Derek M , 12 hours ago
-
RE: Effect of buffer tank or volumiser on heat pump system
I think that you will find that the best location for a...
By Derek M , 12 hours ago
-
RE: ASHP Commissioning: What Questions Should I Ask the Installer?
@derek-m thanks - will look out for the point regarding...
By Declan90 , 1 day ago
-
RE: Noise problems with newly installed Samsung 8kW ASHP
@editor @kenbone Thanks, I would be very interested ...
By Elton , 1 day ago
-
RE: No-code, plug-and-play monitoring for your heat pump
This is all a bit too frequentist for my liking. The pr...
By scrchngwsl , 1 day ago
-
Relax with 4K drone footage of lawn mowing to a smooth Motown tune
Sending out some chilled weekend vibes to everyone. Lis...
By Mars , 2 days ago
-
RE: Incorrect Billing of Customers with a Smart Meter
The starting point of that discussion on Camelot-Forum ...
By Transparent , 2 days ago
-
Share Your Experiences with Heat Pump Manufacturer Support
Have you ever reached out to your air source heat pump ...
By Mars , 2 days ago
-
RE: Is this a bad installation and is there something wrong with my Samsung heat pump?
@ant87 thanks for that.
By David999 , 3 days ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
I might change my mind again, but I'm currently unlikel...
By IvanOpinion , 3 days ago
-
RE: Samsung ASHP scheduling help
@elgreco69 worth reading the GitHub here as that will a...
By morh , 3 days ago
-
RE: ASHP sizing - value of Heat Transfer Coefficient
@toodles Thanks for the explanation I get it now as I h...
By Jancold , 3 days ago
-
RE: Questions about yearly heat pump maintenance
For the installer, I believe servicing and maintenance ...
By Majordennisbloodnok , 3 days ago
-
RE: Rate the quality of your heat pump design and installation
@retrorich It is very worrying that any of this should ...
By Toodles , 3 days ago
-
RE: Spacing for roof fixing bolts ?
There is another consideration...but alas this doesn't ...
By Transparent , 4 days ago
-
RE: Air source heat pumps and noise
Yes, but when they go wrong things get really sticky. D...
By Majordennisbloodnok , 4 days ago
Heat Pump Humour
Latest Topics
-
By David999 8 hours ago
-
Spacing for roof fixing bolts ?
By heat-pump-newbie 6 days ago
-
ASHP sizing - value of Heat Transfer Coefficient
By jamesw 6 days ago
-
Incorrect Billing of Customers with a Smart Meter
By KoRWraith 1 week ago
-
Home energy storage & battery register
By Mars 1 week ago