There will still be a substation number plate on that pole.
Every pole on the grid is numbered, even if it has no transformer and no wires currently 'live' !
Save energy... recycle electrons!
@transparent the only number I can see is RSFCCA1
Our experiences with solar pv, ASHP, battery, and EV: ourhomeelectric.co.uk
Ah yes - I can see it:
Rear of Steevjo's Field - Code? - Couldn't Arrange 1 😉
So what's the number on the next pole?
Save energy... recycle electrons!
@transparent RSF CC13 is next
Our experiences with solar pv, ASHP, battery, and EV: ourhomeelectric.co.uk
I've run those pole numbers (and variations thereof) through NGEDs entire database of substations and that pattern of naming doesn't occur @steevjo
So I've emailed a senior NGED engineering manager to ask for assistance.
It's possible that the asset-number labels for those poles and transformer haven't been applied for some reason.
The labels you're seeing could just as easily refer to something else.
For example, CCA (Copper Covered Aluminium) is a type of cable commonly used for overhead wires in rural locations.
Save energy... recycle electrons!
Just a bit more re powerwall earthing…
The powerwall gateway includes a breaker to disconnect house live and neutral from incoming when there is a power outage - as required by regs.
it also includes a normally open breaker which closes during a power outage to restore the earth neutral bonding which has gone because the neutral has disconnected…
only the earth wire it connects to goes straight to the incoming PEN cable a few feet away - so can’t really see how neutral is still disconnected.
you can see all this in the diagram posted earlier.
NGED had this diagram (actually a similar diagram that better represents our house but with the same earthing arrangements) as part of the G99 application which was approved.
I admit I’m completely confused.
Our experiences with solar pv, ASHP, battery, and EV: ourhomeelectric.co.uk
@steevjo indeed. there are some photos of mine in that speakev thread, that I was able to take at one time when the sparks were here, showing the earths, they're all commoned - house, batteries, earth rod, DNO cable
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Let me provide the background detail which shows the electricity supply used for the majority of the UK population.
Protective Multiple Earth (PME) derives from the way in which local substation transformers are designed.
The 11kV 3-phase supply connects to the three primary coils of the transformer in a Delta pattern.
The Secondary windings are in a Wye pattern.
This not only provides the optimal efficiency for energy transfer using magnetic flux, but the centre-tap becomes the Neutral for houses which are connected to single-phase feeds.
That Neutral is connected to earth (ground) at the transformer.
It can therefore be used to provide an 'earth' to the houses.
In practice it looks more like this...
... where there is local substation called East Village.
This map has been 'anonymised'.
East Village doesn't actually exist, nor is there a location with precisely this layout for the electricity supply.
The 11kV supply to the substation is marked in red.
It has one 440v Feed (blue) which divides into two.
The safety earth for the metal transformer itself isn't directly beneath it, but instead about 40m north.
I've circled that in light red.
The 440v 3-phase feed also has four points at which it is tied to earth.
Those are circled in green.
One of those points, closest to the transformer, is the one that creates the zero-volts reference for the Neutral.
The three other earth points are decided by the DNO according to local circumstances.
They are what makes this Feed a Protective Multiple Earth.
Each pole will have a label "PME", together with the pole number, such as 18/1525-1
If the house I've coloured in purple has a heat pump, EV charge-point or solar panels installed, there may be a regulation which requires the equipment to have its own earth stake.
But that local earth isn't the same as the earth provided by the DNO, which is derived from the Neutral feed.
Installers may not just add further earth points to the DNO's local supply.
Save energy... recycle electrons!
Thanks for the background @Transparent
Posted by: @transparentInstallers may not just add further earth points to the DNO's local supply.
But they clearly do.
To be honest I can see little difference between an earth spike and earth bonding to an incoming conductor. I know the purpose is different but both are wiring a piece of metal coming out of the ground to the DNO provided earth.
I absolutely understand that I don't understand enough of the details/know the rules. One option is I just trust the installers/NGED approval process and forget about it...
... but it's hard when what is there right now makes no sense to me.
Our experiences with solar pv, ASHP, battery, and EV: ourhomeelectric.co.uk
I may not appear to be responding directly to what you post @steevjo
but I am reading every point you've written to ensure that I cover it within my ongoing explanations. 🙂
EV charge points aren't installed by any electrician.
The firms that undertake this work have additional training and certification.
There are a number of safety components and practices which they must ensure are being incorporated.
The main methods of installing an EV charger are these:
Notice the change in earthing arrangement, depending on whether the house earth is provided by the DNO (PME) or by using a ground-stake.
In each case the charger is earthed, and the householder can see a physical copper rod inserted into the ground at their house.
This makes it tricky for less-technical people to know whether it has been done correctly.
I'm now going to 'zoom in' on the PME version, on the left of the above diagram:
This more detailed view shows anti-lightning surge suppression for the EV charger.
It's separate from whatever surge suppressors may or may not be already installed in the house.
The new pair of suppression devices prevent the 'ground wave' created by a nearby lightning strike from entering the house.
The second detail to notice is an RCD Type B in the consumer unit, next to the trip (MCB) which supplies the EV charger.
Type-B Residual Current Devices are the highest level of safety protection.
It's a double-pole device, costing about £250
It will interrupt the supply in case of fault currents occurring
- on the AC sine wave of the mains supply
- on any DC component which is induced by the charger
- on any high-frequency signal imposed on the mains supply by the charger
- on any pulsed or intermittent current imbalance
Some EV installers fit Type-A RCD units, which are a lot cheaper and easy to source.
This chart explains the four categories of 'earth leakage' protection:
So why is the earthing arrangement different for properties served by a PME supply?
This has to do with the possibility of damage to the (underground) feed from the substation which results in the Neutral being cut.
Remember that a house with PME has the earth provided by the wire being linked to Neutral at the 100A Service Fuse.
If the EV charger is incorrectly installed and uses the household earth, then it would look like this:
The EV charger still passes the LIVE to the car.
The return current passes back through the blue/neutral wire to the charger and on to the consumer unit, but can't return to the substation transformer through the DNO's underground cable.
Instead, it crosses the link to the earth wire and goes back to the car.
That causes the external metalwork of the car to rise to the same voltage as the LIVE. 😮
Even if the EV charger were also to have its own earth stake (which it shouldn't), that doesn't solve the problem:
The return current will indeed now find a path back to the transformer through the ground, but there is a high resistance via that route.
Consequently the metalwork of the car tends to 'float' at around 50-120v.
That's still enough to kill you.
When considering the earthing arrangement you have had installed, it is insufficient to consider that "it works, so it must be OK".
The whole point of a safety mechanism is to assess "how does it operate when there is a dangerous fault?"
Save energy... recycle electrons!
@transparent Thanks for the detailed explanation.
I looked into EV chargepoint earthing a couple of years ago when ours was installed. At the time there was a bit of debate about 'unicorn' devices that would enable a charger to detect neutral and earth problems so they could safely be installed in PME systems using the house earth without needing their own earth spike.
Our pod point has such a system - there's a decent write up here: https://pod-point.com/electric-car-news/earth-rod-details Interestingly (I'm sad) when the powerwall was installed and the earth spike added the pod point refused to charge - I'm assuming it saw the new earth spike as some sort of earth problem. Fixed by speaking to Pod point who changed some configuration remotely.
Completely understand your point about "how does it operate when there is a dangerous fault?"
Looking forward to the next instalment 😀
Our experiences with solar pv, ASHP, battery, and EV: ourhomeelectric.co.uk
Posted by: @steevjoLooking forward to the next instalment 😀
Maybe I have found a spoiler!
I’m thinking the isolator in the neutral allows the system to be safely switched to island mode and back again. Once in island mode it’s not really doing anything.
this is a sort of glimpse through the mist for me (although it seems to confirm system is installed correctly!).
A proper explanation or correction would be great!
Our experiences with solar pv, ASHP, battery, and EV: ourhomeelectric.co.uk
- 25 Forums
- 1,513 Topics
- 31.8 K Posts
- 26 Online
- 1,283 Members
Join Us!
Latest Posts
-
RE: Additional Battery v Wind Turbine v Ripple
I should add, being an investment, the value of your in...
By Old_Scientist , 5 hours ago
-
RE: Ecodan - flow rates, sensors, settings
Achieving an accurate flow measurement is probably the ...
By Derek M , 8 hours ago
-
RE: Ecodan ASHP - How to optimise my set up?
Again, thank you for another thorough post, @derek-m - ...
By rhh2348 , 10 hours ago
-
RE: Delivering a smart and secure electricity system: government consultation
@Transparent.Now that I am represented by a new MP I th...
By IanMK13 , 12 hours ago
-
RE: Vaillant aroTHERM plus not level or flat - what base is best under an external unit?
Similar thread here
By Johnmo , 13 hours ago
-
RE: VDI 2035 heating water specification
Been looking and it seems a good little project. Ever...
By Johnmo , 2 days ago
-
RE: Do I accept an ASHP and Solar Panel retrofit under the HUG 2 scheme?
Will do. I'm currently waiting for another survey / vis...
By dssr , 2 days ago
-
The company that did the borehole were expecting us to ...
By Johnmo , 2 days ago
-
-
RE: The Misquote That Ruined the Heating Industry
@abernyte manufacturer training is pretty average. They...
By Mars , 2 days ago
-
-
RE: ECO4 Scheme and EPC ratings
@mellow Thanks. Given there is a scheme requirement to ...
By Old_Scientist , 3 days ago
-
RE: Do I just go with the lowest quote for my heat pump?
@jancold To me its a no-brainer then, a max 40C flow te...
By bontwoody , 3 days ago
-
-
RE: Heat Pump Books Beginners – Bodge Buster & From Zero To Heat Pump Hero
@editor Presumably he had some good weather Compensatio...
By Toodles , 4 days ago
-
RE: New Vaillant 7kW aroTherm ASHP or oil boiler dilemma/decision??
Storage capacity really is dependent on storage tempera...
By Johnmo , 4 days ago
-
RE: HP Cycling, Expected or Undesirable
Just a little update. I ordered a longer shielded twin ...
By bontwoody , 4 days ago
-
RE: Domestic hot water timer doing crazy things on my Grant Aerona3 10kW air source heat pump
Thanks @allyfish for the pics and info. Spoke to the in...
By Mellow , 4 days ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
It's been a busy day for calls and emails from Aira. I ...
By MikeH , 4 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Hmm. A bit of a nuanced answer, methinks. As I've alr...
By Majordennisbloodnok , 4 days ago
Latest Topics
-
Ecodan - flow rates, sensors, settings
By rhh2348 11 hours ago
-
Replacing mains water with well water
By Johnmo 2 days ago
-
Additional Battery v Wind Turbine v Ripple
By bontwoody 2 days ago
-
By jamespipe 3 days ago
-
VDI 2035 heating water specification
By Johnmo 3 days ago
-
Do I just go with the lowest quote for my heat pump?
By Jancold 5 days ago
-
The Misquote That Ruined the Heating Industry
By Alec Morrow 6 days ago
-
Battery Storage Wiring Gauge Question
By Puff 6 days ago
Members Online
No online members at the moment