You can balance a buffer by simply having two flow controller installed either side of it. One should have already been installed on the ashp side, ...
@jamespa thank you for that, I never understand the full maths behind it all and things like that. I just did it on my findings. We did try on a cou...
@jamespa I'm very much in the anti buffer side and looking to revamp my system over summer to see about removing/replacing it in 2026. So I'm going to...
No probs. Looking at screen shot the system is running 55° at -2c to 54° at +16c This means this system is set up more like just using a set flow r...
@jamespa I was more concerned about the HP in the winter. I only run my HP for about 6-8 hrs a day and not overnight. So when the temp outside gets ...
@iraknic At 2 cubic meter/h that is around 33l/min, so the two pumps look like they are much the same flow. But when you stop a zone then flow...
@jamespa most HP recycle water around the system when its below say 4° but not supplying heat. To stop the water freezing. How does that effect the ...
@editor Even though we can see a reason to remove them, there's also a reason to keep then. I've found that they can help greatly in reducing defros...
If the pipe work is connected as per your diagram, then you need to get the installer back and make them change it. I would suspect it is more a flo...
Thank you @mikefl that was what I was looking for. No problems with wires (I hope), as we put two sets out when it was installed, so just need to us...
Okay cheers, looking forward to reading more as you progress
Okay understand now. Even though we get defrosting cycles we could reduce them by running the HP at a much lower flow temp. At present we try to run b...
- 26 Forums
- 2,104 Topics
- 46.3 K Posts
- 111 Online
- 3,393 Members
Join Us!
Latest Posts
-
RE: Ecodan consuming 100kwh per day in new build!!!
The information in this site is very helpful when consi...
By skyefarmer , 5 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist I found the switching between tariff jus...
By Toodles , 15 hours ago
-
RE: Plug and play solar. Thoughts?
Have a read of my previous posts on so-called Balcony S...
By Lucia , 18 hours ago
-
@editor @bart Hi, I can see a few problems with your in...
By Brendon Uys , 21 hours ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
"To tell you the truth, I don't know if HAL is homicida...
By Scalextrix , 23 hours ago
-
RE: Location of hot water isolation valve on cylinder
@rossowheels if you isolate the water supply in it will...
By ASHP-BOBBA , 2 days ago
-
The Importance of Radiator Balancing for Efficient Heating: Introducing the Flow Regulating Valve
It’s fascinating to watch how low-temperature heating i...
By Mars , 2 days ago
-
RE: Servicing Hitachi HP in rural Somerset
I'd give GreenGenUK a call or email them: sales@greenge...
By Mars , 2 days ago
-
RE: Heating coming on when not required
I played with a max heating temp but there is a world o...
By JamesPa , 3 days ago
-
RE: Pressure drop Primary circuit
I've always regarded topping up heating systems as my j...
By JamesPa , 3 days ago
-
RE: Heat pump solutions and/or installer recommendations for France
I’d travel to France for work if you were struggling wi...
By Damon Blakemore , 3 days ago
-
RE: 5 Star Service from Havenwise
That's always a danger with any new good idea, @morgan....
By Majordennisbloodnok , 3 days ago
-
Have your say in the Renewable Heating Hub Awards
It’s time to celebrate the best (and call out the worst...
By Mars , 4 days ago
-
-
RE: Mitsubishi cycling while on chilled water output
@iaack yes there's no denying that cold air sinks! I s...
By downfield , 4 days ago
-
RE: Weather compensated secondary circuits with Biomass
@andycoo that flooring sounds ideal. Extra volume is ...
By Sune , 4 days ago