Reply
RE: The good, the bad and the not that great – my heat pump installation

OK. Its good to hear you want to get it working and you do appear to have a good set of parts, so its a case of getting them set up a bit better. H...

6 months ago
Reply
RE: The good, the bad and the not that great – my heat pump installation

Yes it will be protecting itself from freezing. You cant really stop this unless you decommission it completely. The question that you need to answe...

6 months ago
Reply
RE: The good, the bad and the not that great – my heat pump installation

This is definitely a plumbing 'problem' not a heat pump problem, although it is linked to your heat pump installation. The pressure in the hot circui...

6 months ago
Reply
RE: Ideal Logic 10kW Heat Pump Pipes Noisy and Very Expensive to Run

The ideal r290s are Midea clones (but with ideal controls) made I believe in china. To the best of my knowledge Mitsubishi and Vaillant assemble hea...

6 months ago
Reply
RE: Large ASHP recommendations for listed house

Underfloor heating? - given you are putting insulation in between the floors its got to be worth considering although LB constraints may make it impos...

7 months ago
Reply
RE: Large ASHP recommendations for listed house

The MCS guidelines specify a certain volume per bedroom (I cant remember exactly what) so they will likely have got 400l from that. The penalty for...

7 months ago
Reply
RE: Ideal Logic 10kW Heat Pump Pipes Noisy and Very Expensive to Run

@ajbevster If it's fully pushed in yes, better if it also had some tape over the hole to ensure that circulating air didn't cool down the sensor. ...

7 months ago
Reply
RE: Large ASHP recommendations for listed house

I should clarify that it's possible, given size and lack of insulation, that 80kW could be right, but not 25kW. For me this is the red flag that unde...

7 months ago
Reply
RE: Ideal Logic 10kW Heat Pump Pipes Noisy and Very Expensive to Run

Yes, or not properly pushed into the pocket on the side of the cylinder.

7 months ago