RE: Twin 10kw Grant Aerona Volumiser Tanks using lots of power

I still am not sure you get the point of volumiser tanks. They add water volume to the system. They don't need power. Grant and others take the op...

6 months ago
Reply
RE: Heat loss calculators and spread sheets

Are you saying your design flow temperature (at the lowest oat) for the ashp system is 55C? Fans on fancoils do run constantly, but with a decent...

6 months ago
Reply
RE: Heat loss calculators and spread sheets

I'm sorry but I don't understand your maths. If you need 2.4-3kW output then you will need a radiator rated for about 6kW at 50C DT. That's a very bi...

6 months ago
Reply
RE: Fujitsu Waterstage WOYG160LJL Air Source Heat Pump

I think that's very likely. Thus if you set all external controls to be permanently on you should be able to optimise the wc curve to the lowest poss...

6 months ago
Reply
RE: Twin 10kw Grant Aerona Volumiser Tanks using lots of power

Please post back on how you get on. You need to give some thought to those ufh loops, they can't be allowed to suck energy out during dhw cycle. Re...

6 months ago
Reply
RE: Heat loss calculators and spread sheets

They will run without a fan but output is then less than a radiator of same size. I thought you were struggling to fit a passive radiator in hence w...

6 months ago
Reply
RE: Heat loss calculators and spread sheets

Could a fan coil be suitable. I had a similar problem which was solved with a fan coil.

6 months ago
Reply
RE: Twin 10kw Grant Aerona Volumiser Tanks using lots of power

Ok that's clearer. It's a pity about the manifold pumps, they effectively stop the ashp having the control it needs to make sure everything works pr...

6 months ago
Reply
RE: Twin 10kw Grant Aerona Volumiser Tanks using lots of power

Thanks, thats helpful. There seems to be a circular path around the upper volumiser, is this correct (it could be, perhaps the upper heat pump is the...

6 months ago
Reply
RE: New to world of ASHPs: Ideal Logic Air Monobloc heat pump 8kW questions

Only to the extent that the heat has been produced at a lower COP than your space heating. But as you are probably talking 1-2kWh max per day, who ca...

6 months ago
Reply
Reply
RE: Fujitsu Waterstage WOYG160LJL Air Source Heat Pump

This is indeed ambiguous!. One would expect, since this is in a section called 'room influence' that it means ambient in, but it is unclear. the ba...