Activity
 
Notifications
Clear all
JamesPa
@jamespa
Moderator
Illustrious Member
Joined: Apr 3, 2023
Last seen: Sep 11, 2025
Topics: 17 / Replies: 2824
Reply
RE: Say hello and introduce yourself

Glad to hear that you are pleased with the heating of your house and generally happy. It may well be that there is scope for a bit of optimisation of...

7 months ago
Reply
RE: How To Balance Radiators & the Role of the Lockshield Valve: A Homeowner's Guide

Similar really, rads 5C lower than output of ASHP = 10-15% penalty. Difference of 2C on the return possibly a measurement error. I think @toodles mig...

7 months ago
Reply
RE: How To Balance Radiators & the Role of the Lockshield Valve: A Homeowner's Guide

OK, so 41.9 in from heat pump, 37.1 out to rads, drop of 5C = 10-15% efficiency penalty. Not sure how the return to the heat pump is higher than the ...

7 months ago
Reply
RE: How To Balance Radiators & the Role of the Lockshield Valve: A Homeowner's Guide

To the final question yes. If the HP is delivering 43 and through to rads its 37, then you are losing about 12-20% in efficiency as a result of the...

7 months ago
Reply
RE: Just one room not reaching desired temperature

If the rads are sized correctly then I would normally say that it could (most probably, but not certainly, is) be an emitter balancing issue. However...

7 months ago
Reply
RE: How To Balance Radiators & the Role of the Lockshield Valve: A Homeowner's Guide

OK, the most interesting thing is the temperature drop across the buffer measured between flow from HP and flow to radiators. I dont think I can see ...

7 months ago
Reply
RE: 4 port buffer tank connections

With a very low loss house running at very low flow temperatures its true that the reduction in efficiency from running at the only slightly higher fl...

7 months ago
Reply
RE: 4 port buffer tank connections

FWIW my boiler did the same. Sometimes I heard it coming on at 3am in the morning. It heated as well during these forced 'on' periods. But yes, if...

7 months ago
Reply
RE: Mitsubishi Ecodan 8.5kW Monobloc (FTC5) Defrost Mode

Yuk (comment on the LLH) In this case surely the secondary must be kept running during defrost, otherwise the only water volume available for defros...

7 months ago
Reply
RE: How To Balance Radiators & the Role of the Lockshield Valve: A Homeowner's Guide

Good luck on the modbus. I think you are in with a good chance, these units are based on aircon units used in commercial settings where modbus will l...

7 months ago
Reply
RE: Roughly confirming ASHP sizing using existing heat data

... and the value for air changes. Judging by posts on this forum and elsewhere, and comments from a handful of some more independently thinking ins...

7 months ago
Reply
RE: 4 port buffer tank connections

Probably not a lot unless you have UFH, although there is a risk of condensation on the pipes When ASHPs are used for cooling one problem that occur...

7 months ago
Page 101 / 238
Share:

Join Us!

Latest Posts

Click to access the login or register cheese
x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
ShieldPRO