RE: Another 17kw Grant Heat Pump - Advice Needed!

@bn06amp It takes approximately 3.5kWh of energy to raise the temperature of 300l by 10C.

3 years ago
Reply
RE: Clarification needed for Ecodan ASHP settings

It may be useful if I explain a few things about how heat pump systems function and then you can decide how best to operate yours. The heat pump gath...

3 years ago
Reply
RE: 17kw Grant Aerona heat pump not performing

Did you get warm water to the cold radiator? If not then remove the TRV actuator head and ensure that the valve plunger moves freely.

3 years ago
Reply
RE: Another 17kw Grant Heat Pump - Advice Needed!

@bn06amp If you could post the heat loss calculations that would be highly useful, since the data should indicate how much heat energy is required b...

3 years ago
Reply
RE: Another 17kw Grant Heat Pump - Advice Needed!

Hi Ash, welcome to the forum. You should find that the energy consumption will start to reduce as your home gets up to temperature. What model is ...

3 years ago
Reply
RE: 17kw Grant Aerona heat pump not performing

@soniks Now try closing the TRV's on the warmer radiators for a period of time to see if more water is pushed through the colder radiators. Try blee...

3 years ago
Reply
RE: Mitsubishi ecodan settings

Hi Mars, It is the internals of the valve that are the important factor, not who manufactures it. The flow rate through a valve is limited by the sm...

3 years ago
Reply
RE: 17kw Grant Aerona heat pump not performing

I would suggest that you start by checking that both valves on your 1.6m K2 are fully open. If they are then try to trace back along the pipework for ...

3 years ago
Reply
RE: Yearly maintenance

I remember watching an American video some time ago, where the Technician measured either temperatures, pressures or both on the heat pump unit, that ...

3 years ago
Reply
RE: Mitsubishi ecodan settings

Mars is correct, you don't need to panic, systems can often be improved without ripping everything out and starting again. It is often a matter of loc...

3 years ago
Reply
RE: 17kw Grant Aerona heat pump not performing

The graph for October would appear to show that your heat pump was running for a period of time and producing more energy than that required to satisf...

3 years ago
Reply
RE: 17kw Grant Aerona heat pump not performing

During the defrost cycle the compressor probably runs at full speed to complete the defrost as quickly as possible.

3 years ago