If you don't mind stating, who was your installer?
Why didn't you replace the old GSHP with a new GSHP, since they are more efficient? I would suggest that you read through the manual, particularly t...
@davew The 4:00am graph does show 2 cycles prior to hot water production. The heat demand at 4:00am will probably be slightly greater, since the ext...
As a test, try setting your system in fixed LWT mode with a setting of 29C or 30C to see if you still experience cycling. As I am sure that you are ...
Call me an old cynic, but I am rapidly becoming suspicious of companies with 'green' or 'greener' in their name, since I suspect they have merely jump...
To my knowledge, expansion vessels don't normally get reported to the noise abatement society, can you describe the noise? If it is a gurgling or tink...
If your thermostats are of the on - off variety, they do not send a temperature measurement to the Ecodan controller. The Ecodan controller does con...
Now that I am back with the 'living', so that there is no confusion, could you clarify what is meant by 201 & 202 and to which manual you refer. I...
I'm afraid that I have to go mow the grass (she who must be obeyed has spoken), so I will formulate a reply shortly.
I would suggest that you consider adjusting your weather compensation settings and then set your hive to 1C or 2C above the desired temperature. Doing...
We have had output from our solar PV system every day since it was installed over 10 years ago. I think that the lowest daily production was 30Wh and ...
I would suggest looking at all the settings, particularly the ones in installer mode. If you are not certain if any settings are correctly optimised t...
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 17 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
@jamespa thanks, I appreciate the offer. For n...
By DREI , 2 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
When I tried to balance my rads I ended up causing an a...
By Grantmethestrength , 4 hours ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
@transparent what I don't understand about these "rogue...
By Scalextrix , 5 hours ago
-
RE: Who’s Caved and Switched the Heating On Already?
I have 3 women in the house, 2 little ones, so my heati...
By DREI , 7 hours ago
-
@damon thanks. I will do as you suggest. Hopefully I wi...
By bontwoody , 8 hours ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 1 day ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@dgclimatecontrol I attach the responses from 2 potenti...
By pash44pump , 1 day ago
-
RE: Midea ASHP – how to set weather compensation
Mostly, I think, but with some caveats. I set the TI...
By cathodeRay , 1 day ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 2 days ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
I realise im overdue an update on my situation. first...
By Cleardene-ashp , 2 days ago
-
RE: Replacing Worcester oil boiler with an ASHP
@toodles thanks. I was told by the engineer that this h...
By JulianC , 2 days ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
A week later, I'm finally picking up this comment... ...
By Transparent , 2 days ago
-
RE: COP is not the only measure of efficiency
We keep all our TRVs fully open using the whole house a...
By Old_Scientist , 3 days ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
I am pleased to say at 4pm today we have added another ...
By ASHP-BOBBA , 3 days ago
-
RE: Renewables & Heat Pumps in the News
To unpack this a little.... 1) how many of us in this...
By Lucia , 4 days ago
-
RE: Vaillant aroTherm Plus 10kW thoughts?
@realevil the fans and fan speed / coil size (height, w...
By ASHP-BOBBA , 4 days ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@morgan this can just be done by your sepecilist when t...
By ASHP-BOBBA , 4 days ago
-
RE: Anyone still weathering it out with Agile?
@toodles I guess it all comes down to import averages. ...
By Tim441 , 4 days ago
-
RE: 300 Liter Tank - Do I have to heat it all?
The size of DHW tank affects the anti-legionella cycle....
By Transparent , 4 days ago