@lucia With regard to the bucket analogy, think of your home as a bucket with lots of pin holes covering the whole bucket, with the bucket placed in...
@johnmo You are perfectly correct that what I have previously described as the upper 'switch off' limit and the lower 'switch on' limit can indeed a...
@bontwoody Thank you.
I would be interested to see the results.
This is what is so annoying about the present society in which we live, in that one cannot always trust people to do what you have paid them to do.
I would agree that increasing the LWT is likely to reduce the instantaneous COP value when the heat pump is operating in continuous mode, but it may ...
@lucia The better option would be to get the cavity filled correctly.
One way to try to reduce cycling frequency would be to raise the Leaving Water Temperature (LWT) by means of the Weather Compensation (WC) offset. Thi...
@toodles Page 20 of the attached manual provides a detailed breakdown of the model number.
Most heat pumps will cycle when the OAT is 10ºC or above, the frequency is cycling may be dependent upon quite a number of parameters. If I have tim...
Does the attached manual cover the model in question?
I think the best that can be obtained from assessment is the approximate heat loss, since the actual heat loss will vary with changing weather conditi...
- 26 Forums
- 2,104 Topics
- 46.3 K Posts
- 84 Online
- 3,393 Members
Join Us!
Latest Posts
-
RE: Location of hot water isolation valve on cylinder
@transparent Thank you so much and very helpful. Earlie...
By rossowheels , 2 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@toodles Indeed. On a tariff such as IOF where import a...
By Old_Scientist , 3 hours ago
-
RE: Ecodan consuming 100kwh per day in new build!!!
It does indeed look like that, @skyefarmer. There is ...
By Majordennisbloodnok , 9 hours ago
-
RE: Plug and play solar. Thoughts?
Have a read of my previous posts on so-called Balcony S...
By Lucia , 1 day ago
-
@editor @bart Hi, I can see a few problems with your in...
By Brendon Uys , 1 day ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
"To tell you the truth, I don't know if HAL is homicida...
By Scalextrix , 1 day ago
-
The Importance of Radiator Balancing for Efficient Heating: Introducing the Flow Regulating Valve
It’s fascinating to watch how low-temperature heating i...
By Mars , 2 days ago
-
RE: Servicing Hitachi HP in rural Somerset
I'd give GreenGenUK a call or email them: sales@greenge...
By Mars , 3 days ago
-
RE: Heating coming on when not required
I played with a max heating temp but there is a world o...
By JamesPa , 3 days ago
-
RE: Pressure drop Primary circuit
I've always regarded topping up heating systems as my j...
By JamesPa , 3 days ago
-
RE: Heat pump solutions and/or installer recommendations for France
I’d travel to France for work if you were struggling wi...
By Damon Blakemore , 3 days ago
-
RE: 5 Star Service from Havenwise
That's always a danger with any new good idea, @morgan....
By Majordennisbloodnok , 4 days ago
-
Have your say in the Renewable Heating Hub Awards
It’s time to celebrate the best (and call out the worst...
By Mars , 4 days ago
-
-
RE: Mitsubishi cycling while on chilled water output
@iaack yes there's no denying that cold air sinks! I s...
By downfield , 4 days ago
-
RE: Weather compensated secondary circuits with Biomass
@andycoo that flooring sounds ideal. Extra volume is ...
By Sune , 4 days ago
Members Online
No online members at the moment