Skirting board radiators
Has anyone tried installing these or similar? They claim many '000s installed, with a version optimal for heat pump system
https://www.discreteheat.com/thermaskirt/products-and-information/overview.aspx
Posted by: @neilhHas anyone tried installing these or similar? They claim many '000s installed, with a version optimal for heat pump system
https://www.discreteheat.com/thermaskirt/products-and-information/overview.aspx
Hi Neil,
An interesting concept.
I noticed from their performance data that they are only showing figures for water flow temperatures of 45C, 50C and 55C, which is the inefficient range for operating an ASHP.
Based on their data you would require the following lengths of ThermaSkirt to replace a 1200mm x 600mm radiator, to achieve the same heat output.
Deco BM2 15.4m for type 22 (double panel) and 22.6m for type 33 (triple panel)
Deco BM3 10.4m for type 22 (double panel) and 15.2m for type 33 (triple panel)
It would be interesting to see how they perform at lower water flow temperatures.
Since ASHP's operate at their best efficiency at the lowest water flow temperature that meets the heat demand, it is important to have heat emitters with the greatest output at a given water flow temperature. The larger the area of the heat emitters, the lower the water flow temperature would need to be.
How do ThermaSkirt compare in price to a standard radiator or UFH?
@derek-m Ah yes. Though in princple the lengths are probably not a problem. I'm just in exploratory ideas phase at the moment so no prices sought. I still like in-wall idea, especially the 3Thermo design (if I can get some decent technical details). Perhaps different solutions for different rooms, given good zone control system.
Hi Neil,
One of the things I enjoy about the forum, is that there are people like yourself who just don't accept the norm, but look for alternatives that may or may not be an improvement. For much of my career I have been expanding the envelope to find solutions to long standing problems, just because something has been done a certain way for many years does not mean that it cannot be improved.
Posted by: @neilhPosted by: @derek-mjust because something has been down a certain way for many years does not mean that it cannot be improved.
Else we'd be sitting round a fire in a cave !
Don't knock caves, I'm in my 'man cave' right now.
I have just had a look at the 3Thermo system that you highlighted, it also looks very interesting. They specify an energy output of 250W/m2, but don't state what the water temperature would need to be to provide that output. I wonder if it could be installed over existing plaster or whether the plaster would need to be removed and then the wall re-plastered after installation.
I suppose in an ideal world we would have a system that has underfloor heating, wall heating and skirting heating, all supplied by a heat pump that is running at 25C with an outside air temperature of -10C.
- 22 Forums
- 2,037 Topics
- 44.4 K Posts
- 26 Online
- 3,250 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Help with understanding my Mitsubishi Ecodan air source heat pump
@patch. I understand that this indicates the ASHP is ...
By Morgan , 1 hour ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk, in terms of ballpark pricing, if we assume a st...
By Mars , 2 hours ago
-
RE: Air Source Heat Pump - Side Alley Suitability
@jamespa I used an assumed indoor temperature of 18C. I...
By Ad3628 , 15 hours ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
That’s interesting, but obviously concerning also…. Do ...
By SUNandAIR , 15 hours ago
-
RE: In the middle of an ASHP installation - a few questions (and issues)
Thank you @robs - that very useful data. The issue wa...
By Transparent , 19 hours ago
-
RE: The Rise and Fall of Europe’s Most Generous Green Subsidy
@editor Attached images of external insulation. Think...
By Dwynwen , 1 day ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Thermal Off's
@trebor12345 The Auto function is supposed to adapt au...
By Heatgeek , 2 days ago
-
RE: The Great British Heat Pump Quiz
@allyfish thanks for the feedback and glad it was fun! ...
By Mars , 2 days ago
-
RE: help sizing rads based on room by room heat loss
If its 1988W at DT 50, which is how most radiators are ...
By JamesPa , 2 days ago
-
RE: Career change – entering the world of heating and heat pumps
@editor Mars, thank you. That's along the routes I was ...
By Lakey , 2 days ago
-
@editor thanks Mars, it's a rare occasion I'm looking f...
By big_si , 2 days ago
-
RE: Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW
@ashp-bobba and @jamespa - thank you both for all your ...
By CBrenewable , 3 days ago
-
-
Win one of five "Heat Pumps 101" Courses
Heat pumps are gaining traction in the UK, but between ...
By Mars , 3 days ago
-
RE: Agile: average import cost vs other tariffs?
@toodles thanks for the analysis. I'll be really intere...
By Old_Scientist , 3 days ago
-
RE: Is this normal? Click of the DHW returning to space heating
@grantmethestrength Oh sorry to hear that, there should...
By ASHP-BOBBA , 4 days ago
-
@ashp-bobba TBH the ladies are rather disorganised, so ...
By Cathyem1 , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
And for those of us without an automatic irrigation sys...
By Majordennisbloodnok , 4 days ago
-
Logically, the lower frequency = more gentle, yes, but ...
By SUNandAIR , 4 days ago