Skirting board radiators
Has anyone tried installing these or similar? They claim many '000s installed, with a version optimal for heat pump system
https://www.discreteheat.com/thermaskirt/products-and-information/overview.aspx
Posted by: @neilhHas anyone tried installing these or similar? They claim many '000s installed, with a version optimal for heat pump system
https://www.discreteheat.com/thermaskirt/products-and-information/overview.aspx
Hi Neil,
An interesting concept.
I noticed from their performance data that they are only showing figures for water flow temperatures of 45C, 50C and 55C, which is the inefficient range for operating an ASHP.
Based on their data you would require the following lengths of ThermaSkirt to replace a 1200mm x 600mm radiator, to achieve the same heat output.
Deco BM2 15.4m for type 22 (double panel) and 22.6m for type 33 (triple panel)
Deco BM3 10.4m for type 22 (double panel) and 15.2m for type 33 (triple panel)
It would be interesting to see how they perform at lower water flow temperatures.
Since ASHP's operate at their best efficiency at the lowest water flow temperature that meets the heat demand, it is important to have heat emitters with the greatest output at a given water flow temperature. The larger the area of the heat emitters, the lower the water flow temperature would need to be.
How do ThermaSkirt compare in price to a standard radiator or UFH?
@derek-m Ah yes. Though in princple the lengths are probably not a problem. I'm just in exploratory ideas phase at the moment so no prices sought. I still like in-wall idea, especially the 3Thermo design (if I can get some decent technical details). Perhaps different solutions for different rooms, given good zone control system.
Hi Neil,
One of the things I enjoy about the forum, is that there are people like yourself who just don't accept the norm, but look for alternatives that may or may not be an improvement. For much of my career I have been expanding the envelope to find solutions to long standing problems, just because something has been done a certain way for many years does not mean that it cannot be improved.
Posted by: @neilhPosted by: @derek-mjust because something has been down a certain way for many years does not mean that it cannot be improved.
Else we'd be sitting round a fire in a cave !
Don't knock caves, I'm in my 'man cave' right now.
I have just had a look at the 3Thermo system that you highlighted, it also looks very interesting. They specify an energy output of 250W/m2, but don't state what the water temperature would need to be to provide that output. I wonder if it could be installed over existing plaster or whether the plaster would need to be removed and then the wall re-plastered after installation.
I suppose in an ideal world we would have a system that has underfloor heating, wall heating and skirting heating, all supplied by a heat pump that is running at 25C with an outside air temperature of -10C.
- 26 Forums
- 2,238 Topics
- 49.8 K Posts
- 244 Online
- 5,900 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@andrewj In case the comparison is worth anything, here...
By Toodles , 16 minutes ago
-
@old_scientist @jamespa So this was last nights DHW r...
By bontwoody , 39 minutes ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
@jords I had very similar experience with heat loss sur...
By EGP01 , 53 minutes ago
-
-
@springswood we install these nationwide and I have the...
By dgclimatecontrol , 1 hour ago
-
Daikin Altherma 3M ASHP and British Gas Hive Home
In August 2024, we went all electric had a new Daikin D...
By weoleyric , 2 hours ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
Just returning to this issue after a few days working i...
By Mike Patrick , 3 hours ago
-
RE: The Hidden Secret to a Successful Heat Pump: Pipe Size Matters
I wholeheartedly agree with everything @allyfish has wr...
By Old_Scientist , 4 hours ago
-
RE: Renewables & Heat Pumps in the News
Back again to the Spanish blackout this was in the E...
By Judith , 4 hours ago
-
RE: DESNZ doing a survey which asks the right questions!
Fair comment. I have a feeling that ratings more gen...
By JamesPa , 7 hours ago
-
RE: Daikin Octopus installation update - I saw my first defrost. 😍😂
@jancold Not a plumber but I believe that i...
By RadWhisperer , 7 hours ago
-
Thanks! My consumer unit collection is ready with the W...
By Batpred , 10 hours ago
-
RE: Solar inverters - where does the energy go when clipping?
Since the combination of fitting plus scaffolding makes...
By Judith , 18 hours ago
-
RE: Designing my house system with a mix of air to air and air to water
@jamespa Cheers James, it's great reading. In quite a f...
By pipebaron , 19 hours ago
-
RE: PV Panels on roof in Conservation Area
If there is any way you can determine daily oil consump...
By JamesPa , 19 hours ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
attached is prelagged in case indicates anything. &nb...
By Crimson , 22 hours ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
Via the cloud and via the online, similar data is shown...
By Batpred , 1 day ago
-
RE: Incorrect Billing of Customers with a Smart Meter
How odd @korwraith - that functionality being offered ...
By Transparent , 1 day ago
-
RE: Master & Slave Zones/Setback
Re outdoor probes can be added from the ones attached t...
By bretix , 1 day ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
Thanks for sharing this, it is clearly disappointing, B...
By Batpred , 2 days ago