Skirting board radiators
Has anyone tried installing these or similar? They claim many '000s installed, with a version optimal for heat pump system
https://www.discreteheat.com/thermaskirt/products-and-information/overview.aspx
Posted by: @neilhHas anyone tried installing these or similar? They claim many '000s installed, with a version optimal for heat pump system
https://www.discreteheat.com/thermaskirt/products-and-information/overview.aspx
Hi Neil,
An interesting concept.
I noticed from their performance data that they are only showing figures for water flow temperatures of 45C, 50C and 55C, which is the inefficient range for operating an ASHP.
Based on their data you would require the following lengths of ThermaSkirt to replace a 1200mm x 600mm radiator, to achieve the same heat output.
Deco BM2 15.4m for type 22 (double panel) and 22.6m for type 33 (triple panel)
Deco BM3 10.4m for type 22 (double panel) and 15.2m for type 33 (triple panel)
It would be interesting to see how they perform at lower water flow temperatures.
Since ASHP's operate at their best efficiency at the lowest water flow temperature that meets the heat demand, it is important to have heat emitters with the greatest output at a given water flow temperature. The larger the area of the heat emitters, the lower the water flow temperature would need to be.
How do ThermaSkirt compare in price to a standard radiator or UFH?
@derek-m Ah yes. Though in princple the lengths are probably not a problem. I'm just in exploratory ideas phase at the moment so no prices sought. I still like in-wall idea, especially the 3Thermo design (if I can get some decent technical details). Perhaps different solutions for different rooms, given good zone control system.
Hi Neil,
One of the things I enjoy about the forum, is that there are people like yourself who just don't accept the norm, but look for alternatives that may or may not be an improvement. For much of my career I have been expanding the envelope to find solutions to long standing problems, just because something has been done a certain way for many years does not mean that it cannot be improved.
Posted by: @neilhPosted by: @derek-mjust because something has been down a certain way for many years does not mean that it cannot be improved.
Else we'd be sitting round a fire in a cave !
Don't knock caves, I'm in my 'man cave' right now.
I have just had a look at the 3Thermo system that you highlighted, it also looks very interesting. They specify an energy output of 250W/m2, but don't state what the water temperature would need to be to provide that output. I wonder if it could be installed over existing plaster or whether the plaster would need to be removed and then the wall re-plastered after installation.
I suppose in an ideal world we would have a system that has underfloor heating, wall heating and skirting heating, all supplied by a heat pump that is running at 25C with an outside air temperature of -10C.
- 22 Forums
- 2,058 Topics
- 44.9 K Posts
- 13 Online
- 3,308 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Planning Update: 1 Metre Boundary Rule for Heat Pumps Has Been Scrapped
This is indeed welcome news. In addition the new legi...
By JamesPa , 3 hours ago
-
RE: Heat Pump Manufacturers Recommending Buffer Tanks
On our original boiler install, I did have a 140L buffe...
By Johnmo , 11 hours ago
-
RE: Is your heat pump insured?
@benson fairly typical of some insurers.
By KevinPotts , 14 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@majordennisbloodnok I am wearing a glazed expression n...
By Toodles , 15 hours ago
-
RE: Rate the quality of your heat pump design and installation
Yes the HP is running weather compensation and I’ve lef...
By Davesoa , 21 hours ago
-
RE: IVT Greenline high pressure switch and electrical cassette errors
OK, so when the HP comes on it becomes obvious.It's on ...
By tdudgeon , 1 day ago
-
RE: Is Your 6kW Air Source Heat Pump Really a 6kW?
@johnmo I think we’ve been trudging through the same...
By SUNandAIR , 2 days ago
-
RE: How To Balance Radiators & the Role of the Lockshield Valve: A Homeowner's Guide
Good luck, I hope it all works out!
By JamesPa , 3 days ago
-
@johnd it's a difficult one, because we've seen instanc...
By Mars , 3 days ago
-
Win a 6-panel PV courtesy of egg and Renewable Heating Hub
Our epic giveaway just went live! Want to win a 6-pan...
By Mars , 3 days ago
-
RE: Yes, the "zoning with ASHP" topic again...
James, thanks again for your thoughtful and persistent ...
By HarryRea , 3 days ago
-
RE: Is this normal? Click of the DHW returning to space heating
So the Lone Ranger returned today! Even though we thoro...
By Grantmethestrength , 3 days ago
-
RE: Vaillant & OVO partner up to offer Heat Pump Plus
Hopefully iv done the right thing today by signing up t...
By Westkent , 3 days ago
-
RE: Battery sizing - How low can you go!
My own experience with connecting four batteries to thr...
By Transparent , 4 days ago
-
RE: Plate heat exchanger considerations
Work on 2-3 percent per degree. This is a reasonable e...
By JamesPa , 4 days ago
-
RE: Advice for ground source heat pump in new build with PV and batteries
The useful bit is the bit that specifies the heat loss ...
By JamesPa , 4 days ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
You’re absolutely right that during defrost the refrige...
By Mars , 4 days ago
-
@editor thanks Mars that’s the same table I found in th...
By Gary , 4 days ago
-
RE: Tariff and charging strategy advice please
They haven't asked me to prove that I have an EV (I do)...
By JamesPa , 5 days ago