Skirting board radiators
Has anyone tried installing these or similar? They claim many '000s installed, with a version optimal for heat pump system
https://www.discreteheat.com/thermaskirt/products-and-information/overview.aspx
Posted by: @neilhHas anyone tried installing these or similar? They claim many '000s installed, with a version optimal for heat pump system
https://www.discreteheat.com/thermaskirt/products-and-information/overview.aspx
Hi Neil,
An interesting concept.
I noticed from their performance data that they are only showing figures for water flow temperatures of 45C, 50C and 55C, which is the inefficient range for operating an ASHP.
Based on their data you would require the following lengths of ThermaSkirt to replace a 1200mm x 600mm radiator, to achieve the same heat output.
Deco BM2 15.4m for type 22 (double panel) and 22.6m for type 33 (triple panel)
Deco BM3 10.4m for type 22 (double panel) and 15.2m for type 33 (triple panel)
It would be interesting to see how they perform at lower water flow temperatures.
Since ASHP's operate at their best efficiency at the lowest water flow temperature that meets the heat demand, it is important to have heat emitters with the greatest output at a given water flow temperature. The larger the area of the heat emitters, the lower the water flow temperature would need to be.
How do ThermaSkirt compare in price to a standard radiator or UFH?
@derek-m Ah yes. Though in princple the lengths are probably not a problem. I'm just in exploratory ideas phase at the moment so no prices sought. I still like in-wall idea, especially the 3Thermo design (if I can get some decent technical details). Perhaps different solutions for different rooms, given good zone control system.
Hi Neil,
One of the things I enjoy about the forum, is that there are people like yourself who just don't accept the norm, but look for alternatives that may or may not be an improvement. For much of my career I have been expanding the envelope to find solutions to long standing problems, just because something has been done a certain way for many years does not mean that it cannot be improved.
Posted by: @neilhPosted by: @derek-mjust because something has been down a certain way for many years does not mean that it cannot be improved.
Else we'd be sitting round a fire in a cave !
Don't knock caves, I'm in my 'man cave' right now.
I have just had a look at the 3Thermo system that you highlighted, it also looks very interesting. They specify an energy output of 250W/m2, but don't state what the water temperature would need to be to provide that output. I wonder if it could be installed over existing plaster or whether the plaster would need to be removed and then the wall re-plastered after installation.
I suppose in an ideal world we would have a system that has underfloor heating, wall heating and skirting heating, all supplied by a heat pump that is running at 25C with an outside air temperature of -10C.
- 27 Forums
- 2,495 Topics
- 57.8 K Posts
- 259 Online
- 6,220 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Setback savings - fact or fiction?
@cathoderay The input power is largely determined by...
By RobS , 30 minutes ago
-
RE: Humidity, or lack thereof... is my heat pump making rooms drier?
@editor, this is now an example of greenwashing in the ...
By Majordennisbloodnok , 41 minutes ago
-
RE: Electricity price predictions
@transparent Im impressed by all your work on this. ...
By JamesPa , 2 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
Just to wrap this up here for future readers: The S...
By Batpred , 2 hours ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Welcome to the forums.I assume that you're getting the ...
By Sheriff Fatman , 3 hours ago
-
RE: What determines the SOC of a battery?
I agree. Fogstar confirmed that the Seplos BMS does ...
By Batpred , 3 hours ago
-
RE: Say hello and introduce yourself
@editor @kev1964-irl This discussion might be best had ...
By GC61 , 4 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@benson — as @tasos suggests, plotting multiple variabl...
By cathodeRay , 6 hours ago
-
@painter26 — as @jamespa says, it's for filling and re-...
By cathodeRay , 8 hours ago
-
RE: Oversized 10.5kW Grant Aerona Heat Pump on Microbore Pipes and Undersized Rads
@uknick TBH if I were taking the floor up ...
By JamesPa , 19 hours ago
-
RE: Getting ready for export with a BESS
I would have not got it if it was that tight
By Batpred , 20 hours ago
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
@judith thanks Judith. Confirmation appreciated. The ...
By DavidB , 24 hours ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
That makes sense. I thought better to comment in this t...
By Batpred , 24 hours ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
My heat pump journey began a couple of years ago when I...
By Slartibartfast , 1 day ago
-
RE: How to control DHW with Honeywell EvoHome on Trianco ActiveAir 5 kW ASHP
The last photo is defrost for sure (or cooling, but pre...
By JamesPa , 1 day ago
-
RE: Plug and play solar. Thoughts?
Essentially, this just needed legislation. In Germany t...
By Batpred , 1 day ago
-
RE: A Smarter Smart Controller from Homely?
@toodles Intentional opening of any warranty “can of wo...
By Papahuhu , 1 day ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thanks @transparent Thankyou for your advic...
By Bash , 1 day ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: Odd_LionManufacturer: SamsungModel: Samsu...
By Odd_Lion , 1 day ago
-
RE: Configuring third party dongle for Ecodan local control
Well, it was mentioned before in the early pos...
By F1p , 2 days ago
-
RE: DIY solar upgrade - Considering adding more panels
I know this is a bit old, but it made me wonder what co...
By Batpred , 2 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@majordennisbloodnok Daikin, take note! (In fact, I hav...
By Toodles , 2 days ago
-
RE: Midea ASHP – how to set weather compensation
@mk4 — good work! First, I agree, no evidence of cycl...
By cathodeRay , 2 days ago