Radiator Valves
I am upgrading some of my radiators to meet the specifications of my heat loss survey
Working on the basis that Heat Pumps work more efficiently with a steady but high flow rate what is the advice on which type of radiator valves I should fit with the lowest flow losses?
Regular Lockshield valves seem to have very small internal chambers so I think they a very flow restrictive.
Are there ASHP system specific high flow rate radiator valves available as I can't see this mentioned in any of the tech specs on sellers websites?
Are TRVs at all necessary if house temp is set by a thermostat and Heat Pump modulation?
Hello, the high flow rate is not necessarily what you require; a relatively slow flow through the emitters allow the energy in the water to transfer to the area which it comes into contact with. The water enters the radiator at say 40 degrees and if running quickly, might emerge at the other end of the radiator at 38 degrees but... if running more slowly, it has more ‘dwelling time’ to dissipate that energy and emerge at perhaps 35 degrees. The general guideline for low temperature ASHP’s is a Delta T of 5 degrees. So the speed of flow ideally allows (with the right sized radiator) for a drop of 5 degrees across the radiator.
My system has a pump within the Daikin ASHP cabinet which works at variable speed and does its’ utmost to send the leaving water at one temperature and see a return of 5 degrees lower. This water enters a low loss header which has a secondary pump thus allowing a certain independence to set the flow rate to the emitters. I have spent some time adjusting this pump (Wilo Pico) for least losses (LLH’s are low-loss but not no-loss!) and as near as I can get to 5 degrees Delta T. Nothing is perfect, including my set up but I does me best! 😊 Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
As a follow up on your question about lockshield valves etc. I think Heat Geeks did a YouTube presentation on the subject as there are now some (more expensive!) valve bodies available that have a more ‘swept path’ in the casting to improve flow and reduce turbulence. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
And as a follow-up to my follow-up, this is I think the presentation you might be interested to see.
Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
- 26 Forums
- 2,391 Topics
- 54.2 K Posts
- 115 Online
- 6,074 Members
Join Us!
Worth Watching
Latest Posts
-
RE: ASHP Energy Consumption: Aira 12kW heat pump
@wally can I just check the obvious- the kWh usage you'...
By benson , 48 seconds ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
The Solis has an export limitation feature. This was ac...
By Batpred , 1 hour ago
-
Hot water heating in parallel with space heating
One of the downsides of most ASHP installations (compar...
By Temperature_Gradient , 2 hours ago
-
RE: Heat pump not reaching flow temperature
@johnd, what you’re experiencing is common with air sou...
By Mars , 4 hours ago
-
RE: Gen 6 Samsung ASHP losing 20C of DHW in 60 min directly after generation
@ecobaker Thanks for this. I've had it in both slots. ...
By andbeck , 4 hours ago
-
RE: Air source heat pump circuit not operational
Welcome to the forums. If the thermostat shows it’s c...
By Mars , 4 hours ago
-
RE: Daikin Atherma ASHP Cycling 6 Times an Hour?
From what you describe, it sounds like you’ve done a so...
By Mars , 4 hours ago
-
RE: New Fogstar 15.5kWh upright solution
Of course it is not helpful to frogstar fan club member...
By Batpred , 5 hours ago
-
RE: Ecodan with FTC7 - True Weather Compensation
@danwright90 I've linked two videos below recorded this...
By Sheriff Fatman , 6 hours ago
-
@steelbadger, I’ve pretty much decided now that there’s...
By Majordennisbloodnok , 7 hours ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
That makes plenty of sense. Perhaps more importantly, O...
By Majordennisbloodnok , 8 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
It does but it almost all applies to boiler systems and...
By JamesPa , 11 hours ago
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
So theres a problem for starters. This means that the ...
By JamesPa , 12 hours ago
-
RE: Insulating a pitched roof with kingspan, has anyone done it?
Thank you everyone for all of the information, it looks...
By TRBob , 1 day ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@transparent Yep, they didn’t even mention it. When ...
By Papahuhu , 1 day ago
-
RE: Setback savings - fact or fiction?
They are lovely, and I feel lucky to live in one, but t...
By cathodeRay , 1 day ago
-
RE: Who's your electricity provider and what's your tariff?
Worth adding that, for this tariff, the Octopus app has...
By Batpred , 1 day ago
-
RE: APP for remote Daikin ASHP Operation
Thanks, @newhouse87. Understood. I was only asking on...
By Majordennisbloodnok , 1 day ago
-
@mike-patrick A propos, I think my heat pump generates ...
By dr_dongle , 1 day ago