Low temperature radiators
I've put the room heat loss numbers I generated from the MCS Heat Pump spreadsheet into the 'Domestic RHI SPF Calculator' spreadsheet which has a radiator sizing tab... and all our radiators are too small. This is not a surprise as they're all single-panel from 1970s.
When upgrading the radiators, I can obviously go for type 22 (double panel) or 33 (triple panel), but there's a fairly brutal derating factor. The radiator sizing spreadsheet gives a number for derating the advertised heat output of a Stelrad radiator of 0.3 - in other words, you get 30% of the rated output. Given we're taking radiators designed to run at deltaT of 50C (average water temp 70C) and running them at deltaT of 20C (water temp 40C) this isn't very surprising.
So I wondered, are there any radiator designs which are better at emitting heat at low temperature? There are fan assisted radiators (which I might start another post about) but let's consider passive radiators for now. I could imagine you could do different things with the fins, channels etc to design for a lower temperature.
Any models that are worth looking at?
We have standard Stelrad K2s and they work well at a maximum input temp of 50. The fins make them emit heat/air out the top instead of the front. They are a bit bigger than boiler hesting systems but not excessively so. The K3s emit more heat per unit area but are thicker and also quite a bit more expensive. Have you tried running your existing rads at 50 degrees?
@kev-m I haven't tried running rads at 50C as the old oil boiler is very unhappy if the output temp is set below 70C. I'm just curious whether there are rads that are better designed for low temps than simply oversizing conventional rads. If I'm doing a replacement anyway I would like to see if I can budget for a flow of more like 40-45C to improve the COP.
-
Boiling Mad: Exposing Radiatorgate
6 months ago
-
Eskimo Column Radiator – Fronze Finish
6 months ago
-
Convector options for a small kitchen
1 year ago
-
Stelrad radiators
3 years ago
- 25 Forums
- 1,513 Topics
- 31.8 K Posts
- 40 Online
- 1,283 Members
Join Us!
Latest Posts
-
RE: Delivering a smart and secure electricity system: government consultation
Compared to a poorly executed development and rollout, ...
By ChickenBig , 9 mins ago
-
RE: Ecodan ASHP - How to optimise my set up?
That would seem logical, however do you know if the FTC...
By rhh2348 , 15 mins ago
-
RE: Ecodan - flow rates, sensors, settings
As mentioned above, the one I have 1) has the MITSUBISH...
By rhh2348 , 25 mins ago
-
RE: Additional Battery v Wind Turbine v Ripple
I should add, being an investment, the value of your in...
By Old_Scientist , 8 hours ago
-
RE: Vaillant aroTHERM plus not level or flat - what base is best under an external unit?
Similar thread here
By Johnmo , 16 hours ago
-
RE: VDI 2035 heating water specification
Been looking and it seems a good little project. Ever...
By Johnmo , 2 days ago
-
RE: Do I accept an ASHP and Solar Panel retrofit under the HUG 2 scheme?
Will do. I'm currently waiting for another survey / vis...
By dssr , 2 days ago
-
The company that did the borehole were expecting us to ...
By Johnmo , 2 days ago
-
-
RE: The Misquote That Ruined the Heating Industry
@abernyte manufacturer training is pretty average. They...
By Mars , 2 days ago
-
-
RE: ECO4 Scheme and EPC ratings
@mellow Thanks. Given there is a scheme requirement to ...
By Old_Scientist , 4 days ago
-
RE: Do I just go with the lowest quote for my heat pump?
@jancold To me its a no-brainer then, a max 40C flow te...
By bontwoody , 4 days ago
-
-
RE: Heat Pump Books Beginners – Bodge Buster & From Zero To Heat Pump Hero
@editor Presumably he had some good weather Compensatio...
By Toodles , 4 days ago
-
RE: New Vaillant 7kW aroTherm ASHP or oil boiler dilemma/decision??
Storage capacity really is dependent on storage tempera...
By Johnmo , 4 days ago
-
RE: HP Cycling, Expected or Undesirable
Just a little update. I ordered a longer shielded twin ...
By bontwoody , 4 days ago
-
RE: Domestic hot water timer doing crazy things on my Grant Aerona3 10kW air source heat pump
Thanks @allyfish for the pics and info. Spoke to the in...
By Mellow , 4 days ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
It's been a busy day for calls and emails from Aira. I ...
By MikeH , 5 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Hmm. A bit of a nuanced answer, methinks. As I've alr...
By Majordennisbloodnok , 5 days ago
Latest Topics
-
Ecodan - flow rates, sensors, settings
By rhh2348 14 hours ago
-
Replacing mains water with well water
By Johnmo 2 days ago
-
Additional Battery v Wind Turbine v Ripple
By bontwoody 3 days ago
-
By jamespipe 3 days ago
-
VDI 2035 heating water specification
By Johnmo 3 days ago
-
Do I just go with the lowest quote for my heat pump?
By Jancold 5 days ago
-
The Misquote That Ruined the Heating Industry
By Alec Morrow 6 days ago
-
Battery Storage Wiring Gauge Question
By Puff 6 days ago