Convert Pt1000 to NTC 20 kΩ?
Posted by: @derek-mWhat is the problem with the old controller?
It works fine but the integration with the rest of the system is rather clumsy. For solar back off, a relay in the SKSC2 drives a contactor which adds a resistor that makes the the thermal store appear to the system controller to be hotter than it really is. Also the RESOL DL2 data logger attached to the SKSC2 has died. Both the SKSC2 and RESOL DL2 were installed around 15 years ago.
My current thoughts are to replace my existing Viessmann Vitodens 200-W (type WB2C) with the latest version (type B2HF). The existing uses KM Bus and the latest version uses PlusBus so the wall mounted mixer extension will need to change. It seems like a good time to also change the solar controller to achieve better integration. I'm considering a Vitotrol 300-E as well. Might also replace the solar pump (how long do they last?). The upgrade should be straightforward, apart from the solar collector sensor ...
Posted by: @djhPosted by: @john-connettThe Pt1000 Resistance Table is straightforward. NTC Thermistors, Resistance/Temperature Conversion is more complex. I know it should measure 20 kΩ at 25°C but I'm not sure which of the 17 curves to apply?
Using the curve in the Viessmann guide you can see that the resistance at 140°C is about 0.5. So Rt/R25 is 0.025. You can then look at your 17 curves and see what the best match is. You could just estimate an approximate equation to match the Viessmann curve instead of trying to emulate an actual device. Or ask Viessmann what device it is?
Good suggestion. I am in the process of doing something similar to see which of the 15 (1-14, 17) Vishay curves is a good fit (It will also be interesting to see how the Ohmigo NTC 20 kΩ table compares). A table from Viessmann would have been more convenient for the comparison than the log/linear graph. However, solar thermal doesn't need as high precision as some other processes.
There are also some Vishay Tools that might be useful.
I asked OHMIGO® what curve they used for their NTC 20 kΩ table and received a very swift and useful reply:
There are small variations between suppliers and control manufacturers - most of the NTC values were created from 3rd party suppliers like Produal... the differences in ohms and even so in 'C are small.
Ohmonwifi allows you to set your own table between 'C and ohm. There is an excel spreadsheet on ohmonwifi
A reply from Vishay:
your inquiry: "Are you aware of a device or method of converting the resistance output from a Pt1000 sensor to the equivalent resistance output of an NTC 20 kΩ sensor? Background. The existing solar thermal system in my house has a Pt1000 sensor in a solar thermal collection on the roof. I am considering replacing the solar controller with a Viessmann model which uses an NTC 20 kΩ sensor. The Pt1000 sensor on the roof is difficult to access so I am investigating if it will be possible to reuse it with something to convert its resistance to the NTC 20 kΩ equivalent. My background is in systems software so this is well outside my comfort zone! Vishay's answer: if those circuits are out of your comfort zone, I suggest you do not start to modify them and take contact with the suppliers of those systems and ask them for advice. Converting RTD sensors (Pt1000) signals to be read as an NTC is not advisable.
- 26 Forums
- 2,171 Topics
- 47.8 K Posts
- 18 Online
- 5,744 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Big Changes Coming to Our Heat Pump System
@editor your engineer's attitude is truly horrifying. ...
By GrahamF , 9 hours ago
-
@cliffhanger - seriously though, I have no idea. What I...
By cathodeRay , 11 hours ago
-
RE: How to choose Towel Rails for an ASHP
@rob-nezard yes absolutely. Here is the link and a pho...
By GrahamF , 11 hours ago
-
@mixergy Thanks for the update, I would appreciate some...
By bontwoody , 12 hours ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
Unfortunately I'm not that well connected 😂 ...
By Scalextrix , 16 hours ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
It is interesting to see what our new Grant Aerona 290 ...
By GrahamF , 18 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
I've never physically seen it, but I seem to recall som...
By cathodeRay , 19 hours ago
-
@jamespa Ours is a Daikin EDLA03 8 kW and the Delta T =...
By Toodles , 19 hours ago
-
RE: Midea ASHP – how to set weather compensation
I noticed that too and thought the same thing, but then...
By cathodeRay , 1 day ago
-
RE: Ya can’t win! It is S*d’s Law!
@old_scientist If IOF is still running next late spring...
By Toodles , 1 day ago
-
RE: Electricity price predictions
Those of you on Agile will do well tomorrow; there are ...
By Toodles , 2 days ago
-
RE: Who’s Caved and Switched the Heating On Already?
We've been running our Ecodan system, installed in June...
By Sheriff Fatman , 2 days ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 2 days ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 2 days ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 3 days ago
-
RE: Help me keep the faith with my air source heat pump installation
Er true, it should have read l/hr!
By JamesPa , 3 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 4 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@dgclimatecontrol I attach the responses from 2 potenti...
By pash44pump , 4 days ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 5 days ago
Members Online
No online members at the moment