Any recommendations for smart TRVs possibly compatible with MEL Cloud?
2.5 years into our ASHP. We have our Mitsubishi wireless thermostat in the lounge set at 19 degrees, we found that at night it was getting too warm in the bedrooms, I tried altering the thermostatic valves but it's not ideal, it seems like you get to an all or nothing point with them and I had a couple that were clicking on and off regularly and being a nuisance. We have 2 young kids that are not great sleepers, so getting a good nights sleep without external factors like room temperature is a challenge.
In the end I set up a timer so that at 9pm the temp goes to 17.5 degrees and then 3:45am 18.5 and 5:30 19 degrees (we're on Octopus Cosy), this mostly works ok, but really I'd like to leave the thermostat at 19 degrees all of the time and have much more precise control of the bedroom temperatures.
Mitsubishi Ecodan 8.5kWh
4.4kW Solar PV
5.2 kWh Battery Storage
1983 build, 300mm loft insulation, cavity wall insulation (beads)
@trbob The control of heat output from each radiator or emitter is best set using the lockshield valve rather than using a TRV; the TRV should be thought of as a limiter that ensure the room doesn’t go above your desired maximum due to things like solar gain or perhaps a number of people all in one room causing a temperature rise. By the sound of things, your radiators have not been balanced. By all means the TRV may be employed as this ‘limiter’ once the radiators have been balanced. May I suggest that you may care to read my article on the subject:
https://renewableheatinghub.co.uk/how-to-balance-radiators-the-role-of-the-lockshield-valve
Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Thank you @toodles , I ordered a temperature probe with two clamps and it's taken a while to arrive, I just need some time when the kids are out now so I can get on with it. I've done some research and a lot of sources mention having a 12 degree drop across the radiator, does this apply to ASHP systems as well or are we looking for less of a drop given that our flow temp is much lower than a gas boiler system?
Mitsubishi Ecodan 8.5kWh
4.4kW Solar PV
5.2 kWh Battery Storage
1983 build, 300mm loft insulation, cavity wall insulation (beads)
@trbob 5 degrees is the aim - though some of mine only manage 4 or so, all works well though for all that. Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Adiathermal are developing smart TRVs specifically designed for heat pumps, with an integrated control circuit that controls the flow temperature. I don think they support Mitsubishi yet (but worth asking).
Until they (or someone else) do support your system, smart TRVs are best avoided for heat pump systems or confined to a small minority of rooms. Instead balance all or at least the majority of rads (including all the main living areas) using the lockshields as @toodles says, adjust the weather compensation curve down as far as you can so the house is comfortable, leave it largely alone.
Recently some installers seem to have adopted a slightly modified approach (for larger houses) of having the main living rooms open (ie controlled on solely lockshields/WC) and using TRVs in the bedrooms only. I can see (but don't know by personal experience) that this could be sensible for some houses.
If you have a 12C temperature drop across the rads then the water flow rate is too low, either because the rad is turned down or because the water pump isnt set high enough, or because some installer has installed a bypass to ensure you get poor performance but they don't get call outs.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,104 Topics
- 46.3 K Posts
- 117 Online
- 3,393 Members
Join Us!
Latest Posts
-
RE: BUS Grant: removal of all other fossil fuel heat sources
Hi all, thanks for your help. The installer has confirm...
By Rikiarn , 13 hours ago
-
@pie_eater Try asking the Perplexity AI engine how to t...
By downfield , 1 day ago
-
RE: No-code, plug-and-play monitoring for your heat pump
Just in case anyone is looking at Planet Atmo- we've ma...
By benson , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
Agree, but you may have a hard time convincing them, as...
By JamesPa , 1 day ago
-
RE: Seal the Deal: Don't Let Your Heat Pump Leak Energy
Hi - fyi - there's a dead image link in the 'Optimal In...
By seatonian , 2 days ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
@chandykris Horses and beggars…. 😉 Toodles.
By Toodles , 2 days ago
-
RE: Cleaning up after gas meter removed
@agentgeorge Likewise in the loft space; we have 300mm ...
By Toodles , 2 days ago
-
RE: Ecodan consuming 100kwh per day in new build!!!
This particular example is one of the worst I have seen...
By JamesPa , 2 days ago
-
-
RE: Fan running in hot weather ...why?
I wonder if it has some kind of pressure transducer to ...
By ASHP-BOBBA , 3 days ago
-
RE: Cooling with Samsung Gen6 and Flow error
@iaack The system isnt running long enough for any cond...
By EcoBaker , 3 days ago
-
@heacol thanks for confirming we can only hope NAPIT ag...
By Bart , 3 days ago
-
Sorry to hear that @bruce. Sadly I’ve heard from multip...
By Mars , 4 days ago
-
RE: Crystal Ball Time: Communal or even Area Energy Storage?
I am invested in a couple of listed energy storage fund...
By Old_Scientist , 5 days ago
-
RE: Who's your electricity provider and what's your tariff?
That would be my biggest commitment -time to gain great...
By SUNandAIR , 5 days ago
-
RE: Who has a V2G EV installation
As has been discussed on other threads, trying to justi...
By Majordennisbloodnok , 6 days ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
Thanks @mikeh. Then I will also go back to non smart ta...
By ChandyKris , 6 days ago