Any recommendations for smart TRVs possibly compatible with MEL Cloud?
2.5 years into our ASHP. We have our Mitsubishi wireless thermostat in the lounge set at 19 degrees, we found that at night it was getting too warm in the bedrooms, I tried altering the thermostatic valves but it's not ideal, it seems like you get to an all or nothing point with them and I had a couple that were clicking on and off regularly and being a nuisance. We have 2 young kids that are not great sleepers, so getting a good nights sleep without external factors like room temperature is a challenge.
In the end I set up a timer so that at 9pm the temp goes to 17.5 degrees and then 3:45am 18.5 and 5:30 19 degrees (we're on Octopus Cosy), this mostly works ok, but really I'd like to leave the thermostat at 19 degrees all of the time and have much more precise control of the bedroom temperatures.
Mitsubishi Ecodan 8.5kW
4.4kW Solar PV
5.2 kWh Battery Storage
1983 build, 300mm loft insulation, cavity wall insulation (beads)
@trbob The control of heat output from each radiator or emitter is best set using the lockshield valve rather than using a TRV; the TRV should be thought of as a limiter that ensure the room doesn’t go above your desired maximum due to things like solar gain or perhaps a number of people all in one room causing a temperature rise. By the sound of things, your radiators have not been balanced. By all means the TRV may be employed as this ‘limiter’ once the radiators have been balanced. May I suggest that you may care to read my article on the subject:
https://renewableheatinghub.co.uk/how-to-balance-radiators-the-role-of-the-lockshield-valve
Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Thank you @toodles , I ordered a temperature probe with two clamps and it's taken a while to arrive, I just need some time when the kids are out now so I can get on with it. I've done some research and a lot of sources mention having a 12 degree drop across the radiator, does this apply to ASHP systems as well or are we looking for less of a drop given that our flow temp is much lower than a gas boiler system?
Mitsubishi Ecodan 8.5kW
4.4kW Solar PV
5.2 kWh Battery Storage
1983 build, 300mm loft insulation, cavity wall insulation (beads)
@trbob 5 degrees is the aim - though some of mine only manage 4 or so, all works well though for all that. Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Adiathermal are developing smart TRVs specifically designed for heat pumps, with an integrated control circuit that controls the flow temperature. I don think they support Mitsubishi yet (but worth asking).
Until they (or someone else) do support your system, smart TRVs are best avoided for heat pump systems or confined to a small minority of rooms. Instead balance all or at least the majority of rads (including all the main living areas) using the lockshields as @toodles says, adjust the weather compensation curve down as far as you can so the house is comfortable, leave it largely alone.
Recently some installers seem to have adopted a slightly modified approach (for larger houses) of having the main living rooms open (ie controlled on solely lockshields/WC) and using TRVs in the bedrooms only. I can see (but don't know by personal experience) that this could be sensible for some houses.
If you have a 12C temperature drop across the rads then the water flow rate is too low, either because the rad is turned down or because the water pump isnt set high enough, or because some installer has installed a bypass to ensure you get poor performance but they don't get call outs.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,396 Topics
- 54.3 K Posts
- 101 Online
- 6,077 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Help me keep the faith with my air source heat pump installation
@simonf I’ll ask the installers to get them out. What k...
By AdamK , 2 hours ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
Thanks for all the help/comments. I completely agree w...
By JamesPa , 4 hours ago
-
RE: ASHP Energy Consumption: Aira 12kW heat pump
I doubt that matters, ToU tariffs are for the benefit o...
By JamesPa , 9 hours ago
-
RE: Free Ecoheat Heat Pump Install
@deltona Yes older houses are problematic like that, bu...
By bontwoody , 12 hours ago
-
RE: Radiator sizing sanity check
As I mentioned early on the cost of supplying and fitti...
By JamesPa , 15 hours ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
I hadn't spotted that there were two pumps in the UFH (...
By JamesPa , 17 hours ago
-
RE: Setback savings - fact or fiction?
Never assume it makes an ass of u and me! You need the...
By JamesPa , 17 hours ago
-
RE: New Mitsubishi Ecodan 11.2kW installation - L9 errors and maybe more
Before I answer your specific questions just one more t...
By JamesPa , 17 hours ago
-
RE: Electricity price predictions
Great point, one of the key ones in my chat with Octopu...
By Batpred , 1 day ago
-
RE: Running from backup generaor in powercut?
Definitely and professionals sometimes miss it. I had...
By Batpred , 1 day ago
-
RE: New Fogstar 15.5kWh upright solution
Let me point out that there are many Chinese suppliers ...
By Transparent , 1 day ago
-
RE: Weather compensation- why you should use it
@majordennisbloodnok — The Two Ronnies Mastermind sketc...
By cathodeRay , 1 day ago
-
Just realised that this image of the cylinder cupboard ...
By Sheriff Fatman , 1 day ago
-
RE: Rodents! A word of warning for heat pump owners
Two thoughts: 1: Let's ask @david-s if Primary Pro in...
By Transparent , 2 days ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
In the diagram below, I describe my understanding of th...
By Batpred , 2 days ago
-
I need to have a look out for it. I know IBM feeds some...
By Batpred , 2 days ago
-
-
RE: Daikin Atherma ASHP Cycling 6 Times an Hour?
Thanks for your reply. Yes that's a good idea to try a...
By John Marshall , 2 days ago
-
RE: Hot water heating in parallel with space heating
An external heat exchanger would need a pump which woul...
By bontwoody , 2 days ago
-
RE: Gen 6 Samsung ASHP losing 20C of DHW in 60 min directly after generation
@ecobaker Thanks for this. I've had it in both slots. ...
By andbeck , 2 days ago