Any recommendations for smart TRVs possibly compatible with MEL Cloud?
2.5 years into our ASHP. We have our Mitsubishi wireless thermostat in the lounge set at 19 degrees, we found that at night it was getting too warm in the bedrooms, I tried altering the thermostatic valves but it's not ideal, it seems like you get to an all or nothing point with them and I had a couple that were clicking on and off regularly and being a nuisance. We have 2 young kids that are not great sleepers, so getting a good nights sleep without external factors like room temperature is a challenge.
In the end I set up a timer so that at 9pm the temp goes to 17.5 degrees and then 3:45am 18.5 and 5:30 19 degrees (we're on Octopus Cosy), this mostly works ok, but really I'd like to leave the thermostat at 19 degrees all of the time and have much more precise control of the bedroom temperatures.
Mitsubishi Ecodan 8.5kW
4.4kW Solar PV
5.2 kWh Battery Storage
1983 build, 300mm loft insulation, cavity wall insulation (beads)
@trbob The control of heat output from each radiator or emitter is best set using the lockshield valve rather than using a TRV; the TRV should be thought of as a limiter that ensure the room doesn’t go above your desired maximum due to things like solar gain or perhaps a number of people all in one room causing a temperature rise. By the sound of things, your radiators have not been balanced. By all means the TRV may be employed as this ‘limiter’ once the radiators have been balanced. May I suggest that you may care to read my article on the subject:
https://renewableheatinghub.co.uk/how-to-balance-radiators-the-role-of-the-lockshield-valve
Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Thank you @toodles , I ordered a temperature probe with two clamps and it's taken a while to arrive, I just need some time when the kids are out now so I can get on with it. I've done some research and a lot of sources mention having a 12 degree drop across the radiator, does this apply to ASHP systems as well or are we looking for less of a drop given that our flow temp is much lower than a gas boiler system?
Mitsubishi Ecodan 8.5kW
4.4kW Solar PV
5.2 kWh Battery Storage
1983 build, 300mm loft insulation, cavity wall insulation (beads)
@trbob 5 degrees is the aim - though some of mine only manage 4 or so, all works well though for all that. Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Adiathermal are developing smart TRVs specifically designed for heat pumps, with an integrated control circuit that controls the flow temperature. I don think they support Mitsubishi yet (but worth asking).
Until they (or someone else) do support your system, smart TRVs are best avoided for heat pump systems or confined to a small minority of rooms. Instead balance all or at least the majority of rads (including all the main living areas) using the lockshields as @toodles says, adjust the weather compensation curve down as far as you can so the house is comfortable, leave it largely alone.
Recently some installers seem to have adopted a slightly modified approach (for larger houses) of having the main living rooms open (ie controlled on solely lockshields/WC) and using TRVs in the bedrooms only. I can see (but don't know by personal experience) that this could be sensible for some houses.
If you have a 12C temperature drop across the rads then the water flow rate is too low, either because the rad is turned down or because the water pump isnt set high enough, or because some installer has installed a bypass to ensure you get poor performance but they don't get call outs.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,255 Topics
- 50.3 K Posts
- 664 Online
- 5,918 Members
Join Us!
Podcast Picks
Latest Posts
- 
                          RE: Midea ASHP – how to set weather compensation @pash44pump - thank you By cathodeRay , 30 minutes ago 
- 
                        
- 
                          RE: Mediation with RECC, what's your experience? Welcome to the forums @treewizard and sorry to hear abo... By Mars , 2 hours ago 
- 
                        RE: Help me keep the faith with my air source heat pump installation @jamespa ive had a look at the firmware card in the add... By AdamK , 2 hours ago 
- 
                          RE: New build installation query That accounts for why you start with an overly-high DHW... By Transparent , 2 hours ago 
- 
                        UFH downstairs and radiators upstairs balancing question I am running pure WC on .4 curve in our new build with ... By Walnut-tree-cottage , 2 hours ago 
- 
                        RE: Daikin Altherma 3 / HomeAssistant I would have thought that (instantaneous) power is a fa... By JamesPa , 3 hours ago 
- 
                          RE: Buying large amp bidirectional RCD and RCBO It's the requirement to have 100mA earth-leakage trippi... By Transparent , 4 hours ago 
- 
                        RE: Are We Sleepwalking Into Another Race to the Bottom? Alright, I concede that the Toyotas are, as you say a v... By JamesPa , 5 hours ago 
- 
                        When to use Octopus Intelligent Go tariff with my heat pump and battery I have underfloor heating with 15 room thermostats thro... By ChrisH , 5 hours ago 
- 
                        RE: When will fusion be producing energy? From the time I was a physics undergraduate it’s been 2... By Judith , 17 hours ago 
- 
                        RE: Is it mad to think there should be a minimum SCOP for UK heat pump installs? Sadly I think it is mad. If the BUS is not granted for ... By Judith , 17 hours ago 
- 
                          RE: Who has a V2G EV installation Perfect, @agentgeorge. I’m always up for some edificati... By Majordennisbloodnok , 17 hours ago 
- 
                        RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus Yes but... The evidence is that many heat loss survey... By JamesPa , 18 hours ago 
- 
                          What Adam Chapman gets up to in his Spare Time. Ok, so this just appeared on YouTube (don’t blame me th... By Toodles , 19 hours ago 
- 
                          RE: Radiator Sizing Dilemma: Vertical vs Type 33 for Low-Temperature Heat Pump Systems That's my main concern too. On top of that, I ... By DREI , 20 hours ago 
- 
                        RE: Grant 13kW Aerona3 - issues getting zones to temp Thanks, patience is something I’m trying to ma... By Crimson , 22 hours ago 
- 
                        RE: Solar Power Output – Let’s Compare Generation Figures 2025 - now a record year of Solar PV Generation. Octobe... By AllyFish , 1 day ago 
- 
                        RE: Mitsubishi Ecodan R290 10kW performance Totally agree that any system is reliant on the ability... By Sheriff Fatman , 1 day ago 




 
                                 
                                 
                                 
                                 
                                