That's a great opener, @fabz 🙂
Let me respond to the last point first:
It would be pretty difficult to devise a way to export to the grid without first satisfying the demand from household appliances!
So I think the answer is going to be 'yes'!
If the sun shines, and the Domestic Hot Water (DHW) is already hot enough, then switch on other devices and use that excess electricity.
However, your description raises a number of other issues in my mind.
You might want to copy the following points and put them to your Social Housing Provider.
A: If all the tenants have their own (Smart) Meters, does that mean they receive the SEG payments as a reduction on their bills?
Or does it get paid to the landlord to offset the capital cost of installing the solar panels?
You will probably find that the SEG is so low that it's almost insignificant.
B: An Air-to-Water (Air-Source Heat Pump) should operate all day. It isn't like a gas-boiler which only switches on as required.
For the majority of that time the heat-pump will using peak-rate electricity from the grid (night-time in summer, and most of the winter).
The only way you'll be able to operate such a system is if the heat-losses from the house are low.
Having adequate insulation is vital.
Have you got a heat-loss survey/report for each property on the estate?
C: Since the solar-inverter is to be grid-tied (ie it can export), your Distribution Network Operator (DNO) will state the maximum permitted output.
The installer or landlord completes a form which confirms the G98 credentials for the inverter.
That max export is usually 3.68kW (16amps), and will be guaranteed by the size/type of inverter.
For that reason your roof is likely to be fitted with just under 4kW of PV panels.
In full sun that's enough to operate the ASHP and direct a small amount to your DHW tank (using an immersion heater and a device called a Load Diverter).
But it's unlikely to supply enough current to start the heat-pump.
Starting a typical heat-pump compressor takes around 25-30A, which means it draws on the mains grid.
In turn, that means it's all the more important that the installer properly commissions the system so as to use as little energy as is reasonable in the circumstances.
If it turns off/on several times an hour, then the efficiency plummets.
Hence you'll be buying in electricity every time it restarts.
That phrase in green is stipulated in Part-L of the Building Regulations.
It's not sufficient for the installer merely to state that the system runs ok!
D: I'd be interested to understand why solar-panels are being installed, but no Storage Battery.
A PV Panel is relatively inexpensive to buy... around £100 per 350-400w panel.
The major costs are associated with the scaffolding and labour in fitting the roof-rails and wiring.
Compare that with an off-grid battery to directly operate a heat-pump... say £10,000 for 13kWh Tesla Powerwall 2.
Because you could then opt to refill the battery only during off-peak times, the cost of electricity is significantly reduced.
What would've been spent on scaffolding is instead invested in a permanent energy storage device.
That significantly reduces the payback period.
Save energy... recycle electrons!
Blown away by your response, @Transparent; thanks.
At the moment, some of us are undecided about whether to opt for heat pumps or new storage heaters (27% more efficient than "dreadful"!).
For me it's a no-brainer but it's difficult to make a choice if you haven't got a technical background and you believe rumours of "noise", "ugly pipework", "false efficiency claims", plus the added disruption.
Your confirmation that household appliances are fed first by solar PV is the icing on the cake for this household.
Regarding your other points:
A: I'm assuming that 100% of SEG credits will be made to residents but I'll seek confirmation.
B: I should have mentioned that old double glazing will be replaced and cavity and loft insulation renewed and boosted to minimise heat loss. Once these are completed, a heat-loss assessment will be carried out.
C: We're located in London and fortunate in that all 30 or so properties are more or less South facing (in fact we petitioned for an all Solar PV system but that's another story...).
Thanks for the (new to me) info about the maximum output of the solar array and the start up power draw of the heat pump (30 Amps!).
D: I take your point about the trade-off between the cost of scaffolding and labour, versus the cost of batteries to power the heat pumps (combined with off-peak battery charging).
Each household is being offered a choice between new Storage Heaters or an ASHP. We've waited more than 25 years for this and feel over the moon that our HA has responded positively to our petitioning.
Work is due to start by next month so it's probably too late to propose any major changes. I'll report back on developments as they occur but a massive thank you for the information and advice you've so generously offered.
Hi, I've arrived here via My Home Farm, hoping to get some advice on ASHPs. We live in wet west Wales, and haven't yet made the switch to an ASHP from oil but we're thinking about it! Not sure where to post my questions ...?
@cookie197, welcome to the forums. Start a new thread in our ASHP section detailing your property and the questions you have.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
Follow our sustainability journey at My Home Farm: https://myhomefarm.co.uk
Posted by: @cookie197We live in wet west Wales
If that's wet enough for hydro-generation, there would be a lot of interest here in an ASHP unit powered by water 🤔
Save energy... recycle electrons!
Given the extraordinary weather conditions across the world during 2023, I doubt that West Wales will be seeing any more lumpy water.
Have a look at the Satur-M 500-watt vortex generator, and you'll see what what's on my mind.
Prices start at 2500 Euros without an inverter.
That delivers up to 48v and max output of 12kWh /day
That goes a long way towards the electricity demands of a HP, and will produce most of its output in winter when it's needed.
Save energy... recycle electrons!
Hi everyone.
Just finished our self build with a 14kW Ecodan. Now moved and I'm learning how to drive it!
Questions over how to maintain reasonable hot water temp most of the day, how to see what electricity it's using, what will be best for when CH settings will be best for our underfloor heating etc etc!
Cheers, John
Hello.
I have just discovered this forum while searching for help - today just with DHW. Once I've solved that I'll move on to the UFH.
I am enthused and motivated by the long discussion around tuning heat pumps and COP.
I'll start a fresh post with as much detail as I can manage about our system - and the current challenge.
thanks in advance for any help.
Derek
It's good to have you here @tadpole
Posted by: @tadpoleI am enthused and motivated by the long discussion around tuning heat pumps and COP.
Well indeed!
Let's note here that commissioning the system is a legal requirement under Part-L of the Building Regulations.
Simply running it up isn't sufficient!
Part-L stipulates that it must be tuned so as to use no more (input) energy than is necessary.
Moreover the installation engineer must also train the householder to operate and maintain the system so that it continues to use minimal energy input.
We need a nationwide public-awareness exercise to ensure that everyone knows this.
It's a conversation which should be occurring in the pubs and coffee shops of the country.
Save energy... recycle electrons!
Hello.
I live just outside York in a 50s semi-detached house with good loft insulation and cavity wall insulation. I spent last year installing triple glazed windows and new doors. About 3 weeks ago I installed 4.05 kW of Longi solar panels (5 facing east and 5 facing west), a 5.8kWh Solax battery, 3.68 kW Solax inverter and, last but hardly least, a 6 kW Ecodan ASHP. There were a few hiccups with the installation. After the solar side was wired up my electricity consumption went up 10 fold! Apparently a "CT clamp" was installed up side down, thus reporting solar input as coming from the grid. Quickly corrected. But it has made me feel rather nervous about the whole project. I have several questions in my mind and was glad to come across this forum where I might have space to air my concerns.
Posted by: @minosHello.
I live just outside York in a 50s semi-detached house with good loft insulation and cavity wall insulation. I spent last year installing triple glazed windows and new doors. About 3 weeks ago I installed 4.05 kW of Longi solar panels (5 facing east and 5 facing west), a 5.8kWh Solax battery, 3.68 kW Solax inverter and, last but hardly least, a 6 kW Ecodan ASHP. There were a few hiccups with the installation. After the solar side was wired up my electricity consumption went up 10 fold! Apparently a "CT clamp" was installed up side down, thus reporting solar input as coming from the grid. Quickly corrected. But it has made me feel rather nervous about the whole project. I have several questions in my mind and was glad to come across this forum where I might have space to air my concerns.
Welcome to the forum.
Please feel free to ask whatever questions you wish and we will do our best to answer them.
- 25 Forums
- 1,442 Topics
- 30.2 K Posts
- 19 Online
- 1,225 Members
Join Us!
Latest Posts
-
-
RE: Are Octopuses Slowing Consumer Adoption of Heat Pumps?
Yes, it is one of those two who first alerted me to the...
By IvanOpinion , 8 hours ago
-
RE: EV charger installation question – I don't want to bury the cable
The fact that the MCB is rated 16A tells us what we nee...
By Transparent , 8 hours ago
-
RE: Are You Getting the Most Out of Your Renewable Energy?
Thanks, @editor. Ideally it’d be someone who would li...
By Majordennisbloodnok , 10 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
Unless adequately controlled it could devour your bank ...
By Derek M , 11 hours ago
-
RE: Effect of buffer tank or volumiser on heat pump system
I think that you will find that the best location for a...
By Derek M , 11 hours ago
-
RE: ASHP Commissioning: What Questions Should I Ask the Installer?
@derek-m thanks - will look out for the point regarding...
By Declan90 , 1 day ago
-
RE: Noise problems with newly installed Samsung 8kW ASHP
@editor @kenbone Thanks, I would be very interested ...
By Elton , 1 day ago
-
RE: No-code, plug-and-play monitoring for your heat pump
This is all a bit too frequentist for my liking. The pr...
By scrchngwsl , 1 day ago
-
Relax with 4K drone footage of lawn mowing to a smooth Motown tune
Sending out some chilled weekend vibes to everyone. Lis...
By Mars , 2 days ago
-
RE: Incorrect Billing of Customers with a Smart Meter
The starting point of that discussion on Camelot-Forum ...
By Transparent , 2 days ago
-
Share Your Experiences with Heat Pump Manufacturer Support
Have you ever reached out to your air source heat pump ...
By Mars , 2 days ago
-
RE: Is this a bad installation and is there something wrong with my Samsung heat pump?
@ant87 thanks for that.
By David999 , 3 days ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
I might change my mind again, but I'm currently unlikel...
By IvanOpinion , 3 days ago
-
RE: Samsung ASHP scheduling help
@elgreco69 worth reading the GitHub here as that will a...
By morh , 3 days ago
-
RE: ASHP sizing - value of Heat Transfer Coefficient
@toodles Thanks for the explanation I get it now as I h...
By Jancold , 3 days ago
-
RE: Questions about yearly heat pump maintenance
For the installer, I believe servicing and maintenance ...
By Majordennisbloodnok , 3 days ago
-
RE: Rate the quality of your heat pump design and installation
@retrorich It is very worrying that any of this should ...
By Toodles , 3 days ago
-
RE: Spacing for roof fixing bolts ?
There is another consideration...but alas this doesn't ...
By Transparent , 4 days ago
-
RE: Air source heat pumps and noise
Yes, but when they go wrong things get really sticky. D...
By Majordennisbloodnok , 4 days ago
Heat Pump Humour
Latest Topics
-
By David999 7 hours ago
-
Spacing for roof fixing bolts ?
By heat-pump-newbie 6 days ago
-
ASHP sizing - value of Heat Transfer Coefficient
By jamesw 6 days ago
-
Incorrect Billing of Customers with a Smart Meter
By KoRWraith 1 week ago
-
Home energy storage & battery register
By Mars 1 week ago