Solar Thermal System Design Issue: Resol Delta Sol BS Plus controller
I have a solar thermal system with a Resol Delta Sol BS Plus controller. I have recently had some works done to the system and since then it does not appear to be functioning properly and I wondered if anyone had any ideas about what could be wrong.
The issue is that when the system’s pumps turn off, either because a store has reached its max temperature or because the system is checking its temperature during an Oscillating Break Time, the system (through the collector sensor) no longer detects an increase in temperature at the top of the collectors.
What happens is that the pumps turn off and the collector sensor actually registers a decrease in temperature at the top of the panels. This goes on for as long as the pumps are off and the temperature just falls steadily.
If the pumps are turned back on manually, the flow of the system start circulating again, the temperature reading at the collector sensor then rockets up by 10 – 20 degrees or more and then levels out once the pumps have taken back control, released the heat through the heat exchangers etc.
It’s an issue because it means that (a) the store prioritisation is no longer working properly and (b) the system doesn’t detect when it’s about to overheat and so doesn’t restart the pumps in an emergency fail-safe function (e.g. under the OREC or OCX functions).
It didn’t used to be a problem. On a sunny day, what used to happen is that when the pumps turned off, the collector sensor would detect a steadily rising temperature and then the system behaved as expected, heating the stores in the right priority… with the other system controller functions etc.
Has anyone ever heard of or encountered this issue?
What work was carried out on your system? Did the people carrying out the work not test the systems operation after the work was completed?
If possible I would suggest that you call them back to rectify the problems it would appear that they created.
The work involved upgrading a lot of the pipework and the circuit pumps and installing a new third circuit. The people who installed it are struggling to identify what the problem is. They're coming back again next week but I'm trying to get a head start on the issue to understand from all the experts out there whether anyone has had this sort of issue before, or if anyone has any ideas as to what it could be, so I can make sure things are steered in the right direction.
- 27 Forums
- 2,520 Topics
- 58.6 K Posts
- 464 Online
- 6,800 Members
Join Us!
Worth Watching
Latest Posts
-
Issue with a Grant Air Source Heat Pump & Tado Smart Thermostat
Hi all I'm having some trouble with a Grant ASHP and ...
By Renewables345 , 29 minutes ago
-
RE: Underfloor Heating Installation Issues with Heat Pump
We suffered a water leak last year in two rooms and had...
By MartinHook_UK , 40 minutes ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Now seems a good time to summarise the costs and effici...
By benson , 49 minutes ago
-
RE: Heat Pump vs New Gas Boiler for Inherited House - Worth the Extra Cost?
*** I now see @jamespa has already posted but will stil...
By cathodeRay , 2 hours ago
-
RE: Tell us about your Solar (PV) setup
@mk4 Charge to 100%, discharge down to 10%.
By bobflux , 2 hours ago
-
RE: Daikin Altherma 3 LT compressor longevity question
This mess is intriguing: I wonder if this represent...
By bobflux , 3 hours ago
-
RE: Connecting Growatt SPH5000 over wired ethernet rather than wireless
The simplest wired option is usually the Growatt Ethern...
By Jonatan , 8 hours ago
-
RE: Peak Energy Products V therm 16kW unit heat pump not reaching flow temperature
ASHPs do have a minimum compressor speed. The minimum h...
By bobflux , 14 hours ago
-
RE: Electricity price predictions
@jamespa And it seems some of the nasty public cloud...
By Batpred , 15 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
Technology is rapidly advancing. BBC News reported th...
By Transparent , 18 hours ago
-
What matters for flow and pressure drop is internal dia...
By bobflux , 19 hours ago
-
RE: Do Fridges and Freezers have COP ratings?
@editor Thank you all for your replies and submitted in...
By Toodles , 21 hours ago
-
I know and yes. The secondary deltaT wont necessaril...
By JamesPa , 1 day ago
-
RE: Designing heating system with air to water heat pump in France, near Lyon
Just love the way you put it! 🤣
By Batpred , 2 days ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thank you for sharing. So it seems that your Schneid...
By Batpred , 2 days ago
-
RE: Forum updates, announcements & issues
@upnorthandpersonal thanks for the thoughtful, consider...
By Mars , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@mk4 All 21 panels have their own Enphase IQ7a microinv...
By Toodles , 2 days ago
-
RE: Setback savings - fact or fiction?
Great, so you have proven that MELCloud is consistently...
By RobS , 3 days ago
-
RE: Mitsu PUHZ120Y 'Outdoor Temp 'error?
Thanks David & James It almos...
By DavidAlgarve , 3 days ago
-
RE: Surge protection devices SPDs
@trebor12345 - your original Topic about the right type...
By Transparent , 3 days ago
-
RE: Help needed with Samsung AE120RXYDEG
@tomf I’ve been sent this from a service engineer at Sa...
By Mars , 3 days ago
-
RE: Buying large amp bidirectional RCD and RCBO
Yes... I went through this particular headache and ende...
By bobflux , 4 days ago
-
O-oh! Let's take this as an opportunity to 'pass the ...
By Transparent , 4 days ago