Solar Thermal System Design Issue: Resol Delta Sol BS Plus controller
I have a solar thermal system with a Resol Delta Sol BS Plus controller. I have recently had some works done to the system and since then it does not appear to be functioning properly and I wondered if anyone had any ideas about what could be wrong.
The issue is that when the system’s pumps turn off, either because a store has reached its max temperature or because the system is checking its temperature during an Oscillating Break Time, the system (through the collector sensor) no longer detects an increase in temperature at the top of the collectors.
What happens is that the pumps turn off and the collector sensor actually registers a decrease in temperature at the top of the panels. This goes on for as long as the pumps are off and the temperature just falls steadily.
If the pumps are turned back on manually, the flow of the system start circulating again, the temperature reading at the collector sensor then rockets up by 10 – 20 degrees or more and then levels out once the pumps have taken back control, released the heat through the heat exchangers etc.
It’s an issue because it means that (a) the store prioritisation is no longer working properly and (b) the system doesn’t detect when it’s about to overheat and so doesn’t restart the pumps in an emergency fail-safe function (e.g. under the OREC or OCX functions).
It didn’t used to be a problem. On a sunny day, what used to happen is that when the pumps turned off, the collector sensor would detect a steadily rising temperature and then the system behaved as expected, heating the stores in the right priority… with the other system controller functions etc.
Has anyone ever heard of or encountered this issue?
What work was carried out on your system? Did the people carrying out the work not test the systems operation after the work was completed?
If possible I would suggest that you call them back to rectify the problems it would appear that they created.
The work involved upgrading a lot of the pipework and the circuit pumps and installing a new third circuit. The people who installed it are struggling to identify what the problem is. They're coming back again next week but I'm trying to get a head start on the issue to understand from all the experts out there whether anyone has had this sort of issue before, or if anyone has any ideas as to what it could be, so I can make sure things are steered in the right direction.
- 25 Forums
- 1,513 Topics
- 31.8 K Posts
- 23 Online
- 1,283 Members
Join Us!
Latest Posts
-
RE: Additional Battery v Wind Turbine v Ripple
I should add, being an investment, the value of your in...
By Old_Scientist , 5 hours ago
-
RE: Ecodan - flow rates, sensors, settings
Achieving an accurate flow measurement is probably the ...
By Derek M , 8 hours ago
-
RE: Ecodan ASHP - How to optimise my set up?
Again, thank you for another thorough post, @derek-m - ...
By rhh2348 , 10 hours ago
-
RE: Delivering a smart and secure electricity system: government consultation
@Transparent.Now that I am represented by a new MP I th...
By IanMK13 , 12 hours ago
-
RE: Vaillant aroTHERM plus not level or flat - what base is best under an external unit?
Similar thread here
By Johnmo , 13 hours ago
-
RE: VDI 2035 heating water specification
Been looking and it seems a good little project. Ever...
By Johnmo , 2 days ago
-
RE: Do I accept an ASHP and Solar Panel retrofit under the HUG 2 scheme?
Will do. I'm currently waiting for another survey / vis...
By dssr , 2 days ago
-
The company that did the borehole were expecting us to ...
By Johnmo , 2 days ago
-
-
RE: The Misquote That Ruined the Heating Industry
@abernyte manufacturer training is pretty average. They...
By Mars , 2 days ago
-
-
RE: ECO4 Scheme and EPC ratings
@mellow Thanks. Given there is a scheme requirement to ...
By Old_Scientist , 3 days ago
-
RE: Do I just go with the lowest quote for my heat pump?
@jancold To me its a no-brainer then, a max 40C flow te...
By bontwoody , 3 days ago
-
-
RE: Heat Pump Books Beginners – Bodge Buster & From Zero To Heat Pump Hero
@editor Presumably he had some good weather Compensatio...
By Toodles , 4 days ago
-
RE: New Vaillant 7kW aroTherm ASHP or oil boiler dilemma/decision??
Storage capacity really is dependent on storage tempera...
By Johnmo , 4 days ago
-
RE: HP Cycling, Expected or Undesirable
Just a little update. I ordered a longer shielded twin ...
By bontwoody , 4 days ago
-
RE: Domestic hot water timer doing crazy things on my Grant Aerona3 10kW air source heat pump
Thanks @allyfish for the pics and info. Spoke to the in...
By Mellow , 4 days ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
It's been a busy day for calls and emails from Aira. I ...
By MikeH , 4 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Hmm. A bit of a nuanced answer, methinks. As I've alr...
By Majordennisbloodnok , 4 days ago
Latest Topics
-
Ecodan - flow rates, sensors, settings
By rhh2348 11 hours ago
-
Replacing mains water with well water
By Johnmo 2 days ago
-
Additional Battery v Wind Turbine v Ripple
By bontwoody 2 days ago
-
By jamespipe 3 days ago
-
VDI 2035 heating water specification
By Johnmo 3 days ago
-
Do I just go with the lowest quote for my heat pump?
By Jancold 5 days ago
-
The Misquote That Ruined the Heating Industry
By Alec Morrow 6 days ago
-
Battery Storage Wiring Gauge Question
By Puff 6 days ago
Members Online
No online members at the moment