Solar Thermal System Design Issue: Resol Delta Sol BS Plus controller
I have a solar thermal system with a Resol Delta Sol BS Plus controller. I have recently had some works done to the system and since then it does not appear to be functioning properly and I wondered if anyone had any ideas about what could be wrong.
The issue is that when the system’s pumps turn off, either because a store has reached its max temperature or because the system is checking its temperature during an Oscillating Break Time, the system (through the collector sensor) no longer detects an increase in temperature at the top of the collectors.
What happens is that the pumps turn off and the collector sensor actually registers a decrease in temperature at the top of the panels. This goes on for as long as the pumps are off and the temperature just falls steadily.
If the pumps are turned back on manually, the flow of the system start circulating again, the temperature reading at the collector sensor then rockets up by 10 – 20 degrees or more and then levels out once the pumps have taken back control, released the heat through the heat exchangers etc.
It’s an issue because it means that (a) the store prioritisation is no longer working properly and (b) the system doesn’t detect when it’s about to overheat and so doesn’t restart the pumps in an emergency fail-safe function (e.g. under the OREC or OCX functions).
It didn’t used to be a problem. On a sunny day, what used to happen is that when the pumps turned off, the collector sensor would detect a steadily rising temperature and then the system behaved as expected, heating the stores in the right priority… with the other system controller functions etc.
Has anyone ever heard of or encountered this issue?
What work was carried out on your system? Did the people carrying out the work not test the systems operation after the work was completed?
If possible I would suggest that you call them back to rectify the problems it would appear that they created.
The work involved upgrading a lot of the pipework and the circuit pumps and installing a new third circuit. The people who installed it are struggling to identify what the problem is. They're coming back again next week but I'm trying to get a head start on the issue to understand from all the experts out there whether anyone has had this sort of issue before, or if anyone has any ideas as to what it could be, so I can make sure things are steered in the right direction.
- 26 Forums
- 2,238 Topics
- 49.8 K Posts
- 360 Online
- 5,900 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
EPCI charged £12k after the grant for a 14kW system - s...
By downfield , 11 minutes ago
-
Hi @eliuccio - you are in the right place, and asking...
By Transparent , 2 hours ago
-
RE: Solar inverters - where does the energy go when clipping?
I think I must query the sources on which Greenmatch ha...
By Transparent , 2 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@jamespa I rolled my own storage. £40 per kW...
By swwils , 3 hours ago
-
RE: Replacing knackered oil boiler with Samsung ASHP - Perthshire
This is how I run my Samsung 12kW ASHP with a 3rd party...
By Old_Scientist , 4 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@cathoderay thanks- yes will keep an eye out for the de...
By benson , 18 hours ago
-
RE: Renewables & Heat Pumps in the News
Hoping so as well! I am no specialist. The language use...
By Batpred , 18 hours ago
-
Do you need the DHW tank as high as 50°C @egp01 ? Ha...
By Transparent , 20 hours ago
-
RE: The Hidden Secret to a Successful Heat Pump: Pipe Size Matters
@old_scientist Just to say that during our retrofit, we...
By Toodles , 21 hours ago
-
RE: Daikin Altherma 3M ASHP and British Gas Hive Home
We have a Daikin EDLA08 8kW monobloc (DHW is handled se...
By Toodles , 21 hours ago
-
@old_scientist @jamespa So this was last nights DHW r...
By bontwoody , 22 hours ago
-
-
@springswood we install these nationwide and I have the...
By dgclimatecontrol , 22 hours ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
Just returning to this issue after a few days working i...
By Mike Patrick , 24 hours ago
-
RE: DESNZ doing a survey which asks the right questions!
Fair comment. I have a feeling that ratings more gen...
By JamesPa , 1 day ago
-
RE: Daikin Octopus installation update - I saw my first defrost. 😍😂
@jancold Not a plumber but I believe that i...
By RadWhisperer , 1 day ago
-
Thanks! My consumer unit collection is ready with the W...
By Batpred , 1 day ago
-
RE: Designing my house system with a mix of air to air and air to water
@jamespa Cheers James, it's great reading. In quite a f...
By pipebaron , 2 days ago
-
RE: PV Panels on roof in Conservation Area
If there is any way you can determine daily oil consump...
By JamesPa , 2 days ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
attached is prelagged in case indicates anything. &nb...
By Crimson , 2 days ago