Thank s for the questions @derek-m 

we have had accumulated heat when we are away for several days. It gets up to 70c in one sunny mid-summer day and we have had neighbours letting out hot water in the past, so not ideal.

However we now have a bigger tank with 250ltr volume and a pressure release valve as required. So we don’t know how hot it will get but anticipate it will, as before. 

If I can it would be good to know what the system is capable of before we go away.... and come back to a bigger problem.

addition

the panels are evacuated glass tubes with sealed copper pipe core filled with fluid, pushed into a top manifold collector immersed in a circulating wet system with glycol.

Im not sure if it matters if the copper and glass tubes over heat- just assumed it wasn’t worth testing it out. As for the glycol I don’t know how it would behave at very high temperature. My fear is that water boils at 100c and I think that the tank got pretty close to that at one time.


   
ReplyQuote
Transparent
(@transparent)
Illustrious Member Moderator
11289 kWhs
Veteran Expert
Joined: 3 years ago
Posts: 1938
 

Posted by: @sunandair

just wondered if the Ecodan could work in reverse to cool it while we were away.

Unlikely... because you've got a unit designed for the UK market.

Heat pumps for the USA market usually incorporate a 4-port (2-way) valve which allows them to double-up as an air-conditioner in hot weather.
Here's a typical diagram in which I've highlighted that valve.

image

If your starting point is that you already have the Ecodan ASHP installed, then you need to look for an alternative strategy to get rid of the excess heat in the DHW cylinder.

In my case I have a Thermal Store, which means it also supplies Under-Floor Heating (UFH).

So I've designated one UFH loop which can be opened in the event of an over-temperature sensor triggering on the thermal-store.
That enables the thick concrete pad of that UFH zone to act as a dump-load.

You need to think of somewhere else (other than the Ecodan) which could act as a dump-load for you.

Save energy... recycle electrons!


   
👍
1
ReplyQuote
(@derek-m)
Illustrious Member Member
15282 kWhs
Veteran Expert
Joined: 4 years ago
Posts: 4432
 

Posted by: @sunandair

Thank s for the questions @derek-m 

we have had accumulated heat when we are away for several days. It gets up to 70c in one sunny mid-summer day and we have had neighbours letting out hot water in the past, so not ideal.

However we now have a bigger tank with 250ltr volume and a pressure release valve as required. So we don’t know how hot it will get but anticipate it will, as before. 

If I can it would be good to know what the system is capable of before we go away.... and come back to a bigger problem.

addition

the panels are evacuated glass tubes with sealed copper pipe core filled with fluid, pushed into a top manifold collector immersed in a circulating wet system with glycol.

Im not sure if it matters if the copper and glass tubes over heat- just assumed it wasn’t worth testing it out. As for the glycol I don’t know how it would behave at very high temperature. My fear is that water boils at 100c and I think that the tank got pretty close to that at one time.

Please correct me if I am wrong, but I would assume that your system is designed to pump water through the solar thermal panels, until the water temperature in the hot water cylinder reaches a maximum setting, at which point it would stop pumping water through the panels until the temperature in the hot water cylinder falls to a lower setting. Such a safety system would be required to prevent the water in the cylinder from boiling, and hence pressurising the cylinder.

This would lead me to believe that the solar thermal panels are capable of coping with the high temperatures to which they may be heated, when there is no cooling water flowing through them.

Please provide details of the make and model of your system and size of panels etc.

 


   
ReplyQuote
(@derek-m)
Illustrious Member Member
15282 kWhs
Veteran Expert
Joined: 4 years ago
Posts: 4432
 

@transparent

As far as I am aware, all ASHP's contain a 4-port reversing valve, since this is required to perform the defrost cycle.

According to the operators manual, the Ecodan can be operated in cooling mode, though this would not be the norm when used with radiators, since there could be a high likelihood of puddles of water due to condensation.

It may therefore be possible to pass cooling water through the heating coil within the hot water cylinder, though how successful this may prove could be dependent upon the relative position of the heating coil associated within the heat pump, in relation to that associated with the solar thermal system.

It would also be necessary to force, or manually set, the diverter valve in DHW mode, to prevent the possibility of puddles underneath the radiators.


   
ReplyQuote
Transparent
(@transparent)
Illustrious Member Moderator
11289 kWhs
Veteran Expert
Joined: 3 years ago
Posts: 1938
 

Posted by: @derek-m

I would assume that your system is designed to pump water through the solar thermal panels, until the water temperature in the hot water cylinder reaches a maximum setting,

You are correct @derek-m

A solar thermal system (which is pressurized of course) might contain water above 100degC. The 'proper' pipework has to be operable up to 160degC

image

The circuit will also include a temperature/pressure relief valve.
When it's triggered, it dumps the water/glycol mix into a Collection/Recovery tank.

That then prevents the solar-thermal system from operating of course.

This post was modified 2 years ago by Transparent

Save energy... recycle electrons!


   
ReplyQuote
(@derek-m)
Illustrious Member Member
15282 kWhs
Veteran Expert
Joined: 4 years ago
Posts: 4432
 

@transparent

If my understanding is correct, a solar thermal system should operate in the following manner.

When the temperature of the panels is below that of the hot water cylinder, the circulation pump is stopped, and the liquid, be it water or a water glycol mixture will drain into the reservoir tank. The system, although sealed, contains both liquid and air.

As the temperature of the panels increases above that of the hot water cylinder, by a defined amount, the circulation pump will start, and pump the liquid, at a controlled rate, from the reservoir up through the panels. The liquid flowing through the panels will absorb heat energy, which will be carried via the return pipework to the heating coil inside the hot water cylinder. Thermal energy will therefore be transferred from the panels to the hot water cylinder.

Whilst there is sufficient solar energy available, the temperature in the hot water cylinder will increase. This process is fine, until the temperature of the water within the cylinder starts to approach undesirable levels. I have just had a quick look at the manual for the Resol Controller, which shows a maximum temperature limit, which when reached, stops the circulation pump from operating. The liquid therefore drains back to the reservoir, and no further heat transfer takes place. The system therefore contains over-temperature protection, which in the Resol case can be set as high as 90C.

I believe that once the cylinder temperature falls to the point where the over-temperature limits resets, the system reverts back to normal operation.

Since a solar thermal system is required to operate without constant human monitoring and intervention, I must assume that the panels are designed to cope with the maximum possible temperature that may occur when liquid is not flowing around the system.

I therefore question the need to actually cool the hot water cylinder, with a heat pump or otherwise. If the temperature in the cylinder is getting higher than desired, then check the setting of the maximum temperature limit, and lower this if necessary.


   
ReplyQuote



Transparent
(@transparent)
Illustrious Member Moderator
11289 kWhs
Veteran Expert
Joined: 3 years ago
Posts: 1938
 

Posted by: @derek-m

I have just had a quick look at the manual for the Resol Controller, which shows a maximum temperature limit, which when reached, stops the circulation pump from operating. The liquid therefore drains back to the reservoir, and no further heat transfer takes place [.....]

I believe that once the cylinder temperature falls to the point where the over-temperature limits resets, the system reverts back to normal operation.

Possibly. But I'm not aware of a 'reservoir' which allows that to occur.

The one I have simply holds the liquid which has been allowed to drain out via the escape valve.
You have to retrieve it manually and pour it back into the solar-thermal pipework.
Until then, the system won't work because you've got no fluid to pump! 🤨 

SolarThermalReservoir

 

Save energy... recycle electrons!


   
ReplyQuote
(@alan-m)
Eminent Member Member
419 kWhs
Joined: 2 years ago
Posts: 11
Topic starter  

@transparent @derek-m I have settings for Maximum Store (hot water tank) temperature and Emergency Collector temperature,

exceeding either of which results in the Solar Thermal pump shutting down. The expansion tanks attached to my installation are shown below.

IMG 20230406 151622

It got pretty hot last summer and the system seemed to cope. The data points I am now logging should show if any of these limits get reached.

16kW Midea Monobloc R32 Heat Pump (Heating & DHW)
4kW Solar PV (No battery storage yet)
CPC 12 INOX Solar Thermal (DHW)


   
👍
2
ReplyQuote
Transparent
(@transparent)
Illustrious Member Moderator
11289 kWhs
Veteran Expert
Joined: 3 years ago
Posts: 1938
 

That's a great photo @alan-m - for all sorts of reasons 🙂 

We can see the flow & return stainless-steel flexible pipe run to the roof-top collector, the pump on the return side, and the connections to the pressure-vessel and reservoir.

Better still, it's installed neatly onto a plywood sheet, which is positioned in front of a timber-frame with internal insulation boarding.
It's the sort of "this is how it should be done" pic which we need more of on this forum.

Save energy... recycle electrons!


   
👍
1
ReplyQuote
(@sunandair)
Prominent Member Member
2811 kWhs
Joined: 2 years ago
Posts: 376
 
08B9566D 64D2 42FD AB34 7A28ED8EB48D
EDA14B8E 4D9A 400A B61C C8DA9CD90843

Posted by: @derek-m

Posted by: @sunandair

Thank s for the questions @derek-m 

we have had accumulated heat when we are away for several days. It gets up to 70c in one sunny mid-summer day and we have had neighbours letting out hot water in the past, so not ideal.

However we now have a bigger tank with 250ltr volume and a pressure release valve as required. So we don’t know how hot it will get but anticipate it will, as before. 

If I can it would be good to know what the system is capable of before we go away.... and come back to a bigger problem.

addition

the panels are evacuated glass tubes with sealed copper pipe core filled with fluid, pushed into a top manifold collector immersed in a circulating wet system with glycol.

Im not sure if it matters if the copper and glass tubes over heat- just assumed it wasn’t worth testing it out. As for the glycol I don’t know how it would behave at very high temperature. My fear is that water boils at 100c and I think that the tank got pretty close to that at one time.

Please correct me if I am wrong, but I would assume that your system is designed to pump water through the solar thermal panels, until the water temperature in the hot water cylinder reaches a maximum setting, at which point it would stop pumping water through the panels until the temperature in the hot water cylinder falls to a lower setting. Such a safety system would be required to prevent the water in the cylinder from boiling, and hence pressurising the cylinder.

This would lead me to believe that the solar thermal panels are capable of coping with the high temperatures to which they may be heated, when there is no cooling water flowing through them.

Please provide details of the make and model of your system and size of panels etc.

 

Hi Derek sorry for delay-travelling- ive grabbed a file on the system and I’m photographing info while on a train.

The main controller is a MTDCV2S3 or MTDC Temperature Difference Controller. The system has a program built in to set up a system recooling. What happens is at a given time at night the pump is activated to circulate the water through the solar panel and cooling the water in the cylinder overnight. 

The attached parts list might be helpful. Also attached is schematic Andy a drawing of the pumping station.

as stated previously the solar panel is a 20 glass tube arrangement with sealed copper cores containing a heat transfer liquid inside. These copper cores plug into a top manifold and transfers the heat to the circulating glycol.

we have the st.st. pipework as pictured by @transparent as well as the pressure release valve and discharge tank. 

 

The system operates very effectively and we’ve never had an overheat but I’m wanting to exploit any possible recooling mechanism which might work from the Ecodan or as @transparent says - to dump the heat in some way during holiday periods.

 


   
ReplyQuote
(@sunandair)
Prominent Member Member
2811 kWhs
Joined: 2 years ago
Posts: 376
 
F50247FB 9B1E 43E3 BBF4 A57A92C922A4

   
ReplyQuote
(@sunandair)
Prominent Member Member
2811 kWhs
Joined: 2 years ago
Posts: 376
 
8B86C8BA 43C1 4DAD 9EA2 4246036EFDB1

The pumping station showing the security pressure release valve and the flow regulating valve.etc.


   
ReplyQuote



Page 2 / 3



Share:

Join Us!

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security