GSHP COP with and without backup boiler
Good morning,
I have recently had a GSHP installed (Vaillant Flexotherm) including separate electric meters for the GSHP and GSHP Backup boiler. I also have a Sontex heat meter installed.
I have been monitoring the COP of the system daily to try and improve efficiency. The problem is that the efficiency increase greatly on the days the backup boiler is turned on once per week (for legionella) which I'm struggling to understand?? As far as I'm aware the backup boiler roughly produces 1kw of heat per 1kw electric input.
I'm calculating COP as follows. Heat Kw/ (GSHP Electric + Backup boiler Electic)
For example on the days the backup boiler is not on I'm averaging ~3.8 COP
The days the backup boiler is on I'm averaging ~4.2 COP
Any ideas will be greatly appreciated.
Happy to provide more info if needed?
That does sound surprising!
I expect that you're right - the backup heater is likely to be an inline immersion somewhere.
How do you measure the electrical energy? How well are the Sontex temperature probes attached (perhaps a photo?).
Which Flexotherm unit is it - I think they come in 5/8/11kW. So far as I can see, the units are simple on/off gshp ones with impressive COP, not inverter units(correct me if I'm wrong!).
If you run the unit continuously for (eg) an hour (make sure your thermostat is high) without backup heater, what heat energy do you get, and what Electrical does it take?
Ditto, but now with the heater on - what heat and electrical energy?
Thanks for the reply.
The electrical energy is measured via separate electrical meters, one for renewable (i.e. GSHP) and one for non renewable (i.e. backup boiler). I have attached a photo of this and the heat meters. Also the photo of where the sensors are connected.
It is a Flexotherm 11kw. It is sold as having a COP of 4.73 @ 35c flow temp. I'm unsure about whether it has an inverter.
I've run the pump with and without the backup boiler on.
26/01 - Backup boiler off - Electric 44.38kw; Heat 170kw; COP 3.83
30/01 - Backup boiler on - Electric 46.1kw (of which 5.24kw backup boiler); Heat 219kw; COP 4.75
One thought I had was that the DHW when being run by the GSHP was killing the efficiency/COP somehow? Maybe flow temps too high??
I don't think it's an inverter model - this says not:
https://www.toptenuk.org/consumer/product/view/VaillantGmbHflexoTHERMexclusiveVWF874
Perhaps you're right, and it's a "marginal COP" thing due to the DHW temperature. It seems very surprising. How hot does it run to for DHW?
Can you separate out hot water and heating? I assume that you have a hot water tank - does it have it's own immersion heater that you could use for a while, and stop the GSHP trying to heat it. Then run the experiment again - measure Heat and Elec both with and without the backup heater ?
Yes we have a hot water tank so I will try your suggestion of using the immersion to isolate the Heating and DHW.
The flow temps get up to 60c when the DHW is on. Looking at the 'Marginal COP idea' that could make sense if the flow temps are so high its actually less efficient.
I'll let you know how I get on.
- 26 Forums
- 2,114 Topics
- 46.4 K Posts
- 53 Online
- 3,410 Members
Join Us!
Latest Posts
-
Delighted to hear this went well. It looks very neat ...
By JamesPa , 1 hour ago
-
RE: No-code, plug-and-play monitoring for your heat pump
The issue with the Grant is that you have to wire direc...
By Grantmethestrength , 5 hours ago
-
RE: Is this just haze or something more?
I am not a scientist nor a meteorologist and I know the...
By Toodles , 5 hours ago
-
RE: Benefits of an extra horizontal loop for GSHP
It will improve performance, but by how much depends on...
By Brendon Uys , 10 hours ago
-
RE: The good, the bad and the not that great – my heat pump installation
Said I would pop back with a update. Only Mr Jesus h...
By Burtis , 24 hours ago
-
RE: Buffers, hot water and cooling
Thats presumably heat pump DT, what about radiator DT a...
By JamesPa , 1 day ago
-
RE: Who's your electricity provider and what's your tariff?
@chandykris Exactly the same here. We now have 13.5kWh ...
By Old_Scientist , 1 day ago
-
Compressor and Evaporator Stratification
I have had a few issues with my Hitachi spilt heatpump ...
By trebor12345 , 1 day ago
-
RE: Wood burner with ASHP - direct air?
This depends on the size of your wood burner and size/t...
By Lucia , 2 days ago
-
RE: Difficult positioning of air source heat pump
@rikiarn It's a not a buffer it's a volumiser which is ...
By Lucia , 2 days ago
-
RE: Is your heat pump insured?
To make things clear, lots of insurance companies cover...
By Lucia , 2 days ago
-
RE: Boxt Heat Pump Installation Experience
@adrian any updates since installation? How is it perfo...
By Ashfp , 2 days ago
-
RE: Say hello and introduce yourself
Hi @seatonian - Yes, I know Seaton, and I have the Nat...
By Transparent , 3 days ago
-
@seatonian got your email. Will connect you with a reco...
By Mars , 4 days ago
-
@downfield and @toddles, this isn’t in the settings cur...
By Mars , 6 days ago
-
RE: Homely launched for Grant Aerona ASHP control
I haven't bought the Aerona Smart Controller (£700!) bu...
By Prunus , 6 days ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
For the record, Grant supply ethylene glycol for their ...
By Prunus , 6 days ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
@skyefarmer amazing. Well done!
By Mars , 6 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Ebac 5kw - Monobloc R32. Developed and made in UK - Mit...
By marcinwloch69@gmail.com , 1 week ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Just another thought - it might be worth thinking about...
By JamesPa , 1 week ago