GSHP COP with and without backup boiler
Good morning,
I have recently had a GSHP installed (Vaillant Flexotherm) including separate electric meters for the GSHP and GSHP Backup boiler. I also have a Sontex heat meter installed.
I have been monitoring the COP of the system daily to try and improve efficiency. The problem is that the efficiency increase greatly on the days the backup boiler is turned on once per week (for legionella) which I'm struggling to understand?? As far as I'm aware the backup boiler roughly produces 1kw of heat per 1kw electric input.
I'm calculating COP as follows. Heat Kw/ (GSHP Electric + Backup boiler Electic)
For example on the days the backup boiler is not on I'm averaging ~3.8 COP
The days the backup boiler is on I'm averaging ~4.2 COP
Any ideas will be greatly appreciated.
Happy to provide more info if needed?
That does sound surprising!
I expect that you're right - the backup heater is likely to be an inline immersion somewhere.
How do you measure the electrical energy? How well are the Sontex temperature probes attached (perhaps a photo?).
Which Flexotherm unit is it - I think they come in 5/8/11kW. So far as I can see, the units are simple on/off gshp ones with impressive COP, not inverter units(correct me if I'm wrong!).
If you run the unit continuously for (eg) an hour (make sure your thermostat is high) without backup heater, what heat energy do you get, and what Electrical does it take?
Ditto, but now with the heater on - what heat and electrical energy?
Thanks for the reply.
The electrical energy is measured via separate electrical meters, one for renewable (i.e. GSHP) and one for non renewable (i.e. backup boiler). I have attached a photo of this and the heat meters. Also the photo of where the sensors are connected.
It is a Flexotherm 11kw. It is sold as having a COP of 4.73 @ 35c flow temp. I'm unsure about whether it has an inverter.
I've run the pump with and without the backup boiler on.
26/01 - Backup boiler off - Electric 44.38kw; Heat 170kw; COP 3.83
30/01 - Backup boiler on - Electric 46.1kw (of which 5.24kw backup boiler); Heat 219kw; COP 4.75
One thought I had was that the DHW when being run by the GSHP was killing the efficiency/COP somehow? Maybe flow temps too high??
I don't think it's an inverter model - this says not:
https://www.toptenuk.org/consumer/product/view/VaillantGmbHflexoTHERMexclusiveVWF874
Perhaps you're right, and it's a "marginal COP" thing due to the DHW temperature. It seems very surprising. How hot does it run to for DHW?
Can you separate out hot water and heating? I assume that you have a hot water tank - does it have it's own immersion heater that you could use for a while, and stop the GSHP trying to heat it. Then run the experiment again - measure Heat and Elec both with and without the backup heater ?
Yes we have a hot water tank so I will try your suggestion of using the immersion to isolate the Heating and DHW.
The flow temps get up to 60c when the DHW is on. Looking at the 'Marginal COP idea' that could make sense if the flow temps are so high its actually less efficient.
I'll let you know how I get on.
- 26 Forums
- 2,323 Topics
- 52.1 K Posts
- 161 Online
- 5,979 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Electricity price predictions
@lucia Absolutely. And all this talk about being rea...
By Batpred , 2 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
And I thought I was the one with the taxi on speed dial...
By Majordennisbloodnok , 4 hours ago
-
RE: Solar panels on side of house to heat water
@paultheheating We are looking into PV panels at the...
By Batpred , 6 hours ago
-
@jamespa They are indeed mysterious devices!!! I have o...
By Toodles , 9 hours ago
-
RE: Heat Pump Training vs. Real-World Installation
Congratulations on passing the course. The observation...
By Max Abbey , 10 hours ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Owners
@sim0n0 Here's a reply to help you out. As a owner ...
By trebor12345 , 12 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
The engineer came yesterday and as the rooms were ok te...
By AdamK , 12 hours ago
-
RE: Replacing my 18 month old Hitachi Yutaki ASHP
@jamespa Can I check something that I done some weeks a...
By trebor12345 , 13 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
The problem I see with A2A (and I'm interested if there...
By Temperature_Gradient , 14 hours ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
@temperature_gradient I specifically explained to my po...
By Toodles , 14 hours ago
-
RE: Grant Aerona Short Cycling
@damonc I was refering to the 'standard' energy sticker...
By MikeFl , 17 hours ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
@hcas where do I find Havenwise Support? On...
By Morgan , 18 hours ago
-
RE: Should Our Water Circulation Pump Be Configured to Run All The Time?
We recently (Aug 25) had a Grant Aeorana 3 installed un...
By GA3_USR , 23 hours ago
-
RE: Grant Aerona circulation/system pump staying on
My AERONA 3 circulation pump runs constantly whatever t...
By damonc , 1 day ago
-
RE: Configuring third party dongle for Ecodan local control
Thanks, @sheriff-fatman. Happy for you to search any po...
By Majordennisbloodnok , 1 day ago
-
Thanks, @cathoderay. I was aware of some changes to ...
By Majordennisbloodnok , 1 day ago
-
RE: Trying to understand my Nibe F1245
@greenlight Many thanks for the information, it's set m...
By Chris12 , 2 days ago
-
This is what I answered, I really have no hope: "......
By Batpred , 2 days ago
-