Ground Source Heat Pump Systems and Their Design
This article showcases a ground source heat pump installation I spearheaded, with Darren Jones expertly handling the plant room's pipework. At the heart of this project is a 28kW single-phase CTC heat pump, seamlessly integrated with a ground source collector drilled by my son.
The innovative system configuration includes two 14kW brine to water units directly connected to a robust screed underfloor heating setup, avoiding the need for a buffer tank or system separation. The control strategy for the expansive 650 square meter property is straightforward yet effective, relying on the heat pump and adjustable thermostats in four bedrooms, leaving the remainder of the space to be regulated by the heat pump's built-in temperature sensor. This design epitomises an open zone, low-temperature approach, promising excellent efficiency and significantly reduced operational costs.
Additionally, the inclusion of a passive cooling mechanism ensures the home remains comfortable throughout the year, utilising minimal power for maximum comfort.
From the provided graphs, it is evident that with an ambient temperature of 3°C, the house maintained a comfortable 20°C. The brine temperature entering the unit was between 7-8°C, with an average flow temperature of about 30°C. Based on the manufacturer's data, the extrapolated coefficient of performance (COP) ranges between 6 and 6.5. Given that this is at the end of the heating season, and the system has been operational for nearly a year, this COP is the minimum expected.

The system's efficiency is highlighted by its approximately hourly cycling under partial load conditions, demonstrating that a buffer tank or system separation is unnecessary with proper design. Unlike on-off compressors, which are prone to cycling and resultant performance degradation, this system showcases the benefits of precise design and selection.
Our approach to system design is grounded in practical, real-world training offered at Ultimate Training and Technical. This departs from outdated methodologies, moving beyond mere theoretical concepts to embrace modern, evidence-based strategies. With the national average seasonal coefficient of performance (SCOP) around 2.8, and the need for heat pumps to be more cost-effective than fossil fuels necessitating a SCOP of 3.5, our approach emphasises the importance of high SCOPs achievable through the right equipment and meticulous system design and commissioning.
Currently viewing this topic 1 guest.
- 26 Forums
 - 2,265 Topics
 - 50.6 K Posts
 - 237 Online
 - 5,924 Members
 
Join Us!
Podcast Picks
Latest Posts
- 
                        
RE: UFH downstairs and radiators upstairs balancing question
This is confusing dude. The 'stat which is a vaillant s...
By Walnut-tree-cottage , 13 minutes ago
 - 
                        
RE: Oil Boiler & Heat Pump Hybrid System
thanks for your reply, tried to explain that tenants fo...
By paultheheating , 2 hours ago
 - 
                        
RE: Help me keep the faith with my air source heat pump installation
@jamespa I contacted the installer and asked them to ba...
By AdamK , 6 hours ago
 - 
                        
RE: Who has a V2G EV installation
They certainly look stylish! But it seems that Ander...
By Batpred , 8 hours ago
 - 
                        
                                RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
And if MCS don’t have one on record that’s an issue bec...
By Mars , 9 hours ago
 - 
                        
                                RE: My DIY Heat Pump installation
@polar-bear, I take my hat off to you. I wish I had the...
By Mars , 9 hours ago
 - 
                        
                                RE: Electricity price predictions
One persons view In sync with the Nesta figures s...
By Jeff , 11 hours ago
 - 
                        
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
Ok so that seems to be the key point namely only mcs ca...
By JamesPa , 13 hours ago
 - 
                        
RE: One flow valve appears to be duff
You might want to consider the following common faults:...
By IaAck , 20 hours ago
 - 
                        
                                RE: When to use Octopus Intelligent Go tariff with my heat pump and battery
We are on the Intelligent Octopus Go tariff. We instal...
By GrahamF , 22 hours ago
 - 
                        
RE: New build installation query
@paullacey While the others wait for more info do you m...
By ASHP-BOBBA , 1 day ago
 - 
                        
                                RE: British Gas Heat Pump Installation Complaint
@bgno, the other consideration for legionella cycles ar...
By Mars , 2 days ago
 - 
                        
                                @old_scientist I dont monitor the tank temperature but ...
By bontwoody , 2 days ago
 - 
                        
                                RE: Say hello and introduce yourself
Hello @paultheheating - I'm a rural Moderator! What's...
By Transparent , 2 days ago
 - 
                        
RE: What valves to replace radbots?
Yes. Radbots just replace TRV heads. TRV heads push t...
By JamesPa , 2 days ago
 - 
                        
RE: When will fusion be producing energy?
I am thinking of the case where AI was able to distingu...
By Batpred , 2 days ago
 - 
                        
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
Very definitely. I think the market has changed a bit...
By JamesPa , 3 days ago
 - 
                        
                                RE: Buying large amp bidirectional RCD and RCBO
The following diagram is taken from the Meter Operator'...
By Transparent , 3 days ago
 