Ground Source Heat Pump Systems and Their Design
This article showcases a ground source heat pump installation I spearheaded, with Darren Jones expertly handling the plant room's pipework. At the heart of this project is a 28kW single-phase CTC heat pump, seamlessly integrated with a ground source collector drilled by my son.
The innovative system configuration includes two 14kW brine to water units directly connected to a robust screed underfloor heating setup, avoiding the need for a buffer tank or system separation. The control strategy for the expansive 650 square meter property is straightforward yet effective, relying on the heat pump and adjustable thermostats in four bedrooms, leaving the remainder of the space to be regulated by the heat pump's built-in temperature sensor. This design epitomises an open zone, low-temperature approach, promising excellent efficiency and significantly reduced operational costs.
Additionally, the inclusion of a passive cooling mechanism ensures the home remains comfortable throughout the year, utilising minimal power for maximum comfort.
From the provided graphs, it is evident that with an ambient temperature of 3°C, the house maintained a comfortable 20°C. The brine temperature entering the unit was between 7-8°C, with an average flow temperature of about 30°C. Based on the manufacturer's data, the extrapolated coefficient of performance (COP) ranges between 6 and 6.5. Given that this is at the end of the heating season, and the system has been operational for nearly a year, this COP is the minimum expected.
The system's efficiency is highlighted by its approximately hourly cycling under partial load conditions, demonstrating that a buffer tank or system separation is unnecessary with proper design. Unlike on-off compressors, which are prone to cycling and resultant performance degradation, this system showcases the benefits of precise design and selection.
Our approach to system design is grounded in practical, real-world training offered at Ultimate Training and Technical. This departs from outdated methodologies, moving beyond mere theoretical concepts to embrace modern, evidence-based strategies. With the national average seasonal coefficient of performance (SCOP) around 2.8, and the need for heat pumps to be more cost-effective than fossil fuels necessitating a SCOP of 3.5, our approach emphasises the importance of high SCOPs achievable through the right equipment and meticulous system design and commissioning.
Professional heat pump installer: Technical Director Ultimate Renewables Director at Heacol Ltd
- 24 Forums
- 1,413 Topics
- 29.7 K Posts
- 25 Online
- 1,199 Members
Join Us!
Latest Posts
-
RE: Gas Combi to ASHP - Making sense of survey results and proposal.
@irmartini Hi, Why not lower your gas boiler flow temp ...
By JEH , 9 hours ago
-
In an ideal world a heat pump unit would contain two co...
By Derek M , 11 hours ago
-
RE: ASHP Advice: High Temperature vs. Low Temperature Heat Pump For Microbore
@jamespa I fully agree with James that a HT heat pump...
By Derek M , 13 hours ago
-
RE: Installing your own ASHP - DIY
@tomasmcguinness Have you been able to perform any sani...
By IanMK13 , 16 hours ago
-
-
RE: Viessmann Vitocal 250-A in the UK
For reference, I have a 10 kWh Viessmann 151-A installe...
By GC61 , 18 hours ago
-
RE: Vaillant Arotherm Settings for New Installation
@drew-pa Ah thanks. Good to know I dont have a misconce...
By bontwoody , 19 hours ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
On the whole marketing claims vs reality on performance...
By GunboatDiplomat , 19 hours ago
-
RE: Microbore Central Heating Plumbing, will it be a barrier / pain?
@mattc All the existing (designed for T50) radiators ar...
By IanMK13 , 1 day ago
-
The temporary fix has reconnected about 60% of users, a...
By Abernyte , 1 day ago
-
RE: What is Wrong with our Heat Pump Installation?
Having to run the heat pump during the summer for DHW s...
By Toodles , 2 days ago
-
Issues with Vaillant connectivity via the MyCONNECT gateway
I'm sensing a variety of issues with Vaillant connectiv...
By dr_dongle , 2 days ago
-
Interesting heat pumps installations
Thought it would be cool to share photos of interesting...
By Mars , 2 days ago
-
RE: Say hello and introduce yourself
@Toodles That's very interesting to hear, thanks. I ha...
By dr_dongle , 2 days ago
-
RE: Massive Electricity Cost for Running My Air Source Heat Pump
@allyfish In fairness installer has replied stra...
By Holts , 2 days ago
-
-
RE: Are Solar Diverters Necessary for Homes with ASHPs and Solar PV?
@zzxap19 that's a fair point. With the eddi, is it poss...
By Mars , 3 days ago
-
RE: Delivering a smart and secure electricity system: government consultation
"I don't think I'll need to refer to past iterations of...
By eggnchips , 3 days ago
-
RE: Error on Immersun – Error 8 Load Short Circuit
@julesmp8 fingers crossed. I have to say our Immersu...
By Mars , 3 days ago
-
Latest Topics
-
Interesting heat pumps installations
By Mars 2 days ago
-
What is Wrong with our Heat Pump Installation?
By Mars 3 days ago
-
Fossil Fuel Fired Heating v Heat Pump?
By Toodles 3 days ago
-
Viessmann Vitocal 250-A in the UK
By treehugger 4 days ago
-
By HUBB84 6 days ago
-
By jswhite 7 days ago