Ground Source Heat Pump Systems and Their Design
This article showcases a ground source heat pump installation I spearheaded, with Darren Jones expertly handling the plant room's pipework. At the heart of this project is a 28kW single-phase CTC heat pump, seamlessly integrated with a ground source collector drilled by my son.
The innovative system configuration includes two 14kW brine to water units directly connected to a robust screed underfloor heating setup, avoiding the need for a buffer tank or system separation. The control strategy for the expansive 650 square meter property is straightforward yet effective, relying on the heat pump and adjustable thermostats in four bedrooms, leaving the remainder of the space to be regulated by the heat pump's built-in temperature sensor. This design epitomises an open zone, low-temperature approach, promising excellent efficiency and significantly reduced operational costs.
Additionally, the inclusion of a passive cooling mechanism ensures the home remains comfortable throughout the year, utilising minimal power for maximum comfort.
From the provided graphs, it is evident that with an ambient temperature of 3°C, the house maintained a comfortable 20°C. The brine temperature entering the unit was between 7-8°C, with an average flow temperature of about 30°C. Based on the manufacturer's data, the extrapolated coefficient of performance (COP) ranges between 6 and 6.5. Given that this is at the end of the heating season, and the system has been operational for nearly a year, this COP is the minimum expected.

The system's efficiency is highlighted by its approximately hourly cycling under partial load conditions, demonstrating that a buffer tank or system separation is unnecessary with proper design. Unlike on-off compressors, which are prone to cycling and resultant performance degradation, this system showcases the benefits of precise design and selection.
Our approach to system design is grounded in practical, real-world training offered at Ultimate Training and Technical. This departs from outdated methodologies, moving beyond mere theoretical concepts to embrace modern, evidence-based strategies. With the national average seasonal coefficient of performance (SCOP) around 2.8, and the need for heat pumps to be more cost-effective than fossil fuels necessitating a SCOP of 3.5, our approach emphasises the importance of high SCOPs achievable through the right equipment and meticulous system design and commissioning.
Director at Heacol | Expert Heat Pump Consultant | Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
- 26 Forums
- 2,131 Topics
- 46.8 K Posts
- 23 Online
- 5,656 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Anyone still weathering it out with Agile?
Yes, but now try finding a working phone box….
By Majordennisbloodnok , 2 hours ago
-
RE: Thermostat for Ideal Logic Air with 3 zone support
No harm at all in plumbing it as 3 zones, I would have ...
By JamesPa , 5 hours ago
-
RE: ASHP heat output monitoring
@carlo I see there is a discussion in Facebook user gro...
By Tim441 , 10 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@editor @sandy I tried contacting them via Whatsapp b...
By brad , 1 day ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
MCS have set a potential trap in the new version of MCS...
By JamesPa , 1 day ago
-
RE: Who has a V2G EV installation
General comment on battery care... I guess if ev is on ...
By Tim441 , 2 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@old_scientist I have never cleaned the mag filter myse...
By Toodles , 2 days ago
-
@old_scientist like for like comparisons are almost imp...
By Tim441 , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist There is an option in the Tesla app that...
By Toodles , 2 days ago
-
RE: Mitsu Wireless Controller and MelCloud
On the FTC5 I think this requires the dip switch on the...
By Abernyte , 2 days ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
@old_scientist me too. Just installed my new heat pump ...
By Eliuccio , 4 days ago
-
RE: Is your heat pump insured?
Yup just spoke to Privilege to inform them of my impend...
By Scalextrix , 4 days ago
-
RE: Forum updates, announcements & issues
Just to keep everyone in the loop, as the site continue...
By Mars , 5 days ago
-
RE: Fast DHW setting on Midea (Clivet) heat pump
@simon-w, is this something you could potentially assis...
By Mars , 5 days ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
Fwiw I called my installer out for the first time a few...
By JamesPa , 5 days ago
-
RE: Long term efficiency degradation
@jamespa yes as I thought thanks. We have a reaso...
By Scalextrix , 6 days ago
-
RE: Sunamp Thermino Heat Battery
@jamespa A few days after the installation had been com...
By Toodles , 6 days ago
-
RE: Planning Permission May 2025
Fair enough. I have read the legislation and MCS020a ...
By JamesPa , 1 week ago
-
RE: How do I choose a single room MVHR to prevent losing heat in my bathroom ?
An update on the Heatsava. It is the most difficult thi...
By heat-pump-newbie , 1 week ago
-
RE: Renewables & Heat Pumps in the News
this document extensively describes (in a non-blame, ne...
By Judith , 1 week ago