Ground Source Heat Pump Systems and Their Design
This article showcases a ground source heat pump installation I spearheaded, with Darren Jones expertly handling the plant room's pipework. At the heart of this project is a 28kW single-phase CTC heat pump, seamlessly integrated with a ground source collector drilled by my son.
The innovative system configuration includes two 14kW brine to water units directly connected to a robust screed underfloor heating setup, avoiding the need for a buffer tank or system separation. The control strategy for the expansive 650 square meter property is straightforward yet effective, relying on the heat pump and adjustable thermostats in four bedrooms, leaving the remainder of the space to be regulated by the heat pump's built-in temperature sensor. This design epitomises an open zone, low-temperature approach, promising excellent efficiency and significantly reduced operational costs.
Additionally, the inclusion of a passive cooling mechanism ensures the home remains comfortable throughout the year, utilising minimal power for maximum comfort.
From the provided graphs, it is evident that with an ambient temperature of 3°C, the house maintained a comfortable 20°C. The brine temperature entering the unit was between 7-8°C, with an average flow temperature of about 30°C. Based on the manufacturer's data, the extrapolated coefficient of performance (COP) ranges between 6 and 6.5. Given that this is at the end of the heating season, and the system has been operational for nearly a year, this COP is the minimum expected.

The system's efficiency is highlighted by its approximately hourly cycling under partial load conditions, demonstrating that a buffer tank or system separation is unnecessary with proper design. Unlike on-off compressors, which are prone to cycling and resultant performance degradation, this system showcases the benefits of precise design and selection.
Our approach to system design is grounded in practical, real-world training offered at Ultimate Training and Technical. This departs from outdated methodologies, moving beyond mere theoretical concepts to embrace modern, evidence-based strategies. With the national average seasonal coefficient of performance (SCOP) around 2.8, and the need for heat pumps to be more cost-effective than fossil fuels necessitating a SCOP of 3.5, our approach emphasises the importance of high SCOPs achievable through the right equipment and meticulous system design and commissioning.
Director at Heacol | Expert Heat Pump Consultant | Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 27 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Help me keep the faith with my air source heat pump installation
@jamespa the paving slabs are not cemented down just we...
By AdamK , 1 hour ago
-
@jamespa thanks, I appreciate the offer. For n...
By DREI , 4 hours ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
@transparent what I don't understand about these "rogue...
By Scalextrix , 7 hours ago
-
RE: Who’s Caved and Switched the Heating On Already?
I have 3 women in the house, 2 little ones, so my heati...
By DREI , 9 hours ago
-
@damon thanks. I will do as you suggest. Hopefully I wi...
By bontwoody , 10 hours ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 1 day ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@dgclimatecontrol I attach the responses from 2 potenti...
By pash44pump , 1 day ago
-
RE: Midea ASHP – how to set weather compensation
Mostly, I think, but with some caveats. I set the TI...
By cathodeRay , 2 days ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 2 days ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
I realise im overdue an update on my situation. first...
By Cleardene-ashp , 2 days ago
-
RE: Replacing Worcester oil boiler with an ASHP
@toodles thanks. I was told by the engineer that this h...
By JulianC , 2 days ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
A week later, I'm finally picking up this comment... ...
By Transparent , 2 days ago
-
RE: COP is not the only measure of efficiency
We keep all our TRVs fully open using the whole house a...
By Old_Scientist , 3 days ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
I am pleased to say at 4pm today we have added another ...
By ASHP-BOBBA , 3 days ago
-
RE: Renewables & Heat Pumps in the News
To unpack this a little.... 1) how many of us in this...
By Lucia , 4 days ago
-
RE: Vaillant aroTherm Plus 10kW thoughts?
@realevil the fans and fan speed / coil size (height, w...
By ASHP-BOBBA , 4 days ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@morgan this can just be done by your sepecilist when t...
By ASHP-BOBBA , 4 days ago
-
RE: Anyone still weathering it out with Agile?
@toodles I guess it all comes down to import averages. ...
By Tim441 , 4 days ago
-
RE: 300 Liter Tank - Do I have to heat it all?
The size of DHW tank affects the anti-legionella cycle....
By Transparent , 4 days ago
Members Online
No online members at the moment