Why is my heat pump cooling my DHW?
Just wondered -can you lower the temperature when your hot water reheat starts?
You seem to only have a 5 deg drop. That also means the start of the reheat is at 43 degC which might be a bit high.
I’ve got an 8.5kw HP and have the temp set to 48degC with reheat kicking in at 38degC. That means it’s got a 10 deg drop and so, not switching continually to DHW. And perhaps equally importantly the reheat temp starts when pipe temps roughly match the radiator temps if they’ve been heating the radiators.
I hope this is of interest
Posted by: @sunandair“The cylinder seems to hold the temperature quite well. The problem happens when the system is totally idle, no demand for space heating, no use of hot water. When the temperature drops to 43 (due to normal loss) and the HP starts up to reheat the DHW back to 48, that's when it does the sharp drop.”
I think I’ve encountered something similar. Your paragraph above seems to describe my thoughts.
If HP was idle then the primary pipes are probably cold. HP is slow to build temp up so while water is circulating it’s re absorbing heat from your DHW cyl. This could be confusing for the system (for a while) since the return will be warmer than the flow.perhaps try to coincide DHW reheat while the space heating has been running then the primaries will already have some heat in them. Just a thought from a newbie.
My DHW has always been like this, it drops about 7 or 8 degrees if I recall correctly when it starts heating, I attributed it to what SUNandAIR describes. Since summer I have it set to only heat at midday for an hour and do a manual start if more is required, so its not as noticeable because the tank is mostly cold anyway and I don't watch it like I did when it was first installed.
Mitsubishi Ecodan 8.5kW
4.4kW Solar PV
5.2 kWh Battery Storage
1983 build, 300mm loft insulation, cavity wall insulation (beads)
- 26 Forums
- 2,396 Topics
- 54.3 K Posts
- 347 Online
- 6,077 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Recommended home battery inverters + regulatory matters - help requested
Perhaps the link only works when logged in.. I will i...
By Batpred , 5 minutes ago
-
RE: New Fogstar 15.5kWh upright solution
Thank you. No-one did. You posted some links to ...
By Majordennisbloodnok , 7 minutes ago
-
Just realised that this image of the cylinder cupboard ...
By Sheriff Fatman , 17 minutes ago
-
RE: Rodents! A word of warning for heat pump owners
Two thoughts: 1: Let's ask @david-s if Primary Pro in...
By Transparent , 34 minutes ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
In the diagram below, I describe my understanding of th...
By Batpred , 1 hour ago
-
RE: Running from backup generaor in powercut?
@batpred Thanks for the warning. definately a job for a...
By Pipcart , 1 hour ago
-
RE: Weather compensation- why you should use it
@jamespa We have come a long way since a human lit a fi...
By Toodles , 1 hour ago
-
New Mitsubishi Ecodan 11.2kW installation - L9 errors and maybe more
Hi all, We had an Ecodan installation done as part of...
By anotherdaveuk , 1 hour ago
-
RE: ASHP Energy Consumption: Aira 12kW heat pump
@editor Mars, First of all thank you for your enco...
By Wally , 1 hour ago
-
I need to have a look out for it. I know IBM feeds some...
By Batpred , 2 hours ago
-
-
RE: Daikin Atherma ASHP Cycling 6 Times an Hour?
Thanks for your reply. Yes that's a good idea to try a...
By John Marshall , 7 hours ago
-
RE: Hot water heating in parallel with space heating
An external heat exchanger would need a pump which woul...
By bontwoody , 8 hours ago
-
RE: Gen 6 Samsung ASHP losing 20C of DHW in 60 min directly after generation
@ecobaker Thanks for this. I've had it in both slots. ...
By andbeck , 18 hours ago
-
RE: Air source heat pump circuit not operational
Welcome to the forums. If the thermostat shows it’s c...
By Mars , 18 hours ago
-
RE: Ecodan with FTC7 - True Weather Compensation
@danwright90 I've linked two videos below recorded this...
By Sheriff Fatman , 20 hours ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
That makes plenty of sense. Perhaps more importantly, O...
By Majordennisbloodnok , 22 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
It does but it almost all applies to boiler systems and...
By JamesPa , 1 day ago
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
So theres a problem for starters. This means that the ...
By JamesPa , 1 day ago