Why are my flow and return temperatures reading the same?
so the most likely explanation is that there is another circulating pump in your system, and you also have a buffer tank or low loss header (LLH) in your system.
the other pump will either be in the outdoor unit or near to the buffer tank / LLH, on the heat pump side of the piping. that's what's called the primary pump - its responsible for the flow rate you are seeing. the temperature sensors you are seeing are those of the primary flow and return, in / out of the heat pump.
when your system is in CH mode, the HP supplies warm water to top the buffer tank(or LLH), that water being moved by the primary side circulation pump. and it takes cool(er) water from the bottom of the buffer tank. The UFH takes warmer water fromt he top, uses it to heat the house, and puts it back into the bottom. That called the secondary side. Thus there are two separate circulating loops that join in the middle.
when your system goes into HW mode it'll switch a valve for the water flow so that instead of going from the HP into the LLH, it goes direct to the cylinder. So in that case, the flow rate, and flow/return temps, that you see , are those of water flow directly between cylinder and HP. So the HP is seeing the true DT and flow rate of the cylinder.
But in CH mode, your HP doesn't "see" the heating system. It simply "sees" a buffer/LLH that keeps on losing some heat, and keeps topping it up.
Note in CH mode via the buffer/LLH, that the flow rates of the two loops are completely separate, and if the flow rates differ significantly then the DT will also. Read this about how a system with LLH/buffers works (HeatGeek is always a good place to start) .
edit - I missed your info in previous posts. seems like you have an indoor unit with a PHE (Plate Heat Exchanger) and a separate primary side pump. The PHE is doing similar job to LLH as I mentioned above, separating the two sides. your temperature readings and flow rate that your system reports will still be on the primary side, you will never see the UFH side DT or flow rate without additional sensors.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank Thanks Ian for that explanation.
I have noticed that in recent days with colder weather and a higher LWT temperature, there is more of a difference between leaving and returning water temperatures. Anyway the house is warm and the electricity consumption has been reasonable, so that's really all that matters!
- 26 Forums
- 2,242 Topics
- 49.9 K Posts
- 343 Online
- 5,903 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: End of Summer Time Reminder to Ecodan owners
It advances the system time by one hour. The time is sh...
By downfield , 3 minutes ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
The guidance I was given suggested a regime that I cons...
By Toodles , 18 minutes ago
-
RE: Midea ASHP – how to set weather compensation
Most of what you need is in my post above (15/10/2025 7...
By cathodeRay , 39 minutes ago
-
RE: Faulty Clivet heat pump out of the box
@kenbone No particular party being blamed - just the to...
By Toodles , 1 hour ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
@jords were you not given a copy of the full heat loss ...
By Chas Barry , 1 hour ago
-
@eliuccio Sometimes changes in electrical regs only app...
By Toodles , 2 hours ago
-
RE: Should Our Water Circulation Pump Be Configured to Run All The Time?
I signed up here due to finding this question via a Goo...
By Unsure , 2 hours ago
-
RE: Mitsu PAR-WT60 Wireless Controller
Aslo, subject to FTC version, Your thermostat will cont...
By ASHP-BOBBA , 5 hours ago
-
Ecodan Melcloud Temperature Change
Long time lurker, first time poster 5kW Ecodan, FT6 c...
By Gruff2001 , 5 hours ago
-
@bontwoody Thanks for the info. Quite a spread of value...
By springswood , 5 hours ago
-
RE: Daikin Octopus installation update - I saw my first defrost. 😍😂
Thing is it is one of those intermittent things. Yes I ...
By Jancold , 6 hours ago
-
@transparent Yes to questions 1 to 3. Also, yes to the...
By Morgan , 6 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
OK thats cheap, the commercial price seems to be £400 p...
By JamesPa , 1 day ago
-
RE: Solar inverters - where does the energy go when clipping?
I think I must query the sources on which Greenmatch ha...
By Transparent , 1 day ago
-
RE: Replacing knackered oil boiler with Samsung ASHP - Perthshire
This is how I run my Samsung 12kW ASHP with a 3rd party...
By Old_Scientist , 1 day ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@cathoderay thanks- yes will keep an eye out for the de...
By benson , 2 days ago
-
RE: Renewables & Heat Pumps in the News
Hoping so as well! I am no specialist. The language use...
By Batpred , 2 days ago
-
RE: The Hidden Secret to a Successful Heat Pump: Pipe Size Matters
@old_scientist Just to say that during our retrofit, we...
By Toodles , 2 days ago
-
RE: Daikin Altherma 3M ASHP and British Gas Hive Home
We have a Daikin EDLA08 8kW monobloc (DHW is handled se...
By Toodles , 2 days ago