Why are my flow and return temperatures reading the same?
so the most likely explanation is that there is another circulating pump in your system, and you also have a buffer tank or low loss header (LLH) in your system.
the other pump will either be in the outdoor unit or near to the buffer tank / LLH, on the heat pump side of the piping. that's what's called the primary pump - its responsible for the flow rate you are seeing. the temperature sensors you are seeing are those of the primary flow and return, in / out of the heat pump.
when your system is in CH mode, the HP supplies warm water to top the buffer tank(or LLH), that water being moved by the primary side circulation pump. and it takes cool(er) water from the bottom of the buffer tank. The UFH takes warmer water fromt he top, uses it to heat the house, and puts it back into the bottom. That called the secondary side. Thus there are two separate circulating loops that join in the middle.
when your system goes into HW mode it'll switch a valve for the water flow so that instead of going from the HP into the LLH, it goes direct to the cylinder. So in that case, the flow rate, and flow/return temps, that you see , are those of water flow directly between cylinder and HP. So the HP is seeing the true DT and flow rate of the cylinder.
But in CH mode, your HP doesn't "see" the heating system. It simply "sees" a buffer/LLH that keeps on losing some heat, and keeps topping it up.
Note in CH mode via the buffer/LLH, that the flow rates of the two loops are completely separate, and if the flow rates differ significantly then the DT will also. Read this about how a system with LLH/buffers works (HeatGeek is always a good place to start) .
edit - I missed your info in previous posts. seems like you have an indoor unit with a PHE (Plate Heat Exchanger) and a separate primary side pump. The PHE is doing similar job to LLH as I mentioned above, separating the two sides. your temperature readings and flow rate that your system reports will still be on the primary side, you will never see the UFH side DT or flow rate without additional sensors.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank Thanks Ian for that explanation.
I have noticed that in recent days with colder weather and a higher LWT temperature, there is more of a difference between leaving and returning water temperatures. Anyway the house is warm and the electricity consumption has been reasonable, so that's really all that matters!
- 26 Forums
- 2,323 Topics
- 52.1 K Posts
- 230 Online
- 5,979 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
@temperature_gradient Yes, yes, yes! Along with many ot...
By Toodles , 33 minutes ago
-
RE: Grant Aerona Short Cycling
@damonc I was refering to the 'standard' energy sticker...
By MikeFl , 56 minutes ago
-
RE: Replacing my 18 month old Hitachi Yutaki ASHP
OK noted, although I dont think any of the charts poste...
By JamesPa , 1 hour ago
-
RE: Electricity price predictions
Further falls in wholesale gas will help the next price...
By Jeff , 2 hours ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
@hcas where do I find Havenwise Support? On...
By Morgan , 2 hours ago
-
RE: Grant Aerona circulation/system pump staying on
My AERONA 3 circulation pump runs constantly whatever t...
By damonc , 15 hours ago
-
RE: Configuring third party dongle for Ecodan local control
Thanks, @sheriff-fatman. Happy for you to search any po...
By Majordennisbloodnok , 17 hours ago
-
Thanks, @cathoderay. I was aware of some changes to ...
By Majordennisbloodnok , 18 hours ago
-
RE: Trying to understand my Nibe F1245
@greenlight Many thanks for the information, it's set m...
By Chris12 , 1 day ago
-
This is what I answered, I really have no hope: "......
By Batpred , 2 days ago
-
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@andrewj oh yes they offer Daikin 8kW, they tried to fo...
By AgentGeorge , 2 days ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
@majordennisbloodnok Good point! Just in case anyone re...
By Batpred , 2 days ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Owners
@sim0n0 It would be very useful if you could tell us...
By trebor12345 , 2 days ago
-
RE: Benefits of an extra horizontal loop for GSHP
A correct sized collector is all you need. Saying this,...
By greenlight , 2 days ago
-
-
RE: Here is my heat pump installation with questionable COP in Italy
@jamespa Sorry for the late reply, I apologize for the ...
By materox345 , 2 days ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
@editor Yes BUT that was 3 years ago installed in Janua...
By rob heatpump bob , 3 days ago
-
Thanks for your response. I have UFH downstairs and ...
By GeorgeA , 3 days ago