Vaillant Arotherm monobloc error f.788 - ASHP is not working!
@william1066 so my system did the experiment for me today.
I currently have a commissioned ASHP, the flow side goes to a 50L volumiser, then there is temporary shortcut (i.e. a bypass) back into the return side. I temporarily created demand so the ASHP has warmed up the water in the circuit and volumiser. the routes from the ashp's f+r circuit into the house are currently capped - there is no load on the ashp. the house is still on the boiler.
the graph starts when I got modbus working yesterday evening. RWT goes below 25 right at the start but nothing comes on. When Outside temp goes below 4C, the system switches the circulation pump on. But not the compressor. the lukewarm water in the circuit must be enough to satisfy the warmth needs of the outdoor unit. After that, the pump is leaving "off" gaps of 60 minutes then running for about 6-8 mins each time. I'm not sure what the "off" trigger is at the end of the "on" period. It'll be interesting to see how cool it gets before it puts the compressor on.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Posted by: @iancalderbankI'm not sure what the "off" trigger is at the end of the "on" period.
Probably just "x" amount of time
Hi,
I have the same Error F788 did you finally fix it?
Coule you please tell me Howell did you do?
thanks for tour help
@bobshopsupreme did you ever get this matter sorted out?
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@editor Hello. Yes and no! The original problem was indeed a dead water pump, killed by contamination in the circuit and possibly the power cut during freezing conditions (we do have anti-freeze valves). It took two months to get a replacement part.
We have then had another 2 years of fun with shutdowns caused by low flow due to under-dimensioned pipes, and then we still have a contamination issue which seems to be coming from the radiators. At the moment the flow rate gradually decreases over several weeks until the system cuts out with a low flow error, and then is fine again after cleaning the filters. They are trying to find the right product to protect the inside of the radiators because whatever inhibitor they have in there at the moment clearly isn't working.
@bobshopsupreme very interesting. Do you have a buffer tank or is it an open zone?
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@editor We have a 200 litre buffer between the hydraulic station and the radiator and underfloor heating circuits. The flow rate problem was due to undersizing of the pipes between the outdoor unit and the hydraulic station. Those pipes have now been changed and it now meets the >2000l/hr nominal flow rate when the filters are clean.
-
Vaillant arotherm plus heat pump frost protection
8 months ago
-
Vaillant aroTHERM plus not level or flat - what base is best under an external unit?
10 months ago
-
Has anyone seen this problem before? Huge anticycling times
10 months ago
-
ASHP Reliability Poll - Hall of Fame vs Hall of Shame?
11 months ago
-
British Gas versus Octopus: Two possible heat pump routes - how to evaluate them?
11 months ago
- 26 Forums
- 2,171 Topics
- 47.8 K Posts
- 25 Online
- 5,744 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Powerwall 3 or Myenergi or something else?
Many of those tariffs are simple time of use tariffs, w...
By Temperature_Gradient , 10 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
Yes thats the whole point of the flexis as regards tran...
By JamesPa , 10 hours ago
-
So far as I can tell designing for DT5, which is 'the n...
By JamesPa , 11 hours ago
-
Mitsu PAR-WT60R Wireless Controller - options
I hope I have satisfactorily installed the above wirele...
By DavidAlgarve , 13 hours ago
-
WC curve best discovered by experiment anyway as any lo...
By JamesPa , 17 hours ago
-
RE: Big Changes Coming to Our Heat Pump System
@editor your engineer's attitude is truly horrifying. ...
By GrahamF , 1 day ago
-
RE: How to choose Towel Rails for an ASHP
@rob-nezard yes absolutely. Here is the link and a pho...
By GrahamF , 2 days ago
-
@mixergy Thanks for the update, I would appreciate some...
By bontwoody , 2 days ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
Unfortunately I'm not that well connected 😂 ...
By Scalextrix , 2 days ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
It is interesting to see what our new Grant Aerona 290 ...
By GrahamF , 2 days ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
I've never physically seen it, but I seem to recall som...
By cathodeRay , 2 days ago
-
RE: Midea ASHP – how to set weather compensation
I noticed that too and thought the same thing, but then...
By cathodeRay , 3 days ago
-
RE: Ya can’t win! It is S*d’s Law!
@old_scientist If IOF is still running next late spring...
By Toodles , 3 days ago
-
RE: Electricity price predictions
Those of you on Agile will do well tomorrow; there are ...
By Toodles , 3 days ago
-
RE: Who’s Caved and Switched the Heating On Already?
We've been running our Ecodan system, installed in June...
By Sheriff Fatman , 3 days ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 3 days ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 4 days ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 4 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 5 days ago