The Pros and Cons of an oversized heat pump
We have all read the oversized heat pump threads, and as I'm a glass half full kind of person, I thought I'd try to highlight some of the advantages of living with an oversized heat pump. Make no mistake, a correctly sized heat pump is always going to be preferable and more efficient, but we have to try to make the best of what we have - a 12kW Samsung gen6 in my case. So here are my Pro's for living with an oversized heat pump:
- Heat pumps are most efficient when the compressor is operating in the 30-70 percent range. Having an oversized heat pump means you will likely never need to operate at maximum. Samsung conveniently allow Quiet Mode operation, which basically limits the output to around 70%. Measurements over the summer have shown the heat pump uses less electricity doing the daily DHW cycle in Quiet Mode than when allowed to run flat out (Quiet Mode off). It's a double win, as the heat pump is unsurprisingly also a lot quieter than when allowed to run flat out. Other manufacturers may have similar settings that allow the user to limit the output.
- I can reheat my DHW cylinder in 15-20mins, so no long waits for more hot water after the OH has had a bath and emptied the tank. I can turn on the hot water the moment she finishes running the bath, and the tank is reheated by the time she's finished. I suspect that if starting from a hot tank, and running DHW heating flat out, the heat pump may be able to maintain a 40C shower temp for everyone in the house to shower one after the other, but we haven't had reason to try that as we tend to shower at different times.
- If on Octopus Agile, or other time of use tariff, I can run my heating like it was a gas boiler. For example, tonight the temp may drop a little and there is a single half hour slot of negatively priced electricity, so I've set the WC curve (LWT) to 55-60C, and will run the heat pump flat out circulating 55C water through the radiators for 30mins to pump a bit of free heat into the house. I may just turn the bedroom radiator down if I think the sudden burst of heat may disturb our sleep. That's probably all we need to get up to a warm house in the morning. A 5kW heat pump probably wouldn't be able to do this and a steady 35C flow temp doesn't allow me to leverage those cheap slots in the same way I can with 12kW plus at my disposal. There goes the COP, but free heat is free heat.
How else can you think to taking advantage of an oversized heat pump?
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 3.645kWp solar (south facing), Fox ESS inverter.
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
You've raised some interesting points about living with an oversized heat pump, and it's great to see you making the most out of your situation. While a properly sized heat pump is indeed more efficient, your approach of leveraging Quiet Mode and time-of-use tariffs like Octopus Agile to optimise performance is smart. The ability to reheat your DHW cylinder quickly and take advantage of cheap electricity slots are definite perks.
Another potential advantage might be in resilience; an oversized system could have more headroom to handle particularly cold spells or increased demand in your home, ensuring comfort even in extreme conditions.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Mine is also pretty oversized our -9 heat loss is about 3.5kW, but we have a 6kW heat pump, so in percentage term huge.
You can batch charge thick screed UFH in the E7 down to sub zero, but the coldest days need to run for quite a few extra hrs.
With some tuning you get the cycles under control, mine is currently once per hour. When running within a couple of minutes it seems to run close to manufacturer CoP.
We now heat and cool a summer house, which adds another 1kW+ to heat demand, without having to add additional heat source.
Downside
Because you cycle, you have to slightly compensate with slightly warmer flow temps, so take a hit CoP wise.
Cycling in general takes a CoP hit.
You really HAVE to run single zone to keep things happy.
Posted by: @old_scientistcompressor is operating in the 30-70 percent range.
Are you sure about that? Do you have a reference?
In general the longer the run time the more efficient the heat pump becomes, because the compressor gets to a steady state temp throughout, the refrigerator gases and an the throttle valves are all settled to their correct running position. Plus the water temp is in a steady state.
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
@editor Yes, I have no doubt that we will not be cold in winter. It's generally mild where we are, and our design temp was -1.9C, but I'm sure we are good to go even if we were to see temps much lower. Of course the main "issue" is too much heat output in the milder months, but rather than try to run low and slow, we may just control when the heat pump runs and try to schedule bursts during cheaper Agile slots. Having yet to experience a winter, I'm guessing we'd need temps of below 10C (maybe as low as 5C) to run continuously, even at minimum output.
But I'd much rather be in this boat than those who have cold houses and very high bills.
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 3.645kWp solar (south facing), Fox ESS inverter.
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
Posted by: @old_scientistI'm guessing we'd need temps of below 10C (maybe as low as 5C) to run continuously, even at minimum output.
It may not then either. You can't control your running hysterisis directly, but you can control in a hybrid mode of water law and the controller thermostat. So this mode I believe works by generally following weather compensation but allow some overshoot in room temp, to prolong compressor run, then some undershoot before restarting the compressor. This increases on time and off time. People have seen a best CoP of high 2s go to mid 4s by using this strategy. It's all built in to the controller as an option. Don't know the details of it directly, but there was a discussion on here where it was mentioned (short cycling) also saw it discussed on another forum.
I can change the stop and start hysterisis bands and have done so to get a reasonable run time even when I didn't have a large heat demand.
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
Posted by: @johnmoMine is also pretty oversized our -9 heat loss is about 3.5kW, but we have a 6kW heat pump, so in percentage term huge.
You can batch charge thick screed UFH in the E7 down to sub zero, but the coldest days need to run for quite a few extra hrs.
With some tuning you get the cycles under control, mine is currently once per hour. When running within a couple of minutes it seems to run close to manufacturer CoP.
We now heat and cool a summer house, which adds another 1kW+ to heat demand, without having to add additional heat source.
Downside
Because you cycle, you have to slightly compensate with slightly warmer flow temps, so take a hit CoP wise.
Cycling in general takes a CoP hit.
You really HAVE to run single zone to keep things happy.
Posted by: @old_scientistcompressor is operating in the 30-70 percent range.
Are you sure about that? Do you have a reference?
In general the longer the run time the more efficient the heat pump becomes, because the compressor gets to a steady state temp throughout, the refrigerator gases and an the throttle valves are all settled to their correct running position. Plus the water temp is in a steady state.
@johnmo, I'd taken it from John Cantor's video here, see the slide from ecoforest towards the end of the video at 20:08min
which shows efficiency falling off a cliff below ~30%, which is probably why equipment manufacturers do not allow their ASHPs to modulate below 25% output as COPs would be disastrous so they are restricted to operate in the range in which they are most efficient. It shows a less pronounced roll off at higher compressor speeds which is also somewhat temperature dependant.
I believe this is why I can measure less required electrical input with my heat pump in Quiet Mode (restricted to ~70% of output) when reheating my DHW cylinder to it's set point from the same starting temps and ambient temps. When quiet mode is off, the heat pump ramps up to full output rather than it's output being limited, which is less efficient. Maybe a short DHW run is not a good example as the system never achieves a steady state of operation as LWT is continuously rising until the DHW set point is reached. Maybe I am observing some other effect.
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 3.645kWp solar (south facing), Fox ESS inverter.
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
Posted by: @johnmoPosted by: @old_scientistI'm guessing we'd need temps of below 10C (maybe as low as 5C) to run continuously, even at minimum output.
It may not then either. You can't control your running hysterisis directly, but you can control in a hybrid mode of water law and the controller thermostat. So this mode I believe works by generally following weather compensation but allow some overshoot in room temp, to prolong compressor run, then some undershoot before restarting the compressor. This increases on time and off time. People have seen a best CoP of high 2s go to mid 4s by using this strategy. It's all built in to the controller as an option. Don't know the details of it directly, but there was a discussion on here where it was mentioned (short cycling) also saw it discussed on another forum.
I can change the stop and start hysterisis bands and have done so to get a reasonable run time even when I didn't have a large heat demand.
Yes, I've not had a chance to really play with settings yet as we've not experienced a winter, but because I assume I'd be cycling (of some description), I've initially decided to control that cycling myself rather than allow the heat pump controller to do it based on weather compensation and LWTs.
So I've disabled that setting in the Samsung controller, so my heat pump basically runs continuously and is controlled by my 3rd party add on room thermostat's call for heat (on/off). My room stat has a hysteresis setting of 0.2C to 1C, and we can further modulate that by turning the set temp up and down extending any run/off periods. I plan to run like that a while to get a baseline for performance, and then we can reverse the settings and let the Samsung controller have a go at things based on it's WC curve, and see how that compares COP wise.
I think the hysteresis settings you refer to may only be applicable if using the Samsung controller as the room stat - I'm not using it as my room stat (it's bolted to the front of my DHW tank) as we have a separate add on room stat to control room temp / call for heat, but I can achieve the same hysteresis effect with my room stat controller.
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 3.645kWp solar (south facing), Fox ESS inverter.
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
Posted by: @old_scientistthink the hysteresis settings you refer to may only be applicable
The hysterisis referred to is the difference between target flow temperature and at what temp the compressor starts and stops.
So mine at a target flow temperature of 25, the compressor starts at return temp of 20.1 and runs until water leaving temperature hits 27.8. I can move these numbers about and they are a long way off what was set in the factory.
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
- 22 Forums
- 2,036 Topics
- 44.4 K Posts
- 16 Online
- 3,239 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: The Rise and Fall of Europe’s Most Generous Green Subsidy
@dwynwen welcome back… and glad to hear you made it thr...
By Mars , 6 hours ago
-
RE: Air Source Heat Pump - Side Alley Suitability
@ad3628 I’ve seen loads of heat pumps successfully inst...
By Mars , 6 hours ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Thermal Off's
@trebor12345 The Auto function is supposed to adapt au...
By Heatgeek , 8 hours ago
-
RE: In the middle of an ASHP installation - a few questions (and issues)
@jamespa they didn't provide any contract, or design pr...
By benson , 11 hours ago
-
RE: The Great British Heat Pump Quiz
@allyfish thanks for the feedback and glad it was fun! ...
By Mars , 13 hours ago
-
RE: help sizing rads based on room by room heat loss
If its 1988W at DT 50, which is how most radiators are ...
By JamesPa , 18 hours ago
-
RE: Career change – entering the world of heating and heat pumps
@editor Mars, thank you. That's along the routes I was ...
By Lakey , 18 hours ago
-
@editor thanks Mars, it's a rare occasion I'm looking f...
By big_si , 1 day ago
-
RE: Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW
@ashp-bobba and @jamespa - thank you both for all your ...
By CBrenewable , 1 day ago
-
-
Win one of five "Heat Pumps 101" Courses
Heat pumps are gaining traction in the UK, but between ...
By Mars , 2 days ago
-
RE: Agile: average import cost vs other tariffs?
@toodles thanks for the analysis. I'll be really intere...
By Old_Scientist , 2 days ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
@phoenix15 I'm no plumber so please don't take this as ...
By dnagre , 2 days ago
-
RE: Is this normal? Click of the DHW returning to space heating
@grantmethestrength Oh sorry to hear that, there should...
By ASHP-BOBBA , 2 days ago
-
@ashp-bobba TBH the ladies are rather disorganised, so ...
By Cathyem1 , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
And for those of us without an automatic irrigation sys...
By Majordennisbloodnok , 2 days ago
-
Logically, the lower frequency = more gentle, yes, but ...
By SUNandAIR , 3 days ago
-
RE: Ideal Logic ASHP - change from 55°C to 35°C Heating?
Good point. I’ll keep my eye on the manifold temperatur...
By Tomdad , 3 days ago
-
RE: How hard and expensive would it be to change panel and add battery?
@transparent It is a setting that Octopus make via the ...
By Toodles , 3 days ago