Should I make my radiators smaller?
A deliberately provocative title, forgive me.
The question is really about how important it is to have equally sized radiators in each room, in relation to specific room heat loss.
I had a heat loss calculation done, and with my current radiatiors at a design temperature of 50C flow and -3 OT, some are clearly undersized, the worst being -47%. Okay that needs upgrading, no brainer.
But how much to upgrade it, just to 100% the heat loss of that room, or to match the most oversized radiator in any other room?
What if thats not possible, and room A is sized with 100% of power output to heat loss, and room B is sized to 158% of power output to heat loss; I assume room B is going to get much too hot?
The modern advice is not to have TRVs and to go as "open circuit" as possible, so how do we mitigate the oversized radiator in room B? Should we make it smaller? What % of size deviation can be handled without adding flow restrictions and controls?
Everyone seems to say bigger radiators are better, but should that advice come with the caveat that sizing needs to be equal throught the heating zone?
TIA
Bonus question; if you open up all the radiators in a reasonably balanced system, and let the heating come to equielibreum with OT, and measure the temperature within each room; is that a better way to calculate heat loss? Is there a method for that?
Posted by: @scalextrixWhat if thats not possible, and room A is sized with 100% of power output to heat loss, and room B is sized to 158% of power output to heat loss; I assume room B is going to get much too hot?
The modern advice is not to have TRVs and to go as "open circuit" as possible, so how do we mitigate the oversized radiator in room B? Should we make it smaller? What % of size deviation can be handled without adding flow restrictions and controls?
The deviations can be handled by
a) the lockshield valve. this restricts the flow rate through the rad in question which increases the deltaT for that rad which reduces the average temperature and hence the output.
b) the fact that rooms tend to share heat anyway because the thermal separation is poor.
I had mismatches of 150% plus, no problem
Posted by: @scalextrixBonus question; if you open up all the radiators in a reasonably balanced system, and let the heating come to equielibreum with OT, and measure the temperature within each room; is that a better way to calculate heat loss?
No, you wont leave it like that for long enough to overcome all the other variations that mother nature throws at us.
Posted by: @scalextrixIs there a method for that?
yes, (a) measure it over several weeks monitoring individual radiators and the heat pump, Adia Thermal make the kit to do this or (b) plot your gas/oil usage vs average OAT for several months or preferably a whole season, estimate the efficiency of your boiler, and work from there (gives you whole house only).
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa thanks for the reply, so really in this case we have to reduce the flow to the radiator to achieve it.
In my specific case the oversize radiators are upstairs which isn't really the best from a heat sharing perspective, but I get your point.
Posted by: @scalextrix@jamespa thanks for the reply, so really in this case we have to reduce the flow to the radiator to achieve it.
In my specific case the oversize radiators are upstairs which isn't really the best from a heat sharing perspective, but I get your point.
Mine are also upstairs because I upgraded them before I realised how much the heat pump industry overestimates house losses. Still not a problem although the lack of 'valve authority' with the very old LSVs on a couple of the rads in question makes for a slightly tricky, but not impossible, adjustment . Of course that is my house, yours may be different. The 'excess' upstairs capacity helped my installer to be happy to leave the bathroom well under-provided for, thus I could retain my exiting towel rail rather than replace it.
That said if you can make the downstairs ones bigger go for it. Lower flow temperature = lower cost and greater comfort, as you clearly know!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,171 Topics
- 47.8 K Posts
- 75 Online
- 5,744 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Big Changes Coming to Our Heat Pump System
@editor this is exciting! It will be great to hear how...
By GrahamF , 6 minutes ago
-
RE: Powerwall 3 or Myenergi or something else?
I think you need to be sure you are comparing like for ...
By Old_Scientist , 39 minutes ago
-
RE: Help me keep the faith with my air source heat pump installation
Water pump will certainly make a hum (which could conce...
By JamesPa , 3 hours ago
-
@jamespa Thanks. Yeah any adjustments Ive made at pr...
By cliffhanger , 3 hours ago
-
RE: Mitsu PAR-WT60R Wireless Controller - options
I have been running mine in auto adapt since 2019 and i...
By Abernyte , 5 hours ago
-
So far as I can tell designing for DT5, which is 'the n...
By JamesPa , 16 hours ago
-
RE: How to choose Towel Rails for an ASHP
@rob-nezard yes absolutely. Here is the link and a pho...
By GrahamF , 2 days ago
-
@mixergy Thanks for the update, I would appreciate some...
By bontwoody , 2 days ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
Unfortunately I'm not that well connected 😂 ...
By Scalextrix , 2 days ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
It is interesting to see what our new Grant Aerona 290 ...
By GrahamF , 2 days ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
I've never physically seen it, but I seem to recall som...
By cathodeRay , 2 days ago
-
RE: Midea ASHP – how to set weather compensation
I noticed that too and thought the same thing, but then...
By cathodeRay , 3 days ago
-
RE: Ya can’t win! It is S*d’s Law!
@old_scientist If IOF is still running next late spring...
By Toodles , 3 days ago
-
RE: Electricity price predictions
Those of you on Agile will do well tomorrow; there are ...
By Toodles , 3 days ago
-
RE: Who’s Caved and Switched the Heating On Already?
We've been running our Ecodan system, installed in June...
By Sheriff Fatman , 3 days ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 4 days ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 4 days ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 4 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 6 days ago