Should I make my radiators smaller?
A deliberately provocative title, forgive me.
The question is really about how important it is to have equally sized radiators in each room, in relation to specific room heat loss.
I had a heat loss calculation done, and with my current radiatiors at a design temperature of 50C flow and -3 OT, some are clearly undersized, the worst being -47%. Okay that needs upgrading, no brainer.
But how much to upgrade it, just to 100% the heat loss of that room, or to match the most oversized radiator in any other room?
What if thats not possible, and room A is sized with 100% of power output to heat loss, and room B is sized to 158% of power output to heat loss; I assume room B is going to get much too hot?
The modern advice is not to have TRVs and to go as "open circuit" as possible, so how do we mitigate the oversized radiator in room B? Should we make it smaller? What % of size deviation can be handled without adding flow restrictions and controls?
Everyone seems to say bigger radiators are better, but should that advice come with the caveat that sizing needs to be equal throught the heating zone?
TIA
Bonus question; if you open up all the radiators in a reasonably balanced system, and let the heating come to equielibreum with OT, and measure the temperature within each room; is that a better way to calculate heat loss? Is there a method for that?
Posted by: @scalextrixWhat if thats not possible, and room A is sized with 100% of power output to heat loss, and room B is sized to 158% of power output to heat loss; I assume room B is going to get much too hot?
The modern advice is not to have TRVs and to go as "open circuit" as possible, so how do we mitigate the oversized radiator in room B? Should we make it smaller? What % of size deviation can be handled without adding flow restrictions and controls?
The deviations can be handled by
a) the lockshield valve. this restricts the flow rate through the rad in question which increases the deltaT for that rad which reduces the average temperature and hence the output.
b) the fact that rooms tend to share heat anyway because the thermal separation is poor.
I had mismatches of 150% plus, no problem
Posted by: @scalextrixBonus question; if you open up all the radiators in a reasonably balanced system, and let the heating come to equielibreum with OT, and measure the temperature within each room; is that a better way to calculate heat loss?
No, you wont leave it like that for long enough to overcome all the other variations that mother nature throws at us.
Posted by: @scalextrixIs there a method for that?
yes, (a) measure it over several weeks monitoring individual radiators and the heat pump, Adia Thermal make the kit to do this or (b) plot your gas/oil usage vs average OAT for several months or preferably a whole season, estimate the efficiency of your boiler, and work from there (gives you whole house only).
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa thanks for the reply, so really in this case we have to reduce the flow to the radiator to achieve it.
In my specific case the oversize radiators are upstairs which isn't really the best from a heat sharing perspective, but I get your point.
Posted by: @scalextrix@jamespa thanks for the reply, so really in this case we have to reduce the flow to the radiator to achieve it.
In my specific case the oversize radiators are upstairs which isn't really the best from a heat sharing perspective, but I get your point.
Mine are also upstairs because I upgraded them before I realised how much the heat pump industry overestimates house losses. Still not a problem although the lack of 'valve authority' with the very old LSVs on a couple of the rads in question makes for a slightly tricky, but not impossible, adjustment . Of course that is my house, yours may be different. The 'excess' upstairs capacity helped my installer to be happy to leave the bathroom well under-provided for, thus I could retain my exiting towel rail rather than replace it.
That said if you can make the downstairs ones bigger go for it. Lower flow temperature = lower cost and greater comfort, as you clearly know!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,306 Topics
- 51.7 K Posts
- 280 Online
- 5,970 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
So this morning marked 24 hours up for installer. Rooms...
By Crimson , 3 hours ago
-
RE: Buffer tank bypass on EDF Ideal heat pump installation
@kevb, many of these companies look for the smallest of...
By Mars , 5 hours ago
-
RE: Don’t Install a Heat Pump Until You Read This
@briansprankle, good luck. Keep us posted. Glad they’re...
By Mars , 5 hours ago
-
RE: Commencing on an ASHP Installation Process
Me too, but I think we are in the minority. Most homeo...
By JamesPa , 7 hours ago
-
RE: Electricity price predictions
Simple article with a DENZ graph showing how gas which ...
By Jeff , 7 hours ago
-
RE: 10kw heat pump run in 24*7 data?
Thats really helpful as it clearly says target 49C. So...
By JamesPa , 7 hours ago
-
RE: Heat Pump on Flat Roof Low Frequency Noise from Detached Neighbor
@davidnolan22 Yes have been communicating woth the neig...
By People_Noise , 7 hours ago
-
Power Cut - Heat Pump Evaporator Iced Up
We have just had a power cut and 1 hour later power was...
By trebor12345 , 8 hours ago
-
@sand Yes. The COP is reported and you can split it int...
By bontwoody , 10 hours ago
-
RE: Why Millions of UK Homes Struggle With Heat Pumps
A few weeks ago, I was having a discussion with someone...
By Majordennisbloodnok , 10 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk Hi I see you posted on openenergymon...
By JamesPa , 12 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Often the default password is in the installation manua...
By JamesPa , 13 hours ago
-
RE: Cashback Incentives That Reward Shorter Heat Pump Warranties
@andrewj Indeed, ’Appalling’ is a rather mild term for ...
By Toodles , 13 hours ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira
@editor When do “Mars Heat Pump Installation and Servic...
By Toodles , 14 hours ago
-
@morgan Likewise, I realise that some readers will appr...
By Toodles , 14 hours ago
-
A Smarter Smart Controller from Homely?
I received an email from Homely this morning enquiring ...
By Toodles , 14 hours ago
-
RE: Grant Aerona 3 and Drayton system questions
Yes in general terms (obviously I cant tell if its exac...
By JamesPa , 16 hours ago
-
Yes, the Grundfos pump has a built in timer. However, t...
By DavidAlgarve , 17 hours ago
-
Ecodan - Flow temperature spiking causing shutdown
Hi everyone, looking for some help. I am in a new bu...
By Gl3484 , 1 day ago
-
Solis AI is on the right track to leverage the battery:...
By Batpred , 1 day ago