Should I make my radiators smaller?
A deliberately provocative title, forgive me.
The question is really about how important it is to have equally sized radiators in each room, in relation to specific room heat loss.
I had a heat loss calculation done, and with my current radiatiors at a design temperature of 50C flow and -3 OT, some are clearly undersized, the worst being -47%. Okay that needs upgrading, no brainer.
But how much to upgrade it, just to 100% the heat loss of that room, or to match the most oversized radiator in any other room?
What if thats not possible, and room A is sized with 100% of power output to heat loss, and room B is sized to 158% of power output to heat loss; I assume room B is going to get much too hot?
The modern advice is not to have TRVs and to go as "open circuit" as possible, so how do we mitigate the oversized radiator in room B? Should we make it smaller? What % of size deviation can be handled without adding flow restrictions and controls?
Everyone seems to say bigger radiators are better, but should that advice come with the caveat that sizing needs to be equal throught the heating zone?
TIA
Bonus question; if you open up all the radiators in a reasonably balanced system, and let the heating come to equielibreum with OT, and measure the temperature within each room; is that a better way to calculate heat loss? Is there a method for that?
Posted by: @scalextrixWhat if thats not possible, and room A is sized with 100% of power output to heat loss, and room B is sized to 158% of power output to heat loss; I assume room B is going to get much too hot?
The modern advice is not to have TRVs and to go as "open circuit" as possible, so how do we mitigate the oversized radiator in room B? Should we make it smaller? What % of size deviation can be handled without adding flow restrictions and controls?
The deviations can be handled by
a) the lockshield valve. this restricts the flow rate through the rad in question which increases the deltaT for that rad which reduces the average temperature and hence the output.
b) the fact that rooms tend to share heat anyway because the thermal separation is poor.
I had mismatches of 150% plus, no problem
Posted by: @scalextrixBonus question; if you open up all the radiators in a reasonably balanced system, and let the heating come to equielibreum with OT, and measure the temperature within each room; is that a better way to calculate heat loss?
No, you wont leave it like that for long enough to overcome all the other variations that mother nature throws at us.
Posted by: @scalextrixIs there a method for that?
yes, (a) measure it over several weeks monitoring individual radiators and the heat pump, Adia Thermal make the kit to do this or (b) plot your gas/oil usage vs average OAT for several months or preferably a whole season, estimate the efficiency of your boiler, and work from there (gives you whole house only).
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa thanks for the reply, so really in this case we have to reduce the flow to the radiator to achieve it.
In my specific case the oversize radiators are upstairs which isn't really the best from a heat sharing perspective, but I get your point.
Posted by: @scalextrix@jamespa thanks for the reply, so really in this case we have to reduce the flow to the radiator to achieve it.
In my specific case the oversize radiators are upstairs which isn't really the best from a heat sharing perspective, but I get your point.
Mine are also upstairs because I upgraded them before I realised how much the heat pump industry overestimates house losses. Still not a problem although the lack of 'valve authority' with the very old LSVs on a couple of the rads in question makes for a slightly tricky, but not impossible, adjustment . Of course that is my house, yours may be different. The 'excess' upstairs capacity helped my installer to be happy to leave the bathroom well under-provided for, thus I could retain my exiting towel rail rather than replace it.
That said if you can make the downstairs ones bigger go for it. Lower flow temperature = lower cost and greater comfort, as you clearly know!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,367 Topics
- 53.7 K Posts
- 166 Online
- 6,042 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@mosibi — thanks. That's an interesting find, one I hav...
By cathodeRay , 47 minutes ago
-
RE: Forum updates, announcements & issues
As we head into 2026, I just wanted to take a moment to...
By Mars , 49 minutes ago
-
RE: A Smarter Smart Controller from Homely?
@toodles Thanks. Yes I’ve tried three or four times and...
By Papahuhu , 50 minutes ago
-
RE: Setback savings - fact or fiction?
I agree, and I think there are two things in play here....
By cathodeRay , 2 hours ago
-
RE: Changing from 4-port buffer to volumizer
Thank you so much for your help. After New Years I'll g...
By Andy1618 , 5 hours ago
-
RE: Water Hammer After Heat Pump Install
That's really helpful. Yor last sentence confirms it'...
By JamesPa , 8 hours ago
-
RE: Connecting Growatt SPH5000 over wired ethernet rather than wireless
Having had another little look around, it seems Growatt...
By Majordennisbloodnok , 8 hours ago
-
Data Accuracy Problem: Daikin 8kW Heat Pump's Onecta App vs MMI Power Consumption
Good Evening. Has anyone found the following when usi...
By Nursethescreens , 21 hours ago
-
RE: Help needed with Grant Aerona 3 issues
First time posting so bear with me. Some bits that have...
By Adamp , 1 day ago
-
RE: Mitsu PUHZ-SW120YHA + EHSC-VM20Uk - Performance
All understood. Obviously its a bit house de...
By JamesPa , 1 day ago
-
RE: Who's your electricity provider and what's your tariff?
@majordennisbloodnok This may be a better thread to ...
By Batpred , 2 days ago
-
RE: Best Heat Pump Brand in the UK
Last Call to Vote & Win! Haven't voted for your Hea...
By Mars , 2 days ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
Interesting question. To be frank, since I have no inte...
By Majordennisbloodnok , 2 days ago
-
RE: New Fogstar 15.5kWh upright solution
The video shows the JK balancer, but the connection of ...
By Batpred , 3 days ago
-
RE: Ecodan unable to hit legionella target temp - what's the consensus?
@9jwr9 Hi, yes this is the issue with every (stand alon...
By ASHP-BOBBA , 3 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk FWIW I managed unintentionally to 'coax' mine in...
By JamesPa , 3 days ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
You are in essence right. Adia only works with selecte...
By JamesPa , 3 days ago
-
No, you haven’t missed out, @batpred. This thread’ll st...
By Majordennisbloodnok , 3 days ago
-
RE: Tesla Powerwall – More of a ‘Luxury’ Than an ROI Winner!
Also, though they weren’t prepared to match the price t...
By Toodles , 3 days ago