Samsung gen 6 - how to manually turn on/off immersion (booster)
Hi all,
New to the forums - I've just had a Samsung gen6 12kW ASHP installed, and initial impressions are good - install seems good and it's running well.
One thing I can't figure out is a quick/easy way to manually (and/or schedule) the immersion to come on/off.
We are on Octopus Agile tariff, so occasionally get very cheap or free electricity slots. I've disabled the scheduled legionella cycle (we empty and reheat the tank twice daily), and try to schedule DHW reheats during cheaper periods. But I'd like to be able to manually turn on/off the immersion to take advantage of cheap/free pricing slots to manually manage heating the DHW tank to higher temps when it's cheap/free (as a cheap/free store of energy and manual legionella protection). Is there an easy way to turn on/off the immersion?
In the control panel schedule, I use Standard DHW to schedule the overnight reheat, and it reheats in around 20-25mins depending on starting/ambient temps (Max Operating Time (3025) and Delay Time (3032) both set to 60min to prevent immersion from kicking in on normal DHW reheat cycle). I understand the Power option uses the immersion - does the Power option use the immersion for the whole cycle? If so, I could use this, but not sure how to then heat above my max DHW temp setting of 50C (FSV 3021) or does 3021 limit only apply to the ASHP, not the immersion?
I'd like to understand exactly how the legionella (disinfection) cycle operates? I have a set point of 47C for DHW, with a max temp set to 50C (FSV 3021). Does the legionella programme heat to 50C using the ASHP and then use the immersion to boost this to 60C (or whatever it's set at in FSV 3044), or does the whole cycle use the immersion (booster) heater?
Thanks in advance,
OS
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
@old_scientist HI OS, yeah you're right using the power mode or forced mode the delay timer for the immersion heater will be neglected and will switch on straight away.
You can use the over shoot setting #3033 and increase to 4, so it will heat 4 degrees over your set temperature.
So I think you can set a very long delay for the booster heater, when running the DWH on standard mode, that way the booster will almost never turn on. Then when you want to do a manual heat up, use the power/forced mode to fire up the immersion heater straight away.
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
@ecobaker Thanks. Hopefully we may have some cheap pricing slots on Agile this weekend, so I will be able to have a play and observe how these settings behave in practice.
I have already set a long Delay Time (3032) of 60mins to prevent the immersion kicking in in normal operation, but have not tried Power or Forced mode yet to see how they behave. I'll check #3033, but I suspect it's at the default value of zero.
Not sure how I can use this to get to higher temps though (for manual legionella cycle), as the max temp is 55C, and the max overshoot is 4C, giving a combined max achievable temp of 59C?
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
@old_scientist My one thought is that if you’re getting 100% efficient very cheap hot water, is that still more expensive than 400% efficient heat at your standard rate?
How cheap are the cheap rates? It might not actually be worth doing because of the reduced efficiency.
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
@ecobaker absolutely correct - I'd only manually kick in the immersion when prices turn negative, so (a) I can store energy by heating DHW as high as possible (above my normal set point), and (b) allow me to run the DHW through the immersion AND the heating simultaneously (in winter), thus capitalising on any negative pricing slots.
Under normal circumstances (i.e, if I'm paying for it), the immersion stays off as it's far more efficient to use the ASHP.
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
- 26 Forums
- 2,271 Topics
- 50.8 K Posts
- 213 Online
- 5,933 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@cathoderay yes I did rather gloss over the graphs. I...
By benson , 59 seconds ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
Seeing no effect from circulating pump replacement and ...
By Crimson , 2 minutes ago
-
RE: My DIY Heat Pump installation
This is very kind. However software is not really my ...
By Polar bear , 35 minutes ago
-
This is a plot from a Shelly EM monitoring the supply t...
By Ubert767 , 11 hours ago
-
RE: Request for feedback on where we're at with our quest to get an ASHP or ideas.
thanks, heatpunk looks great, being able to do the calc...
By giryan , 13 hours ago
-
RE: Is Your House Warmer Upstairs Than Downstairs?
Why arent you expecting them to make much difference. ...
By JamesPa , 13 hours ago
-
RE: Oil Boiler & Heat Pump Hybrid System
@paultheheating I wonder if you are being a bit pessimi...
By GrahamF , 13 hours ago
-
@toodles sounds good. I started with cosy but then plug...
By Eliuccio , 14 hours ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
It has been just over a year since we changed over to a...
By npru , 16 hours ago
-
RE: Finding a Thermostatic Shower Valve That Works with Heat Pump Systems
@morgan I should just have written ‘Mea Culpa’ shouldn’...
By Toodles , 18 hours ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
'We learn from history that we do not learn from histor...
By Lawrence Leask FInstR , 18 hours ago
-
Mitsubishi Ecodan FTC7 Legionella date set
I can set the number of days between Legionella cycles ...
By DRB01 , 23 hours ago
-
RE: When to use Octopus Intelligent Go tariff with my heat pump and battery
@treewizard Yes, I like the extra facilities that NetZe...
By Toodles , 1 day ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk downstairs rads are less prone to airlocks, you ...
By AgentGeorge , 1 day ago
-
RE: My Octopus Cosy 6 Heat Pump Journey: From Quote to Completion
@editor thanks for highlighting my name. Yes I did get ...
By Chansug , 1 day ago
-
RE: balancing radiators with a mixture of different size pipework and a few undersize rads.
@editor Thanks for your input Mars. No I think the comm...
By baxtDave , 2 days ago
-
RE: Rate the quality of your heat pump design and installation
We’re looking to expand our list of recommended list of...
By Mars , 2 days ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@transparent Along with the right workers, they can’t b...
By Toodles , 2 days ago
-
RE: Midea ASHP – how to set weather compensation
I have just looked at my heat pump 'long interval' (27 ...
By cathodeRay , 2 days ago