Hi everyone,
I heard on the podcast recently that Daikin have changed to a 10C delta-T, and that this could reduce the flow rate needed which has intrigued me as I think our house is pipework limited (also heat pump power output limited but that's another story). I then read around a bit and saw that natural refrigerants can operate with a much larger deltaT than synthetic refrigerants like R32, e.g. R290 can operate happily with more than 10C deltaT I believe and CO2 (R744) actually needs a very large deltaT to operate effectively.
This made me wonder, what's the optimum deltaT for an R32 heat pump? I see most default to 5, Daikin just started using 10, and I'd read but without explanation that 8 is the magic number. I'm sure there's a good scientific calculation for this, something to do with PT curves?
Cheers 🙂
There’s no definitive magic deltaT for a heatpump, just pragmatic ‘generally optimum’. If you put more power into the water pump, the deltaT will reduce, and so then does the refrigerant gas-liquid transition temperature, making the heatpump more efficient. This lower deltaT requires a faster water flow though - so the pump needs more power. There’s an overall minimum power - and it’s generally found somewhere around deltaT=5 ish. If your pipes are thin, it’s likely higher.
In our case the pipe run for the heat pump is short and large bore to a heat exchanger, so it's a bit more complicated. Interesting that a smaller deltaT is more efficient, I had thought that a higher deltaT would be more efficient, because it would mean the water was extracting more energy from the refrigerant per m3 of flow. Anyway, for us I think it's irrelevant as I don't think our Midea heat pump allows the deltaT to be changed, it seems to be fixed at 5C.
- 27 Forums
- 2,495 Topics
- 57.8 K Posts
- 385 Online
- 6,220 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
@batpred I reckon Andy might know a thing or 2 about...
By Bash , 3 minutes ago
-
RE: What determines the SOC of a battery?
@batpred Ironically you didn't have anything good to...
By Bash , 59 minutes ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Here’s a current graph showing a bit more info. The set...
By benson , 1 hour ago
-
RE: Setback savings - fact or fiction?
True there is a variation but importantly it's understa...
By RobS , 1 hour ago
-
Below is a better quality image. Does that contain all ...
By trebor12345 , 2 hours ago
-
Sorry to bounce your thread. To put to bed some concern...
By L8Again , 2 hours ago
-
@painter26 — they (the analogue gauges) are subtly diff...
By cathodeRay , 2 hours ago
-
RE: Electricity price predictions
I am always impressed with how you keep abreast of so m...
By Batpred , 3 hours ago
-
RE: Humidity, or lack thereof... is my heat pump making rooms drier?
@majordennisbloodnok I’m glad I posted this. There see...
By AndrewJ , 3 hours ago
-
Our Experience installing a heat pump into a Grade 2 Listed stone house
First want to thank everybody who has contributed to th...
By Travellingwave , 6 hours ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Welcome to the forums.I assume that you're getting the ...
By Sheriff Fatman , 9 hours ago
-
RE: Say hello and introduce yourself
@editor @kev1964-irl This discussion might be best had ...
By GC61 , 10 hours ago
-
RE: Oversized 10.5kW Grant Aerona Heat Pump on Microbore Pipes and Undersized Rads
@uknick TBH if I were taking the floor up ...
By JamesPa , 1 day ago
-
RE: Getting ready for export with a BESS
I would have not got it if it was that tight
By Batpred , 1 day ago
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
@judith thanks Judith. Confirmation appreciated. The ...
By DavidB , 1 day ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
That makes sense. I thought better to comment in this t...
By Batpred , 1 day ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
My heat pump journey began a couple of years ago when I...
By Slartibartfast , 1 day ago
-
RE: How to control DHW with Honeywell EvoHome on Trianco ActiveAir 5 kW ASHP
The last photo is defrost for sure (or cooling, but pre...
By JamesPa , 1 day ago
-
RE: Plug and play solar. Thoughts?
Essentially, this just needed legislation. In Germany t...
By Batpred , 1 day ago
-
RE: A Smarter Smart Controller from Homely?
@toodles Intentional opening of any warranty “can of wo...
By Papahuhu , 1 day ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thanks @transparent Thankyou for your advic...
By Bash , 1 day ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: Odd_LionManufacturer: SamsungModel: Samsu...
By Odd_Lion , 1 day ago
-
RE: Configuring third party dongle for Ecodan local control
Well, it was mentioned before in the early pos...
By F1p , 2 days ago