R32, "optimum" delta T
Hi everyone,
I heard on the podcast recently that Daikin have changed to a 10C delta-T, and that this could reduce the flow rate needed which has intrigued me as I think our house is pipework limited (also heat pump power output limited but that's another story). I then read around a bit and saw that natural refrigerants can operate with a much larger deltaT than synthetic refrigerants like R32, e.g. R290 can operate happily with more than 10C deltaT I believe and CO2 (R744) actually needs a very large deltaT to operate effectively.
This made me wonder, what's the optimum deltaT for an R32 heat pump? I see most default to 5, Daikin just started using 10, and I'd read but without explanation that 8 is the magic number. I'm sure there's a good scientific calculation for this, something to do with PT curves?
Cheers 🙂
There’s no definitive magic deltaT for a heatpump, just pragmatic ‘generally optimum’. If you put more power into the water pump, the deltaT will reduce, and so then does the refrigerant gas-liquid transition temperature, making the heatpump more efficient. This lower deltaT requires a faster water flow though - so the pump needs more power. There’s an overall minimum power - and it’s generally found somewhere around deltaT=5 ish. If your pipes are thin, it’s likely higher.
In our case the pipe run for the heat pump is short and large bore to a heat exchanger, so it's a bit more complicated. Interesting that a smaller deltaT is more efficient, I had thought that a higher deltaT would be more efficient, because it would mean the water was extracting more energy from the refrigerant per m3 of flow. Anyway, for us I think it's irrelevant as I don't think our Midea heat pump allows the deltaT to be changed, it seems to be fixed at 5C.
- 26 Forums
 - 2,265 Topics
 - 50.6 K Posts
 - 194 Online
 - 5,924 Members
 
Join Us!
Podcast Picks
Latest Posts
- 
                        
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
@editor thank you. Can I ask who actually issues the MC...
By MairiA , 9 minutes ago
 - 
                        
Thanks @bontwoody!It's worth noting that you did purcha...
By F1p , 16 minutes ago
 - 
                        
                                RE: Oil Boiler & Heat Pump Hybrid System
OK. Got it. As a fellow rural West Country resident, ...
By Transparent , 36 minutes ago
 - 
                        
RE: Grant 13kW Aerona3 - issues getting zones to temp
@crimson I asked Eskimo about their correction facto...
By JamesPa , 1 hour ago
 - 
                        
                                RE: My DIY Heat Pump installation
@pollar-bear Top job, I installed my own too and even t...
By bontwoody , 1 hour ago
 - 
                        
RE: Help me keep the faith with my air source heat pump installation
There are two definitions of sufficient volume. The fi...
By JamesPa , 2 hours ago
 - 
                        
                                RE: Who has a V2G EV installation
Not sure how you got that information, @batpred. As of ...
By Majordennisbloodnok , 2 hours ago
 - 
                        
                                RE: Midea ASHP – how to set weather compensation
@pash44pump - I stopped using the Mide app ages ago, so...
By cathodeRay , 2 hours ago
 - 
                        
RE: UFH downstairs and radiators upstairs balancing question
@ashp-bobba Can I pick you brain about mine ...
By davidnolan22 , 3 hours ago
 - 
                        
                                RE: Electricity price predictions
One persons view In sync with the Nesta figures s...
By Jeff , 15 hours ago
 - 
                        
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
Ok so that seems to be the key point namely only mcs ca...
By JamesPa , 17 hours ago
 - 
                        
RE: One flow valve appears to be duff
You might want to consider the following common faults:...
By IaAck , 24 hours ago
 - 
                        
                                RE: When to use Octopus Intelligent Go tariff with my heat pump and battery
We are on the Intelligent Octopus Go tariff. We instal...
By GrahamF , 1 day ago
 - 
                        
RE: New build installation query
@paullacey While the others wait for more info do you m...
By ASHP-BOBBA , 1 day ago
 - 
                        
                                RE: British Gas Heat Pump Installation Complaint
@bgno, the other consideration for legionella cycles ar...
By Mars , 2 days ago
 - 
                        
                                @old_scientist I dont monitor the tank temperature but ...
By bontwoody , 2 days ago
 - 
                        
                                RE: Say hello and introduce yourself
Hello @paultheheating - I'm a rural Moderator! What's...
By Transparent , 2 days ago
 - 
                        
RE: What valves to replace radbots?
Yes. Radbots just replace TRV heads. TRV heads push t...
By JamesPa , 2 days ago
 


 