Placement of Samsung R290 ASHP
Posted by: @jancold@jamespa I notice they talk of untrapped drain or cellar entry. I'm pretty sure my rainwater drains connect to the main sewer so surely they must have a trap? So they should not be a problem?
To be honest I hadn't noticed this subtlety. Drains connected to sewers should have a trap, mine certainly do.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I wanted to put our r290 gshp near a kitchen drain. And found to my dismay that it didn’t have a trap! Bit of a faff, but managed to swap it out for one with a bottle trap (in piccy left is new bottle trap, right one is direct to sewer). Didn’t particularly smell, weird.
Wandering around the internet I find there are ice making machines with R290 that are allowed to be inside buildings albeit with only 150 gm of charge.
I also came across this showing the result of a "perfect" gas mix explosion on a yacht. Of interest is the first failed ignition showing how the explosive mix ( 2 to 10%) had not been achieved.
A heat pump is outside in free air so a leak would normally disperse, however I agree it's not worth the risk.
In an earlier life I was a Deck officer with Shell. They had two VLCC's (Very large crude carriers) returning from the Gulf and cleaning tanks with high pressure hot water. An explosive mix built up and an electrostatic spark set it off. One sank and the other had to be scrapped. Thereafter the tanks were always kept filled with inert gas from the boiler! This was just before I started my training with Shell and I did not hear about it until some time afterwards!
Maybe I'll go with R32. 😀
Compared to having ‘natural’ gas piped continuously into a home -a permanent gas source, the tiny amount of r290 kept safely in a heatpump for many many years seems benign. If indeed it did leak out fast enough in a small enough enclosure to achieve an explosive mixture, you’d have a limited time window to apply a spark before it all leaked out into atmosphere anyway.
@jancold I think that that is the argument; the gas may disperse into the drain - hence to the sewers. As mentioned though, the quantities are very small compared with say a BBQ propane or butane tank. Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Also, as indicated in the video up-thread, worse things happen at sea
Toodles, he heats his home with cold draughts and cooks his food with magnets.

Posted by: @roblCompared to having ‘natural’ gas piped continuously into a home -a permanent gas source, the tiny amount of r290 kept safely in a heatpump for many many years seems benign. If indeed it did leak out fast enough in a small enough enclosure to achieve an explosive mixture, you’d have a limited time window to apply a spark before it all leaked out into atmosphere anyway.
In general I would agree, but there are a few specifics to bear in mind, some obvious, some less so.
Firstly, propane is denser than air and so, in an enclosed space, will pool. Outside or in a room with good airflow it will indeed dissipate but obviously not in a sewer or septic tank.
Secondly, propane is pretty stable so won't break down over time. Any propane released into the outside atmosphere will still remain propane until burned (even if the concentrations when that happens will mean its effects are undiscernable). What that means is that if any propane did escape from a heat pump into a sewer and pool there it would remain as a pocket of propane that could be added to at a later date by the escape of more propane from another heat pump/ice machine/leaky gas bottle etc. Just because one device contains very little doesn't necessarily mean you can ignore cumulative effects.
Thirdly, the time window is a bit of a weird one. I remember way back when I was at school a demonstration whereby two holes were made in a catering-sized instant coffee tin; one in the base, one in the lid. A gas pipe was removed from a bunsen burner and put into the bottom hole, and the tin was filled with gas. Once full, the gas escaping from the top was lit and, of course, burned just as one would expect - in effect, the tin had just become an extension to the tube. The gas was then turned off and the tube immediately removed from the bottom, and the flame at the top of the tin steadily worked its way back into the tin as the gas was used up, being replaced by air from the outside. At the point the gas concentration got low enough to form the perfect ratio the remaining gas reacted all at once and the explosion blew the lid off the tin. I'm sure you could find plenty of videos of this demonstration on Youtube. The point, though, is that if your escaped propane pools in an enclosed space it doesn't need to be ignited quickly or even when the gas/air ratio is exactly right; all it needs is to be ignited when there's more than enough propane to burn and then chemistry will do the rest with an explosion following shortly afterwards.
I should point out that I'm not trying to teach good ol' Granny to suck eggs; I'm guessing you already know these details. All I'm trying to do is give a bit of context to the reasoning behind the regulations for anyone who isn't already aware. And with that context in mind, it becomes clearer not just why treating a heat pump like a 47kg propane bottle is inappropriate but also why the propane in a heat pump shouldn't be ignored completely.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; suus solum profundum variat"
The choice of refrigerant is always a compromise. So far as I'm aware, they are generally:
Poisonous / High GWP / ozone depleting / flammable / super high pressure
I don't think there is an obvious "perfect" refrigerant - ie. one with no compromises. Propane used to be the refrigerant of choice some 100 years ago, then we had ozone depleting ones, then high GWP ones; now back to propane. I appreciate there's always new ones out like R1234yf (Tetrafluoropropene) - maybe that has no downsides?.
Posted by: @roblI appreciate there's always new ones out like R1234yf (Tetrafluoropropene) - maybe that has no downsides?
Sadly a very significant downside, turned out the 'too good to be true' HFO synthetic refrigerants like R1234yf and R1234ze were, well, too good to be true. They contain PFAS compounds, so-called 'forever synthetic chemicals' which don't break down in the environment. There is planned legislation in the EU to ban PFAS substances, which, if adopted, will kill off the tranche of popular HFO refrigerants such as those above and many of the R45* numbered HFO commercial products.
R290 propane is the refrigerant which the domestic ASHP heat pump industry will adopt. Ideal (part of Groupe Atlantic) has just launched their R290 ASHP models only a year after launching their R32 model range. In hindsight, they didn't quite anticipate or consider the EU legislating so quickly to further drawn down on higher GWP refrigerants such as R32. Grant has R290 models planned for launch later this year and currently on trial - Chinese made & badged up sadly, so not made locally.
Some of the restrictions on locating R290 ASHPs are a little over-cautious, and not based on an accurate risk assessment of the unit charge, probable leakage rate & explosion potential. Hopefully some common sense will prevail in due course.
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 49 Online
- 2,278 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
@jamespa @bontwoodyHeat loss calculations found and att...
By BAMi , 58 minutes ago
-
RE: What is the best strategy for operating a very oversized heat pump?
I think you are right to frame the question as you did,...
By Old_Scientist , 1 hour ago
-
RE: Setback savings - fact or fiction?
Here's the same plot, less the R squared values, done q...
By cathodeRay , 2 hours ago
-
RE: SolarPV tables / online calculator
We've only had our solar since last June, but so far fo...
By Old_Scientist , 2 hours ago
-
@jamespa thanks, it's way off of the MCS performance es...
By big_si , 2 hours ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
@jamespa Agreed. I think it’s a case of much over muchn...
By Mars , 5 hours ago
-
@eliuccio Unfortunately, whilst I agree with a lot of...
By JamesPa , 5 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Definitely its in the 20xx FSVs. Conversely it may be...
By JamesPa , 6 hours ago
-
RE: Towel rails. An unexpected final hurdle
We have both Normal Rad for heating the room and then a...
By IRMartini , 8 hours ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 10 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 24 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 1 day ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 1 day ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 1 day ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 1 day ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 12 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 13 hours ago
-
SolarPV tables / online calculator
By MichelleC 20 hours ago
-
By Toodles 2 days ago