Performance in the current cold snap…
Posted by: @derek-mPosted by: @hughf@derek-m single heat pump, just run on weather comp, no stats, no setback.
The Carel platform that my heat pump is built on allows full tuning of the PID settings, along with full control of the compressor ramp speeds. It’s close to maintaining setpoint, but I’ve still got some work to do. I’d like to deal with the initial overshoot next, I think I’ve got the oscillation damped quite well.
When it’s around freezing outside, it runs happily for a long period of time, it’s dealing with the overshoot when it’s cycling that’s the next area of tuning that needs my attention.
I suspect that it will not be possible to accurately control the LWT during milder weather conditions, simply due to the fact that the heat pump will be starting to operate outside its control envelope. i.e. it cannot turn-down any further.
As far as controlling IAT is concerned this should not be a major issue, though it could take some time to optimise for maximum efficiency.
Out of interest what are your PID settings?
It is my suspicion too, that in milder weather, we are simply oversized. I didn't take into consideration the possibility that the ACH value used in the heat loss spreadsheet (and by heating engineer) could be considerably higher than we actually achieve.
The fact that it was tracking the requested setpoint to within 0.1 degree during the last 2 weeks of freezing weather leads me to think my PID settings aren't a million miles off.
At the moment they are: P = 5 deg. C, I = 50 secs, D = 0 secs.
The controller also allows me to open up the overshoot window, which gives headroom for compressor rampdown - currently set to 5 degrees. I can't remember the rampdown settings though, it's specified in Hz/sec inside the Power+ inverter settings.
To comment on the original question in the thread title - I was away for a lot of the 2 week freeze, but the residents reported stable internal temperatures (21-22) 24/7 and there were no issues with defrosting, even with our limited system volume.
Whole house electric consumption was running around 50kWh/day - all electric house now.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
- 26 Forums
- 2,129 Topics
- 46.8 K Posts
- 23 Online
- 5,654 Members
Podcast Picks
Latest Posts
-
RE: Mitsu Wireless Controller and MelCloud
It would seem that I have a problem (at least one!) in ...
By DavidAlgarve , 1 hour ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
For reference, our installer has just contacted us afte...
By Old_Scientist , 21 hours ago
-
@toodles Of course. I've also used Tim and Kat's Gree...
By Old_Scientist , 21 hours ago
-
RE: Who's your electricity provider and what's your tariff?
Yes, I noticed that change too. The software really doe...
By Old_Scientist , 21 hours ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
@old_scientist me too. Just installed my new heat pump ...
By Eliuccio , 2 days ago
-
RE: Is your heat pump insured?
Yup just spoke to Privilege to inform them of my impend...
By Scalextrix , 2 days ago
-
RE: Forum updates, announcements & issues
Just to keep everyone in the loop, as the site continue...
By Mars , 2 days ago
-
RE: Fast DHW setting on Midea (Clivet) heat pump
@simon-w, is this something you could potentially assis...
By Mars , 2 days ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
Fwiw I called my installer out for the first time a few...
By JamesPa , 3 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@sandy, I'll send Vaillant an email tomorrow and see if...
By Mars , 3 days ago
-
RE: Long term efficiency degradation
@jamespa yes as I thought thanks. We have a reaso...
By Scalextrix , 3 days ago
-
RE: Who has a V2G EV installation
I agree, but a word of caution. V2X is also sometimes u...
By Majordennisbloodnok , 4 days ago
-
RE: Sunamp Thermino Heat Battery
@jamespa A few days after the installation had been com...
By Toodles , 4 days ago
-
RE: Planning Permission May 2025
Fair enough. I have read the legislation and MCS020a ...
By JamesPa , 6 days ago
-
RE: How do I choose a single room MVHR to prevent losing heat in my bathroom ?
An update on the Heatsava. It is the most difficult thi...
By heat-pump-newbie , 6 days ago
-
RE: ASHP heat output monitoring
@carlo - not much better, is it. It looks more like a u...
By cathodeRay , 7 days ago
-
RE: Renewables & Heat Pumps in the News
this document extensively describes (in a non-blame, ne...
By Judith , 7 days ago
-
RE: Ecodan - Legionella Operation Time and Target Temperature
Once the white plastic cap is removed, my immersion loo...
By Old_Scientist , 1 week ago
-
RE: Replacing Refrigerant on Mitsubishi Heat Pump
@dgclimatecontrol I don't know, but they were not happy...
By DavidAlgarve , 1 week ago
-
RE: Why do we need pressurised systems?
A good question @toodles. My old open thermal store and...
By AllyFish , 1 week ago