Our Vaillant VWL year end review - North East Scotland
Evening all,
Happy New Year to one and all, I hope this finds you all fit and well.
I have finally completed my energy data spreadsheet for our system which was installed in March of last year. I love numbers so this has been quite an interesting exercise. I "think" it gives a good summary of our system. We are still learning our system, I think we are at the tweaking stage now. The ground floor with UFH is now a single zone, we are still trying to find the best settings to get the unit running full time when the temp drops. We are just trying to find the best curves to use for upstairs and downstairs that suit our needs. One thing this cold spell has shown us is that our unit is potentially smaller than it should be. When required to have both upstairs and downstairs heated at the same time, the unit runs flat out. Monitoring this situation closely, it's never let us down, just runs flat out for longer than I would like.
We have a Valiant VWL 75/6 A 230V S2.
Hope these numbers are of use to someone on here, it would be good to see how others got on in December.
ATB
Drew Parkes
Happy New Year to you too. Good numbers for your size of house. Our December was 970 for heating and HW for a similar sized place.
When it's very cold does the ASHP maintain the room temp you want? What was your highest consumption/lowest temp in December? (can't see the detail in the ss)
Your 'other' consumption seems quite high compared to your heating and HW.
Hi Kev,
From what I can see the highest daily electricity consumption by the heat pump inc DHW was 42kwh (39 for CH, 3 for DHW). All the individual months data is in the desperate sheets in the document .
- I forgot to mention, our base load is high due to an EV being charged at home.
- The unit always managed to reach required temps in the house, albeit with it running flat out for longer periods.
- We still haven’t reached the point where the unit is running at a lower load all the time, it still starts stops a fair bit.
- the learning curve with this is steep.
How does our system compare to others out there?
ATB.
Drew
Posted by: @drew-paHi Kev,
From what I can see the highest daily electricity consumption by the heat pump inc DHW was 42kwh (39 for CH, 3 for DHW). All the individual months data is in the desperate sheets in the document .
- I forgot to mention, our base load is high due to an EV being charged at home.
- The unit always managed to reach required temps in the house, albeit with it running flat out for longer periods.
- We still haven’t reached the point where the unit is running at a lower load all the time, it still starts stops a fair bit.
- the learning curve with this is steep.
How does our system compare to others out there?
ATB.
Drew
All the months except December are there?
My ASHP will run constantly if it's between about 2 degrees and 9 degrees outside. Below 2 it can defrost maybe once an hour and above 9 it cycles (switches on and off) twice an hour or so.
Do you know if your thermostats are causing the starts and stops or is it the flow temp target being met?
@drew-pa, a good collection of data. Thank you for sharing. Your consumption numbers are quite low, which is good, but it would be good to know what your target temperature is across the house and, like Kev says, to know whether that temperature has been hit.
A bit trickier, but very helpful, is to have the average daily ambient temperature (or a low and a max) for each day to see how the heat pump copes when things get really chilly (and how chilly it got). For me, that's a very useful reference point to understand at what temperatures our heat pump loses significant efficiency and whether we can supplement that with a log fire for a few hours, for example. The software for our heat pump gives a daily temperature average for each day it collects data. That would be very interesting to see, but a bit of hassle to do manually.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
it’s good to hear we are heading in the right direction.
- target temps - upstairs 19c constant - downstairs 20c constant.
- upstairs is controlled by the Vaillant controller, presently in the hall, soon to be in the coldest room. All valves wide open now.
- Down stairs has Vaillant controller, but this is redundant at present. Presently running the whole downstairs off one of the rooms(zones) controllers. All zone heads disconnected so effectively running a single zone. All other controllers set low enough so as not to call for heat.
- would like to reinstate the Vaillant controller, but as far as I am aware it won’t call for the UFH pump to turn on so this is the reason we are using the UFH room controller.
- All temps have been hit. Albeit with higher loads on the heat pump. We have never had a situation yet where the heat pump hadn’t reached a required temp.
- I am intrigued regarding the outside temps. We can see it in the Vaillant controller, but it’s not logged. There must be a website I can pull historical data for the area for analysis purposes. I have a list of improvement suggestions to email Vaillant, let’s see what they say.
- We have a 6kw solar PV coming in the next few months along with a battery so fingers crossed that will drop costs.
- @kev I’m sure it’s the controller that’s shutting down, not the flow temps if that makes sense. Downstairs it’s a room temp controller we are using, upstairs it’s the Vaillant controller operating to a set point of 19c.
hope that makes some more sense.
What is the size of your house?
I have only been collecting numbers for a short while but it looks like my total consumption for December was almost identical to yours at 762 kWh, for a three-bedroom house in southern England.
However the system was not set up properly with weather compensation for some of that period. Based on more recent days when the weather was milder it looks like it should be about 500-550 kWh for January, barring any more cold snaps.
Visual Crossing and Time and Date websites both do historical weather data.
If u like numbers as u say u will love all the data from visual crossing. 😀
Posted by: @sandVisual Crossing and Time and Date websites both do historical weather data.
If u like numbers as u say u will love all the data from visual crossing
Another valuable source of weather data is the Met Office's WOW website:
You have to sign up (free) but then you get access to very detailed local weather data. Just find an observation station near you and you can download data in csv format until you are blue in the face. The one I use has observations every few minutes, these can be converted into hourly obs using pivot tables.
Midea 14kW (for now...) ASHP heating both building and DHW
it’s been very noticeable this last week. The temp has risen by a couple of degrees, and the consumption has dropped again. The efficiency of our unit seems a lot greater around the present temps (circa 5-6c). I will get all the data merged into one data set and then present it to show the findings.
From what I can see at present
- Our unit is a little smaller than it should ideally be.
- the efficiency dropped massively when the temp got to -2/-4c. Adjusted curves slightly to try and improve efficiency.
- So far, we have never not reached desired temp.
- Think I’ve found a solution so that the Vaillant control system will be able to control the UFH pump on and off. Work in progress.
- looking forward to getting our solar PV/batteries in the coming months.
- really enjoying the forum, great work by all involved. Thank you.
Drew
@drew-pa. At risk of sounding like one of the Four Yorkshiremen, I dream of a monthly consumption like that, 760kWh - you were lucky!
I live in a c100yr old four bed detached in the Cairngorms, around 175m2, solid stone walls and suspended floors. Never going to be a passivhaus it's true but we've installed secondary glazing throughout and are zealously chasing out draughts to try and improve matters and we've a C-rated EPC (79 score). We've 2 x 12kW Samsung heat pumps operating on a master and slave basis.
During December we managed to consume an eye-watering 2536kWh, with a daily peak of around 130kWh, that's around twice a typical daily figure for November or over the last week. Obviously not sustainable. I ended up switching the slave heat pump off as I'm not convinced it's adding much value - the controller shows its output temp consistently some 6° C lower than the master (so presumably just lowering the buffer tank temperature) and heat power generated is recorded as virtually zero which may be a measurement issue. Neither unit gets anywhere near their WC set point.
Like you I've seen a significant improvement in efficiency over the last few days as temperatures have risen to 3-4°C or so. Nevertheless I'm far from convinced the system is set up optimally and I'm currently waiting for a visit from the installer and Joules. I'm not holding my breath.
Simon
2 x 12kW Samsung Gen6 ASHP, 5.6kW solar PV ground mounted c/w 10kWh Puredrive battery & Solis inverter.
- 22 Forums
- 2,032 Topics
- 44.3 K Posts
- 22 Online
- 3,237 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Agile: average import cost vs other tariffs?
@toodles thanks for the analysis. I'll be really intere...
By Old_Scientist , 6 hours ago
-
RE: Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW
Welcome to the forums. It’s clear that you’ve taken t...
By Mars , 6 hours ago
-
RE: help sizing rads based on room by room heat loss
By JamesPa , 7 hours ago
-
Hi Thanks for the reply, the walls are being constru...
By Fingers , 8 hours ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
@phoenix15 I'm no plumber so please don't take this as ...
By dnagre , 9 hours ago
-
RE: Is this normal? Click of the DHW returning to space heating
@grantmethestrength Oh sorry to hear that, there should...
By ASHP-BOBBA , 13 hours ago
-
@ashp-bobba TBH the ladies are rather disorganised, so ...
By Cathyem1 , 14 hours ago
-
The Rise and Fall of Europe’s Most Generous Green Subsidy
This story came to my attention thanks to Graham Hendra...
By Mars , 14 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
And for those of us without an automatic irrigation sys...
By Majordennisbloodnok , 14 hours ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Thermal Off's
From the Full SAP Report: Space heating requirements:...
By trebor12345 , 14 hours ago
-
Logically, the lower frequency = more gentle, yes, but ...
By SUNandAIR , 18 hours ago
-
RE: Ideal Logic ASHP - change from 55°C to 35°C Heating?
Good point. I’ll keep my eye on the manifold temperatur...
By Tomdad , 21 hours ago
-
RE: How hard and expensive would it be to change panel and add battery?
@transparent It is a setting that Octopus make via the ...
By Toodles , 21 hours ago
-
RE: Performance of Heat Pumps in Mild Weather
@heatgeek The flow rate isnt controlled by Mitsub...
By RobS , 24 hours ago
-
RE: Say hello and introduce yourself
I might put a couple of speakers in the ceiling if fund...
By Fingers , 1 day ago
-
RE: Bathroom Radiator replacement
@rob-nezard can you please offer your professional advi...
By Mars , 2 days ago
-
-
RE: Questions on my Hitachi Yutaki SCombi Heat Pump
OK, thats good and low. With low flow temperatures lik...
By JamesPa , 3 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@jamespa “They are all equal but, some are more equal t...
By Toodles , 3 days ago
-
RE: Is it KISS or constant – weather compensation vs. set flow temperature?
@cliffhanger Mine has a 'space heating off' setting! O...
By JamesPa , 3 days ago