If you are going to keep records over a period of time, it may be useful to also note the weather conditions, to try to quantify the effects of solar gain and the other elemental changes that could affects the results.
@derek-m - good point, I will see if I can pull that out from the weather data as well. It may have cloud cover or hours of sunshine or something I can use as a proxy.
Here's a photo of the Midea app on my non-SIM mobile (easier to photo it than try and transfer a screen grab). The integer values are a bit suspicious, and I am not sure what happened to the DHW heating, which was definitely in use for about 20 mins between 1300 and 1400 and shows up as 2kWh on the History page, and it is a pity it records the Set LWT (which I presume is the weather comp set temp) rather than the actual LWT, and I am not sure how it knows the 1900 hour value at 1930 hours but at least I have something!
Midea 14kW (for now...) ASHP heating both building and DHW
The reading shown at 19:00 will be for the period from 18:00 to 19:00.
Because it is displaying energy consumption as integers, hourly calculations will not be very productive. At least it confirms that the weather compensation is working.
Posted by: @derek-mThe reading shown at 19:00 will be for the period from 18:00 to 19:00.
Because it is displaying energy consumption as integers, hourly calculations will not be very productive. At least it confirms that the weather compensation is working.
Hopefully the rounding errors will cancel out over time, so summed usage over a longer period will be more accurate, unless it always rounds up or down. This is typical black box stuff, no way of telling what is going on inside the black box. On the History page, it says it has produced 77kWh out for 23kWh in so far today (ie midnight to 0900), giving a nominal COP of 3.3 over a period when the ambient was around 4 degrees most of the time. If it carries on at the same rate, it will clock up around 60kWh used today, or 430kWh over the week. This is somewhat on the high side, around 11,162kWh over a six month heating season, or £3795 at today's current price cap of 0.34p per kWh plus of course standing charges as well as other non-heating use. That said, average temp over the whole heating season should be a bit higher than 4 degrees, so maybe the total will be a bit less. Time will tell.
Midea 14kW (for now...) ASHP heating both building and DHW
@cathoderay Honestly I think those 0.x numbers aren't really an issue. In the grand scheme when the heating really matters you are going to be using quite a lot of kW and the nominal difference a 0.x will make gets smaller and smaller. In the end the overall trend matters more than the figures. Increasing COP is the aim.
From my experience ambient SEEMS to be an average of the temperature over the whole day as I have never seen one below 3 degrees on my own system.
Also as a note the removal of the LLH seems to have made a big difference to my rads and ASHP settings. I've dropped the flow temps significantly for no downside (yet)
Posted by: @bataltoFrom my experience ambient SEEMS to be an average of the temperature over the whole day as I have never seen one below 3 degrees on my own system.
Sounds as though it may well be some sort of average. The ambients I will be using come from weather stations, I have one near enough to me to be good enough. The data are recorded every few minutes, I then average them over the hour to get hourly (average) temp. I think I may have posted this before, but this is the sort of chart I get, this one being April this year:
It's that cold snap at the beginning of the month and the ASHP in weather comp mode not coping that had me worried (and still does, as we haven't had sub zero temps yet this year). My kWh use went through the roof last April...
Midea 14kW (for now...) ASHP heating both building and DHW
@cathoderay heating will always be highest in the coldest weather. We had a few days last year of very high use. Below is the worst day when it averaged 3 degrees. I think we used well over 100kw total that day when you account for lights, oven etc - so at todays cap £34 a day...
Posted by: @bataltoI think we used well over 100kw total that day when you account for lights, oven etc - so at todays cap £34 a day...
Ouch.
I have currently got the hour by hour monitoring running, and will try to do some calculations tomorrow afternoon, once the 24 hour period has completed. This is just a test run, to see whether it works, ie the data is collectable and the analysis doable. It seems the local weather station doesn't record cloud cover or hours of sunshine, so that won't be in the analysis for now. Still no way of getting usable flow and LWT/RWT data, so unfortunately can't try the third method (Q=m×c×ΔT, energy = mass x specific heat capacity x temp difference method).
In another thread a while back @kev-m noted "I...have got weather comp working just about spot on with little intervention from the thermostats." It seems to me this is based on the premise that building heat loss equals ASHP heat input, and the weather comp curve adjusts the heat pump output to match the predicted building heat loss, and the end result is a steady state. It also suggests both curves are linear. If all this is the case, then it may not bo so crazy after all to work back from predicted heat loss to ASHP output, providing the building temp is in steady state.
Midea 14kW (for now...) ASHP heating both building and DHW
@cathoderay Its not quite linear from my own data collection - but pretty close. In essence what @kev-m noted is that you can adjust the weather compensation to get your steady state. You can do this by just cranking up your thermostat to always call for heat e.g. set it to 30, and control the actual temperature by adjusting your weather compensation. If its hotter than your desired temps, just lower it until you get to the right place. That's what I did previously. Set the controller to 22 and kept things at 21 through WC. Its not ideal, but its good enough.
@batalto - to my simple mind it should be linear, and I think I am right in saying the energy/flow/specific heat formula assumes it is but I can't argue with that trend line! Unless it is linear, and something is else affecting the readings at each end?
The Post LLH readings are interesting, in that they are all below the With LLH line, with possibly the difference more marked at higher ambients. With only three data points, its too early to say, but it will be interesting to see if that pattern remains over time. I think it might.
Midea 14kW (for now...) ASHP heating both building and DHW
@cathoderay in that graph the Y axis is power used. Below the line is better. Once I have more data I'll also plot a trend line
Posted by: @bataltoBelow the line is better.
I know! That's why I made the observation I did, and then said its early days ie only three data points.
As a matter of interest, what did you use to do the plot? It looks like the sort of thing that might have come from R, if so, I am impressed!
Midea 14kW (for now...) ASHP heating both building and DHW
- 22 Forums
- 2,078 Topics
- 45.6 K Posts
- 75 Online
- 3,361 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@benson Rain will always have its’ wicked way into anyt...
By Toodles , 8 hours ago
-
RE: Home energy storage & battery register
Tesla Powerwall 3 with Gateway.
By Broadsman , 12 hours ago
-
-
RE: All your heat pump problems solved by -- a plate heat exchanger in a plinth!
@allyfish As you say, all the ‘plus points’ and ‘advant...
By Toodles , 1 day ago
-
RE: Say hello and introduce yourself
I think my trouble is that I could easily write a whole...
By Transparent , 1 day ago
-
RE: Renewable Heating Hub Homeowners' Q&A Podcast
In our latest episode, we hand the mic to four homeowne...
By Mars , 3 days ago
-
RE: Forum updates, announcements & issues
@andrewj I’m currently away and only back this weekend....
By Mars , 3 days ago
-
RE: Help Stop the MCS Heat Pump Monopoly
Response sent. Thank you for highlighting the document...
By Sheriff Fatman , 3 days ago
-
RE: I worry I've messed my Samsung settings up somehow
Yes , this time of year . Unfortuneately I dont have ...
By Alfapat , 3 days ago
-
RE: Feasible solutions to expand existing Sunsynk battery capacity
Ours is a loft installation, which is where both invert...
By Sheriff Fatman , 3 days ago
-
RE: 5 Star Service from Havenwise
@sheriff-fatman Exactly this is why a lot of our users ...
By HCas , 4 days ago
-
RE: Solar Thermal DHW and ASHP
I'm beginning to think solar thermal is something that ...
By Alex_N , 4 days ago
-
RE: Commencing on an ASHP Installation Process
I received the BUS Grant permission email yesterday eve...
By Sheriff Fatman , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
510kWh of solar PV from my 4kW Hyundai panels and SMA S...
By JulianC , 6 days ago
-
RE: Is my Samsung heat pump working too well?
Thats in itself is interesting. I have a Vaillant heat...
By JamesPa , 6 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@transparent Not a swell season then ☹️
By Toodles , 6 days ago
-
RE: Air Changes per Hour - ACH and the MCS requirement
update - my old installer insisted on a heat loss of 11...
By MatWin , 1 week ago
-
I agree it's not very helpful. Generally, the max heat ...
By Old_Scientist , 1 week ago
-
RE: Why Your MCS-Certified Installer Might Not Be As Competent As You Think
Hive and most other smart thermostats don't play well w...
By JamesPa , 1 week ago
-
RE: Enabling WiFi: Samsung ASHP on Smart Things App
Thanks for the input. I've been running various experim...
By Grahamh-uk , 1 week ago