Newbie: utterly confused with my Mitsubishi Zubadan air source heat pump running on 55C set flow temperature

94 Posts
9 Users
36 Reactions
971 Views
(@sandman1600)
Trusted Member Member
158 kWhs
Joined: 3 days ago
Posts: 39
Topic starter  

Posted by: @robs
 

The specs of the 14kW Mitsubishi give a minimum output at 7C OAT of 4.2kW with a 35C flow temp, 3.7kW with a 40C flow temp, and 3.2kW with 45C flow. At higher OATs it's even worse, for example 6.2kW minimum at 12C OAT and 35C flow temp.

Thanks for that. Where did you find this? I've been trying to get the same info for the 8.5 R32 EcoDan to compare but Google hasn't been any help.

 


   
ReplyQuote
(@sandman1600)
Trusted Member Member
158 kWhs
Joined: 3 days ago
Posts: 39
Topic starter  

Posted by: @jamespa

Further to the above here is a template for what you might say if you wish to decline sign off.  ? indicates info from melcloud or elsewhere, or references to legislation ( I am happy to find these tomorrow).

 

That is brilliant! Thanks. I've got to dash out but I'll have a proper read through when I get back later but it looks great. Thanks again!

 


   
ReplyQuote
(@davidnolan22)
Estimable Member Member
320 kWhs
Joined: 2 months ago
Posts: 56
 

@sandman1600 

 

Lots of graphs there.  In the middle of the night its close to 0 degrees and it starts to run more stable, still the odd wobble but no great concerns.  Your DTs are 3, you flow rate is 16-17l.  assuming you have glycol, that means your KW its needing is about 3.5 to 4.  Does that keep you warm?  If so you are 3-4 degrees above design temp (if its -3, depends where you live) and your needing not much power to keep the house warm. But this is NOT a heat loss estimate.  

In the day its much warmer and it cycles a lot, but its fairly normal to cycle 1-2 an hour in warm weather and for it to turn off for a bit.

James giving really good advice. My point on the flow to the unit is that the minimum for the the 14kw is 18l/min.  I can't imagine it's happy with that little flow and how that affects the heat exchange, but I'm no expert in that, and don't turn the flow up through the unit as you'll get a bigger problem. But its running just below the minimum flow and still has narrow DTs, to me it means that its struggling to operate to such a small load.

My 11.2 has 28 l/m, runs DTs normal 4-5, but when its cold and I really need it, they will stretch to 7 or even 8.  

One thing that might help some of the wobbles is to turn on the quiet mode all the time and set it to one bar. That restricts to compressor to 50% max output and might help some on the wobbles, but won't change the cycling much. 

 

 


   
ReplyQuote
 RobS
(@robs)
Trusted Member Member
777 kWhs
Joined: 5 months ago
Posts: 35
 

Posted by: @sandman1600

Thanks for that. Where did you find this? I've been trying to get the same info for the 8.5 R32 EcoDan to compare but Google hasn't been any help.

It's from: https://library.mitsubishielectric.co.uk/pdf/book/Ecodan_ATW_Databook_Vol.6_.0_.pdf#page-1

Suggest you use the menu (top right) and download the PDF - it's a big document as it has all of Mitsubishi's air to water heat pumps. The image I posted was from page 92.

The 8.5kW can modulate down more than the 14kW, 3.2kW vs 4.2kW at 7C OAT and 35C flow. But the newer 8kW R290 heat pumps (PUZ-WZ80VAA) are even better and can modulate down to 1.8kW at 7C and 35C. 

 


   
ReplyQuote
(@davidnolan22)
Estimable Member Member
320 kWhs
Joined: 2 months ago
Posts: 56
 

@robs 

And its also go an external sensor that you can place away from the back of the machine that makes weather comp much better. 


   
ReplyQuote
(@sandman1600)
Trusted Member Member
158 kWhs
Joined: 3 days ago
Posts: 39
Topic starter  

@davidnolan22

Thanks and apologies for the graph dump. I was hoping a bigger picture might be useful. Temperature overnight was around 0, maybe -1 degree. The temperatures we're getting are fine. Maybe a little cooler than I'd like in some rooms but nothing dramatic and definitely not cold.

So 3 is a bad DT?  

I noticed the flow rate had increased to 18l occasionally but is also currently showing as zero for long periods. Is this when it's off? I've attached the updated images below.

So if we're only using 3.5 to 4 kWh, then an even smaller pump would work. Would an 8.5 model be worth considering?

IMG 4392
IMG 4394
IMG 4395
IMG 4393
IMG 4396

 

 


   
ReplyQuote



(@sandman1600)
Trusted Member Member
158 kWhs
Joined: 3 days ago
Posts: 39
Topic starter  

@robs Thats's great thanks. Has a lot of useful info.

Trying to figure out the best option if we get an opportunity to swap it. The new 8kW model sounds interesting. We were warned off R290 coolant for some reason... fire/insurance risk maybe? I can't remember why.


   
ReplyQuote
(@davidnolan22)
Estimable Member Member
320 kWhs
Joined: 2 months ago
Posts: 56
 

@sandman1600 

it’s showing 0 when it’s off.

there is nothing wrong with a DT of 3, but it’s about energy. The energy to the house is carried in the water and transmitted to the house via your emitters (UFh). If it comes into the house at 38 and leaves at 35, this is a DT of 3, and that tells you the energy transmitted. The heat pump then tops that 35 back to 38 via the heat exchange in the unit and the cycle continues.

nothing wrong with DT3, but tells me it’s not working very hard. If you have a flow of 40 litres a minute coming into the house (which is more typical if you think the heat loss is actually 14) then a DT of 3 would be 8 to 8.5kw depending on how much glycol in your system. But you have a flow of 18, which is the minimum the 14 unit can run, and that is 3.5 to 4kw of heat with DT of 3.

so, there is plenty of ways of getting 3 to 4 kw of heat onto a house, but the question for your installer might be: have they found the best one.

The mitshi machine I think is generaly a fixed flow rate pump on the primary circuit. So your installer has set that flow rate. That indicates they may know that you won’t need the full power of the 14 often or at all.

The other thing to check is the house flows. Are to running it fully open, and plenty of flows going through each loop on the manifold?  Sometimes people run zonne and close loops, and this can further restrict the available surface area to get rid of the heat

normally it’s fine to close the odd loop a bit, but I think your total system volume and emitter power might be on the low side for your unit. 

I would also like to add: I am NOT a heating engineer and have never installed a heat pump. I have one that has been a tricky little bugger, but please take my advice in the knowledge of that.  Advice from James and others over various web sites has been very helpful. 

This post was modified 47 minutes ago by davidnolan22
This post was modified 35 minutes ago by davidnolan22

   
ReplyQuote
(@davidnolan22)
Estimable Member Member
320 kWhs
Joined: 2 months ago
Posts: 56
 

@sandman1600 

it’s a bit of propane, I really would lose sleep over it 


   
👍
1
ReplyQuote
(@sandman1600)
Trusted Member Member
158 kWhs
Joined: 3 days ago
Posts: 39
Topic starter  

@davidnolan22 Thanks yet again. I appreciate that its not your profession but its a lot more than my knowledge so its helpful to figure out what's going on.

Thanks to @jamespa I've been looking at the various bits of legislation and even their documentation and RECC that details what to do if things aren't performing as described, so I'm really hoping we can agree an exchange of the heat pump for something more suitable.

I'm pretty sure the flows are all fully open but I will double check.  

 

 

 

 


   
ReplyQuote
Page 8 / 8
Share:

Join Us!

Heat Pump Dramas?

Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.

Pre-Installation Planning
Post-Installation Troubleshooting
Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)

👉 Book a one-to-one consultation now.

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security