@davidnolan22 Thanks. It looks like this is some kind of Mitsubishi "collab" so I think arguing that this is wrong be tough. 

We'd never have known any better if we'd have specced this ourselves so I think it's something we might need to just live with.

So should this help to minimise short cycling too? I'm just trying to anticipate the installers response.

The flow rate still needs addressing by them.

 

 


   
ReplyQuote
(@sandman1600)
Estimable Member Member
208 kWhs
Joined: 6 days ago
Posts: 52
Topic starter  

@jamespa Thanks for the information. I will ask for the justification but I'm guessing it's a kind of "easy" package along with the heat pump. Saves them having to spec too much for each individual install.


   
ReplyQuote
(@davidnolan22)
Estimable Member Member
421 kWhs
Joined: 2 months ago
Posts: 76
 

@sandman1600 

yeah, they'll just turn the pump speed up. might not help you as much as you think. you need someone to measure what's happening across both manifolds to see what's happening ton the secondary side. and you might get it working OK.  But, you'll keep running up against the fact is probably oversized by some way and them swapping units will cost 4-5k.  so I imagine this may be a sticking point. I've never heard of 14kw pump in a 130m2 house before. but I'm no expert. 


   
ReplyQuote
(@jamespa)
Famed Member Moderator
11140 kWhs
Veteran
Joined: 2 years ago
Posts: 2121
 

Posted by: @sandman1600

So should this help to minimise short cycling too? I'm just trying to anticipate the installers response

Not necessarily, wrongly set up it will make cycling worse (sorry, comment refers to buffer not turning up pump speed)

The solution is to replumb as a 2 port volumiser and delete the secondary pumps.  I doubt they will do that but it's worth a try. 

Heating industry has form when it comes to setting up heating sub-optimally.  Almost all condensing boilers installed since they became mandatory in 2005 are installed so they don't condense, negating the benefits of condensing boilers and costing us all 10% on our gas bills.  Why?-to reduce call outs.

I reckon that if the buffer and size were fixed, you have a very good chance of achieving the performance quoted in the proposal.  Unless they do that you won't.  The buffer is probably the more important, it's labour only no parts to change this so no material cost to the installers.  With a handful of shut off valves it's even possible to do it reversibly so it can be reverted in a few minutes.

 

Posted by: @sandman1600

I will ask for the justification but I'm guessing it's a kind of "easy" package along with the heat pump. Saves them having to spec too much for each individual install.

Yes, it means they can ignore what's already there.  Although really this doesn't provide much advantage in most real cases.

This post was modified 17 hours ago 4 times by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
Page 12 / 12
Share:

Join Us!

Heat Pump Dramas?

Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.

Pre-Installation Planning
Post-Installation Troubleshooting
Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)

👉 Book a one-to-one consultation now.

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security