My Mitsubishi ASHP has used 1078kWh from 25 November to 31 December – Help please
Posted by: @harriupAt the bottom of page 6 it states the water flow rate range is 10.0 to 24.8 l/m. Similar to mine, though I have also seen the tank installation manual be a bit more specific that the flow rate should be 24l/m. Not sure what to make of that difference. There is discussion in other threads about altering the flow rate to manage the difference between flow and return temperatures to 5°C, but if the manifold temps of 28 and 21 are typical then you have a slightly too large difference, which is to be expected if the flow rate is lower than it is meant to be.
Hi @Harriup
i thought I ought to add some comments on this for Sarah to consider.
Theres a good reason why there is a flow rate range quoted, and probably other reasons too.
It was generally believed in an earlier thread (Keystone COP) that Ecodan does not have an internal pump to regulate deltaT so there are 2 things that can control it. 1. Adjusting the flow rate via the circulation pump of the primary flow and primary return and 2. The internal modulating electronics which cannot regulate the circulating pump. In other words the ecodan operates at a constant flow rate depending on the chosen set pump speed.
A flow rate must therefore be measured on the return primary pipe since that is precisely en-route back to the heat pump and will give a near accurate measurement of flow through the heat exchanger. (I would say it’s essential to check this before any adjustment of flow rate)
another thing to point out is that a 28 to 21 differential is only 7c which is quite common when the hp is still settling down. I’ve noticed it fluctuates all the time between 3c and 8c and when it starts up it can be more.
So a flow rate of 13LPM is within the acceptable band of the ecodan 8.5 provided it is being measured in the correct place in the circuit. But if the temperature difference never settles close to 5c then a slightly faster pump speed will lower the temperature difference. However there are other issues such as balancing flow rates between the primary loop and other heating circuits so this kind of adjustment really needs to be done by a professional.
Hope this helps
@sunandair hi - yes that does help and again makes sense that it's set by the gauge on the pump itself - i.e. that is the maximum it will flow. I've had a manic week this week - but I need to look at the manifold on a regular basis for the living area to see what the return is. The thermostat is set to 18 for the living area - but rarely gets to that, unless there is solar gain - for the past two days it is still 17 degrees at 18:00 - when it was 16 degrees at 09:00. In all honesty this could be what I have to live with and it doesn't feel cold. The other 2 zones always get up to their set temp - although their set temps are 16 (bathroom area) and 17(bedroom area). Everything generally is SO MUCH BETTER since I first found this forum 🙂
- 26 Forums
- 2,227 Topics
- 49.5 K Posts
- 177 Online
- 5,892 Members
Join Us!
Podcast Picks
Latest Posts
-
It’s my sole reason to always deter homeowners from goi...
By Mars , 1 hour ago
-
RE: New Fogstar 15.5kWh upright solution
😉 😉 Some folks get spare BMSs.. &...
By Batpred , 1 hour ago
-
Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
I ended up with a Solis S6-EH1P8K-L-PLUS (8 kW) hybrid ...
By Batpred , 1 hour ago
-
Crazy if that is the case. It will surely be the norm ...
By JamesPa , 2 hours ago
-
RE: Options on flushing my system
@grantmethestrength with your pragmatic approach and &#...
By SUNandAIR , 3 hours ago
-
RE: Samsung Heat Pump – Can't Activate TW2 Pipe Sensor (for Delta T Control)
@batpred For the moment I'm sticking with what I have, ...
By bubuontheweb , 5 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@jamespa ive found out today the Thermix plinth heaters...
By AdamK , 5 hours ago
-
RE: Electricity price predictions
Nice to be back on track! If we all had the interest, s...
By Batpred , 5 hours ago
-
RE: Say hello and introduce yourself
I think this is where we may differ. Nothing makes sen...
By JamesPa , 5 hours ago
-
RE: Daikin Octopus installation update - I saw my first defrost. 😍😂
Enable installer mode - 5678 Enter the Space Heating/...
By RadWhisperer , 6 hours ago
-
Is your installer MCS certified? If so, they should reg...
By Old_Scientist , 6 hours ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
@hcas So the answer from Mitsu was: To Confirm you ca...
By bontwoody , 8 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Grant Aerona 3 10 HPID10R32
By MDG , 9 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
I don't know! The Midea manuals and what actually happe...
By cathodeRay , 10 hours ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
If you’re interested in finding out which of your neigh...
By AgentGeorge , 11 hours ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
It is a crazy situation. It also seems not enough 400kv...
By Batpred , 13 hours ago
-
RE: Rate the quality of your heat pump design and installation
More like Octopus wanted to fit a Cosy 6 at the end of ...
By RadWhisperer , 15 hours ago
-
RE: How good is the app support for your heat pump?
Yes. Personally I would only use a heating control app ...
By Batpred , 1 day ago