My Mitsubishi ASHP has used 1078kWh from 25 November to 31 December – Help please
Posted by: @harriupAt the bottom of page 6 it states the water flow rate range is 10.0 to 24.8 l/m. Similar to mine, though I have also seen the tank installation manual be a bit more specific that the flow rate should be 24l/m. Not sure what to make of that difference. There is discussion in other threads about altering the flow rate to manage the difference between flow and return temperatures to 5°C, but if the manifold temps of 28 and 21 are typical then you have a slightly too large difference, which is to be expected if the flow rate is lower than it is meant to be.
Hi @Harriup
i thought I ought to add some comments on this for Sarah to consider.
Theres a good reason why there is a flow rate range quoted, and probably other reasons too.
It was generally believed in an earlier thread (Keystone COP) that Ecodan does not have an internal pump to regulate deltaT so there are 2 things that can control it. 1. Adjusting the flow rate via the circulation pump of the primary flow and primary return and 2. The internal modulating electronics which cannot regulate the circulating pump. In other words the ecodan operates at a constant flow rate depending on the chosen set pump speed.
A flow rate must therefore be measured on the return primary pipe since that is precisely en-route back to the heat pump and will give a near accurate measurement of flow through the heat exchanger. (I would say it’s essential to check this before any adjustment of flow rate)
another thing to point out is that a 28 to 21 differential is only 7c which is quite common when the hp is still settling down. I’ve noticed it fluctuates all the time between 3c and 8c and when it starts up it can be more.
So a flow rate of 13LPM is within the acceptable band of the ecodan 8.5 provided it is being measured in the correct place in the circuit. But if the temperature difference never settles close to 5c then a slightly faster pump speed will lower the temperature difference. However there are other issues such as balancing flow rates between the primary loop and other heating circuits so this kind of adjustment really needs to be done by a professional.
Hope this helps
@sunandair hi - yes that does help and again makes sense that it's set by the gauge on the pump itself - i.e. that is the maximum it will flow. I've had a manic week this week - but I need to look at the manifold on a regular basis for the living area to see what the return is. The thermostat is set to 18 for the living area - but rarely gets to that, unless there is solar gain - for the past two days it is still 17 degrees at 18:00 - when it was 16 degrees at 09:00. In all honesty this could be what I have to live with and it doesn't feel cold. The other 2 zones always get up to their set temp - although their set temps are 16 (bathroom area) and 17(bedroom area). Everything generally is SO MUCH BETTER since I first found this forum 🙂
- 26 Forums
- 2,262 Topics
- 50.5 K Posts
- 658 Online
- 5,922 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Oil Boiler & Heat Pump Hybrid System
@paultheheating, where in the country are you?
By Mars , 1 hour ago
-
RE: British Gas Heat Pump Installation Complaint
@bgno, the other consideration for legionella cycles ar...
By Mars , 1 hour ago
-
RE: Help me keep the faith with my air source heat pump installation
@agentgeorge Which you then took round to your local po...
By Toodles , 4 hours ago
-
RE: Electricity price predictions
Remember that almost all submissions to Government Publ...
By Transparent , 4 hours ago
-
@old_scientist I dont monitor the tank temperature but ...
By bontwoody , 6 hours ago
-
RE: Say hello and introduce yourself
Hello @paultheheating - I'm a rural Moderator! What's...
By Transparent , 6 hours ago
-
RE: What valves to replace radbots?
Yes. Radbots just replace TRV heads. TRV heads push t...
By JamesPa , 9 hours ago
-
RE: Who has a V2G EV installation
Im looking at Anderson or Simpson and Partners, somethi...
By AgentGeorge , 10 hours ago
-
RE: When will fusion be producing energy?
I am thinking of the case where AI was able to distingu...
By Batpred , 20 hours ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
@majordennisbloodnok Thanks for the welcome and yes I...
By Mark Nelson , 1 day ago
-
RE: When to use Octopus Intelligent Go tariff with my heat pump and battery
I’ve got 5.4kW array, 9.6kWh battery, 5kW heat pump, EV...
By Gruff2001 , 1 day ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
Very definitely. I think the market has changed a bit...
By JamesPa , 1 day ago
-
RE: Buying large amp bidirectional RCD and RCBO
The following diagram is taken from the Meter Operator'...
By Transparent , 1 day ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@allyfish It was going so well with month after month s...
By Toodles , 2 days ago
-
RE: UFH downstairs and radiators upstairs balancing question
Have you tried turning up the stat and turning down the...
By JamesPa , 2 days ago
-
-
RE: Mediation with RECC, what's your experience?
Welcome to the forums @treewizard and sorry to hear abo...
By Mars , 2 days ago
-
RE: New build installation query
That accounts for why you start with an overly-high DHW...
By Transparent , 2 days ago
-
RE: Daikin Altherma 3 / HomeAssistant
I would have thought that (instantaneous) power is a fa...
By JamesPa , 2 days ago