My Mitsubishi ASHP has used 1078kWh from 25 November to 31 December – Help please
Posted by: @harriupAt the bottom of page 6 it states the water flow rate range is 10.0 to 24.8 l/m. Similar to mine, though I have also seen the tank installation manual be a bit more specific that the flow rate should be 24l/m. Not sure what to make of that difference. There is discussion in other threads about altering the flow rate to manage the difference between flow and return temperatures to 5°C, but if the manifold temps of 28 and 21 are typical then you have a slightly too large difference, which is to be expected if the flow rate is lower than it is meant to be.
Hi @Harriup
i thought I ought to add some comments on this for Sarah to consider.
Theres a good reason why there is a flow rate range quoted, and probably other reasons too.
It was generally believed in an earlier thread (Keystone COP) that Ecodan does not have an internal pump to regulate deltaT so there are 2 things that can control it. 1. Adjusting the flow rate via the circulation pump of the primary flow and primary return and 2. The internal modulating electronics which cannot regulate the circulating pump. In other words the ecodan operates at a constant flow rate depending on the chosen set pump speed.
A flow rate must therefore be measured on the return primary pipe since that is precisely en-route back to the heat pump and will give a near accurate measurement of flow through the heat exchanger. (I would say it’s essential to check this before any adjustment of flow rate)
another thing to point out is that a 28 to 21 differential is only 7c which is quite common when the hp is still settling down. I’ve noticed it fluctuates all the time between 3c and 8c and when it starts up it can be more.
So a flow rate of 13LPM is within the acceptable band of the ecodan 8.5 provided it is being measured in the correct place in the circuit. But if the temperature difference never settles close to 5c then a slightly faster pump speed will lower the temperature difference. However there are other issues such as balancing flow rates between the primary loop and other heating circuits so this kind of adjustment really needs to be done by a professional.
Hope this helps
@sunandair hi - yes that does help and again makes sense that it's set by the gauge on the pump itself - i.e. that is the maximum it will flow. I've had a manic week this week - but I need to look at the manifold on a regular basis for the living area to see what the return is. The thermostat is set to 18 for the living area - but rarely gets to that, unless there is solar gain - for the past two days it is still 17 degrees at 18:00 - when it was 16 degrees at 09:00. In all honesty this could be what I have to live with and it doesn't feel cold. The other 2 zones always get up to their set temp - although their set temps are 16 (bathroom area) and 17(bedroom area). Everything generally is SO MUCH BETTER since I first found this forum 🙂
- 26 Forums
- 2,114 Topics
- 46.4 K Posts
- 86 Online
- 3,410 Members
Join Us!
Latest Posts
-
@eliuccio good to hear you’re happy with the install. A...
By Mars , 55 minutes ago
-
RE: No-code, plug-and-play monitoring for your heat pump
The issue with the Grant is that you have to wire direc...
By Grantmethestrength , 17 hours ago
-
RE: Is this just haze or something more?
I am not a scientist nor a meteorologist and I know the...
By Toodles , 17 hours ago
-
RE: Benefits of an extra horizontal loop for GSHP
It will improve performance, but by how much depends on...
By Brendon Uys , 21 hours ago
-
RE: The good, the bad and the not that great – my heat pump installation
Said I would pop back with a update. Only Mr Jesus h...
By Burtis , 1 day ago
-
RE: Buffers, hot water and cooling
Thats presumably heat pump DT, what about radiator DT a...
By JamesPa , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
@chandykris Exactly the same here. We now have 13.5kWh ...
By Old_Scientist , 2 days ago
-
Compressor and Evaporator Stratification
I have had a few issues with my Hitachi spilt heatpump ...
By trebor12345 , 2 days ago
-
RE: Wood burner with ASHP - direct air?
This depends on the size of your wood burner and size/t...
By Lucia , 3 days ago
-
RE: Difficult positioning of air source heat pump
@rikiarn It's a not a buffer it's a volumiser which is ...
By Lucia , 3 days ago
-
RE: Is your heat pump insured?
To make things clear, lots of insurance companies cover...
By Lucia , 3 days ago
-
RE: Boxt Heat Pump Installation Experience
@adrian any updates since installation? How is it perfo...
By Ashfp , 3 days ago
-
RE: Say hello and introduce yourself
Hi @seatonian - Yes, I know Seaton, and I have the Nat...
By Transparent , 4 days ago
-
@seatonian got your email. Will connect you with a reco...
By Mars , 4 days ago
-
@downfield and @toddles, this isn’t in the settings cur...
By Mars , 6 days ago
-
RE: Homely launched for Grant Aerona ASHP control
I haven't bought the Aerona Smart Controller (£700!) bu...
By Prunus , 7 days ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
For the record, Grant supply ethylene glycol for their ...
By Prunus , 7 days ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
@skyefarmer amazing. Well done!
By Mars , 7 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Ebac 5kw - Monobloc R32. Developed and made in UK - Mit...
By marcinwloch69@gmail.com , 1 week ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Just another thought - it might be worth thinking about...
By JamesPa , 1 week ago