Sorry I have no idea what you are talking about. Above I reproduce 3 graphs you posted purporting to show instantaneous power, flow rate and deltaT. At any point in time these should be consistent.
Looking at the peaks, which must be at the same time given that flow rate is constant, deltaT peaks around 3.5C, flow rate is 7l/min and 'power' peaks at 200W
Yet 7l/min at 3.5C is 7/60*4200*3.5 =1715W
If I look at midpoints they are 2C. and 7l/s, about 900W not 100W.
Your power graphs (or flow or delta T graphs) are wrong. I don't know where they are coming from but if you are averaging them (as you suggest above) then thats incorrect, its an instantaneous measurement.
So we dont lose sight of it can I also remind you of what @derek-m said on the previous page, which I endorse:
"Could you please confirm the model of Sharky that you have installed.
I'm afraid that I am becoming confused by the multitude of graphs (both requested and not requested) that you keep posting, since it is not clear which sensor is being monitored. As requested previously could you please add the sensor number to each graph.
Have you made any progress collecting data for IAT and OAT? Little progress can be made until you provide this requested data.
Could you please provide graphs for sensor 1, sensor 3 and sensor 7, with adequate labeling, for the previous 24 hour period.Please don't add any further graphs or information."
This post was modified 6 months ago 5 times by JamesPa
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Manufactured and built in Germany with the CE Test stamp and Calibration Parameters printed on the outer case.
As the French Samsung Engineer said " only the Germans Really know how the Samsung Heat Pump works".
Flow Rates:
My Samsung Pulse Width Output from the MIM Control board Does NOT Work with or without the B1/B6 continuous motor or Relay switched B8/B7 Power supply or with the Field bits 4050 to 4061 PWM Controls.
Secondary PWM Motor Control:
My Samsung has no provision for any input to the Secondary PWM Motor control.
The PWM input was , initially left exposed and unused.
I , now provide a PWM Signal Generated by an Arduino, to supply the missing signal controlling the secondary Flow rate .
Arduino Flow Control:
With no functioning PWM Motor control from the Samsung MIM board I currently use a pair of Arduino PWM Ports to vary and control the DIFFERING Flow rates on both the Primary and Secondary Water loops.
Both water flow rates are currently constant as can be seen from the flow rate graphs.
The Arduino was originally that used to measure the room , and outside Temperature but later used , successfully , to control the Water flow rates on BOTH Water circuits.
Delta_T on BOTH Primary and Secondary Water circuits:
Advised by yourself, @derek-m, I used an Arduino to generate and control the Delta_T on BOTH Primary and Secondary Water circuits.
Delta_T was , successfully increased by setting and adjusting the flow rates controlled by the variable Pulse width Modulation drive.
Please read my response above regarding the power/flow/deltaT measured by the sharky. The graphs you present, which purport to be instantaneous power, flow and deltaT, are inconsistent, which means your energy and COP measurements are also likely incorrect.
Is one of the three figures you plot calculated by you if so which and how or is the sharky faulty, misconfigured or being mis-read
So we don't lose sight of it can I also remind you of what@derek-msaid on the previous page, which I endorse:
"Could you please confirm the model of Sharky that you have installed (done)
I'm afraid that I am becoming confused by the multitude of graphs (both requested and not requested) that you keep posting, since it is not clear which sensor is being monitored. As requested previously could you please add the sensor number to each graph.
Have you made any progress collecting data for IAT and OAT? Little progress can be made until you provide this requested data.
Could you please provide graphs for sensor 1, sensor 3 and sensor 7, with adequate labeling, for the previous 24 hour period.Please don't add any further graphs or information."
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Thank for supplying the model number for the energy meter.
Could you please explain why you included the additional information that was not requested, but failed to provide the three graphs that were requested?
There are too many anomalies here so far as I can see, are you sure you have the sensors correctly labelled?
eg Sensor 3 goes down whilst sensor 1 goes up during the period, yet these should follow each other
The value of sensor 9 is higher than sensor 1, how can that happen?
According to your diagram sensor 7 and sensor 9 are on the same side of the radiators, yet you describe this as 'radiator delta_T' and there is a 2C difference whereas there should be almost none.
I'm sorry but I don't see how we can currently trust the measurements. We know that the power measurement is incorrect, it appears that this may be true of some of the temperature measurements also.
Please supply the sensor measurements that @derek-m has requested. Please spend the time to ensure that they are labelled/measured correctly and that your diagram is correct rather than on producing additional graphs.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Your idea of increasing the Water Law defining coordinates [+15:25] to [+20:25] has revealed a great deal about the Heat Pump performance.
For the first , and only time the Room Temperature has soared to 24.8 C this morning. Currently a roasting 25 C with the Radiators just producing , for the first time a perceptible heat.
Despite your reservations , all of the sensors , including the Sharky , now confirm the situation as of this morning 16th Sept 24:
Sorry , but I will have to use the sensor information as relayed to my P.C.
1) Radiator Water Temperatures:
A) Outgoing Radiator water Temperature:
The Outgoing Radiator Water Temperature rises to a saturation point at 0400 when the Run Time equals the Cycle time!
B) Radiator Difference Temperature , Delta_T :
Again , note the sudden stop in cycling at 0400 in the morning when Run Time =Cycle Time.
2) Power
A) The Power as measured by the Sharky is :
Again , notice the Saturation , when the Run Time = Cycle Time.
Note also the Power has a peak value of ~200 Watts.
Im glad you are warm however the water power as you present it from the sharky (and thus your claimed COP and real COP) is nonsense, as explained several posts above. The 'deeper malaise' you speak of is based on this, and since the basis is nonsense, so is the conclusion.
Currently we are making very little real progress, other than showing that the laws of thermodynamics apply (which was never in doubt). Please concentrate on what has been requested.
I presume (but please confirm) you have set the water law offset at 0. If not please do so and leave for a day before changing the water law coordinates again.
Please post the sensor readings requested by @derek-m. Until you do this I cannot help further, and if you continue drawing incorrect conclusions from flawed data, you will end up back where you were 75 pages ago.
This post was modified 6 months ago 2 times by JamesPa
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Here are the readings from the Thermocouples as requested.
1) Sen1, Thermocouple .
Note the Saturation , Run Time = Cycle Time
2) Delta_ T , Sen1-Sen2 , Thermocouples
Note , again , the Cycle stopping at saturation. Even bathed in Thermocouple noise the Saturation condition when Run Time =Cycle Time is clearly shown.
3) HEX input Sen3 , DS18B20 Sensor
Again, note the behaviour at Saturation .
4) HEX Delta_ T Sen3-Sen4, DS18B20 Sensors
Again, note the Saturation display
5) Radiator out , Sen7 , Thermocouple Sensor
Again note the performance at Saturation when Run Time = Cycle Time
I have again reduced the /water Law Defining coordinates to [+17:25] .
Currently , my room Temperature has reached 24.5 C , too hot even for me.
But , the System does heat, albeit with a maximum Consumed power of 200 Watts and an output Water power of 150 Watts.