Posted by: @iantelescopeCheaper, and quicker to Replace the entire system than to continuously repair my current system?
Each month , new evidence appears about the poor performance of this heat pump.
It's not the heat pump, it's the plumbing of the system that is poor.
Assuming a 5kW heat pump is sufficient for your house, you appear to have all the components needed to make a working system.
Unfortunately your installer appears to be a cowboy and has plumbed them together in the wrong order and omitted several key stages. Regrettably the plumbing industry, indeed the whole construction industry, has quite a few cowboys as well as many good people. I'm sorry you have encountered a cowboy. It happened to me with a flat roof, which resulted in a boxing day flood and a large unexpected expense without any practical redress.
Ultimately only you can decide whether to fix it up using what you have, or replace entirely. The people on this forum can advise you how to fix it up, but whether you choose to do so is up to you
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Hi James,
Last straw
With "an Annual Service" now demanded, but unobtainable from both Samsung and Telford "to maintain my guarantee", I have lost confidence in either my "installer" or the MCS,NIC.
If my Heat Pump were, as promised last year , to be taken over by an NIC appointed "installer" I would be more confident. Maybe!
Many thanks
ian
My previous post was to highlight how I think that your system should be plumbed for correct operation. You therefore have various options-
a) You can try to convince your installer to follow the Samsung design and position the Volumiser correctly in the heat pump return pipe.
b) If your installer is reluctant you could try to get NIC to convince your installer to reposition the Volumiser.
c) You could ask your installer to provide details of his indemnity insurer and see if you can make a claim for the corrective work to be carried out by a competent installer, under your incompetent installer's insurance.
d) I would not at this stage recommend employing your own plumber to carry out the proposed corrections since it may cause problems in getting whatever grants are available.
Whilst I prefer to work through problems in a logical and systematic manner, you could, in the meantime, take Jame's advice and isolate the Volumiser from the system, assuming that there is an isolation valve in the pipework to or from the Volumiser. If there are valves on both the inlet and outlet then only close one of them.
I was going to leave the next stage until the start of the heating system, but it should be possible to carryout a number of test and adjustments, though you may have to open some windows to create more load on the system. Ensure that all the radiators have been correctly bled and that the system water pressure is correct.
If the Volumiser can be isolated then the next stage would be to fully open all the TRV's except for possibly one's located in bedrooms. Also turn any thermostats that may be present, to a setting 1C or 2C above the desired room temperature.
Adjust the 'Water Law' settings to say 25C Leaving Water Temperature (LWT) at an Outside Air Temperature (OAT) of 20C, and a LWT of 50C at an OAT of -5C.
Set both the primary water pump and secondary water pump to slow speed, either using the manual pump controls or using your Arduino system.
Monitor the temperatures around the system and post back the results.
assuming it's a unvented cylinder the requirement for an annual service is pretty much ubiquitous whatever the heat source. Any half decent plumber should be able to do it.Posted by: @iantelescopeHi James,
Last straw
With "an Annual Service" now demanded, but unobtainable from both Samsung and Telford "to maintain my guarantee", I have lost confidence in either my "installer" or the MCS,NIC.
If my Heat Pump were, as promised last year , to be taken over by an NIC appointed "installer" I would be more confident. Maybe!
Many thanks
ian
As to the failings of those organisations that justify their existence largely on the basis of consumer protection, no comment!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Hi James,
Is "pipe Flushing under BS 7593:2019 an Annual service?
I have , at a cost of £600 had my pipes "flushed and cleaned" by a local "Pipe flushing company".
Is "pipe Flushing an Annual service?
Outwith pipe Flushing, what is involved in the Annual service for the Tank on a Heat Pump ?
ian
Posted by: @iantelescopeHi James,
Is "pipe Flushing under BS 7593:2019 an Annual service?
I have , at a cost of £600 had my pipes "flushed and cleaned" by a local "Pipe flushing company".
Is "pipe Flushing an Annual service?
Outwith pipe Flushing, what is involved in the Annual service for the Tank on a Heat Pump ?
ian
No, pipe flushing is not part of the annual service.
So far as I know the annual uvc cylinder 'service' is just an inspection and partial test of the safety vent arrangement which it is recommended be carried out for any UVC irrespective of the heat source, by a 'competent'person'. I don't believe it's a legal requirement but others may be able to prove me wrong. This is nothing heat pump specific, those with gas boilers and a UVC, a common pairing, also are subject to the same recommendation.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Many thanks ,again, James.
Black Ink
Having discovered "black ink " with "iron particles" in one of my pipe water circuits, I, and a Flushing engineer , cleaned the pipes with F3 Fernox cleaner until the water was "clear".
How do I find the Cause of the "Black ink with metallic particles"?
Would "short cycling" "cause or increase " the black ink from excessive switching.?
ian
Posted by: @iantelescope
Many thanks ,again, James.
Black Ink
Having discovered "black ink " with "iron particles" in one of my pipe water circuits, I, and a Flushing engineer , cleaned the pipes with F3 Fernox cleaner until the water was "clear".
How do I find the Cause of the "Black ink with metallic particles"?
Would "short cycling" "cause or increase " the black ink from excessive switching.?
ian
Sorry I don't know definitively the answer to that question.
Having said that I think its much, much more likely that the 'black ink' and 'iron particles' are nothing more than the residues from radiator corrosion over the years. My heating system, currently gas fired, certainly featured both of these when I recently drained it down and removed some radiators, despite having a mag filter in circuit.
I am pretty sure both collect as sludge at the bottom of radiators and aren't flushed through in normal use thus never reach the mag filter.
If I were you I would worry about it only if it recurs quickly, otherwise just put it down to normal (albeit unwanted) behaviour for a central heating system!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @iantelescopeI have checked the flow directions through the HEX and the Heat Pump itself. Nothing wrong.
Ok that's good.
So you could:
Switch the volumiser out of circuit using the valve you mentioned earlier.
Take the heads only off about half of the trvs (the ones in the rooms you use most downstairs) to ensure that there is always sufficient system volume, or simply turn them up to max.
Tweak the WC/water law if necessary
That should give you a system that works tolerably well (and certainly much better than current) and heats your house without doing any plumbing or anything else that your installer could moan about.
This buys you time to sort the matter out properly with nic/MCS/your installer/trading standards/any other body you want to involve.
Then once you have sorted the contract side, or concluded it's not sortable, proceed logically with a rebuild (if by now it's not been done by your installer) as @derek-m suggests above
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @iantelescope
Many thanks ,again, James.
Black Ink
Having discovered "black ink " with "iron particles" in one of my pipe water circuits, I, and a Flushing engineer , cleaned the pipes with F3 Fernox cleaner until the water was "clear".
How do I find the Cause of the "Black ink with metallic particles"?
Would "short cycling" "cause or increase " the black ink from excessive switching.?
ian
I believe the major cause of magnetite (black ink) is as described below:-
Magnetite, commonly referred to as sludge, is the black substance comprised of dissolved and rusted metal from the pipework of your central heating system. It forms when air and water react with ferrous components – for instance, the water within the system reacts with the steel inside your radiators
Hi Derek ,
All of my Radiators, with ONE exception, were replaced during the installation.
Also, All of the pipes were replaced with a 22 mm Bus Backbone running the length of the house.
Finally, all of the new radiators were connected by 15mm pipes to the 22mm Bus Backbone.
So, I think that you and James are correct...............................the Black ink with the magnetic particles may be coming from the sole veteran Radiator.
However, I am also suspicious about the condition of the 50 l "Volumising tank" being covered in warnings about "annual service ".
What "Maintenance" does a 50 L Tank need?
Many thanks for your patience ............
ian
I think that you, James, is correct...............................the Black ink with the magnetic particles may be coming from the sole veteran Radiator.
The other source may be the "volumising Tank " being covered in Warnings about "Annual maintenance being required!.
What "Maintenance do you need to do on a Tank?
Your advice is spot on................
However, the NIC are saying that " my Installer should be given another chance to fix the problems."
I have strongly objected to my "installer" making matters worse.
Anti-freezing Valves?
Could I improve the performance of my Heat Pump by fitting Anti-freezing Valves to replace the Glycol .
Glycol reduces the Specific Heat of Water from 4.3 to 4.0 , a reduction of 7.5 %.
I would do the fitting myself.
Thanks for your patience....your advice is appreciated
ian
- 22 Forums
- 2,038 Topics
- 44.4 K Posts
- 29 Online
- 3,259 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Help with understanding my Mitsubishi Ecodan air source heat pump
@sunandair interesting, thank you. Is there any ...
By Patch , 2 hours ago
-
RE: Commencing on an ASHP Installation Process
11kW does sound way over in that case! As you say it w...
By JamesPa , 4 hours ago
-
RE: Installing your own ASHP - DIY
Hi @tomasmcguinness, how are you progressing with this?...
By Ashfp , 4 hours ago
-
RE: Say hello and introduce yourself
Welcome to the forum. If you are new to ASHPs I sug...
By JamesPa , 10 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@editor I have been with Havenwise for about three week...
By Broadsman , 10 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@editor guess the reason im asking is cause ive looked ...
By AdamK , 18 hours ago
-
RE: The Rise and Fall of Europe’s Most Generous Green Subsidy
This is where the cold water storage tank was situated;...
By Dwynwen , 1 day ago
-
RE: Air Source Heat Pump - Side Alley Suitability
Thats probably fair enough. The degree-days calculatio...
By JamesPa , 1 day ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
That’s interesting, but obviously concerning also…. Do ...
By SUNandAIR , 2 days ago
-
RE: In the middle of an ASHP installation - a few questions (and issues)
Thank you @robs - that very useful data. The issue wa...
By Transparent , 2 days ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Thermal Off's
@trebor12345 The Auto function is supposed to adapt au...
By Heatgeek , 3 days ago
-
RE: The Great British Heat Pump Quiz
@allyfish thanks for the feedback and glad it was fun! ...
By Mars , 3 days ago
-
RE: help sizing rads based on room by room heat loss
If its 1988W at DT 50, which is how most radiators are ...
By JamesPa , 3 days ago
-
RE: Career change – entering the world of heating and heat pumps
@editor Mars, thank you. That's along the routes I was ...
By Lakey , 3 days ago
-
@editor thanks Mars, it's a rare occasion I'm looking f...
By big_si , 4 days ago
-
RE: Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW
@ashp-bobba and @jamespa - thank you both for all your ...
By CBrenewable , 4 days ago
-
-
Win one of five "Heat Pumps 101" Courses
Heat pumps are gaining traction in the UK, but between ...
By Mars , 4 days ago
-
RE: Agile: average import cost vs other tariffs?
@toodles thanks for the analysis. I'll be really intere...
By Old_Scientist , 5 days ago