On this , and other forums I suspect that I have overdone my criticism of some of the Engineers who have appeared in my kitchen over the last two years.
All Heat Pump Engineers are not however uniformly incompetent , innumerate or illiterate. Many are trying to repair devices without experience , measuring equipment, circuit diagrams or spare parts.
Some Heat Pump engineers have said that "in their opinion , Heat Pumps are NOT THE SOLUTION to the energy crisis ................they are BUT ONE SOLUTION ."
The Next "Engineer" who appears in my kitchen , however, would be advised NOT to use You Tube as the SINGLE source for repairing my HEAT PUMP.
Warning, the next " Engineer" who, under the supervision of a You Tube video , who installs pumps or flow sensors on the wrong pipe will be promptly ejected through my front door.
Questions about Octopus?
My Energy supplier, the woeful Shell Energy, has been taken over by Octopus.
Does anyone know if Octopus any good as HEAT PUMP repairers or Installers?
Apart from my Faulty Heat Pump , my Shell supplied Smart Energy Meter has not worked for the last two years!
Again, Do Octopus have a good record with Smart Meter installations or repair?
Hi,
You seem to be in a similar frustrating situation to me.
I, like you, have been repeatedly let down by my , now former , installer , the MCS and the NIC-EIC .
Unlike you, my "installer" has now been STRUCK OFF and subjected to multiple unspecified "sanctions" by the NIC on several occasions.
With my installer STUCK OFF, Home Energy Scotland refused to repay my initial down payment of £6k covering the initial Heat Pump installation.
The HES ( rightly !!) refused repayment of the Loan and Grant given the failure of my installer to test the system and provide the warranties for the Samsung Heat Pump and two Telford cylinders.
After many months my MSP obtained a direct contact with a manager within EST Scotland, with the EST agreeing to a " DRAW DOWN " payment in late December 2023.
Draw Down payments provide the Heat Pump customer with the , otherwise substantial , upfront funds, required for the installation.
If we can establish a system of direct communication I will safely give you the names of the managerial contacts within EST.
Please send me your Heat Pump story?
I understand that Octopus want to be trendy and be ahead of the curve but there aren't many houses in the UK that will pull off this purple look.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@editor There is a solution! https://www.creative-solutions-direct.co.uk/shop/category/air-source-heat-pump-wrapping-service#:~:text=Most%20Air%20Source%20Heat%20Pumps,its%20warranty%2C%20running%20or%20efficiency.
Regards with tongue in cheek, Toodles
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@editor I found this on YouTube and it would appear the presenter has had an Octopus Energy onstallation recently and perhaps someone who uses social media (I don’t) might like to invite him to tell us how he rates his installation.
Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@toodles good suggestion. If anyone knows this chap or follows him please invite him. I’d be very curious to find out more.
On semi-related note, if anyone is on Facebook and is inclined to promote our forums to attract more users and grow our community, please feel free to do so.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
My "installer" was finally STRUCK-OFF for modifying the MCS House Energy Requirements to justify the installation of a Heat Pump they just happened to have available in their back room.
This feat of backward Engineering was accomplished by changing the Thermal conductivity of my walls .......until the total power equalled that provided by the Back room Heat Pump.
One of the installation engineers blushed , bright red, when discovered.
Adjustment of the Wall Thermal conductivity makes a mockery of the MCS House Energy requirements!.
Now entering my second year in my attempt at getting a stable and economic replacement for my Gas boiler can I vent my exasperation with the conflicting advice of Heat Pump experts.
I have a system, that , according to many of the "experts" is totally unnecessary , and constitutes an act of rear end protection.
Needless to say, many other "experts", including BOTH of my system manufacturers demand a Buffer for four different reasons:
1: To dump hot water during very cold Scottish nights, thus preventing icing.
2: To help isolate the Heat pump from changes in the water flow rate in the radiator circuit.
3: To reduce , or eliminate "Short Cycling" when the water temperature is reducing.
4: To reduce , or eliminate "Short Cycling " in Spring and Autumn when the Heat Pump is operating at it's lowest controlled power , usually one third of the system maximum power.
Similar arguments are put forward , and virulently opposed by other "experts" for my Heat Exchanger.
Both the buffer and the heat exchanger taken together loose some 22-23% in energy, so this is no academic conversation.
Buffer ....Yes or No?
Heat Exchanger........ Yes or No?
I understand the arithmetic for calculating the buffer size , but, as the MCS says, "a buffer will increase your running costs".
Hi Ian,
I understand your frustration, particularly when being provided with conflicting advice.
It is still my considered opinion that if at all possible buffer tanks should not be installed in the first place, and if one has been installed it should be re-piped to convert it into a volumiser.
Item 1. A buffer tank will not prevent icing, and unless it has a reasonably large volume will not help too much during the defrosting process.
Item 2. You actually need sufficient water flowrate through both the heat pump and the heat emitters. Having a buffer tank that is not correctly balanced can dramatically reduce overall efficiency.
Items 3 & 4. A heat pump is always going to cycle once the heating demand falls below the minimum continuous thermal energy output of the heat pump. As has been discussed previously on the forum, there are different methods of control that can be used to minimise cycling to improve overall efficiency, it is a matter of finding the method that works best for your system.
Without reading back through the various threads, where is the PHE that you mention?
Hi Derek,
Please accept my apologies , I am at my wits end with the second anniversary of my Heat Pump odyssey.
A recent visit by a pair of "engineers" from my , now former, Installer, accompanied by an " NIC Inspector" totally destroyed any confidence in both my Installer and the NIC.
The trio of "engineers" attempted to force the Water Temperature when the Water Temperature was controlled by the Samsung Weather Compensation module , aka Samsung Water Law.
The trio abandoned the attempt leaving the Heat Pump faulty and inoperative .
I repaired the heat Pump within 30 minutes of their departure.
The NIC "engineer Inspector" was upset by the Buffer tank and the Heat Exchanger saying he had no knowledge or experience of Weather compensation , Continuous Power control , Buffer Tanks or Heat Exchangers!
Despite having no knowledge or experience , the NIC "Expert Engineer" proceeded to attack me for fitting the buffer tank?
Plate Heat Exchanger, PHE
The PHE came with the Telford 200 litre tank fitted by Telford to "provide hydraulic isolation and prevent Glycol from entering the radiator circuit".
The PHE (hopefully) protected the Heat Pump when my "installer" ran the heat pump without fitting a Expansion vessel, flow rate meter or PRV, whilst attempting to run the heat pump during the first month of the installation.
I do not know what damage was done to the Heat Pump , running for a month without sufficient cooling water !!
50 litre Buffer
Telford, the tank manufacturer, said , in a telephone call that "All their Tanks should be fitted with 50 L Buffer tanks , without exception"!
Samsung -Dalliam in Wigan also recommended the installation of a Buffer tank "to prevent Ice build up on the fins of the Heat Exchanger".
My "installer" then intervened saying that "their boys are perfectly capable of installing the Buffer Tank".
My "installer", then STRUCK-OFF for the first time, went silent for two months before announcing that " a 50L tank had been found under the table of the , now former , chief maintenance "engineer".
NIC Engineer
The NIC engineer , a very nice personable character, abandoned me to a broken heat pump after the last visit.
de-icing
The de-icing routine, where the contents of the Buffer tank are dumped into the heat pump , does seem to work during the cold Scottish nights , often dumping water up to four times while consuming no electricity.
De-icing works ........but I do not know how well!
Since fitting the Buffer tank , no vast water vapour clouds have appeared .......but that could be different weather conditions.
"Short Cycling"
I can reduce, and almost eliminate, short Cycling, by increasing the Samsung water law Graph and/or increasing the setting on the Water law Thermostat but at the cost of efficiency.
Short Cycling has however contaminated the pipe water resulting in a black ink like residue , even after cleaning the pipes to BS7593:2019 at a cost of £600.
Many thanks Derek, your patience is appreciated!
Let me have a read back through your previous posts to see what suggestions I may be able to make.
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 63 Online
- 2,276 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
Whilst I agree with the final conclusion (flow side pla...
By JamesPa , 3 minutes ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
@bami I think if the heat loss documentation matches a ...
By bontwoody , 5 minutes ago
-
@eliuccio Hi. Firstly, I am not associated with any co...
By Heatgeek , 8 minutes ago
-
RE: What is the best strategy for operating a very oversized heat pump?
@jamespa I'm afraid that's over my head but if anyon...
By IRMartini , 33 minutes ago
-
RE: Setback savings - fact or fiction?
And here in case any one wants it is the code I used in...
By cathodeRay , 43 minutes ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Definitely its in the 20xx FSVs. Conversely it may be...
By JamesPa , 1 hour ago
-
RE: Towel rails. An unexpected final hurdle
We have both Normal Rad for heating the room and then a...
By IRMartini , 3 hours ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 5 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 7 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 19 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 21 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 23 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 1 day ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 1 day ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 7 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 8 hours ago
-
SolarPV tables / online calculator
By MichelleC 15 hours ago
-
By Toodles 2 days ago