Posted by: @gary@leftbacks unfortunately it does look like the heat pump is just too small for your property then
Sorry Gary, it is the property that is too large for the heat pump. 😋Â
Â
Posted by: @leftbacksThanks both, I believe I have my answers and although a costly one I need to get the system redesigned, calculated and installed correctly by a reputable and knowledgeable installer.
If it was my system, I would be taking the matter up with the installer and his professional indemnity insurer, since the design and installation of the system is not fit for purpose.
Â
@derek-m This will be taken up with the building contractor as it was procured by them and we have been going through the process legally for the past 2 years of allowing the installer the opportunity to rectify but fair to say after 10 visits and points raised on this forum still haven't been picked up says it all.Â
For my sanity is there a heat pump that would actually be able to service my home?Â
My brother has a similar size home just next door but timber frame construction and near passive haus and his system is of similar size but with 2 separate 7kw heat pumps and works great.
Posted by: @leftbacks@derek-m This will be taken up with the building contractor as it was procured by them and we have been going through the process legally for the past 2 years of allowing the installer the opportunity to rectify but fair to say after 10 visits and points raised on this forum still haven't been picked up says it all.Â
For my sanity is there a heat pump that would actually be able to service my home?Â
My brother has a similar size home just next door but timber frame construction and near passive haus and his system is of similar size but with 2 separate 7kw heat pumps and works great.
You need to accurately establish the heat loss for your home, then multiply this value by 1.25 to 1.5, dependent upon the make and model of heat pump required.
Â
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 65 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@cathoderay yes there is the modbus register list at th...
By benson , 9 minutes ago
-
RE: Big Changes Coming to Our Heat Pump System
Yup Sadly consumerism, the foundation of our economy,...
By JamesPa , 15 minutes ago
-
RE: Heat Pump Damage on install - useable or dealbreaker?
@benson I imagine that this may well be a Daikin unit a...
By Toodles , 21 minutes ago
-
RE: Electricity price predictions
@diverted-energy sounds like good tariff for you. Octop...
By JulianC , 13 hours ago
-
RE: Who’s Caved and Switched the Heating On Already?
In the last week, the external temperature in south Man...
By GrahamF , 15 hours ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 16 hours ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 16 hours ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
I hear you on the locality issue @transparent, and I ag...
By Scalextrix , 18 hours ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 19 hours ago
-
RE: Midea ASHP – how to set weather compensation
@pash44pump Referring to the problem of rooms with diff...
By Tasos , 20 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
Er true, it should have read l/hr!
By JamesPa , 21 hours ago
-
@damon thanks. I will do as you suggest. Hopefully I wi...
By bontwoody , 2 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 3 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@dgclimatecontrol I attach the responses from 2 potenti...
By pash44pump , 3 days ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 4 days ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
I realise im overdue an update on my situation. first...
By Cleardene-ashp , 4 days ago
-
RE: Replacing Worcester oil boiler with an ASHP
@toodles thanks. I was told by the engineer that this h...
By JulianC , 4 days ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
A week later, I'm finally picking up this comment... ...
By Transparent , 4 days ago
-
RE: COP is not the only measure of efficiency
We keep all our TRVs fully open using the whole house a...
By Old_Scientist , 4 days ago