Mitsubishi Ecodan controller upgrade - your opinion please?
BACKGROUND
After two years of trial and error with fixed-flow and compensation curve running, I reckon we can keep the flow temperature really low most of the time, and stay warm. Something like flow-temp:
- Nighttime - off or 26degrees (even in deepest winter, having it on at all does make the bedrooms hot, and the COP is really poor so sometimes feels worth switching off till outside temp increases)
- Daytime - 30-40 degrees depending on weather, and activities in the house (cooking heats up; kids opening doors for hours on end cools down)
CURRENT CONTROLS
- I cannot for the life of me get the MelCloud app to do this (change flow temp between night/day) reliably, automatically, so essentially do it myself manually using either the app or the wired controller.
- There are four floors - each one currently has a basic dial-type thermostat - when the set temp is reached, it switches off the circuit to that floor only. They're a bit unreliable, and I've read HeatGeek etc about avoiding having cold bits within a well-insulated home (which this is - 1800s terrace with massive retrofit) - so thinking of swapping them out
PLAN FOR COMMENT
- Now I'm wondering whether to upgrade to: Mistubishi PAR-WT50R-E Remote Controller ( https://library.mitsubishielectric.co.uk/pdf/book/PAR-WT50R-E-PI-Sheet#page-1-2) - one for each floor, which according to the nice man on the helpline today offers up opportunities for auto-adaption mode: http://www.sunergy.ps/data/itemfiles/0a597ef3b3346a2451fbbda7f02ea637.pdf
THOUGHTS
- Well-insulated property that can be kept warm with flow temps of 26-35 degrees - great! Still costing a lot with electric at 38p/unit but ok
- I don't like the current set up - it's too manual
- But I'm not made of money! So no point wasting money on new hardware if it's not going to help
- I want to be able to control the flow temp at night and day separately, and not use the compensation curve which I find an odd thing (happy to be corrected)
- Maybe sticking with mitsubishi instead of going third party will help?
- Maybe this wireless thing is the way forward?
- Is auto-adaption mode going to revolutionise this thing???
The problem with homes is that many of them will insist on being different, so that a 'one size fits all' heating system is not possible.
Correct me if I am wrong, but it sounds like your heat pump is operating in weather compensation mode, but also being controlled by four thermostats. If that is the case then I don't think that your system will be operating at maximum efficiency.
In an ideal World all the thermostats would be set 1C or 2C above the desired temperature, the weather compensation would be adjusted such that the rooms are heated to the desired temperature and correct balancing of the radiators ensures that correct desired temperatures are maintained throughout your home.
Of course we don't live in an ideal World. Bedrooms can be possibly kept cooler by lowering the thermostat or using TRV's. As far as the 'kid's' problem is concerned, have you considered threatening that you will 'sell' one of them to pay the heating bill, if they do not stop leaving the doors open? Obviously don't indicate which one you would 'sell', otherwise the other's may leave the doors open deliberately. 😋
Whilst auto adaptation should control the temperature in the room within which the temperature sensor is located, it cannot control the temperature in numerous rooms all at the same time. If the selected temperature sensor is located in the living area, it will not prevent other areas of the home from getting warmer unless the cause is also affecting the living area.
Fine tuning of the weather compensation and correct balancing of the radiators is not a 5 minute job, and could take quite some time to achieve.
Very well said, especially the selling of said-child! Fully agree re difference between all of our homes - it's a challenge! Thanks for your help - here's a few further comments. Looking to learn from anyone who can help on here.
Correct me if I am wrong, but it sounds like your heat pump is operating in weather compensation mode, but also being controlled by four thermostats. If that is the case then I don't think that your system will be operating at maximum efficiency.
I have turned off the weather compensation mode and am controlling the flow temperature manually (using the app); I've also disabled the four thermostats, just leaving them open - i.e it's a fully open system with low flow temp water running round the radiators most of the time
In an ideal World all the thermostats would be set 1C or 2C above the desired temperature, the weather compensation would be adjusted such that the rooms are heated to the desired temperature and correct balancing of the radiators ensures that correct desired temperatures are maintained throughout your home.
Fully agreed - I think, the more I think about it, this is essentially what I'm trying to do in a very manual sort of a way.
Whilst auto adaptation should control the temperature in the room within which the temperature sensor is located, it cannot control the temperature in numerous rooms all at the same time. If the selected temperature sensor is located in the living area, it will not prevent other areas of the home from getting warmer unless the cause is also affecting the living area.
Can I check if I've understood this correctly - so if I went ahead with this new mitsubishi controller - there would be four thermostats, one on each of the four floors, but of course only in one room of each of the rooms on that floor - so the ideal is that the temp set on that new controller, say 19 degrees in the living room, would also apply to the next door room which may only be 18 degrees. So there's still a trial and error in finding the correct setting for that floor. BUT - this could possibly be overcome by balancing of radiators between the rooms on a specific floor given enough time and attention?
AND the second part - is that this auto-adaptation would be superior to the current on/off old fashioned thermostat that is in place? Clearly the heat pump won't supply different flow temp to each of the four floors, so I imagine this isn't the case.
Correctly adjusted weather compensation will vary the LWT automatically, rather than your present manual adjustment. Let me explain how weather compensation is designed to operate.
The laws of thermodynamics would indicate that the rate of heat energy loss from your home is primarily determined by the temperature difference between the indoor temperature and the outdoor temperature. To maintain a constant indoor temperature it is therefore necessary to replace this heat energy at the same rate as it is being lost. If the heat energy supplied is insufficient then the indoor temperature will start to fall, but as it does so the temperature difference reduces, which in turn reduces the rate at which heat energy is lost. It is all a balancing act.
Weather compensation measures the outside temperature, and using the weather compensation curve calculates the required LWT necessary to maintain the indoor temperature. The weather compensation curve needs to be adjusted to each individual home, and can take some time to achieve, which is probably why many designers and installers are not in favour of using it.
Even correctly optimised weather compensation may not keep the indoor temperature constant, because there are other factors such as solar gain, wind chill, rain effect and even 'children' that the controller cannot take into account when setting the required LWT.
Mitsubishi developed auto adaptation to help get around some of these problems, though it also has its limitations. A temperature sensor, either hard wired or wireless, is placed in the room where the temperature is to be controlled, which will also help control the temperature in the other rooms in the home.
In your situation having four remote controllers I don't think will allow you to control the individual temperature on each floor, since if my understanding is correct it will only control the temperature in the room with the designated remote controller. The master controller will only accept the temperature reading from one of the four remote controllers, though I do believe that the master controller can accept setpoint changes from each remote controller, but responds to the last instruction.
Even with a remote controller and auto adaptation it would still be necessary to balance your radiators to achieve reasonably constant temperatures throughout your home.
- 21 Forums
- 1,960 Topics
- 42.5 K Posts
- 47 Online
- 2,275 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
Volumisers in Heat Pump Systems: Does Placement Matter?
The debate over buffer tanks in heat pump systems has b...
By Mars , 8 minutes ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
@johnr An extra rad was installed in the lounge when th...
By BAMi , 10 minutes ago
-
RE: SolarPV tables / online calculator
By Gary , 42 minutes ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Yes, that sounds correct. I would say try both options...
By Old_Scientist , 10 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 11 hours ago
-
RE: Setback savings - fact or fiction?
The great thing about science is that it doesn't care o...
By JamesPa , 12 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 14 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 15 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 18 hours ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 19 hours ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 20 hours ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 23 hours ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 24 hours ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
-
RE: Towel rails. An unexpected final hurdle
@jamespa Beware; the use of the term ‘WC’ might lead to...
By Toodles , 2 days ago
-
RE: Visit a Heat Pump sessions.
Congratulations @toodles, that's a fantastic result. We...
By Old_Scientist , 2 days ago
-
RE: Baxi Air Source Heat Pump tips and tricks please
@cathyem1 - thanks for the update. Let us know how it g...
By cathodeRay , 2 days ago
-
RE: Low COP and unevenly heated rooms with 12kW Samsung AE120MXTPEH / AE260TNWTEH
@editor But do you wear your peaked cap the right way r...
By Toodles , 2 days ago
Latest Topics
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 8 minutes ago
-
SolarPV tables / online calculator
By MichelleC 7 hours ago
-
Samsung Gen 7 R290 12kW is not behaving how I expected
By Joshua 19 hours ago
-
Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
By BAMi 21 hours ago
-
By Toodles 2 days ago
-
Solid manhole cover within r290 exclusion zone
By dbrb2 2 days ago
-
Towel rails. An unexpected final hurdle
By Davesoa 2 days ago