Mitsubishi Ecodan controller upgrade - your opinion please?
BACKGROUND
After two years of trial and error with fixed-flow and compensation curve running, I reckon we can keep the flow temperature really low most of the time, and stay warm. Something like flow-temp:
- Nighttime - off or 26degrees (even in deepest winter, having it on at all does make the bedrooms hot, and the COP is really poor so sometimes feels worth switching off till outside temp increases)
- Daytime - 30-40 degrees depending on weather, and activities in the house (cooking heats up; kids opening doors for hours on end cools down)
CURRENT CONTROLS
- I cannot for the life of me get the MelCloud app to do this (change flow temp between night/day) reliably, automatically, so essentially do it myself manually using either the app or the wired controller.
- There are four floors - each one currently has a basic dial-type thermostat - when the set temp is reached, it switches off the circuit to that floor only. They're a bit unreliable, and I've read HeatGeek etc about avoiding having cold bits within a well-insulated home (which this is - 1800s terrace with massive retrofit) - so thinking of swapping them out
PLAN FOR COMMENT
- Now I'm wondering whether to upgrade to: Mistubishi PAR-WT50R-E Remote Controller ( https://library.mitsubishielectric.co.uk/pdf/book/PAR-WT50R-E-PI-Sheet#page-1-2) - one for each floor, which according to the nice man on the helpline today offers up opportunities for auto-adaption mode: http://www.sunergy.ps/data/itemfiles/0a597ef3b3346a2451fbbda7f02ea637.pdf
THOUGHTS
- Well-insulated property that can be kept warm with flow temps of 26-35 degrees - great! Still costing a lot with electric at 38p/unit but ok
- I don't like the current set up - it's too manual
- But I'm not made of money! So no point wasting money on new hardware if it's not going to help
- I want to be able to control the flow temp at night and day separately, and not use the compensation curve which I find an odd thing (happy to be corrected)
- Maybe sticking with mitsubishi instead of going third party will help?
- Maybe this wireless thing is the way forward?
- Is auto-adaption mode going to revolutionise this thing???
Â
Â
The problem with homes is that many of them will insist on being different, so that a 'one size fits all' heating system is not possible.
Correct me if I am wrong, but it sounds like your heat pump is operating in weather compensation mode, but also being controlled by four thermostats. If that is the case then I don't think that your system will be operating at maximum efficiency.
In an ideal World all the thermostats would be set 1C or 2C above the desired temperature, the weather compensation would be adjusted such that the rooms are heated to the desired temperature and correct balancing of the radiators ensures that correct desired temperatures are maintained throughout your home.
Of course we don't live in an ideal World. Bedrooms can be possibly kept cooler by lowering the thermostat or using TRV's. As far as the 'kid's' problem is concerned, have you considered threatening that you will 'sell' one of them to pay the heating bill, if they do not stop leaving the doors open? Obviously don't indicate which one you would 'sell', otherwise the other's may leave the doors open deliberately. 😋Â
Whilst auto adaptation should control the temperature in the room within which the temperature sensor is located, it cannot control the temperature in numerous rooms all at the same time. If the selected temperature sensor is located in the living area, it will not prevent other areas of the home from getting warmer unless the cause is also affecting the living area.
Fine tuning of the weather compensation and correct balancing of the radiators is not a 5 minute job, and could take quite some time to achieve.
Â
Very well said, especially the selling of said-child! Fully agree re difference between all of our homes - it's a challenge! Thanks for your help - here's a few further comments. Looking to learn from anyone who can help on here.
Correct me if I am wrong, but it sounds like your heat pump is operating in weather compensation mode, but also being controlled by four thermostats. If that is the case then I don't think that your system will be operating at maximum efficiency.
I have turned off the weather compensation mode and am controlling the flow temperature manually (using the app); I've also disabled the four thermostats, just leaving them open - i.e it's a fully open system with low flow temp water running round the radiators most of the time
In an ideal World all the thermostats would be set 1C or 2C above the desired temperature, the weather compensation would be adjusted such that the rooms are heated to the desired temperature and correct balancing of the radiators ensures that correct desired temperatures are maintained throughout your home.
Fully agreed - I think, the more I think about it, this is essentially what I'm trying to do in a very manual sort of a way.Â
Whilst auto adaptation should control the temperature in the room within which the temperature sensor is located, it cannot control the temperature in numerous rooms all at the same time. If the selected temperature sensor is located in the living area, it will not prevent other areas of the home from getting warmer unless the cause is also affecting the living area.
Can I check if I've understood this correctly - so if I went ahead with this new mitsubishi controller - there would be four thermostats, one on each of the four floors, but of course only in one room of each of the rooms on that floor - so the ideal is that the temp set on that new controller, say 19 degrees in the living room, would also apply to the next door room which may only be 18 degrees. So there's still a trial and error in finding the correct setting for that floor. BUT - this could possibly be overcome by balancing of radiators between the rooms on a specific floor given enough time and attention?
AND the second part - is that this auto-adaptation would be superior to the current on/off old fashioned thermostat that is in place? Clearly the heat pump won't supply different flow temp to each of the four floors, so I imagine this isn't the case.
Â
Correctly adjusted weather compensation will vary the LWT automatically, rather than your present manual adjustment. Let me explain how weather compensation is designed to operate.
The laws of thermodynamics would indicate that the rate of heat energy loss from your home is primarily determined by the temperature difference between the indoor temperature and the outdoor temperature. To maintain a constant indoor temperature it is therefore necessary to replace this heat energy at the same rate as it is being lost. If the heat energy supplied is insufficient then the indoor temperature will start to fall, but as it does so the temperature difference reduces, which in turn reduces the rate at which heat energy is lost. It is all a balancing act.
Weather compensation measures the outside temperature, and using the weather compensation curve calculates the required LWT necessary to maintain the indoor temperature. The weather compensation curve needs to be adjusted to each individual home, and can take some time to achieve, which is probably why many designers and installers are not in favour of using it.
Even correctly optimised weather compensation may not keep the indoor temperature constant, because there are other factors such as solar gain, wind chill, rain effect and even 'children' that the controller cannot take into account when setting the required LWT.
Mitsubishi developed auto adaptation to help get around some of these problems, though it also has its limitations. A temperature sensor, either hard wired or wireless, is placed in the room where the temperature is to be controlled, which will also help control the temperature in the other rooms in the home.
In your situation having four remote controllers I don't think will allow you to control the individual temperature on each floor, since if my understanding is correct it will only control the temperature in the room with the designated remote controller. The master controller will only accept the temperature reading from one of the four remote controllers, though I do believe that the master controller can accept setpoint changes from each remote controller, but responds to the last instruction.
Even with a remote controller and auto adaptation it would still be necessary to balance your radiators to achieve reasonably constant temperatures throughout your home.
- 22 Forums
- 2,031 Topics
- 44.2 K Posts
- 45 Online
- 3,236 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: help sizing rads based on room by room heat loss
The output of a rad is proportional to DT to the power ...
By JamesPa , 45 minutes ago
-
RE: Agile: average import cost vs other tariffs?
@toodles Thank you for sharing that. I note you have a...
By Old_Scientist , 1 hour ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
@phoenix15 just wondering did you eventually find the o...
By SUNandAIR , 2 hours ago
-
RE: Is this normal? Click of the DHW returning to space heating
@grantmethestrength Oh sorry to hear that, there should...
By ASHP-BOBBA , 4 hours ago
-
@ashp-bobba TBH the ladies are rather disorganised, so ...
By Cathyem1 , 4 hours ago
-
The Rise and Fall of Europe’s Most Generous Green Subsidy
This story came to my attention thanks to Graham Hendra...
By Mars , 4 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
And for those of us without an automatic irrigation sys...
By Majordennisbloodnok , 4 hours ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Thermal Off's
From the Full SAP Report: Space heating requirements:...
By trebor12345 , 4 hours ago
-
Logically, the lower frequency = more gentle, yes, but ...
By SUNandAIR , 8 hours ago
-
I'm just trying to imagine this construction approach @...
By Transparent , 11 hours ago
-
RE: Ideal Logic ASHP - change from 55°C to 35°C Heating?
Good point. I’ll keep my eye on the manifold temperatur...
By Tomdad , 11 hours ago
-
RE: How hard and expensive would it be to change panel and add battery?
@transparent It is a setting that Octopus make via the ...
By Toodles , 11 hours ago
-
RE: Performance of Heat Pumps in Mild Weather
@heatgeek The flow rate isnt controlled by Mitsub...
By RobS , 14 hours ago
-
RE: Say hello and introduce yourself
I might put a couple of speakers in the ceiling if fund...
By Fingers , 1 day ago
-
RE: Bathroom Radiator replacement
@rob-nezard can you please offer your professional advi...
By Mars , 1 day ago
-
-
RE: Questions on my Hitachi Yutaki SCombi Heat Pump
OK, thats good and low. With low flow temperatures lik...
By JamesPa , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@jamespa “They are all equal but, some are more equal t...
By Toodles , 2 days ago
-
RE: Is it KISS or constant – weather compensation vs. set flow temperature?
@cliffhanger Mine has a 'space heating off' setting! O...
By JamesPa , 2 days ago
-
RE: Replacing Worcester oil boiler with an ASHP
Is this something you are thinking of doing? Or has thi...
By Cliff-Arnold , 3 days ago