Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that is set to 23LWT @ 16OAT The ASHP doesn't allow a min LWT of less than 23 but as the OAT starts going above 16c there'll be a point where I'd rather the ASHP just stopped completely rather than producing 23c. I do have room thermostats which are set high to run the system open but I don't really want to use them to shut down the heating room by room as I'll probably end up with the ASHP pushing water through one rad in the last bedroom to turn off. I've hunted through the manual but I can't find a setting which says 'stop heating when OAT reaches a set temp' or similar. Has anyone found one?
Hi @damonc, parameter 2015 is the maximum outdoor air temperature corresponding to minimum outgoing water temperature. Default setting is 20degC, in your case you need this set to 16degC if you don't want heating when the outdoor air temperature is above 16degC. Refer to Grant Aerona 3 installation manual 0136 Rev 2.4 page 36
@allyfish thanks for replying, did you mean 2105? (I can't find a parameter 2015) if so that's already set to 16 but I thought it would just carry on producing 23 LWT above 16 rather than turn off heating completely, my reasoning was at the other end of the curve it doesn't get any hotter when you go past your lowest OAT just plateaus there but I guess that assumption doesn't make a lot of sense or it would still be producing 23 LWT right through summer so I think my settings are ok, will see when it gets warmer but I think the pump may continue circulating as I'm sure I was above 16 last week and it didn't cut out .
Sorry, yes, 2105. OOPS! If I recall the unit circulates water if the heating is scheduled to be on, but simply doesn't heat the circulating water if the ambient temperature is >2105 parameter setting.
- 26 Forums
- 2,129 Topics
- 46.8 K Posts
- 23 Online
- 5,654 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Who has a V2G EV installation
General comment on battery care... I guess if ev is on ...
By Tim441 , 41 minutes ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@old_scientist I have never cleaned the mag filter myse...
By Toodles , 52 minutes ago
-
@old_scientist like for like comparisons are almost imp...
By Tim441 , 55 minutes ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist There is an option in the Tesla app that...
By Toodles , 1 hour ago
-
RE: Mitsu Wireless Controller and MelCloud
On the FTC5 I think this requires the dip switch on the...
By Abernyte , 1 hour ago
-
RE: ASHP heat output monitoring
@carlo I have a 16kw LG Therma V. Installed 2020 so eve...
By Tim441 , 4 hours ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
@old_scientist me too. Just installed my new heat pump ...
By Eliuccio , 2 days ago
-
RE: Is your heat pump insured?
Yup just spoke to Privilege to inform them of my impend...
By Scalextrix , 2 days ago
-
RE: Forum updates, announcements & issues
Just to keep everyone in the loop, as the site continue...
By Mars , 2 days ago
-
RE: Fast DHW setting on Midea (Clivet) heat pump
@simon-w, is this something you could potentially assis...
By Mars , 3 days ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
Fwiw I called my installer out for the first time a few...
By JamesPa , 3 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@sandy, I'll send Vaillant an email tomorrow and see if...
By Mars , 3 days ago
-
RE: Long term efficiency degradation
@jamespa yes as I thought thanks. We have a reaso...
By Scalextrix , 3 days ago
-
RE: Sunamp Thermino Heat Battery
@jamespa A few days after the installation had been com...
By Toodles , 4 days ago
-
RE: Planning Permission May 2025
Fair enough. I have read the legislation and MCS020a ...
By JamesPa , 6 days ago
-
RE: How do I choose a single room MVHR to prevent losing heat in my bathroom ?
An update on the Heatsava. It is the most difficult thi...
By heat-pump-newbie , 6 days ago
-
RE: Renewables & Heat Pumps in the News
this document extensively describes (in a non-blame, ne...
By Judith , 1 week ago
-
RE: Ecodan - Legionella Operation Time and Target Temperature
Once the white plastic cap is removed, my immersion loo...
By Old_Scientist , 1 week ago
-
RE: Replacing Refrigerant on Mitsubishi Heat Pump
@dgclimatecontrol I don't know, but they were not happy...
By DavidAlgarve , 1 week ago
-
RE: Why do we need pressurised systems?
A good question @toodles. My old open thermal store and...
By AllyFish , 1 week ago