Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that is set to 23LWT @ 16OAT The ASHP doesn't allow a min LWT of less than 23 but as the OAT starts going above 16c there'll be a point where I'd rather the ASHP just stopped completely rather than producing 23c. I do have room thermostats which are set high to run the system open but I don't really want to use them to shut down the heating room by room as I'll probably end up with the ASHP pushing water through one rad in the last bedroom to turn off. I've hunted through the manual but I can't find a setting which says 'stop heating when OAT reaches a set temp' or similar. Has anyone found one?
Hi @damonc, parameter 2015 is the maximum outdoor air temperature corresponding to minimum outgoing water temperature. Default setting is 20degC, in your case you need this set to 16degC if you don't want heating when the outdoor air temperature is above 16degC. Refer to Grant Aerona 3 installation manual 0136 Rev 2.4 page 36
@allyfish thanks for replying, did you mean 2105? (I can't find a parameter 2015) if so that's already set to 16 but I thought it would just carry on producing 23 LWT above 16 rather than turn off heating completely, my reasoning was at the other end of the curve it doesn't get any hotter when you go past your lowest OAT just plateaus there but I guess that assumption doesn't make a lot of sense or it would still be producing 23 LWT right through summer so I think my settings are ok, will see when it gets warmer but I think the pump may continue circulating as I'm sure I was above 16 last week and it didn't cut out .
Sorry, yes, 2105. OOPS! If I recall the unit circulates water if the heating is scheduled to be on, but simply doesn't heat the circulating water if the ambient temperature is >2105 parameter setting.
- 27 Forums
- 2,781 Topics
- 65.6 K Posts
- 2,320 Online
- 7,187 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Tesla Powerwall (2) Calibration Cycles
@old_scientist You mean you didn’t know about that secr...
By Toodles , 4 hours ago
-
RE: Replacing Storage Heaters with a Heat Pump in a Stone Cottage
That sounds like a better approach (being able to see a...
By cathodeRay , 4 hours ago
-
RE: DIY Heat Pump Installations: Navigating Legal and Regulatory Hurdles
Thanks for the reference @jamespa I can't see any te...
By Transparent , 5 hours ago
-
RE: battery storage without solar
Indeed, current on the grid input = current used for ch...
By bobflux , 6 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@papahuhu @papahuhu A lot of tears and sweat went into ...
By Andris , 9 hours ago
-
RE: Getting closer to a finished Haier system
Very nice! Congratulations. Big MLC looks neat whe...
By bobflux , 14 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
We have the same problem, 12 mature trees clip the morn...
By Papahuhu , 1 day ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
I had a battery and inverter installed a while ago, my ...
By Batpred , 1 day ago
-
RE: Is This Initial Free Quote From Octopus Trusted Partner Reasonable?
@ltron2 The EPC on our house is A-92, however that i...
By Rob of York , 1 day ago
-
RE: Heat pump branding. Clever, contemporary… or a bit too much?
The layout is confusing - much better like this: We b...
By downfield , 2 days ago
-
RE: Is it just me, or does tradesperson timekeeping and communication drive you absolutely mad?
My experience, backed up by opinions from various frien...
By Majordennisbloodnok , 2 days ago
-
RE: Analysis of the economics of switching to an A2W ASHP compared to other heat sources
I had a meeting today with a company based out of Swede...
By Mars , 3 days ago
-
RE: Review your electricity provider
We were with Octopus in our old house and it was fault...
By ian33a , 3 days ago
-
RE: Estimating true heat loss from twelve months of consumption data
I did, indeed, go with the 12 KW Vaillant unit.  ...
By ian33a , 3 days ago