Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that is set to 23LWT @ 16OAT The ASHP doesn't allow a min LWT of less than 23 but as the OAT starts going above 16c there'll be a point where I'd rather the ASHP just stopped completely rather than producing 23c. I do have room thermostats which are set high to run the system open but I don't really want to use them to shut down the heating room by room as I'll probably end up with the ASHP pushing water through one rad in the last bedroom to turn off. I've hunted through the manual but I can't find a setting which says 'stop heating when OAT reaches a set temp' or similar. Has anyone found one?
Hi @damonc, parameter 2015 is the maximum outdoor air temperature corresponding to minimum outgoing water temperature. Default setting is 20degC, in your case you need this set to 16degC if you don't want heating when the outdoor air temperature is above 16degC. Refer to Grant Aerona 3 installation manual 0136 Rev 2.4 page 36
@allyfish thanks for replying, did you mean 2105? (I can't find a parameter 2015) if so that's already set to 16 but I thought it would just carry on producing 23 LWT above 16 rather than turn off heating completely, my reasoning was at the other end of the curve it doesn't get any hotter when you go past your lowest OAT just plateaus there but I guess that assumption doesn't make a lot of sense or it would still be producing 23 LWT right through summer so I think my settings are ok, will see when it gets warmer but I think the pump may continue circulating as I'm sure I was above 16 last week and it didn't cut out .
Sorry, yes, 2105. OOPS! If I recall the unit circulates water if the heating is scheduled to be on, but simply doesn't heat the circulating water if the ambient temperature is >2105 parameter setting.
- 26 Forums
- 2,171 Topics
- 47.8 K Posts
- 28 Online
- 5,744 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Mitsu PAR-WT60R Wireless Controller - options
I have been running mine in auto adapt since 2019 and i...
By Abernyte , 20 minutes ago
-
RE: Powerwall 3 or Myenergi or something else?
Many of those tariffs are simple time of use tariffs, w...
By Temperature_Gradient , 11 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
Yes thats the whole point of the flexis as regards tran...
By JamesPa , 11 hours ago
-
So far as I can tell designing for DT5, which is 'the n...
By JamesPa , 11 hours ago
-
WC curve best discovered by experiment anyway as any lo...
By JamesPa , 18 hours ago
-
RE: Big Changes Coming to Our Heat Pump System
@editor your engineer's attitude is truly horrifying. ...
By GrahamF , 1 day ago
-
RE: How to choose Towel Rails for an ASHP
@rob-nezard yes absolutely. Here is the link and a pho...
By GrahamF , 2 days ago
-
@mixergy Thanks for the update, I would appreciate some...
By bontwoody , 2 days ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
Unfortunately I'm not that well connected 😂 ...
By Scalextrix , 2 days ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
It is interesting to see what our new Grant Aerona 290 ...
By GrahamF , 2 days ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
I've never physically seen it, but I seem to recall som...
By cathodeRay , 2 days ago
-
RE: Midea ASHP – how to set weather compensation
I noticed that too and thought the same thing, but then...
By cathodeRay , 3 days ago
-
RE: Ya can’t win! It is S*d’s Law!
@old_scientist If IOF is still running next late spring...
By Toodles , 3 days ago
-
RE: Electricity price predictions
Those of you on Agile will do well tomorrow; there are ...
By Toodles , 3 days ago
-
RE: Who’s Caved and Switched the Heating On Already?
We've been running our Ecodan system, installed in June...
By Sheriff Fatman , 3 days ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 3 days ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 4 days ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 4 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 5 days ago